Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
Supply voltages | |
Connection | See EtherCAT P connection |
US nominal voltage | 24 VDC (-15 % / +20 %) |
US sum current: IS,sum | max. 3 A |
Current consumption from US | 100 mA |
UP nominal voltage | 24 VDC (-15 % / +20 %) |
UP sum current: IP,sum | max. 3 A |
Current consumption from UP | 20 mA + Output currents of the digital outputs + Output currents of the auxiliary voltage outputs |
Digital outputs | |
Number | 16 |
Connection | 1 x D-sub socket, 25-pin, UNC4–40 thread |
Cable length | max. 30 m |
Load type | resistive, inductive, lamp load |
Rated voltage | 24 V DC from UP |
Output current | max. 0.5 A per channel max. 3.0 A in total |
Short-circuit current | max. 1.5 A per channel |
Switching times | TON: 60 µs typ., TOFF: 300 µs typ. |
Diagnostics | Yes |
Auxiliary voltage | 24 V DC from UP, short-circuit proof
Housing data | |
Dimensions W × H × D | 30 mm × 126 mm × 26.5 mm (without connectors) |
Weight | approx. 165 g |
Material |
PA6 (polyamide) |
Environmental conditions | |
Ambient temperature during operation | -25…+60 °C |
Ambient temperature during storage | -40…+85 °C |
Vibration resistance, shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 |
Protection rating | IP65, IP66, IP67 (conforms to EN 60529) |
Approvals / markings | |
Approvals / markings *) | CE, cULus |
Additional tests
The devices have undergone the following additional tests:
Test | Explanation |
Vibration | 10 frequency sweeps in 3 axes |
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude | |
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude | |
Shocks | 1000 shocks in each direction, in 3 axes |
35 g, 11 ms |