![]()  | IO-Link IODD Device Description The display corresponds to the display of the IO-Link device parameters. It is advisable to download the latest IO-Link IODD device description files from the Download section of the Beckhoff website and install them according to the installation instructions.  |
Parameter server (data storage)
The IO-Link box modules support the data storage functionality according to protocol revision 1.1. The parameters 0x0018 (application-specific tag) and 0x08n0 (settings) are secured with the IO-Link master. In order to use this functionality, the IO-Link master must also support it. (e.g. with the Beckhoff EP6224-xxxx IO-Link master from firmware 10) Changes to these parameters are saved by the IO-Link master and restored when the box is replace with an identical IO-Link box. How to use the data storage functionality is explained in chapter Setting of the IO-Link device parameters.
Index 0000 direct parameters 1
Index (hex)  | Name  | Meaning  | Data type  | Flags  | Default  |
0000:01  | Reserved  | -  | UINT8  | RO  | 0  |
0000:02  | Master Cycle Time  | IO-Link specific  | UINT8  | RO  | 0  |
0000:03  | Min Cycle Time  | IO-Link specific  | UINT8  | RO  | 0  |
0000:04  | M-Sequence Capability  | IO-Link specific  | UINT8  | RO  | 0  |
0000:05  | IO-Link Version ID  | IO-Link specific  | UINT8  | RO  | 0  |
0000:06  | Process Data Input Length  | IO-Link specific  | UINT8  | RO  | 0  |
0000:07  | Process Data Output Length  | IO-Link specific  | UINT8  | RO  | 0  |
0000:08  | Vendor ID  | Vendor ID 1  | UINT8  | RO  | 0  |
0000:09  | Vendor ID  | Vendor ID 2  | UINT8  | RO  | 0  |
0000:0A  | Device ID  | Device ID 1  | UINT8  | RO  | 0  |
0000:0B  | Device ID  | Device ID 2  | UINT8  | RO  | 0  |
0000:0C  | Device ID  | Device ID 3  | UINT8  | RO  | 0  |
0000:0D  | Reserved  | -  | UINT8  | RO  | 0  |
0000:0E  | Reserved  | -  | UINT8  | RO  | 0  |
0000:0F  | Reserved  | -  | UINT8  | RO  | 0  |
0000:10  | System Command  | IO-Link specific  |
  | RO  | 0  |
Index 0001 direct parameters 2
0001:01  | Device Specific Parameter 1  | IO-Link specific  | UINT8  | RW  | 0  |
0001:02  | Device Specific Parameter 2  | IO-Link specific  | UINT8  | RW  | 0  |
0001:03  | Device Specific Parameter 3  | IO-Link specific  | UINT8  | RW  | 0  |
0001:04  | Device Specific Parameter 4  | IO-Link specific  | UINT8  | RW  | 0  |
0001:05  | Device Specific Parameter 5  | IO-Link specific  | UINT8  | RW  | 0  |
0001:06  | Device Specific Parameter 6  | IO-Link specific  | UINT8  | RW  | 0  |
0001:07  | Device Specific Parameter 7  | IO-Link specific  | UINT8  | RW  | 0  |
0001:08  | Device Specific Parameter 8  | IO-Link specific  | UINT8  | RW  | 0  |
0001:09  | Device Specific Parameter 9  | IO-Link specific  | UINT8  | RW  | 0  |
0001:0A  | Device Specific Parameter 10  | IO-Link specific  | UINT8  | RW  | 0  |
0001:0B  | Device Specific Parameter 11  | IO-Link specific  | UINT8  | RW  | 0  |
0001:0C  | Device Specific Parameter 12  | IO-Link specific  | UINT8  | RW  | 0  |
0001:0D  | Device Specific Parameter 13  | IO-Link specific  | UINT8  | RW  | 0  |
0001:0E  | Device Specific Parameter 14  | IO-Link specific  | UINT8  | RW  | 0  |
0001:0F  | Device Specific Parameter 15  | IO-Link specific  | UINT8  | RW  | 0  |
0001:10  | Device Specific Parameter 16  | IO-Link specific  | UINT8  | RW  | 0  |
