Register description
The registers are used for the parameterization of the Bus Terminals and are available for each channel. They can be read or written by means of register communication.
R0: Raw ADC value
Register R0 contains the raw value of the analog/digital converter. This is the unchanged analog value prior to any scaling.
R1: Calibration value - offset
After a calibration, the offset value that was determined is entered in register R1 and used for the correction calculation.
R2: Calibration value - gain
After a calibration, the gain value that was determined is entered in register R2 and used for the correction calculation.
R6: Diagnostic register
Status byte SB1 is placed into register R6.
R7: Command register
Register description 1:
User code word
For the following commands to be executed, it is first necessary for the user code word, 0x1235, to be entered into register R31.
Command 0x7000: Restore Factory Settings
Entering 0x7000 in register R7 restores the factory settings for the following registers of both channels:
KL3162, KL3172, KL3142, KL3152:
R32: 0x0180 (384dec)
R33: 0x0000 (0dec)
R34: 0x0100 (256dec)
R35: 0x0000 (0dec)
R36: 0x0000 (0dec)
R37: 0x35C0 (13760dec)
R40: 0x0708 (1800dec)
R44: 0x0003 (3dec)
R47: 0x0032 (50dec)
R48: 0x0005 (5dec)
KL3132, KL3182:
R32: 0x0182 (386dec)
R33: 0x0000 (0dec)
R35: 0x0000 (0dec)
R36: 0x0000 (0dec)
R44: 0x0003 (3dec)
R47: 0x0032 (50dec)
R48: 0x0005 (5dec)
Register description 2:
The Restore Factory Settings command simultaneously resets both terminal channels to the delivery state, irrespective from which register it is called.
R8: Terminal description
The description of the terminal is contained in register R8.
KL3172: 0x0C64 (3172dec)
KL3182: 0x0C6E (3182dec)
KL3132: 0xC3C (3132dec)
KL3162: 0xC5A (3162dec)
KL3142: 0xC46 (3142dec)
KL3152: 0xC50 (3152dec)
R9: Firmware version
Register R9 contains the ASCII coding of the terminal's firmware version, e.g. 0x3141 = '1A'. The '0x31' corresponds here to the ASCII character '1', while the '0x41' represents the ASCII character 'A'.
This value can not be changed.
R12: Minimum data length of a channel
Bits 0 to 6 of the high-order byte specify the minimum number of output data in bits: 000.0000bin = 0dec, so 0 bytes.
Bits 0 to 6 of the low-order byte specify the minimum number of input data in bits: 001.1000bin = 24dec, hence 3 bytes.
The fact that bit 7 is set indicates that the control and status byte are not mandatory for the terminal function and are not transferred in compact mode.
R16: Hardware version number
Register R16 contains the hardware version of the terminal.
R17: Vendor calibration - offset
This register contains the vendor calibration offset (16 bit signed integer).
R18: Vendor calibration - gain
This register contains the vendor calibration gain (16 bit unsigned integer x 2-16 + 1). Examples:
0x0000 means factor 1
0xFFFF means factor 2
R19: Manufacturer scaling - offset:
This register contains the offset of the manufacturer scaling. Can be activated via R32.1 in the feature register (16 bit signed integer).
R20: Manufacturer scaling - gain:
This register contains the gain of the manufacturer scaling. Can be activated via R32.1 in the feature register (16 bit unsigned integer x 2-8 + 1). Examples:
0x0100 means factor 1.
0x0080 means factor 0.5
R21: Upper measuring range limit
This register contains the upper measuring range limit. It can be activated by R32.8 in the feature register.
R22: Lower measuring range limit
This register contains the lower measuring range limit. It can be activated by R32.8 in the feature register.
R23: Reference calibration value: Offset
This register contains the reference value of the calibration, which is determined during the vendor calibration.
R24: Reference calibration value: Gain
R31: Code word register
The code word is reset if the terminal is restarted.
R32: Feature register
The feature register specifies the terminal's configuration.
Bit
R32.15
R32.14
R32.13
R32.12
R32.11
R32.10
R32.9
R32.8
Callibration
Display
Display StabilityError
disChannel
enTh2
enTh1
enOverProt
Bit
R32.7
R32.6
R32.5
R32.4
R32.3
R32.2
R32.1
R32.0
enStable
disDiff
Measure
disCali
enSiemensFormat
enAverageFormat
disWd
Timer
enManScal
enUsrScal
Key
Bit
default
R32.15*
CallibrationDisplay
0bin
During the calibration, the terminal sets the overload bit SB1.1 and the underload bit SB1.0.
0bin
1bin
 Compatibility mode: During calibration, the terminal sets the error bit SB1.6.
R32.14*
0bin
Stability error is not displayed.
0bin
1bin
If no stabilization of the calibration values is achieved, the terminal indicates this by setting the error bit SB1.6. (see note below)
Register description 3:
Fluctuating measuring signals
Strongly fluctuating measuring signals can make stabilization of the calibration values impossible. In this case, skip the stabilization and disable it with bit R32.7.
