Limit value monitoring (Limit)
For the analog input, two limit values can be defined: "Limit 1" and "Limit 2". For each limit value, a variable of the same name in the process data indicates whether the current measured value is above or below the limit value.
Enabling limit value monitoring
In the factory setting, the limit value monitoring is disabled. To enable limit value monitoring, set the following parameters to TRUE
- 0x80A0:07 "Enable Limit 1"
- 0x80A0:08. "Enable Limit 2"
Definition of limit values
You can define the limit values in the following parameters:
- 0x80A0:13 "Limit 1"
- 0x80A0:14 "Limit 2"
Enter the limit values as signed integers in these parameters. Example: Formula for positive voltage limit values:
Inverting the limit value monitoring
You can invert the limit function by setting the parameter 0x80A0:0E "Swap limit bits" to TRUE.
Evaluation
If the limit values are exceeded or not reached, the values of the status bits Limit 1 and Limit 2 are set accordingly in the process data:
„Swap Limit“ = FALSE (Default) | „Swap Limit“ = TRUE |
![]() | Linking "Limit" in TwinCAT The process data values "Limit1" and "Limit2" are two bits each. There is no suitable data type in the PLC that is also two bits in size.
Example:
Specification: | |||
Presentation | Swap Limit | Limit 1 | Limit 2 |
Signed integer | FALSE (Default) | "Enable Limit 1" = TRUE | "Enable Limit 2" = TRUE |
"Limit 1" = 2.8 V Input "Limit 1" 0x80A0:13 | "Limit 2" = 7.4 V, Input "Limit 1" 0x80A0:14 | ||
Output: | ||
Input value | "Limit 1" (0x60A0:03) | "Limit 2" (0x60A0:05) |
1.8 V | 0x01hex, (limit value undershot) | 0x01hex, (limit value undershot) |
2.8 V | 0x03hex, (limit value reached) | 0x01hex, (limit value undershot) |
4.2 V | 0x02hex, (limit value exceeded) | 0x01hex, (limit value undershot) |
8.5 V | 0x02hex, (limit value exceeded) | 0x02hex, (limit value exceeded) |