Index 0002 standard command
0002  | Standard Command  | IO-Link specific  | UINT8  | RW  | 0  |
Index 000C Device Access Locks
000C:01  | Parameter (write) Access Lock  | 0: Write access for the parameters is enabled. 1: Write access for the parameters is disabled.  | BOOL  | RW  | FALSE  |
000C:02  | Data Storage Lock  | 0: The data storage function is enabled. 1: The data storage function is disabled.  | BOOL  | RW  | FALSE  |
000C:03  | Local Parameterization Lock  | 0: Local parameterization is enabled. 1: Local parameterization is disabled.  | BOOL  | RW  | FALSE  |
000C:04  | Local User Interface Lock  | 0: The local user interface is enabled. 1: The local user interface is disabled.  | BOOL  | RW  | FALSE  |
Index 0010 vendor name
0010  | Vendor Name  | Vendor name  | String  | R  | Beckhoff Automation GmbH & Co. KG  |
Index 0011 vendor text
0011  | Vendor Text  | Vendor-specific text  | String  | R  | www.beckhoff.com  |
Index 0012 product name
0012  | Product Name  | Product designation  | String  | R  | EPI3174-0002, ERI3174-0002  |
Index 0013 product ID
0013  | Product ID
Index 0014 product text
0014  | Product Text  | Product description  | String  | R  | 4 AI Modules  |
Index 0015 serial number
0015  | Serial Number  | Serial number  | String  | R  | 00000000  |
Index 0016 Hardware version
0016  | Hardware version  | Hardware version  | String  | R  | 00  |
Index 0017 firmware version
0017  | Firmware version  | Firmware version  | String  | R  | 00  |
Index 0018 application-specific tag
0018:00  | Application Specific Tag  | Application-specific description  | String  | RW  | ********************** **********  |
Index 0050 IO status
0050:01  | State  | Indicates the status of the IO board. The IO board is working properly if state = 8dec. and status code = 0 Other values indicate an error on the IO board.  | UINT16  | RO  | 0x0000 (0dec)  |
0050:02  | Status code  | UINT16  | RO  | 0x0000 (0dec)  |
Index 0800 AI Settings Ch.1 (parameterization of channel 1)
Index (hex)  | Name  | Meaning  | Data type  | Flags  | Default  | |
0800:00  | AI Settings Ch1  | Maximum subindex  | UINT8  | RO  | 0x18 (24dec)  | |
0800:01  | Enable User Scale  | 1  | User scale is active.  | BOOLEAN  | RW  | 0x00 (0dec)  |
0800:02  | Presentation  | 0  | Signed presentation (default)  | UINT3  | RW  | 0x00 (0dec)  |
1  | Unsigned presentation  | |||||
2  | Absolute value with MSB as sign (signed amount representation)  | |||||
0800:05  | Siemens bits  | 1  | Status indicators are displayed on the lowest 3 bits in the status word.  | BOOLEAN  | RW  | 0x00 (0dec)  |
0800:06  | Enable filter  | 1  | Enable filter, which makes PLC-cycle-synchronous data exchange unnecessary  | BOOLEAN  | RW  | 0x01 (1dec)  |
0800:07  | Enable Limit 1  | 1  | Limit 1 enabled  | BOOLEAN  | RW  | 0x00 (0dec)  |
0800:08  | Enable Limit 2  | 1  | Limit 2 enabled  | BOOLEAN  | RW  | 0x00 (0dec)  |
0800:0A  | Enable User Calibration  | 1  | Enabling of the user calibration  | BOOLEAN  | RW  | 0x00 (0dec)  |
0800:0B  | Enable Vendor Calibration  | 1  | Enabling of the vendor calibration  | BOOLEAN  | RW  | 0x01 (1dec)  |
0800:0E  | Swap Limit Bits  | 1  | Swaps the two limit bits, in order to achieve compatibility with older hardware versions.  | BOOLEAN  | RW  | 0x00 (0dec)  |
0800:11  | User Scale Offset  | User scale offset  | INT16  | RW  | 0x0000 (0dec)  | |
