Thermocouple (TC)
Comparative overview of Beckhoff thermocouple (TC) devices (terminals, boxes, modules)
The following table is intended to provide a quick overview of the available Beckhoff I/O devices for the direct connection of thermocouples for temperature and mV measurement.
Notice | |
Device documentation is solely authoritative The values may be shortened extracts from the respective documentation, which is decisive and recommended for detailed analysis. |
All devices feature:
- Transformation of many common TC types;
Note: the implemented measuring ranges may vary slightly in the end points, - internal cold junction.
If applicable, the following functions are still available
- Wire break detection
- External cold junction
Notice | |
Measurement uncertainty in TC measurement The measurement uncertainty in the table is only a rough orientating value, since it depends strongly on the TC type and the measuring temperature; details in the respective documentation. |
For a possibly more up-to-date overview, please consult www.beckhoff.com.
Design |
Number of TC |
Connection technology |
Resolution |
Maximum sampling rate per channel for control |
KL3311, KL3312, KL3314 |
K-bus terminal IP20 |
1-4 |
Spring-loaded technology |
0.1 °C |
4 sps |
EL3311, EL3312, EL3314, EL3318 |
EtherCAT terminal IP20 |
1-8 |
0.1/0.01 °C |
50 sps |
EL3314-0090 |
4 |
0.1/0.01 °C |
50 sps |
EL3314-0010 |
4 |
0.1/0.01/0.001 °C |
50 sps |
EL3314-0002 |
4 |
0.1/0.01/0.001 °C |
200 sps |
ELM3344, ELM3348 |
2/4 |
Push-In |
0.1/0.01/0.001 °C |
1,000 sps |
ELM3344-0003, ELM3348-0003 |
2/4 |
Mini-TC |
0.1/0.01/0.001 °C |
1,000 sps |
ELM3702-xxxx, ELM3704-xxxx |
2/4 |
Push-In, LEMO |
0.1/0.01/0.001 °C |
10,000 sps |
EP3314-0002 |
EtherCAT Box IP67 |
4 |
M12 |
0.1/0.01 °C |
50 sps |
EPP3314-0002 |
EtherCAT P Box IP67 |
4 |
M12 |
0.1/0.01 °C |
50 sps |
EJ3318 |
EtherCAT plug-in module |
8 |
On application-specific signal distribution boards |
0.1 °C/ digit |
25 Sps |
Continuation:
| Measurement uncertainty of temperature measurement incl. | Measuring ranges - mV measurement | Oversampling | Operation with | Distributed Clocks for |
KL3311, KL3312, KL3314 | < ±0.5 % | 30/60/120 mV | - | - | - |
EL3311, EL3312, EL3314, EL3318 | < ±0.3 % | 30/75 mV | - | X | - |
EL3314-0090 | < ±0.3 % | 30/75 mV | - | X | - |
EL3314-0010 | < ±0.2 % | 78 mV | - | X | - |
EL3314-0002 | < ±0.2 % | 78 mV / 2.5 V | - | X | - |
ELM3344, ELM3348 | < ±0.1 % | 20 mV to 10 V | X | X | X |
ELM3344-0003, ELM3348-0003 | < ±0.05 % | 20 mV to 10 V | X | X | X |
ELM3702-xxxx, ELM3704-xxxx | < ±0.1 % | 20 mV to 10 V | X | X | X |
EP3314-0002 | < ±0.3 % | 30/60/75 mV | - | X | - |
EPP3314-0002 | < ±0.3 % | 30/60/75 mV | - | X | - |
EJ3318 | < ±0.3 % | 30//6075 mV | - | X | - |
Continuation:
| Electrically isolated | TwinSAFE SC | Measured value | Extended | Special features |
KL3311, KL3312, KL3314 | - | - | - | - | - |
EL3311, EL3312, EL3314, EL3318 | - | - | Various predefined internal digital filters | - | - |
EL3314-0090 | - | X | Various predefined internal digital filters | - | TSC variant of the EL3314-0000 |
EL3314-0010 | - | - | Various predefined internal digital filters | - | Calibrated version EL3314-0030 available |
EL3314-0002 | Yes, 2500 V functional | - | Various predefined internal digital filters | - | - |
ELM3344, ELM3348 | - | - | Various predefined internal digital filters Freely parameterizable with TwinCAT Filter Designer | Yes, with | - |
ELM3344-0003, ELM3348-0003 | - | - | Various predefined internal digital filters Freely parameterizable with TwinCAT Filter Designer | Yes, with | - |
ELM3702-xxxx, ELM3704-xxxx | - | - | Various predefined internal digital filters Freely parameterizable with TwinCAT Filter Designer | Yes | Multi-function terminal |
EP3314-0002 | - | - | Various predefined internal digital filters | - | - |
EPP3314-0002 | - | - | Various predefined internal digital filters | - | - |
EJ3318 | - | - | Various predefined internal digital filters | - | - |