Objects to be parameterized during commissioning
Index 1011: Restore default parameters
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1011:0 |
Restore default parameters |
UINT8 |
RO |
0x01 (1dec) |
1011:01 |
SubIndex 001 |
If this object is set to "0x64616F6C" in the set value dialog, all backup objects are reset to their delivery state. |
UINT32 |
RW |
0x00000000 (0dec) |
Index 8000: TC Settings Ch.1
Index (hex) | Name | Meaning | Data type | Flags | Default | |
8000:0 | TC Settings Ch.1 | Maximum subindex | UINT8 | RO | 0x1B (27dec) | |
8000:01 | Enable user scale | Activates user scaling | BOOLEAN | RW | 0x00 (0dec) | |
8000:02 | Presentation | Presentation of the measured value | BIT3 | RW | 0x00 (0dec) | |
0 | Signed, in two's complement | |||||
1 | Most significant bit as sign | |||||
2 | High-resolution (1/100 °C steps) | |||||
8000:05 | Siemens bits | The S5 bits are displayed in the three low-order bits | BOOLEAN | RW | 0x00 (0dec) | |
8000:06 | Enable filter | This parameter is without effect. The filter is always enabled. | BOOLEAN | RW | 0x00 (0dec) | |
8000:07 | Enable limit 1 | Activates limit check for limit 1 | BOOLEAN | RW | 0x00 (0dec) | |
8000:08 | Enable limit 2 | Activates limit check for limit 2 | BOOLEAN | RW | 0x00 (0dec) | |
8000:0A | Enable user calibration | Activates user calibration | BOOLEAN | RW | 0x00 (0dec) | |
8000:0B | Enable vendor calibration | Activates vendor calibration | BOOLEAN | RW | 0x01 (1dec) | |
8000:0C | Cold junction compensation | Cold junction compensation | BIT2 | RW | 0x00 (0dec) | |
0 | Cold junction compensation takes place via the Pt1000 in the plug connector. | |||||
1 | Cold junction compensation is not active. | |||||
2 | Cold junction compensation takes place via the process data. | |||||
3 | Same as value 0. | |||||
8000:0E | Swap limit bits | Swaps the two limit bits, in order to achieve compatibility with older hardware versions. | BOOLEAN | RW | 0x00 (0dec) | |
8000:11 | User scale offset | User scaling: Offset | INT16 | RW | 0x0000 (0dec) | |
8000:12 | User scale gain | User scaling: Gain | INT32 | RW | 0x00010000 (65536dec) | |
8000:13 | Limit 1 | Value for limit 1 | INT16 | RW | 0x0000 (0dec) | |
8000:14 | Limit 2 | Value for limit 2 | INT16 | RW | 0x0000 (0dec) | |
8000:15 | Filter settings | Filter settings (Ch1. applies to all channels) | UINT16 | RW | 0x0000 (0dec) | |
0 | 50 Hz | |||||
1 | 60 Hz | |||||
2 | 100 Hz | |||||
3 | 500 Hz | |||||
4 | 1 kHz, | |||||
5 | 2 kHz | |||||
6 | 3.75 kHz | |||||
7 | 7.5 kHz | |||||
8 | 15 kHz | |||||
9 | 30 kHz | |||||
10 | 5 Hz | |||||
11 | 10 Hz | |||||
8000:16 | Calibration interval | reserved | UINT16 | RW | 0x0000 (0dec) | |
8000:17 | User calibration offset | User calibration: Offset | INT16 | RW | 0x0000 (0dec) | |
8000:18 | User calibration gain | User calibration: Gain | UINT16 | RW | 0x4000 (16384dec) |
8000:19 | Sensor type | Thermocouple | UINT16 | RW | 0x0000 (0dec) | |
0 | Type K -200 °C to 1370 °C | |||||
1 | Type J -100°C to 1200°C | |||||
2 | Type L 0°C to 900°C | |||||
3 | Type E -100°C to 1000°C | |||||
4 | Type T -200°C to 400°C | |||||
5 | Type N -100°C to 1300°C | |||||
6 | Type U 0°C to 600°C | |||||
7 | Type B 600°C to 1800°C | |||||
8 | Type R 0°C to 1767°C | |||||
9 | Type S 0°C to 1760°C | |||||