0800:12  | User Scale Gain  | User scale gain.  | INT32  | RW  | 0x00010000 (65536dec)  | |
0800:13  | Limit 1  | First limit value for setting the status bits  | INT16  | RW  | 0x0000 (0dec)  | |
0800:14  | Limit 2  | Second limit value for setting the status bits  | INT16  | RW  | 0x0000 (0dec)  | |
0800:15  | Filter Settings  | This object determines the digital filter settings for all channels of the module, if it is activated via Enable filter (index 0x80n0:06). The possible settings are sequentially numbered.  | UINT16  | RW  | 0x0000 (0dec)  | |
0  | 50 Hz FIR  |
1  | 60 Hz FIR  | |||||
2  | IIR 1  | |||||
3  | IIR 2  | |||||
4  | IIR 3  | |||||
5  | IIR 4  | |||||
6  | IIR 5  | |||||
7  | IIR 6  | |||||
8  | IIR 7  | |||||
9  | IIR 8  | |||||
0800:17  | User Calibration Offset  | User calibration: Offset  | INT16  | RW  | 0x0000 (0dec)  | |
0800:18  | User Calibration Gain  | User calibration: Gain  | INT16  | RW  | 0x4000 (16384dec)  | |
Index 080E ADC raw value
080E:01  | ADC raw value  | Raw value of the analog/digital converter  | INT16  | RO  | 0x0000 (0dec)  |
Index 080F Al vendor data Ch1
080F:0  | Al Vendor data Ch1  | Maximum subindex  |
  | RO  | 0x0C (12dec)  |
080F:01  | R0 offset  | Offset (vendor calibration)  | INT16  | RW  | 0x0000 (0dec)  |
08 F:02  | R0 gain  | Gain (vendor calibration)  | INT16  | RW  | 0x4000 (16384dec)  |
080F:03  | R1 offset  | Offset (vendor calibration)  | INT16  | RW  | 0x0000 (0dec)  |
080F:04  | R1 gain  | Gain (vendor calibration)  | INT16  | RW  | 0x4000 (16384dec)  |
080F:05  | R2 offset  | Offset (vendor calibration)  | INT16  | RW  | 0x0000 (0dec)  |
080F:06  | R2 gain  | Gain (vendor calibration)  | INT16  | RW  | 0x4000 (16384dec)  |
Index 0810 AI Settings Ch.2 (parameterization of channel 2)
0810:0  | AI Settings Ch2  | Maximum subindex  |
0810:01  | Enable User Scale  | 1  | User scale is active.  | BOOLEAN  | RW  | 0x00 (0dec)  |
0810:02  | Presentation  | 0  | Signed presentation (default)  | UINT3  | RW  | 0x00 (0dec)  |
0810:05  | Siemens bits  | 1  | Status indicators are displayed on the lowest 3 bits in the status word.  | BOOLEAN  | RW  | 0x00 (0dec)  |
0810:07  | Enable Limit 1  | 1  | Limit 1 enabled  | BOOLEAN  | RW  | 0x00 (0dec)  |
0810:08  | Enable Limit 2  | 1  | Limit 2 enabled  | BOOLEAN  | RW  | 0x00 (0dec)  |
0810:0A  | Enable User Calibration  | 1  | Enabling of the user calibration  | BOOLEAN  | RW  | 0x00 (0dec)  |
0810:0B  | Enable Vendor Calibration  | 1  | Enabling of the vendor calibration  | BOOLEAN  | RW  | 0x01 (1dec)  |
0810:0E  | Swap Limit Bits  | 1  | Swaps the two limit bits, in order to achieve compatibility with older hardware versions.  | BOOLEAN  | RW  | 0x00 (0dec)  |
0810:11  | User Scale Offset  | User scale offset  | INT16  | RW  | 0x0000 (0dec)  | |
0810:12  | User Scale Gain  | User scale gain.  | INT32  | RW  | 0x00010000 (65536dec)  | |
0810:13  | Limit 1  | First limit value for setting the status bits  | INT16  | RW  | 0x0000 (0dec)  | |
0810:14  | Limit 2  | Second limit value for setting the status bits  | INT16  | RW  | 0x0000 (0dec)  | |
0810:17  | User Calibration Offset  | User calibration: Offset  | INT16  | RW  | 0x0000 (0dec)  | |
0810:18  | User Calibration Gain  | User calibration: Gain  | INT16  | RW  | 0x4000 (16384dec)  | |
Index 081E ADC raw value
