Configuration data
Index 8000 ENC Settings
8000:0 | ENC Settings | Maximum subindex | UINT8 | RO | 0x17 (23dec) |
8000:01 | The counter is reset via the C input. | BOOLEAN | RW | 0x00 (0dec) | |
8000:02 | A counter reset is triggered via the external latch input (24 V). | BOOLEAN | RW | 0x00 (0dec) | |
8000:03 | Enablement of the up/down counter in place of the encoder with the bit set. | BOOLEAN | RW | 0x00 (0dec) | |
8000:04 | 0: Disable gate | BIT2 | RW | 0x01 (1dec) | |
8000:08 | Disable filter | 0: Activates the input filter (inputs A, /A, B, /B, C, /C only) | BOOLEAN | RW | 0x01 (1dec) |
8000:0A | If DC mode is activated, the Box interpolates micro-increments between the integer encoder increments. The lower 8 bits of the Counter Value are used in each case for the display. A 32-bit counter thus becomes a 24+8-bit counter, a 16-bit counter becomes an 8+8-bit counter. | BOOLEAN | RW | 0x00 (0dec) | |
8000:0B | An open circuit on track A is indicated in object Open circuit (index 0x6000:07) and as a process data. Diagnosis is only possible if the corresponding input is wired differentially. A differential voltage < 3.5 V (typical, subject to change) is detected as a broken wire. | BOOLEAN | RW | 0x01 (1dec) | |
8000:0C | An open circuit on track B is indicated in object Open circuit (index 0x6000:07) and as a process data. Diagnosis is only possible if the corresponding input is wired differentially. A differential voltage < 3.5 V (typical, subject to change) is detected as a broken wire. | BOOLEAN | RW | 0x01 (1dec) | |
8000:0D | An open circuit on track C is indicated in object Open circuit (index 0x6000:07) and as a process data. Diagnosis is only possible if the corresponding input is wired differentially. A differential voltage < 3.5 V (typical, subject to change) is detected as a broken wire. | BOOLEAN | RW | 0x00 (0dec) | |
8000:0E | Activates reversion of rotation | BOOLEAN | RW | 0x00 (0dec) | |
8000:10 | 0: Fall (the counter is set to zero with a falling edge) | BIT2 | RW | 0x01 (1dec) | |
8000:11 | This is the minimum time over which the frequency is determined; default value 10 ms [resolution: 1 µs]. | UINT16 | RW | 0x2710 (10000dec) | |
8000:13 | Scaling of the frequency measurement (must be divided by this value to obtain the unit in Hz): 100: “0.01 Hz” | UINT16 | RW | 0x0064 (100dec) | |
8000:14 | Resolution of the period value in the process data: 100: “100 ns” period value is a multiple of 100 ns 500: “500 ns” period value is a multiple of 500 ns | UINT16 | RW | 0x0064 (100dec) | |
8000:15 | Resolution of the frequency measurement: 100: “0.01 Hz” | UINT16 | RW | 0x0064 (100dec) |
8000:16 | Internal resolution of the period value measurement: 100: “100 ns” period value is a multiple of 100 ns The period is calculated internally with a resolution of 100 ns. The max. measurable period can then be approx. 1.6 seconds. 500: “500 ns” period value is a multiple of 500 ns Internally the period is calculated with 500 ns resolution. The maximum measurable period is approx. 32.7 ms. The resolution of the process data continues to be the value according to object Period scaling (index 0x8000:14) (e.g., 100 ns [default]). | UINT16 | RW | 0x0064 (100dec) | |
8000:17 | Waiting time [ms] for frequency measurement | UINT16 | RW | 0x0640 (1600dec) |