AC input
AC input
AC input
Nom.
AC 200 - 240 V
Suitable for TN, TT and IT networks
AC input range
Min.
180 - 264 Vac
Continuous operation
Min.
264 - 300 Vac
For up to 500 ms max.
Permissible voltage L or N to earth
Max.
300 Vac
Continuous according to IEC 60664-1
Input frequency
Nom.
50 - 60 Hz
±6 %
Turn-on voltage
Typ.
150 Vac
Static, see Fig. Input voltage range; switch-on behavior definitions
Shut-down voltage
Typ.
130 Vac
External input protection
see recommendations in chapter "Further notes on installation requirements"
Input current
Typ.
2.2 A
At 24 V, 20 A, 230 Vac, see fig. Input to output current; power factor to output current
Power factor*)
Typ.
0.99
Peak factor**)
Typ.
1.6
Start-up delay
Typ.
170 ms
See Fig. Input voltage range; switch-on behavior definitions
Rise time
Typ.
60 ms
At 24 V, 20 A constant current load, 0 mF load capacity, see Fig. Input voltage range; switch-on behavior definitions
Typ.
240 ms
At 24 V, 20 A constant current load, 20 mF load capacity, see Fig. Input voltage range; switch-on behavior definitions
Turn-on overshoot
Max.
200 mV
Ohmic load, See fig. Input voltage range; switch-on behavior definitions
*) The power factor is the ratio of real (or active) power to apparent power in an AC circuit.
**) The peak factor is the mathematical ratio of the peak value to the RMS value of the input current waveform.
AC input 1:Fig.1: Input voltage range; switch-on behavior definitions
AC input 2:Fig.2: Input current over output current; power factor over output current