081E:01  | ADC raw value  | Raw value of the analog/digital converter  | INT16  | RO  | 0x0000 (0dec)  |
Index 081F Al vendor data Ch2
081F:0  | Al Vendor data Ch2  | Maximum subindex  |
  | RO  | 0x0C (12dec)  |
081F:01  | R0 offset  | Offset (vendor calibration)  | INT16  | RW  | 0x0000 (0dec)  |
081F:02  | R0 gain  | Gain (vendor calibration)  | INT16  | RW  | 0x4000 (16384dec)  |
081F:03  | R1 offset  | Offset (vendor calibration)  | INT16  | RW  | 0x0000 (0dec)  |
081F:04  | R1 gain  | Gain (vendor calibration)  | INT16  | RW  | 0x4000 (16384dec)  |
081F:05  | R2 offset  | Offset (vendor calibration)  | INT16  | RW  | 0x0000 (0dec)  |
081F:06  | R2 gain  | Gain (vendor calibration)  | INT16  | RW  | 0x4000 (16384dec)  |
Index 0820 AI Settings Ch.3 (parameterization of channel 3)
0820:0  | AI Settings Ch3  | Maximum subindex  |
0820:01  | Enable User Scale  | 1  | User scale is active.  | BOOLEAN  | RW  | 0x00 (0dec)  |
0820:02  | Presentation  | 0  | Signed presentation (default)  | UINT3  | RW  | 0x00 (0dec)  |
0820:05  | Siemens bits  | 1  | Status indicators are displayed on the lowest 3 bits in the status word.  | BOOLEAN  | RW  | 0x00 (0dec)  |
0820:07  | Enable Limit 1  | 1  | Limit 1 enabled  | BOOLEAN  | RW  | 0x00 (0dec)  |
0820:08  | Enable Limit 2  | 1  | Limit 2 enabled  | BOOLEAN  | RW  | 0x00 (0dec)  |
0820:0A  | Enable User Calibration  | 1  | Enabling of the user calibration  | BOOLEAN  | RW  | 0x00 (0dec)  |
0820:0B  | Enable Vendor Calibration  | 1  | Enabling of the vendor calibration  | BOOLEAN  | RW  | 0x01 (1dec)  |
0820:0E  | Swap Limit Bits  | 1  | Swaps the two limit bits, in order to achieve compatibility with older hardware versions.  | BOOLEAN  | RW  | 0x00 (0dec)  |
0820:11  | User Scale Offset  | User scale offset  | INT16  | RW  | 0x0000 (0dec)  | |
0820:12  | User Scale Gain  | User scale gain.  | INT32  | RW  | 0x00010000 (65536dec)  | |
0820:13  | Limit 1  | First limit value for setting the status bits  | INT16  | RW  | 0x0000 (0dec)  | |
0820:14  | Limit 2  | Second limit value for setting the status bits  | INT16  | RW  | 0x0000 (0dec)  | |
0820:17  | User Calibration Offset  | User calibration: Offset  | INT16  | RW  | 0x0000 (0dec)  | |
0820:18  | User Calibration Gain  | User calibration: Gain  | INT16  | RW  | 0x4000 (16384dec)  | |
Index 082E ADC raw value
082E:01  | ADC raw value  | Raw value of the analog/digital converter  | INT16  | RO  | 0x0000 (0dec)  |
Index 082F Al vendor data Ch3
082F:0  | Al Vendor data Ch3  | Maximum subindex  |
  | RO  | 0x0C (12dec)  |
082F:01  | R0 offset  | Offset (vendor calibration)  | INT16  | RW  | 0x0000 (0dec)  |
082F:02  | R0 gain  | Gain (vendor calibration)  | INT16  | RW  | 0x4000 (16384dec)  |
082F:03  | R1 offset  | Offset (vendor calibration)  | INT16  | RW  | 0x0000 (0dec)  |
082F:04  | R1 gain  | Gain (vendor calibration)  | INT16  | RW  | 0x4000 (16384dec)  |
082F:05  | R2 offset  | Offset (vendor calibration)  | INT16  | RW  | 0x0000 (0dec)  |
082F:06  | R2 gain  | Gain (vendor calibration)  | INT16  | RW  | 0x4000 (16384dec)  |
Index 0830 AI Settings Ch.4 (parameterization of channel 4)
0830:0  | AI Settings Ch4  | Maximum subindex  |
0830:01  | Enable User Scale  | 1  | User scale is active.  | BOOLEAN  | RW  | 0x00 (0dec)  |
0830:02  | Presentation  | 0  | Signed presentation (default)  | UINT3  | RW  | 0x00 (0dec)  |
