Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
EtherCAT P
Connection
2 x M8 socket, 4-pin, P-coded, shielded
Supply voltages
Connection
See EtherCAT P connection
US nominal voltage
24 VDC (-15 % / +20 %)
US sum current: IS,sum
max. 3 A
Current consumption from US
100 mA
UP nominal voltage
UP sum current: IP,sum
max. 3 A
Current consumption from UP
20 mA
+ Output currents of the digital outputs
+ Output currents of the auxiliary voltage outputs
Digital outputs
EPP2028-0001
EPP2028-0002
Number
8
Connection
8 x M8 socket, 3-pin, A-coded
4 x M12 socket, 5-pin, A-coded
Cable length
max. 30 m
Load type
Resistive, inductive, lamp load
Rated voltage
24 V DC from UP
Output current IOUT
max. 2.0 A per channel
max. 3.0 A in total
Short-circuit current
15 A typ.
Switching times
TON: 200 µs typ., TOFF: 200 µs typ.
Auxiliary voltage
24 V DC from UP, short-circuit proof
max. 0.5 A in total
Housing data
Dimensions W × H × D
30 mm × 126 mm × 26.5 mm (without connectors)
Weight
approx. 165 g
Installation position
variable
Material
PA6 (polyamide)
Environmental conditions
Ambient temperature during operation
-25…+60 °C
-25…+55 °C according to cULus
Ambient temperature during storage
-40…+85 °C
Vibration resistance, shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
Additional tests
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection rating
IP65, IP66, IP67 (conforms to EN 60529)
Approvals / markings
Approvals / markings *)
CE, cULus
Additional tests
The devices have undergone the following additional tests:
Test
Explanation
Vibration
10 frequency sweeps in 3 axes
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude
Shocks
1000 shocks in each direction, in 3 axes
35 g, 11 ms