Calibration and scaling
The signal path contains three functions for calibrating and scaling the measured values:
- Vendor calibration
- User calibration
- User scale
Vendor calibration
Notice | |
Increased measurement uncertainty when disabled If you disable the vendor calibration, the measurement uncertainty specified in the technical data is no longer guaranteed. |
The vendor calibration is enabled in the factory setting. You can disable it via the parameter 0x80A0:0B "Enable vendor calibration".
The coefficients of the vendor calibration cannot be adjusted. You can view them in the following parameters:
- Offset: 0x80AF:01
- Gain: 0x80AF:02
User calibration
Notice | |
The user calibration affects the measuring range monitoring. Incorrect calibration coefficients can lead to the status bits and status LEDs no longer behaving as expected. |
The user calibration is disabled in the factory setting. It can be enabled via the parameter 0x80A0:0A “Enable user calibration”.
If you use the user calibration, it may be useful to disable the vendor calibration.
You can set the coefficients of the user calibration in the following parameters:
- Offset: 0x80A0:17
- Gain: 0x80A0:18.
User scale
The user scale is disabled in the factory setting. It can be enabled via index 0x80A0:01 "Enable user scale".
You can set the coefficients of the user scale in the following parameters:
- Offset: 0x80A0:11
- Gain: 0x80A0:12
Summary
Calibration / scaling | Status | Correction function | Meaning |
Vendor calibration
| enabled (default): | YH = (XADC – BH) x AH x 2-14 | YH: Measured value after the vendor calibration BH: Offset vendor calibration (0x80AF:01) AH: Gain vendor calibration (0x80AF:02) |
Disabled: | YH = XADC | ||
User calibration
| enabled: | YA = (YH – BA) x AA x 2-14 | YA: Measured value after vendor and user calibration BA: Offset user calibration (0x80A0:17) AA: Gain user calibration (0x80A0:18) |
Disabled (default): | YA = YH | ||
User scale
| enabled: | YS= YA x AS x 2-16 + BS | YS: Measured value after user scale BS: Offset user scale (0x80A0:11) AS: Gain user scale (0x80A0:12) |
Disabled (default): | YS= YA |