0830:05  | Siemens bits  | 1  | Status indicators are displayed on the lowest 3 bits in the status word.  | BOOLEAN  | RW  | 0x00 (0dec)  |
0830:07  | Enable Limit 1  | 1  | Limit 1 enabled  | BOOLEAN  | RW  | 0x00 (0dec)  |
0830:08  | Enable Limit 2  | 1  | Limit 2 enabled  | BOOLEAN  | RW  | 0x00 (0dec)  |
0830:0A  | Enable User Calibration  | 1  | Enabling of the user calibration  | BOOLEAN  | RW  | 0x00 (0dec)  |
0830:0B  | Enable Vendor Calibration  | 1  | Enabling of the vendor calibration  | BOOLEAN  | RW  | 0x01 (1dec)  |
0830:0E  | Swap Limit Bits  | 1  | Swaps the two limit bits, in order to achieve compatibility with older hardware versions.  | BOOLEAN  | RW  | 0x00 (0dec)  |
0830:11  | User Scale Offset  | User scale offset  | INT16  | RW  | 0x0000 (0dec)  | |
0830:12  | User Scale Gain  | User scale gain.  | INT32  | RW  | 0x00010000 (65536dec)  | |
0830:13  | Limit 1  | First limit value for setting the status bits  | INT16  | RW  | 0x0000 (0dec)  | |
0830:14  | Limit 2  | Second limit value for setting the status bits  | INT16  | RW  | 0x0000 (0dec)  | |
0830:17  | User Calibration Offset  | User calibration: Offset  | INT16  | RW  | 0x0000 (0dec)  | |
0830:18  | User Calibration Gain  | User calibration: Gain  | INT16  | RW  | 0x4000 (16384dec)  | |
Index 083E ADC raw value
083E:01  | ADC raw value  | Raw value of the analog/digital converter  | INT16  | RO  | 0x0000 (0dec)  |
Index 083F Al vendor data Ch4
083F:0  | Al Vendor data Ch4  | Maximum subindex  |
  | RO  | 0x0C (12dec)  |
083F:01  | R0 offset  | Offset (vendor calibration)  | INT16  | RW  | 0x0000 (0dec)  |
083F:02  | R0 gain  | Gain (vendor calibration)  | INT16  | RW  | 0x4000 (16384dec)  |
083F:03  | R1 offset  | Offset (vendor calibration)  | INT16  | RW  | 0x0000 (0dec)  |
083F:04  | R1 gain  | Gain (vendor calibration)  | INT16  | RW  | 0x4000 (16384dec)  |
083F:05  | R2 offset  | Offset (vendor calibration)  | INT16  | RW  | 0x0000 (0dec)  |
083F:06  | R2 gain  | Gain (vendor calibration)  | INT16  | RW  | 0x4000 (16384dec)  |
Index 0A00 diagnostics
0A00:0  | Diagnostics  | Maximum subindex  |
  | RO  | 0x02 (2dec)  |
0A00:01  | Overtemperature  | Overheating of the IO-Link module  | BOOLEAN  | RW  | 0x00 (0dec)  |
0A00:02  | Short detected  | Short circuit on the IO-Link C/Q data line  | BOOLEAN  | RW  | 0x00 (0dec)  |
0A00:03  | L+ low  | Power supply voltage too low (< 18 V)  | BOOLEAN  | RW  | 0x00 (0dec)  |
0A00:04  | 2L+ low 1)  | The supply voltage P24 is too low (< 18 V)  | BOOLEAN  | RW  | 0x00 (0dec)  |
0A00:05  | 2L+ stat 1)  | The supply voltage P24 is not available (< 8 V)  | BOOLEAN  | RW  | 0x00 (0dec)  |
0A00:06 -   | Reserved  | -  | BOOLEAN  | RW  | 0x00 (0dec)  |
1) „2L+“ was the original name for „P24” in the IO-Link specification.
Index 3800 Al range settings
3800:0  | Al Range Settings  | Maximum subindex  |
  | RW  | 0x0A (10dec)  |
3800:01  | Input type Ch1  | Input signal range for channel 1 0: -10 V...+10 V 1: 0 mA…20 mA 2: 4 mA…20 mA 3: 0 V…10 V  | UINT16  | RW  | 0x0000 (0dec)  |
3800:02  | Input type Ch2  | Input signal range for channel 2 (values see channel 1)  | UINT16  | RW  | 0x0000 (0dec)  |
3800:03  | Input type Ch3  | Input signal range for channel 3 (values see channel 1)  | UINT16  | RW  | 0x0000 (0dec)  |
3800:04  | Input type Ch4  | Input signal range for channel 4 (values see channel 1)  | UINT16  | RW  | 0x0000 (0dec)  |