10 | Type C 0°C to 2320°C | |||||
100 | ± 30 mV (1 µV resolution) | |||||
101 | ± 60 mV (2 µV resolution) | |||||
102 | ± 75 mV (4 µV resolution) | |||||
8000:1B | Wire calibration 1/32 ohm | Only for 2-wire measurements: | INT16 | RW | 0x0000 (0dec) |
Index 8010: TC Settings Ch.2
8010:0 | TC Settings Ch.2 | Maximum subindex | UINT8 | RO | 0x1B (27dec) | |
8010:01 | Enable user scale | Activates user scaling | BOOLEAN | RW | 0x00 (0dec) | |
8010:02 | Presentation | Presentation of the measured value | BIT3 | RW | 0x00 (0dec) | |
8010:05 | Siemens bits | The S5 bits are displayed in the three low-order bits | BOOLEAN | RW | 0x00 (0dec) | |
8010:06 | Enable filter | This parameter is without effect. The filter is always enabled. | BOOLEAN | RW | 0x00 (0dec) | |
8010:07 | Enable limit 1 | Activates limit check for limit 1 | BOOLEAN | RW | 0x00 (0dec) | |
8010:08 | Enable limit 2 | Activates limit check for limit 2 | BOOLEAN | RW | 0x00 (0dec) | |
8010:0A | Enable user calibration | Activates user calibration | BOOLEAN | RW | 0x00 (0dec) | |
8010:0B | Enable vendor calibration | Activates vendor calibration | BOOLEAN | RW | 0x01 (1dec) | |
8010:0C | Cold junction compensation | Cold junction compensation | BIT2 | RW | 0x00 (0dec) | |
3 | Cold junction compensation takes place via the Pt1000 in the plug connector of channel 1. | |||||
8010:0E | Swap limit bits | Swaps the two limit bits, in order to achieve compatibility with older hardware versions. | BOOLEAN | RW | 0x00 (0dec) | |
8010:11 | User scale offset | User scaling: Offset | INT16 | RW | 0x0000 (0dec) | |
8010:12 | User scale gain | User scaling: Gain | INT32 | RW | 0x00010000 (65536dec) | |
8010:13 | Limit 1 | Value for limit 1 | INT16 | RW | 0x0000 (0dec) | |
8010:14 | Limit 2 | Value for limit 2 | INT16 | RW | 0x0000 (0dec) |
8010:15 | Filter settings | This parameter is without effect. The respective parameter of channel 1 applies to all channels: 0x8000:15 “Filter settings”. | UINT16 | RW | 0x0000 (0dec) | |
8010:16 | Calibration interval | reserved | UINT16 | RW | 0x0000 (0dec) | |
8010:17 | User calibration offset | User calibration: Offset | INT16 | RW | 0x0000 (0dec) | |
8010:18 | User calibration gain | User calibration: Gain | UINT16 | RW | 0x4000 (16384dec) | |
8010:19 | Sensor type | Thermocouple | UINT16 | RW | 0x0000 (0dec) | |
8010:1B | Wire calibration 1/32 Ohm | Only for 2-wire measurements: | INT16 | RW | 0x0000 (0dec) |
Index 8020: TC Settings Ch.3
8020:0 | TC Settings Ch.3 | Maximum subindex | UINT8 | RO | 0x1B (27dec) | |
8020:01 | Enable user scale | Activates user scaling | BOOLEAN | RW | 0x00 (0dec) | |
8020:02 | Presentation | Presentation of the measured value | BIT3 | RW | 0x00 (0dec) | |
8020:05 | Siemens bits | The S5 bits are displayed in the three low-order bits | BOOLEAN | RW | 0x00 (0dec) | |
8020:06 | Enable filter | This parameter is without effect. The filter is always enabled. | BOOLEAN | RW | 0x00 (0dec) | |
8020:07 | Enable limit 1 | Activates limit check for limit 1 | BOOLEAN | RW | 0x00 (0dec) | |
8020:08 | Enable limit 2 | Activates limit check for limit 2 | BOOLEAN | RW | 0x00 (0dec) | |
8020:0A | Enable user calibration | Activates user calibration | BOOLEAN | RW | 0x00 (0dec) | |
8020:0B | Enable vendor calibration | Activates vendor calibration | BOOLEAN | RW | 0x01 (1dec) |
