Encoder parameters
The encoder parameters can be found in CoE object 0x8000 "ENC Settings".
EPP5101-0011
EPP5151-0002
EPP5101-x002
Frequency
- The time window for the frequency calculation and the resolution can be parameterized in the CoE objects Frequency window 0x8000:11, Frequency scaling 0x8000:13, Frequency resolution 0x8000:15 and Frequency wait time 0x8000:17.
- The positive edges of track A are counted within the specified timeframe and the next edge including the time up to it are counted. The waiting time can be set in CoE object 0x8000:17 Frequency Wait Time (unit: ms). The default value is 1.6 sec. This is also the maximum value.
- The time window is 10 ms (default), min. 1 µs. With the default setting it is possible to measure frequencies up to approx. 800 kHz. At higher frequencies a smaller value must be selected for the timeframe.
- The time is measured with a resolution of 100 ns.
- This calculation is carried out in the slave without reference to the distributed clocks system. It is therefore independent of the DC mode.
- No frequency measurement is possible if the counter is blocked by the gate. In this case the period can be measured regardless.
- A C or external reset restarts the frequency measurement. The last frequency value remains unchanged until a new frequency value is determined.
Frequency measurement
- Basic unit 1 µs: all window sizes
Measurement sequence
- The measurement starts with a positive edge at track A. The current counter value and time (resolution: 100 ns) are stored.
- After the measuring window time has elapsed (index 0x8000:11), the system waits for the subsequent rising edge at track A, or a maximum of 1.6 seconds, or the time from Frequency Wait Time 0x8000:17.
- The frequency is calculated from the edge difference and the actual elapsed time.
Period calculation
- During each cycle the interval between 2 positive edges of input A is counted.
- If no edge change occurs for approx. 1.6 s, any period specification is canceled.
Latch
- Activation of latch C input (Enable latch C index 0x7000:01) and saving ("latching") of the counter value
- The counter value is saved when the first external latch pulse (positive edge at input "C") is encountered after the bit has been set (TRUE) in Enable latch C index 0x7000:01 (this has priority over Enable latch extern on positive / negative edge 0x7000:02 / 0x7000:04). The subsequent pulses at the other inputs have no influence on the latch value in index 0x6000:12 if the bit is set.
- Note for Latch C valid bit: A new counter value at the latch input can only be written once the value of the Latch C valid bit (index 0x6000:01) is FALSE.
- Activation of the external latch input ("Gate/Latch") and latching of the counter value (index 0x7000:02, 0x7000:04) (not for product version x002)
- When the bit is set (TRUE) in Enable latch extern on positive edge index 0x7000:02, the counter value is saved on the latch input (index 0x6000:12) when the first external latch pulse with rising edge is encountered. The subsequent pulses have no influence on the latch value in index 0x6000:12.
- When the bit is set (TRUE) in Enable latch extern on negative edge index 0x7000:04, the counter value is saved on the latch input (index 0x6000:12) when the first external latch pulse with falling edge is encountered. The subsequent pulses have no influence on the latch value in index 0x6000:12.
- Note for Latch extern valid bit: A new counter value cannot be written to the latch input until the value of the Latch extern valid (index 0x6000:02) is FALSE.
Reset
- Counter reset via input C:
- To reset the counter, set the bit in Enable latch C index 0x8000:01.
- Resetting the counter via the external latch input (not for product version -x002)
- For a reset via the external latch input, set the bit in Enable extern reset index 0x8000:02
- Extern reset polarity index 0x8000:10 can be used to select the edge for setting the counter to zero.
• Bit not set: Counter is set to zero with falling edge.
• Bit set: Counter is set to zero with rising edge. - The functions Enable C reset (0x8000:01) and Enable extern reset (0x8000:02) cannot be enabled simultaneously.
Up/down counter
- The mode (encoder or up/down counter) can be set via Enable up/down counter index 0x8000:03. (not for product version -2011)
- Click the corresponding row of the index to be parameterized,
- enter the value "1" in the SetValue dialog and
- confirm with OK.
- Set the gate polarity accordingly via object 0x8000:04.
- An additional option for reversing the direction of rotation is to set the Reversion of rotation bit index: 0x8000:0E.
Overflow/underflow (not for product version -2011)
- Overflow/underflow control is inactive in combination with an activated reset function (C/external).
- The underflow bit (0x6000:04) is set if an underflow ...00 ->...FF occurs. It is reset if 2/3 of the counter range are underrun.
- The overflow bit (0x6000:05) is set if an overflow FF...-> 0... occurs. It is reset if 1/3 of the counter range is exceeded.
Open circuit detection
- A separate open circuit detection can be activated for each of the channels A, B, and C (index 0x80n0:0B, 0x80n0:0C, 0x80n0:0D).
- Open circuit detection is activated for channels A and B by default.
- A differential voltage of < 1.5 V (typical, subject to modification) is interpreted as an open circuit.
- If an open circuit is detected, it is indicated as process data Open circuit = TRUE (bit in object Open circuit 0x6000:07 is set). An open circuit is also indicated separately in indices 0xA000:01 (track A), 0xA000:02 (track B), and 0xA000:03 (track C).
- TxPDO state also becomes TRUE if an open circuit is detected, since invalid data have to be assumed.
Micro-increments
- Works with and without distributed clocks, but it is only meaningful in conjunction with one of the DC modes.
- By setting the counter value only the integer component can be modified.
- The frequency measurement principle in enhanced operation mode:
The highly constant query cycles (accuracy: 100 ns) of the distributed clocks systems enable the Box to interpolate axis positions between the counted encoder increments from a certain speed. The interpolation resolution is 8 bit, corresponding to 256 values. A standard encoder with 1,024 lines with 4-way evaluation and micro-increments thus becomes a high-resolution axis encoder with 4096 x 256 = 1,048,567 lines.
If the velocity value falls below the minimum value, this is indicated by the object Extrapolation stall 0x6000:08 in the process data (not for product version -2011).