Register description
The registers can be read or written via the register communication. They are used for the parameterization of the terminal.
General description of registers
Complex terminals that possess a processor are able to exchange data bi-directionally with the higher-level controller. These terminals are referred to below as intelligent Bus Terminals. These include the analog inputs (0 to 10 V, -10 to 10 V, 0 to 20 mA, 4 to 20 mA), the analog outputs (0 to 10 V, -10 to 10 V, 0 to 20 mA, 4 to 20 mA), serial interface terminals (RS485, RS232, TTY, data exchange terminals), counter terminals, encoder interfaces, SSI interfaces, PWM terminals and all other parameterizable modules.
The main features of the internal data structure are the same for all the intelligent terminals. This data area is organized as words, and includes 64 memory locations. The important data and parameters of the terminal can be read and set through this structure. It is also possible for functions to be called by means of corresponding parameters. Each logical channel in an intelligent terminal has such a structure (so a 4-channel analog terminal has 4 sets of registers).
This structure is divided into the following areas:
Range
Register number
Process variables
0 to 7
Type register
8 to 15
Manufacturer parameters
16 to 30
User parameters
31 to 47
Extended user area
48 to 63
R0 to R7: Registers in the internal RAM of the terminal
The process variables can be used in addition to the actual process image. Their function is specific to the terminal.
Bit no.
Meaning
Bit 0
1
The receive buffer has overflowed, incoming data is lost.
Bit 1
1
A parity error has occurred.
Bit 2
1
A framing error has occurred.
Bit 3
1
An overrun error has occurred.
Bit 4
1
Buffer is full
Bit 5 - 15
not used – do not change!
R8 to R15: Registers in the internal ROM of the terminal
The type and system parameters are hard programmed by the manufacturer, and the user can read them but cannot change them.
Data type register
Meaning
0x00
Terminal with no valid data type
0x01
Byte array
0x02
Structure 1 byte n bytes
0x03
Word array
0x04
Structure 1 byte n words
0x05
Double word array
0x06
Structure 1 byte n double words
0x07
Structure 1 byte 1 double word
0x08
0x11
Byte array with variable logical channel length
0x12
Structure 1 byte n bytes with variable logical channel length (e.g. 60xx)
0x13
Word array with variable logical channel length
0x14
Structure 1 byte n words with variable logical channel length
0x15
Double word array with variable logical channel length
0x16
Structure 1 byte n double words with variable logical channel length
R16 to R30: Manufacturer parameter area (SEEROM)
The manufacturer parameters are specific for each type of terminal. They are programmed by the manufacturer, but can also be modified by the controller. The manufacturer parameters are stored in a serial EEPROM in the terminal, and are retained in the event of voltage drop-out.
These registers can only be altered after a code word has been set in R31.
R31 to R47: User parameter area (SEEROM)
The user parameters are specific for each type of terminal. They can be modified by the programmer. The user parameters are stored in a serial EEPROM in the terminal, and are retained in the event of voltage drop-out. The user area is write-protected by a code word.
Register description 1:
• R31: Code word register in RAM
The code word 0x1235 must be entered here so that parameters in the user area can be modified. If any other value is entered into this register, the write-protection is active. When write protection is not active, the code word is returned when the register is read. If the write protection is active, the register contains a zero value.
Bit no.
Baud rate
Bit 2, Bit 1, Bit 0
011
1200 baud
100
2400 baud
101
4800 baud
110
9600 baud [110]
111
19200 baud
Bit 3 - 15
Furthermore, the baud rate can be set according to the following equation:
Baud rate = 4 MHz/(16*(HB+1))
It is necessary for 0xFF to be written into the low byte here, while the high byte (HB) provides the operator.
Bit no.
Baud rate
Bit 2, Bit 1, Bit 0
0 0 1
7 data bits, even parity
0 1 0
7 data bits, odd parity
0 1 1
8 data bits, no parity [0 1 1]
1 0 0
8 data bits, even parity
1 0 1
8 data bits, odd parity
Bit 3
0/1
0: 1 stop bit [0]
1: 2 stop bits
Bit 4 - 15
Feature bit no.
Description of the operation mode
Bit 0
0/1
1 half duplex: Reception of data sent by the terminal is suppressed.
0 full duplex: Data transmission is monitored in RS485 mode. [0]
Bit 1
0/1
0: Standard output format
1: Alternative output format [1]
Bit 2
1
The status byte is copied from the terminal into the shift registers of the K-bus one cycle later than the higher data bytes. This reduces the rate of data transmission to the controller. [0]
Bit 3
1
The XON/XOFF protocol is supported by the terminal when data is sent, i.e. the terminal sends the data transferred by the controller until it receives the XOFF character (DC3==0x13) from the partner device. Once this has occurred, transmission is halted until the XON character (DC1==0x11) is received. [0]
Bit 4
1
The XON/XOFF protocol is supported by the terminal when data is received. The terminal sends the control character XOFF when the terminal buffer contains 118 characters. XON is sent if XOFF was sent previously and the value falls below the lower buffer limit of 18 bytes. [0]
Bit 5
0/1
0: The terminal is used in a bus structure according to the RS485 standard. [0]
1: The terminal is used as a point-to-point connection (RS422), which means that the controller no longer switches the data line to high impedance.
Bit 6
1
Continuous sending of data from the FIFO. The send buffer is filled (up to 16 bytes) by the controller. The filled buffer content is transmitted with a rising edge in Control Byte 3. The terminal acknowledges the data transfer to the controller by setting the Status Byte 2 bit. Status Byte 2 is reset with Control Byte 3.
Bit 7-15
Register description 2:
Note on bit 6
This feature is available for all terminals with software version 3x or higher. The version information can be found on the right-hand side of the terminal in the serial number: xxxx3xxx
Example: 52983A2A = software version 3A