Variables
The intelligence in the DALI system is not 100% centralized. This means that a large number of settings and light values are stored in the form of variables in the ballasts.
Click on Variables. A dialog mask in which you can inspect and edit the variables for the selected DALI device appears.
Variables 1:Fig.21: KS2000 - parameterization of the DALI/DSI devices - variables
Actual dim level
This variable contains the power currently applying to the lamp.
Power ON level
This variable specifies the lamp power that the DALI device is to adopt after the power supply has been switched on, if the DALI bus is already under power and is idle.
System failure level
This variable specifies the lamp power that the DALI device is to adopt in the event of a system error.
MIN level
You specify the minimum lamp power that the DALI device is to adopt here, so that the illuminance does not fall below a level that you want. The MIN value cannot be less than the smallest physically possible value specified by the manufacturer of the DALI device.
MAX level
You specify the maximum lamp power that the DALI device is to adopt here, so that the illuminance does not exceed a level that you want.
Fade rate
Enter the velocity in steps per second (step/s), with which the DALI device dims for 200 ms when the commands Brighter (DALI command 1dec) or Darker (DALI command 2dec) are issued. The absolute fade rate is not entered directly, but it is calculated according to the following formula:
Variables 2:
T = absolute fade rate
n = value that is stored in the Fade rate variable
The following values result:
n
absolute fade rate
0
Not permitted
1
357.796 steps/s
2
253.000 steps/s
3
178.898 steps/s
4
126.500 steps/s
5
89.449 steps/s
6
63.250 steps/s
7
44.725 steps/s
8
31.625 steps/s
9
22.362 steps/s
10
15.813 steps/s
11
11.181 steps/s
12
7.906 steps/s
13
5.591 steps/s
14
3.953 steps/s
15
2.795 steps/s
Fade time
Enter here the time in seconds that the DALI device is to take to change the brightness when, for instance, changing a scene, or to execute direct DALI commands for lamp power. This time is independent of the size of the change, so that all the lamps complete their change over the same period. In the case of a lamp that is switched off, the pre-heating and ignition time is not included in the fade time.
The absolute fade time is not entered directly, but it is calculated according to the following formula:
Variables 3:
T = absolute fade time
n = value that is stored in the Fade time variable
n
absolute fade time
0
< 0.707 s
1
0.707 s
2
1.000 s
3
1.414 s
4
2.000 s
5
2.828 s
6
4.000 s
7
5.657 s
8
8.000 s
9
11.314 s
10
16.000 s
11
22.627 s
12
32.000 s
13
45.255 s
14
64.000 s
15
90.510 s
Direct address
This variable contains the DALI device's short address. A valid short address lies in the range between 0dec and 63dec. If 255dec is written into the variable, the short address is deleted.
Status information
This variable can only be read. It contains the DALI device's status byte. The bits in the status byte have the following significance:
Bit
Meaning
7
Power supply fault
0bin
No
6
Missing short address
0bin
No
5
Reset status
0bin
No
4
Fading done
0bin
Fading has been completed
1bin
Fading in progress
3
Limit value error
0bin
The most recently requested lamp power value was between the MIN and MAX values, or was OFF.
2
Lamp power
0bin
OFF
1bin
ON
1
Lamp failure
0bin
OK
0
Status of the DALI device
0bin
OK
Version number
Displays the DALI device's version number. This variable is entered by the device manufacturer, and can only be read!
Physical minimum level
Indicates the lowest physically possible lamp power that the DALI device can adopt. This variable is entered by the device manufacturer, and can only be read!