Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
Supply voltages | |
Connection | See EtherCAT P connection |
US nominal voltage |
24 VDC (-15 % / +20 %) |
US sum current: IS,sum |
max. 3 A |
Current consumption from US |
100 mA |
Rated voltage UP | 24 VDC (-15 % / +20 %) |
UP sum current: IP,sum |
max. 3 A |
Current consumption from UP | = Current consumption of connected sensors. |
Analog inputs | EPP3174-0002 | EPP3174-0002 |
Number | 4 | |
Connection technology | two-wire, four-wire | single ended |
Connection | ||
Measuring range | Configurable:
Internal resistance | > 200 kΩ (typ. 85 Ω + diode voltage) | |
Common-mode voltage UCM | max. 35 V | |
Resolution | 16 bits (including sign) | |
Input filter | configurable | |
Input filter limit frequency | 5 kHz | |
Conversion time | ~ 100 μs | |
Measurement deviation | < ±0.3 %, relative to full scale value. See chapter Measurement error/measurement deviation/measurement uncertainty, output uncertainty. | |
Sensor power supply | from the load voltage UP | |
Housing data | |
Dimensions W x H x D | 30 mm x 126 mm x 26.5 mm (without connectors) |
Weight | approx. 165 g |
Material |
PA6 (polyamide) |
Environmental conditions | |
Ambient temperature during operation | -25 … +60 °C |
Ambient temperature during storage | -40 … +85 °C |
Vibration resistance, shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 |
Protection class | IP65, IP66, IP67 (conforms to EN 60529) |
Approvals / markings | |
Approvals / markings *) | CE, cULus |
Additional tests
The devices have undergone the following additional tests:
Test | Explanation |
Vibration | 10 frequency sweeps in 3 axes |
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude | |
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude | |
Shocks | 1000 shocks in each direction, in 3 axes |
35 g, 11 ms |