DC input
The input can be powered from batteries or similar DC sources and must be a PELV or SELV source or an "Isolated Secondary Circuit" in order to maintain a SELV or PELV output.
DC input
DC input
Nom.
DC 24V
-25%/+46%
DC input range
18.0-35.0Vdc
Allowed voltage between input and earth/ground
Max.
60Vdc or
42.2Vac
according to IEC 62477-1
Allowed input ripple voltage
Max.
5Vpp
In the frequency range from 47 to 500Hz, the momentary input voltage must always be within the specified limits.
Turn-on voltage
Typ.
17.5Vdc
Steady-state value, see Fig. “Input voltage range”
Shut-down voltage
Typ.
15.5Vdc
Input current
Typ.
10.5A
At 24Vdc input and 24V, 10A output load , see Fig. “Input current vs. output load”
14.3A
At 18Vdc input and 24V, 10A output load , see Fig. “Input current vs. output load”
Start-up delay
Typ.
150ms
See Fig. “Input voltage range”
Rise time
Typ.
110ms
At 24V, 10A constant current load, 0mF load capacitance, see Fig. “Turn-on behavior, definitions”
250ms
At 24V, 10A constant current load, 10mF load capacitance, see Fig. “Turn-on behavior, definitions”
Turn-on overshoot
Max.
250mV
See Fig. “Turn-on behavior, definitions”
Input capacitance
Typ.
4 300µF
Installed inside the device, external capacitors on the input are allowed without any limitations.
External input protection
Non-user replaceable slow blow, high breaking capacity fuse.
See chapter “Further notes on installation requirements”
DC input 1:
Input voltage range, Turn-on behavior, definitions
DC input 2:
Requirements for the Supplying Source
In certain circumstances, the input filter of the DC/DC converter can show a resonant effect which is caused by the supplying network. Especially when additional external input filters are utilized, a superimposed AC voltage can be generated on the input terminals of the DC/DC converter which might cause a malfunction of the unit. Therefore, additional input filters are not recommended. To avoid the resonant effects, the minimal resistance of the supplying network which depends on the inductance of the input network, shall be above the boundary curve in Fig. “External input filter requirements to avoid filter instabilities”.
DC input 3: