Safety instructions
Description of instructions
In this documentation the following instructions are used.
These instructions must be read carefully and followed without fail!
DANGER
Serious risk of injury!
Failure to follow this safety instruction directly endangers the life and health of persons.
WARNING
Risk of injury!
Failure to follow this safety instruction endangers the life and health of persons.
CAUTION
Personal injuries!
Failure to follow this safety instruction can lead to injuries to persons.
Notice
Damage to environment/equipment or data loss
Failure to follow this instruction can lead to environmental damage, equipment damage or data loss.
Safety instructions 1:
Tip or pointer
This symbol indicates information that contributes to better understanding.
Intended use
This device is designed for installation in a housing and is intended for general professional use, for example in industrial control systems or office, communication and measuring equipment.
Do not use this power supply in installations where a malfunction could cause serious injury or danger to human life.
Exclusion of liability
All the components are supplied in particular hardware and software configurations appropriate for the application. Modifications to hardware or software configurations other than those described in the documentation are not permitted, and nullify the liability of Beckhoff Automation GmbH & Co. KG.
Personnel qualification
This description is only intended for trained specialists in control, automation and drive engineering who are familiar with the applicable national standards.
Safety regulations
Please note the following safety instructions and explanations!
Product-specific safety instructions can be found on following pages or in the areas mounting, wiring, commissioning etc.
Safety instructions and installation requirements for the PS1061-2420-0000 power supply
DANGER
Danger of electric shock, fire, injuries, injuries resulting in death!
  • Do not use the power supply without proper grounding (protective conductor). Use the terminal at the input terminal strip for the earth connection, not one of the screws on the housing.
  • Switch off the power supply before working on the device. Provide protection against unintentional reconnection.
  • Ensure proper wiring by following all local and national regulations.
  • Do not modify or attempt to repair the device.
  • Do not open the device, as high voltages are present inside.
  • Avoid foreign bodies entering the housing.
  • Do not use the device in damp locations or in areas where moisture or condensation is likely to occur.
  • Do not touch the device when it is switched on or immediately after it has been switched off. Hot surfaces can cause burns.
  • If this device is operated outside of the specification, the protection offered by the device may be negatively affected
Safety instructions 2:
Further notes on installation requirements
  • If any damage or malfunction occurs during installation or operation, turn off the power supply immediately and return the device to the factory for inspection.
  • Mount the device on a DIN rail so that the input terminals are at the bottom of the device.
  • Install the device in a housing that provides protection against electrical, mechanical and fire hazards.
  • Make sure that the wiring is correct by complying with all local and national regulations.
  • Use suitable copper cables designed for a minimum operating temperature of
    60 °C at ambient temperatures up to +45 °C,
    75 °C at ambient temperatures up to +55 °C and
    90 °C at ambient temperatures up to +70 °C.
  • Make sure that all individual strands of a wire are inside the terminal connection.
  • Unused screw terminals should be tightened firmly.
  • The maximum temperature of the ambient air is +70 °C. The operating temperature corresponds to the ambient air temperature and is defined 2 cm below the device.
  • This device is designed for convection cooling and does not require an external fan. Do not obstruct the air circulation. The ventilation grille must not be covered (e.g. by cable ducts)!
  • Maintain the following installation distances:
  • 40 mm at the top, 20 mm at the bottom and 5 mm on the left and right are recommended if the device continuously runs at more than 50 % of the rated output.
  • Increase this distance to 15 mm if the adjacent device is a heat source (e.g., another power supply).
  • The distance can be reduced from 5 mm to zero if the device is permanently loaded with less than 50 %.
  • The device is designed, tested and approved for branch circuits up to 20 A without an additional protective device.
    Use an additional protective device for branch circuits with larger current values. If an external input protection device is used, do not use one smaller than a 10 A B or 6 A C characteristic in order to avoid incorrect triggering of the circuit breaker.
  • The device is designed as equipment of "Protection Class I" according to IEC 61140.
  • Do not use the device without a proper PE (Protective Earth) connection!
Safety instructions 3:
Further notes on operation
  • This device contains no parts that require maintenance. If an internal fuse trips, this is due to an internal defect.
  • The device is designed for areas with a degree of pollution 2 in controlled environments. No condensation or frost is allowed.
  • The device housing offers IP20 protection. The housing offers no protection against spilled liquids.
  • The device is designed for operation in the relative humidity range between 5 % and 95 %.
  • The device is designed for overvoltage category II zones. Below an altitude of 2000 m the device is tested for surge voltages up to 4 kV, which corresponds to the OVC III according to IEC 60664-1.
  • The device is suitable for supply from TN, TT or IT networks. The continuous voltage between the input terminal and the PE potential must not exceed 300 Vac.
  • The device is designed for altitudes up to 5000 m. A reduction of the output current is required above 2000 m.