Protective functions and safety features
Protective functions and safety features  | ||
Insulation resistance  | Min. 500MOhm  | In the delivery state between input and output, measured with 500Vdc  |
Min. 500MOhm  | In the delivery state between input and PE, measured with 500Vdc  | |
Min. 500MOhm  | In the delivery state between output and PE, measured with 500Vdc  | |
Min. 500MOhm  | In the delivery state between output and DC OK contacts, measured with 500Vdc  | |
PE resistance  | Max. 0.1 ohm  | Resistance between PE terminal and housing in the area of the DIN rail mounting bracket.  |
Output overvoltage protection  | Typ. 30.5Vdc   | In the event of an internal power supply fault, a redundant circuit limits the maximum output voltage. The output switches off and automatically tries to switch on again.  |
Protection class  | I  | According to EN/IEC 61140  |
Protection class  | IP 20  | According to EN/IEC 60529  |
Overtemperature protection  | yes  | Output shutdown with automatic restart.  |
Protection against input transients  | MOV (metal oxide varistor)  | For further information see EMC chapter  |
Input fuse  | included  | Non-replaceable slow-blow fuse with high load capacity  |
Leakage current  | Typ. 0.12mA / 0.30mA  | At 100Vac, 50Hz, TN, TT / IT network  |
Typ. 0.17mA / 0.45mA  | At 120Vac, 60Hz, TN, TT / IT network  | |
Typ. 0.27mA / 0.71mA  | At 230Vac, 50Hz, TN, TT / IT network  | |
Max. 0.15mA / 0.38mA  | At 110Vac, 50Hz, TN, TT / IT network  | |
Max. 0.21mA / 0.56mA  | At 132Vac, 60Hz, TN, TT / IT network  | |
Max. 0.35mA / 0.91mA  | At 264Vac, 50Hz, TN, TT / IT network  | |