IP3312-Bxxx, IE3312
4 Channel Analog Input Thermocouple
The IP3312 analog input module permits four thermocouples to be directly connected. The module's circuit can operate thermocouple sensors using the 2-wire technique. Linearization over the full temperature range is realized with the aid of a microprocessor. The temperature range can be selected freely. The module can also be used for voltage measurements in the mV range. The module's standard settings are: Resolution 0.1 °C over the temperature range of type K sensors. Sensor malfunctions such as broken wires are indicated by error LEDs. Compensation for the cold junction is made through a temperature measurement in the connecting plug. This means that standard extension leads can be connected.
The module is quite versatile, but default settings have been selected in such a way that in most cases it is not necessary to perform configuration. The input filter and associated conversion times can be set within a wide range, and several data output formats may be chosen. The inputs can, if required, be scaled differently, and automatic limit monitoring is also available. Parameterization may be carried out either via the fieldbus or using the KS2000 software tool.
IP3312-Bxxx, IE3312 1:
Technical data
IP3312-Bxxx / IE3312
Number of channels
4 analog inputs
Output connections
M12 screw-in
Nominal input range
Types J, K, L, B, E, N, R, S, T, U (default setting type K), mV measurement
Resolution
0.1°C per digit
Conversion time
260 ms
Measurement error
< +/- 0.5 % (of the full scale value)
Input filter
4 versions
Cold junction compensation
via ZS2000-3712
Sensor supply
From the load voltage, US
Power supply
Feed: 1 x M8 connector, 4-pin; downstream connection: 1 x M8 socket, 4-pin
Bits in process image
I: 4 x 16 bits, optional I/O: 4 x 8 bits control/state + 4 x 16 bits
Electrical isolation
control voltage / fieldbus: yes
channels / control voltage: 500 V
between the channels: no
Permissible ambient temperature during operation
0°C ... +55°C
Permissible ambient temperature during storage
-25 °C ... +85°C
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC resistance burst / ESD
conforms to EN 61000-6-2 / EN 61000-6-4
Protection class
IP65, IP66, IP67 (conforms to EN 60529)
Installation position
variable
See the connection diagram for details of the connection.
See the parameterization description for details of the parameterization.
See the mapping description for details of the mapping.
See dimension page for weight and dimensions.