8020:0C | Cold junction compensation | Cold junction compensation | BIT2 | RW | 0x00 (0dec) | |
8020:0E | Swap limit bits | Swaps the two limit bits, in order to achieve compatibility with older hardware versions. | BOOLEAN | RW | 0x00 (0dec) | |
8020:11 | User scale offset | User scaling: Offset | INT16 | RW | 0x0000 (0dec) | |
8020:12 | User scale gain | User scaling: Gain | INT32 | RW | 0x00010000 (65536dec) | |
8020:13 | Limit 1 | Value for limit 1 | INT16 | RW | 0x0000 (0dec) | |
8020:14 | Limit 2 | Value for limit 2 | INT16 | RW | 0x0000 (0dec) | |
8020:15 | Filter settings | This parameter is without effect. The respective parameter of channel 1 applies to all channels: 0x8000:15 “Filter settings”. | UINT16 | RW | 0x0000 (0dec) | |
8020:16 | Calibration interval | reserved | UINT16 | RW | 0x0000 (0dec) | |
8020:17 | User calibration offset | User calibration: Offset | INT16 | RW | 0x0000 (0dec) | |
8020:18 | User calibration gain | User calibration: Gain | UINT16 | RW | 0x4000 (16384dec) | |
8020:19 | Sensor type | Thermocouple | UINT16 | RW | 0x0000 (0dec) | |
8020:1B | Wire calibration 1/32 ohm | Only for 2-wire measurements: | INT16 | RW | 0x0000 (0dec) |
Index 8030: TC Settings Ch.4
8030:0 | TC Settings Ch.4 | Maximum subindex | UINT8 | RO | 0x1B (27dec) | |
8030:01 | Enable user scale | Activates user scaling | BOOLEAN | RW | 0x00 (0dec) | |
8030:02 | Presentation | Presentation of the measured value | BIT3 | RW | 0x00 (0dec) | |
8030:05 | Siemens bits | The S5 bits are displayed in the three low-order bits | BOOLEAN | RW | 0x00 (0dec) | |
8030:06 | Enable filter | This parameter is without effect. The filter is always enabled. | BOOLEAN | RW | 0x00 (0dec) | |
8030:07 | Enable limit 1 | Activates limit check for limit 1 | BOOLEAN | RW | 0x00 (0dec) | |
8030:08 | Enable limit 2 | Activates limit check for limit 2 | BOOLEAN | RW | 0x00 (0dec) | |
8030:0A | Enable user calibration | Activates user calibration | BOOLEAN | RW | 0x00 (0dec) | |
8030:0B | Enable vendor calibration | Activates vendor calibration | BOOLEAN | RW | 0x01 (1dec) | |
8030:0C | Cold junction compensation | Cold junction compensation | BIT2 | RW | 0x00 (0dec) | |
8030:0E | Swap limit bits | Swaps the two limit bits, in order to achieve compatibility with older hardware versions. | BOOLEAN | RW | 0x00 (0dec) | |
8030:11 | User scale offset | User scaling: Offset | INT16 | RW | 0x0000 (0dec) | |
8030:12 | User scale gain | User scaling: Gain | INT32 | RW | 0x00010000 (65536dec) | |
8030:13 | Limit 1 | Value for limit 1 | INT16 | RW | 0x0000 (0dec) | |
8030:14 | Limit 2 | Value for limit 2 | INT16 | RW | 0x0000 (0dec) | |
8030:15 | Filter settings | This parameter is without effect. The respective parameter of channel 1 applies to all channels: 0x8000:15 “Filter settings”. | UINT16 | RW | 0x0000 (0dec) | |
8030:16 | Calibration interval | reserved | UINT16 | RW | 0x0000 (0dec) | |
8030:17 | User calibration offset | User calibration: Offset | INT16 | RW | 0x0000 (0dec) | |
8030:18 | User calibration gain | User calibration: Gain | UINT16 | RW | 0x4000 (16384dec) |
8030:19 | Sensor type | Thermocouple | UINT16 | RW | 0x0000 (0dec) | |
8030:1B | Wire calibration 1/32 ohm | Only for 2-wire measurements: | INT16 | RW | 0x0000 (0dec) |
