Ground reference: single-ended/differential typification
For analog inputs Beckhoff makes a basic distinction between two types: single-ended (SE) and differential (DIFF), referring to the difference in electrical connection with regard to the potential difference.
The diagram shows two-channel versions of an SE module and a DIFF module as examples for all multi-channel versions.
Ground reference: single-ended/differential typification 1:
Fig.33: SE and DIFF module as 2-channel version
Note: Dashed lines indicate that the respective connection may not necessarily be present in each SE or DIFF module. Electrical isolated channels are operating as differential type in general, hence there is no direct relation (voltaic) to ground within the module established at all. Indeed, specified information to recommended and maximum voltage levels have to be taken into account.
The basic rule
Explanation
Typification of the 2/3/4-wire connection of current sensors
Current transducers/sensors/field devices (referred to in the following simply as ‘sensor’) with the industrial 0/4-20 mA interface typically have internal transformation electronics for the physical measured variable (temperature, current, etc.) at the current control output. These internal electronics must be supplied with energy (voltage, current). The type of cable for this supply thus separates the sensors into self-supplied or externally supplied sensors:
Self-supplied sensors
Ground reference: single-ended/differential typification 2:
Fig.34: 2-wire connection
Therefore, they are to be connected according to the Beckhoff terminology as follows:
preferably to ‘single-ended’ inputs if the +Supply connections of the device are also to be used - connect to +Supply and Signal.
They can, however, also be connected to ‘differential’ inputs, if the termination to GND is then manufactured on the application side – to be connected with the right polarity to +Signal and –Signal
It is important to refer to the information page Configuration of 0/4…20 mA differential inputs (see documentation for the EL30xx terminals, for example)!
Externally supplied sensors
Note: expert organizations such as NAMUR demand a usable measuring range <4 mA/>20 mA for error detection and adjustment, see also NAMUR NE043.
The Beckhoff device documentation must be consulted in order to see whether the respective device supports such an extended signal range.
Usually there is an internal diode existing within unipolar terminals/ box modules (and related product groups), in this case the polarity/direction of current have to be observed.
Ground reference: single-ended/differential typification 3:
Fig.35: Connection of externally supplied sensors
Classification of Beckhoff Terminals/ Box modules - Beckhoff 0/4-20 mA Terminals/ Box modules (and related product groups) are available as differential and single-ended:
Single-ended
EL3x4x: 0-20 mA, EL3x5x: 4-20 mA, same as KL and related product groups
Differential
EL3x1x: 0-20 mA, EL3x2x: 4-20 mA, same as KL and related product groups
Preferred current direction because of internal diode
Designed for the connection of externally-supplied sensors with a 3/4-wire connection.
The terminal/box is a passive differential current measuring device; passive means that the sensor is not supplied with power.
Designed for the connection of self-supplied sensors with a 2-wire connection
Ground reference: single-ended/differential typification 4:
Fig.36: 2-, 3- and 4-wire connection at single-ended and differential inputs
