IP3102-Bxxx, IE3102
4 Channel Analog Input ± 10 V
The IP3102 analog input module handles signals in the range from -10 V to +10 V. The voltage is digitized to a resolution of 16 bits, and is transmitted, electrically isolated, to the higher-level automation device. The input channels have differential inputs and possess a common, internal ground potential. The applied load voltage (which can be any value up to 30 VDC) is fed through to supply the sensor. It is thus possible, for instance, to supply a measuring potentiometer with 10 VDC from an external voltage source. The module is quite versatile, but default settings have been selected in such a way that in most cases it is not necessary to perform configuration. The input filter and associated conversion times can be set within a wide range, and several data output formats may be chosen. The inputs can, if required, be scaled differently, and automatic limit monitoring is also available. Parameterization may be carried out either via the fieldbus or using the KS2000 software tool.
IP3102-Bxxx, IE3102 1:
Technical data
IP3102-Bxxx / IE3102
Number of channels
4 analog inputs
Output connections
M12 screw-in
Nominal input range
-10 V ... +10 V
Input resistance
> 100 kΩ
Common mode voltage
35 V max.
Conversion time
250 ms (default), configurable to 5 ms
Resolution
15 bits + arithmetic sign
Relative measurement error
< ± 0,3% of the full scale value
Input filter
10 variations inc. averaging, configurable
Sensor supply
from load supply voltage UP, DC, any value up to 30 V
Power supply
Feed: 1 x M8 connector, 4-pin; downstream connection: 1 x M8 socket, 4-pin
Bits in process image
I: 4 x 16 bits, optional I/O: 4 x 8 bits control/state + 4 x 16 bits
Electrical isolation
control voltage / fieldbus: yes
channels / control voltage: 500 V
between the channels: no
Permissible ambient temperature during operation
0°C ... +55°C
Permissible ambient temperature during storage
-25 °C ... +85°C
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC resistance burst / ESD
conforms to EN 61000-6-2 / EN 61000-6-4
Protection class
IP65, IP66, IP67 (conforms to EN 60529)
Installation position
variable
See the Connection diagram for details of the connection.
See the Parameterization description for details of the parameterization.
See the Mapping description for details of the mapping.
See dimension page for weight and dimensions.