Configuration data
Index 8000 ENC Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8000:0
ENC Settings Ch.1
Max. Subindex
UINT8
RO
0x0E (14dec)
8000:08
Disable filter
0: Activates the input filter (inputs A, /A, B, /B, C, /C only)
1: Deactivates the input filter
If a filter is activated a signal edge must be present for at least 2.4 µs in order to be counted as an increment.
BOOLEAN
RW
0x00 (0dec)
8000:0A
Enable micro increments
If activated, the terminal interpolates micro-increments between the integral encoder increments in DC mode. The lower 8 bits of the counter value are used in each case for the display.
A 32-bit counter thus becomes a 24 +8 bit counter,
a 16-bit counter becomes a 8 +8 bit counter.
BOOLEAN
RW
0x00 (0dec)
8000:0E
Reversion of rotation
Activates reversion of rotation
BOOLEAN
RW
0x00 (0dec)
Index 8010 ENC Settings Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8010:0
ENC Settings Ch.2
Max. Subindex
UINT8
RO
0x0E (14dec)
8010:08
Disable filter
BOOLEAN
RW
0x00 (0dec)
8010:0A
a 16-bit counter becomes a 8 + 8 bit counter.
BOOLEAN
RW
0x00 (0dec)
8010:0E
BOOLEAN
RW
0x00 (0dec)
Index 8020 DCM Motor Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8020:0
Max. Subindex
UINT8
RO
0x0F (15dec)
8020:01
Maximal current
Maximum permanent motor coil current
(unit: 1 mA)
UINT16
RW
0x1388 (5000dec)
8020:02
Nominal current
Motor nominal current
(unit: 1 mA)
UINT16
RW
0x0DAC (3500dec)
8020:03
Nominal voltage
Nominal voltage (supply voltage) of the motor
(unit: 1 mV)
UINT16
RW
0xC350 (50000dec)
8020:04
Motor coil resistance
Internal resistance of the motor
(unit: 0.01 ohm)
UINT16
RW
0x0064 (100dec)
8020:05
Reduced current (positive)
Reduced torque in positive direction of rotation
(unit: 1 mA)
UINT16
RW
0x07D0 (2000dec)
8020:06
Reduced current (negative)
Reduced torque in negative direction of rotation
(unit: 1 mA)
UINT16
RW
0x07D0 (2000dec)
8020:07
Encoder increments (4-fold)
Number of encoder increments per revolution with quadruple evaluation
UINT16
RW
0x0000 (0dec)
8020:08
Maximal motor velocity
Nominal speed of the motor at the nominal voltage
(unit: 1 rpm)
UINT16
RW
0x0000 (0dec)
8020:0C
Time for switch-off at overload
(unit: 1 ms)
UINT16
RW
0x00C8 (200dec)
8020:0D
Time for current lowering at overload
Time for current lowering at overload (from max. current to nominal current,
unit: 1 ms)
UINT16
RW
0x07D0 (2000dec)
8020:0E
Torque auto-reduction threshold (positive)
Process data threshold for automatic torque reduction in the positive direction of rotation
(unit: 1 %)
UINT8
RW
0x00 (0dec)
8020:0F
Torque auto-reduction threshold (negative)
Process data threshold for automatic torque reduction in the negative direction of rotation
(unit: 1 %)
UINT8
RW
0x00 (0dec)
Index 8021 DCM Controller Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8021:0
Max. Subindex
UINT8
RO
0x12 (18dec)
8021:01
Kp factor (curr.)
Kp control factor of the current controller
UINT16
RW
0x00C8 (200dec)
8021:02
Ki factor (curr.)
Ki control factor of the current controller
UINT16
RW
0x0002 (2dec)
8021:03
Inner window (curr.)
Inner window for the I component
(unit: 1%)
UINT8
RW
0x00 (0dec)
8021:05
Outer window (curr.)
Outer window for the I component
(unit: 1%)
UINT8
RW
0x00 (0dec)
8021:06
Filter cut off frequency (curr.)
