Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
EtherCAT P
Connection
2 x M8 socket, 4-pin, P-coded, shielded
Supply voltages
Connection
See EtherCAT P connection
US rated voltage
24 V DC (-15%, +20%)
US sum current: IS,sum
max. 3 A
Current consumption from US
100 mA
Rated voltage UP
24 V DC (-15 %, +20 %)
UP sum current: IP,sum
max. 3 A
Current consumption from UP
20 mA
+ Output currents of the digital outputs
+ sensor supply
Digital inputs
Number
max. 16
Each digital input can alternatively be used as a digital output.
Connection
2 x ZS2001
Cable length
max. 30 m
Characteristics
Type 3 according to EN 61131–2, compatible with type 1
Input filter
3 ms
Signal voltage "0"
-3…+5 V DC
Signal voltage "1"
+11…+30 V DC
Input current
6 mA at 24 V DC
Sensor power supply
24 V DC from UP, short-circuit proof
max. 0.5 A per connection
Digital outputs
Number
max. 16
Each digital output can alternatively be used as a digital input.
Connection
2 x ZS2001
Cable length
max. 30 m
Sensor power supply
24 V DC from UP,
max. 0.5 A in total, short-circuit proof
Nominal voltage
24 V DC from UP
Load type
Resistive, inductive, lamp load
Output current
max. 0.5 A per channel
max. 3.0 A in total
Short circuit current
max. 1.5 A per channel
Switching times
typ. TON: 25 µs, typ. TOFF: 75 µs
Housing data
Dimensions W × H × D
30 mm × 126 mm × 26.5 mm (without connectors)
Weight
approx. 165 g
Installation position
variable
Material
PA6 (polyamide)
Environmental conditions
Ambient temperature during operation
-25…+60 °C
Ambient temperature during storage
-40…+85 °C
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection rating
IP20
Approvals/markings
Approvals/markings *)
CE
Additional tests
The devices have undergone the following additional tests:
Test
Explanation
Vibration
10 frequency sweeps in 3 axes
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude
Shocks
1000 shocks in each direction, in 3 axes
35 g, 11 ms