Safety instructions and installation requirements for PS9711-2410-0000
Safety instructions and installation requirements for PS9711-2410-0000 power supply
DANGER
Danger of electric shock, fire, injuries, injuries resulting in death!
  • Turn power off before working on the device. Protect against inadvertent re-powering.
  • Do not modify or repair the device.
  • Do not open the device, as high voltages are present inside.
  • Use caution to prevent any foreign objects from entering the housing.
  • Do not use in wet locations or in areas where moisture or condensation can be expected.
  • Do not touch the components during and immediately after operation. Hot surfaces may cause burns.
Safety instructions and installation requirements for PS9711-2410-0000 1:
Further notes on installation requirements
  • This device may only be installed and put into operation by qualified personnel.
  • If damage or malfunction should occur during installation or operation, immediately turn power off and send the device to the factory for inspection.
  • Install the device onto a DIN rail according to EN 60715 with the input terminals on the bottom of the device. Other mounting orientations require a reduction in output current.
  • Install device in an enclosure providing protection against electrical, mechanical and fire hazards.
  • Ensure that the wiring is correct by following all local and national regulations.
  • Use appropriate copper cables that are designed for a minimum operating temperature of
    70 °C for ambient temperatures up to +45 °C,
    75 °C for ambient temperatures up to +60 °C and
    90 °C for ambient temperatures up to +70 °C.
  • Ensure that all strands of a stranded wire enter the terminal connection.
  • Unused screw terminals should be securely tightened.
  • The maximum surrounding air temperature is +70 °C. The operational temperature is the same as the ambient or surrounding air temperature and is defined 2 cm below the device.
  • The device is designed for convection cooling and does not require an external fan. Do not obstruct airflow and do not cover ventilation grid!
  • Observe the following minimum mounting distances:
  • 40 mm at the top, 20 mm at the bottom and 5 mm on the left and right if the device is continuously loaded with more than 50% of its rated power
  • Increase the distance from 5 mm to 15 mm if the adjacent device is a heat source (e.g., another power supply).
  • When the device is permanently loaded with less than 50%, the 5 mm can be reduced to zero.
  • The device is designed, tested and approved for branch circuits up to 50 A without additional protection device. If an external fuse is utilized, a circuit breaker with a minimum value of 20 A with a B or C characteristic should be implemented to avoid unwanted tripping of the circuit breaker.
  • The input can also be supplied by batteries or similar DC sources. The voltage between the input terminals and ground must not exceed 60 Vdc continuously.
  • The input must be powered from a PELV or SELV source or an “Isolated Secondary Circuit” in order to maintain a SELV or PELV output. If the input is supplied via the output of a power supply, the supply voltage of this power supply must not exceed 300/520 V, overvoltage category (OVC) II.
  • The insulation of the devices is designed such that it can withstand pulse voltages up to 1.5 kV in accordance with IEC 60664-1. This enables supply from upstream power supplies connected to a supply network of overvoltage category II and voltages of up to 300 Vac (L to N) or 520 Vac (L to L), for example.
  • Check for correct input polarity. The device does not work if the voltage polarity is reversed.
  • A disconnecting means shall be provided for the input of the device.
  • The device is designed as “Protection Class III” equipment according to IEC 61140.
  • Do not use without a proper PE (Protective Earth) connection.
Safety instructions and installation requirements for PS9711-2410-0000 2:
Further notes on operation
  • This device does not contain serviceable parts. The tripping of an internal fuse is caused by an internal defect.
  • The device is designed for areas with a pollution degree 2 in controlled environments. No condensation or frost allowed.
  • The device housing has an IP20 protection rating. The housing does not provide protection against spilled liquids.
  • The device is designed to operate in areas between 5 % and 95 % relative humidity.
  • The device is designed for altitudes up to 5000 m. See additional requirements in this document for use above 2000 m.