Limit frequency of the current controller
(unit: 1 Hz)
UINT16
RW
0x0000 (0dec)
8021:11
Voltage adjustment enable
Activates the compensation of voltage fluctuations (only in the operating mode "Direct velocity")
BOOLEAN
RW
0x00 (0dec)
8021:12
Current adjustment enable
Activates the R x I compensation
BOOLEAN
RW
0x00 (0dec)
Index 8022 DCM Features Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8022:0
DCM Features Ch.1
Max. Subindex
UINT8
RO
0x36 (54dec)
8022:01
Operation mode
Operation mode
0: Automatic
1: Velocity direct
2: Velocity controller
3: Position controller
...: reserved
15: Chopper resistor
Existing overvoltage (10 % > nominal voltage 0x8020:03) is reduced via connected chopper resistor.
BIT4
RW
0x00 (0dec)
8022:09
Invert motor polarity
Inverts the direction of rotation of the motor
BOOLEAN
RW
0x00 (0dec)
8022:0A
Torque error enable
Activates the automatic overload cut-off (see also subindex 0x8020:0C)
BOOLEAN
RW
0x00 (0dec)
8022:0B
Torque auto reduce
Activates the automatic torque reduction (see also subindex 0x8020:0D - 0x8020:0F)
BOOLEAN
RW
0x00 (0dec)
8022:11
Select info data 1
Selection "Info data 1"
0: Status word
1: Motor coil voltage
2: Motor coil current
3: Current limit
4: Control error
5: Duty cycle
....: reserved
7: Motor velocity
8: Overload time
...: reserved
101: Internal temperature
...: reserved
103: Control voltage
104: Motor supply voltage
...: reserved
150: Status word (drive controller)
151: State (drive controller)
...: reserved
UINT8
RW
0x01 (1dec)
8022:19
Select info data 2
Selection "Info data 2"
see subindex 0x8022:11
UINT8
RW
0x02 (2dec)
8022:30
Invert digital input 1
Inversion of digital input 1
BOOLEAN
RW
0x00 (0dec)
8022:31
Invert digital input 2
Inversion of digital input 2
BOOLEAN
RW
0x00 (0dec)
8022:32
Function for input 1
Function of digital input 1
0: Normal input
1: Hardware enable
…: reserved
BIT4
RW
0x00 (0dec)
8022:36
Function for input 2
Function of digital input 2
see subindex 0x8022:32
BIT4
RW
0x00 (0dec)
Index 8023 DCM Controller Settings 2 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8023:0
Max. Subindex
UINT8
RO
0x08 (8dec)
8023:01
Kp factor (velo./pos.)
Kp control factor of the velocity/position controller
UINT16
RW
0x00C8 (200dec)
8023:02
Ki factor (velo./pos.)
Ki control factor of the velocity/position controller
UINT16
RW
0x0002 (2dec)
8023:03
Inner window (velo./pos.)
(unit: 1%)
UINT8
RW
0x00 (0dec)
8023:05
Outer window (velo./pos.)
(unit: 1%)
UINT8
RW
0x00 (0dec)
8023:06
Filter cut off frequency (velo./pos.)
Limit frequency of the velocity/position controller
(unit: 1 Hz)
UINT16
RW
0x0000 (0dec)
8023:07
Ka factor (velo./pos.)
Ka control factor of the velocity/position controller
UINT16
RW
0x0000 (0dec)
8023:08
Kd factor (velo./pos.)
Kd control factor of the velocity/position controller
UINT16
RW
0x0014 (20dec)
Index 8030 DCM Motor Settings Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8030:0
Max. Subindex
UINT8
RO
0x0F (15dec)
8030:01
Maximal current
(unit: 1 mA)
UINT16
RW
0x1388 (5000dec)
8030:02
Nominal current
(unit: 1 mA)
UINT16
RW
0x0DAC (3500dec)
8030:03
Nominal voltage
(unit: 1 mV)
UINT16
RW
0xC350 (50000dec)
8030:04
(unit: 0.01 ohm)
UINT16
RW
0x0064 (100dec)
8030:05
(unit: 1 mA)
UINT16
RW
0x07D0 (2000dec)
8030:06
(unit: 1 mA)
UINT16
RW
0x07D0 (2000dec)
8030:07
UINT16
RW
0x0000 (0dec)
8030:08
Rated motor velocity at nominal voltage
(unit: 1 rpm)
UINT16
RW
0x0000 (0dec)
8030:0C
(unit: 1 ms)
UINT16
RW
0x00C8 (200dec)
8030:0D
unit: 1 ms)
UINT16
RW
0x07D0 (2000dec)
8030:0E
(unit: 1 %)
UINT8
RW
0x00 (0dec)
8030:0F
(unit: 1 %)
UINT8
RW
0x00 (0dec)
Index 8031 DCM Controller Settings Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8031:0
Max. Subindex
UINT8
RO
0x12 (18dec)
8031:01
Kp factor (curr.)
UINT16
RW
0x00C8 (200dec)
8031:02
Ki factor (curr.)
UINT16
RW
0x0002 (2dec)
8031:03
(unit: 1%)
UINT8
RW
0x00 (0dec)
8031:05
(unit: 1%)
UINT8
RW
0x00 (0dec)
8031:06
(unit: 1 Hz)
UINT16
RW
0x0000 (0dec)
8031:11
BOOLEAN
RW
0x00 (0dec)
8031:12
BOOLEAN
RW
0x00 (0dec)
Index 8032 DCM Features Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8032:0
DCM Features Ch.2
Max. Subindex
UINT8
RO
0x36 (54dec)
8032:01
Operation mode
Operation mode
0: Automatic
1: Velocity direct
...: reserved
Existing overvoltage (10% > nominal voltage 0x8030:03) is reduced via connected chopper resistor.
BIT4
RW
0x00 (0dec)
8032:09
BOOLEAN
RW
0x00 (0dec)
8032:0A
Torque error enable
Activates the automatic overload cut-off (see also subindex 0x8030:0C)
BOOLEAN
RW
0x00 (0dec)
8032:0B
Torque auto reduce
Activates the automatic torque reduction (see also subindex 0x8030:0D – 0x8030:0F)
BOOLEAN
RW
0x00 (0dec)
8032:11
Select info data 1
0: Status word
3: Current limit
4: Control error
5: Duty cycle
....: reserved
7: Motor velocity
8: Overload time
...: reserved
...: reserved
...: reserved
...: reserved
UINT8
RW
0x01 (1dec)
8032:19
Select info data 2
see subindex 0x8032:11
UINT8
RW
0x02 (2dec)
8032:30
BOOLEAN
RW
0x00 (0dec)
8032:31
BOOLEAN
RW
0x00 (0dec)
8032:32
0: Normal input
1: Hardware enable
...: reserved
BIT4
RW
0x00 (0dec)
8032:36
see subindex 0x8032:32
BIT4
RW
0x00 (0dec)
Index 8033 DCM Controller Settings 2 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8033:0
Max. Subindex
UINT8
RO
0x08 (8dec)
8033:01
UINT16
RW
0x00C8 (200dec)
8033:02
UINT16
RW
0x0002 (2dec)
8033:03
(unit: 1%)
UINT8
RW
0x00 (0dec)
8033:05
(unit: 1%)
UINT8
RW
0x00 (0dec)
8033:06
(unit: 1 Hz)
UINT16
RW
0x0000 (0dec)
8033:07
UINT16
RW
0x0000 (0dec)
8033:08
UINT16
RW
0x0014(20dec)
Index 8040 POS Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8040:0
POS Settings Ch.1
Max. Subindex
UINT8
RO
0x10 (16dec)
8040:01
Velocity min.
Minimum set velocity
(range: 0-10000)
INT16
RW
0x0064 (100dec)
8040:02
Velocity max.
Maximum set velocity
(range: 0-10000)
INT16
RW
0x2710 (10000dec)
8040:03
Acceleration pos.
Acceleration time in positive direction of rotation
(unit: 1 ms)
UINT16
RW
0x03E8 (1000dec)
8040:04
Acceleration neg.
Acceleration time in negative direction of rotation
(unit: 1 ms)
UINT16
RW
0x03E8 (1000dec)
8040:05
Deceleration pos.
Deceleration time in positive direction of rotation
(unit: 1 ms)
UINT16
RW
0x03E8 (1000dec)
8040:06
Deceleration neg.
Deceleration time in negative direction of rotation
(unit: 1 ms)
UINT16
RW
0x03E8 (1000dec)
8040:07
Emergency deceleration
Emergency deceleration time (both directions of rotation,
unit: 1 ms)
UINT16
RW
0x0064 (100dec)
8040:08
Calibration position
UINT32
RW
0x00000000 (0dec)
8040:09
Calibration velocity (towards plc cam)
Calibration velocity towards the cam
(range: 0-10000)
INT16
RW
0x03E8 (1000dec)
8040:0A
Calibration Velocity (off plc cam)
Calibration velocity away from the cam
(range: 0-10000)
INT16
RW
0x0064 (100dec)
8040:0B
Target window
Target window
UINT16
RW
0x000A (10dec)
8040:0C
In-Target timeout
Timeout at target position
(unit: 1 ms)
UINT16
RW
0x03E8 (1000dec)
8040:0D
Dead time compensation
(unit: 1 µs)
INT16
RW
0x0064 (100dec)
8040:0E
Modulo factor
Modulo factor/position
UINT32
RW
0x00000000 (0dec)
8040:0F
Modulo tolerance window
Tolerance window for modulo positioning
UINT32
RW
0x00000000 (0dec)
8040:10
Position lag max.
Max. permitted position lag
UINT16
RW
0x0000 (0dec)
Index 8041 POS Features Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8041:0
POS Features Ch.1
UINT8
RO
0x16 (22dec)
8041:01
Start type
Standard start type
UINT16
RW
0x0001 (1dec)
8041:11
Time information
Time information in subindex 0x6pp0: 22 (“Actual drive time”)
0: Elapsed time
current drive time since start of the travel command
...: reserved
BIT2
RW
0x00 (0dec)
8041:13
Invert calibration cam search direction
Inversion of the direction of rotation towards the cam
BOOLEAN
RW
0x01 (1dec)
8041:14
Invert sync impulse search direction
Inversion of the direction of rotation away from the cam
BOOLEAN
RW
0x00 (0dec)
8041:15
Emergency stop on position lag error
- Lag error monitoring has triggered
- an emergency stop is triggered as soon as "Position lag" = 1.
The "Misc Error" is set to 1 and a PDO error is generated.
BOOLEAN
RW
0x00 (0dec)
8041:16
Enhanced diag history
TRUE:
Additional messages are output during the travel command (each change of the state machine (index 0x9040:03))
BOOLEAN
RW
0x00 (0dec)
Index 8050 POS Settings Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8050:0
POS Settings Ch.2
Max. Subindex
UINT8
RO
0x10 (16dec)
8050:01
Velocity min.
(range: 0-10000)
INT16
RW
0x0064 (100dec)
8050:02
Velocity max.
(range: 0-10000)
INT16
RW
0x2710 (10000dec)
8050:03
Acceleration pos.
(unit: 1 ms)
UINT16
RW
0x03E8 (1000dec)
8050:04
Acceleration neg.
(unit: 1 ms)
UINT16
RW
0x03E8 (1000dec)
8050:05
Deceleration pos.
(unit: 1 ms)
UINT16
RW
0x03E8 (1000dec)
8050:06
Deceleration neg.
(unit: 1 ms)
UINT16
RW
0x03E8 (1000dec)
8050:07
Emergency Deceleration
unit: 1 ms)
UINT16
RW
0x0064 (100dec)
8050:08
UINT32
RW
0x00000000 (0dec)
8050:09
(range: 0-10000)
INT16
RW
0x03E8 (1000dec)
8050:0A
(range: 0-10000)
INT16
RW
0x0064 (100dec)
8050:0B
Target window
Target window
UINT16
RW
0x000A (10dec)
8050:0C
In-Target timeout
(unit: 1 ms)
UINT16
RW
0x03E8 (1000dec)
8050:0D
(unit: 1 µs)
INT16
RW
0x0064 (100dec)
8050:0E
Modulo factor
UINT32
RW
0x00000000 (0dec)
8050:0F
UINT32
RW
0x00000000 (0dec)
8050:10
Position lag max.
UINT16
RW
0x0000 (0dec)
Index 8051 POS Features Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8051:0
POS Features Ch.2
Max. Subindex
UINT8
RO
0x16 (22dec)
8051:01
Start type
Standard start type
UINT16
RW
0x0001 (1dec)
8051:11
Time information
0: Elapsed time
...: reserved
BIT2
RW
0x00 (0dec)
8051:13
BOOLEAN
RW
0x01 (1dec)
8051:14
BOOLEAN
RW
0x00 (0dec)
8051:15
  • Lag error monitoring has triggered
  • an emergency stop is triggered as soon as "Position lag" = 1.
BOOLEAN
RW
0x00 (0dec)
8051:16
TRUE:
Additional messages are output during the travel command (each change of the state machine (index 0x9050:03))
BOOLEAN
RW
0x00 (0dec)