Bit
default
R32.13
reserved
0bin
R32.12
reserved
0bin
R32.11
disChannel
0bin
Channel switched on
0bin
1bin
Channel switched off
R32.10
enTh2
0bin
Limit value 2 is not active
0bin
1bin
Limit value 2 is active
R32.9
enTh1
0bin
Limit value 1 is not active
0bin
1bin
Limit value 1 is active
R32.8
enOverProt
0bin
Measuring range limitation not active
1bin
1bin
Measuring range limitation active
R32.7
enStable
0bin
Stabilization of the calibration value not active
1bin
1bin
Stabilization of the calibration value active
R32.6
disDiffMeasure
0bin
Differential measurement active
0bin
1bin
Differential measurement not active (only KL3132, KL3162, KL3172, KL3182)
R32.5
disCali
0bin
Cyclic calibration of the A/D converter active
0bin
1bin
Cyclic calibration of the A/D converter not active
R32.4
enSiemensFormat
0bin
Siemens output format not active
0bin
1bin
Siemens output format active
R32.3
enAverageFormat
0bin
Signed amount representation not active
0bin
1bin
Signed amount representation active
R32.2
disWdTimer
0bin
Watchdog timer is active (the watchdog is triggered if no process data are received for 100 ms)
0bin
1bin
Watchdog timer is not active
R32.1
enManScal
0bin
Manufacturer scaling is not active
0bin
1bin
Manufacturer scaling is active
KL3132, KL3182:
1bin
R32.0
enUsrScal
0bin
User scaling is not active
0bin
1bin
User scaling is active
*) Bit R32.14 and bit R32.15 are only available with the following firmware versions:
For lower firmware versions, bits R32.14 and R32.15 are not evaluated.
These terminals always set the error bit SB1.6 during the calibration and cannot indicate the stability error!
R33: User scaling - offset
This register contains the offset of the user scaling. The user scaling can be activated in the feature register through bit R32.0 (16 bit signed integer).
R34: User scaling - gain
This register contains the gain of the user scaling. The user scaling can be activated in the feature register through bit R32.0 (16 bit unsigned integer x 2-8 + 1. 1dec corresponds to 0x0100).
R35: Limit value 1
Limit value 1 is entered in register R35. The limit value can be activated in the feature register through bit R32.9.
R36: Limit value 2
Limit value 2 is entered in register R36. The limit value can be activated in the feature register through bit R32.10.
R37: Filter constants of the A/D converter, and configuration bits for the filter
(default value: 35C0hex)
The terminal has two low-pass filter stages:
Bit
15
14
13
12
11
10
9
8
7
6
5
4
3
2
1
0
Filter constants SF (SF.11 to SF.0)
Zero
Zero
SkipFIR
Fast
Key
Bit
Default
R37.15
Filter constant SF
(SF.11 - SF.0)
The filter constant SF specifies the 3dB limit frequency of the sinc3 filter. The value ranges from 150 to 2047.
The 3 dB limit frequency FLimit and the 64.5 dB stop frequency FStop are calculated as follows: (see following table)
35Chex
(860dec)
R37.4
Skip = 0
FLimit = 11981 / SF
FStop = 43008 / SF
Skip = 1
FLimit = 80486 / SF
Bit
Default
R37.3
Zero
0bin
See note below
0bin
R37.2
Zero
0bin
0bin
Register description 4:
Do not change
Bits R37.2 and R37.3 must always be ZERO, otherwise errors will occur in the A/D converter!
Bit
Default
R37.1
SkipFIR
0bin
FIR filter is active.
0bin
1bin
FIR filter is bypassed.
R37.0
Fast
0bin
Fast Step Mode is not active.
0bin
1bin
Fast Step Mode is active: a fast reaction will follow jumps at the input, in spite of the filter stage being active. In this case the filter is bypassed!
Examples
Value in R37
FStop
Cycle time
0x35C0
50 Hz
140 ms
0x2660
70 Hz
100 ms
0x1330
140 Hz
50 ms
0x7FF1
40 ms
0x3FF1
20 ms
0x1001
<4 ms
Value in R37
FLimit
Cycle time
0x7FF2
39.6 Hz
40 ms
0x3FF2
77.36 Hz
20 ms
0x1002
158 Hz
<4 ms
R40: Calibration interval
This register contains the calibration interval for the terminal's automatic calibration. The unit is 100 ms. The automatic calibration can be activated through bit R32.5 in the feature register.
R44: Forced calibration interval
This register contains the interval for the terminal's forced calibration. This interval is always a multiple (the default is 3dec) of the calibration interval. (R40). The interval for forced calibration when the terminal leaves the factory is therefore 3 x 180 s = 540 s. The forced calibration can be activated through bit R32.5 in the feature register.
R47: Number of stable measured values
This register contains the number of stable measured values recorded during the calibration.
R48: Tolerance for measured value stability
This register contains the specified stable measured value tolerance.