Standard objects (0x1000 .. 0x1FFF)
The standard objects have the same meaning for all EtherCAT slaves.
Index 1000 Device type
1000:0 | Device type | Device type of the EtherCAT slave: The Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile. | UINT32 | RO | 0x00001389 (5001dec) |
Index 1008 Device name
1008:0 | Device name | Device name of the EtherCAT slave | STRING | RO | EP7041-3002 |
Index 1009 Hardware version
1009:0 | Hardware version | Hardware version of the EtherCAT slave | STRING | RO | 00 |
Index 100A Software version
100A:0 | Software version | Firmware version of the EtherCAT slave | STRING | RO | 02 |
Index 1018 Identity
1018:0 | Identity | Information for identifying the slave | UINT8 | RO | 0x04 (4dec) |
1018:01 | Vendor ID | Vendor ID of the EtherCAT slave | UINT32 | RO | 0x00000002 (2dec) |
1018:02 | Product code | Product code of the EtherCAT slave | UINT32 | RO | 0x1B814052 (461455442dec) |
1018:03 | Revision | Revision number of the EtherCAT slave; the low word (bit 0-15) indicates the special terminal number, the high word (bit 16-31) refers to the device description | UINT32 | RO | 0x00100BBA (1051578dec) |
1018:04 | Serial number | Serial number of the EtherCAT slave; the low byte (bit 0-7) of the low word contains the year of production, the high byte (bit 8-15) of the low word contains the week of production, the high word (bit 16-31) is 0 | UINT32 | RO | 0x00000000 (0dec) |
10F0:0 | Backup parameter handling | Information for standardized loading and saving of backup entries | UINT8 | RO | 0x01 (1dec) |
10F0:01 | Checksum | Checksum across all backup entries of the EtherCAT slave | UINT32 | RO | 0x00000000 (0dec) |
Index 10F3 Diagnosis History
10F3:0 | Diagnosis History | Maximum Subindex | UINT8 | RO | 0x37 (55dec) |
10F3:01 | Maximum Messages | Maximum number of stored messages. A maximum of 50 messages can be stored. | UINT8 | RO | 0x00 (0dec) |
10F3:02 | Newest Message | Subindex of the latest message | UINT8 | RO | 0x00 (0dec) |
10F3:03 | Newest Acknowledged Message | Subindex of the last confirmed message | UINT8 | RW | 0x00 (0dec) |
10F3:04 | New Messages Available | Indicates that a new message is available | BOOLEAN | RO | 0x00 (0dec) |
10F3:05 | Flags | not used | UINT16 | RW | 0x0000 (0dec) |
10F3:06 | Diagnosis Message 001 | Message 1 | OCTET-STRING[28] | RO | {0} |
10F3:37 | Diagnosis Message 050 | Message 50 | OCTET-STRING[28] | RO | {0} |
Index 10F8 Actual Time Stamp
10F8:0 | Actual Time Stamp | Time stamp | UINT64 | RO |
Index 1400 ENC RxPDO-Par Control compact
1400:0 | ENC RxPDO-Par Control compact | PDO Parameter RxPDO 1 | UINT8 | RO | 0x06 (6dec) |
1400:06 | Exclude RxPDOs | Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 1 | OCTET-STRING[6] | RO | 01 16 00 00 00 00 |
Index 1401 ENC RxPDO-Par Control
1401:0 | ENC RxPDO-Par Control | PDO Parameter RxPDO 2 | UINT8 | RO | 0x06 (6dec) |
1401:06 | Exclude RxPDOs | Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 2 | OCTET-STRING[6] | RO | 00 16 00 00 00 00 |
Index 1403 STM RxPDO-Par Position
1403:0 | STM RxPDO-Par Position | PDO Parameter RxPDO 4 | UINT8 | RO | 0x06 (6dec) |
1403:06 | Exclude RxPDOs | Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 4 | OCTET-STRING[6] | RO | 04 16 05 16 06 16 |
Index 1404 STM RxPDO-Par Velocity
1404:0 | STM RxPDO-Par Velocity | PDO Parameter RxPDO 5 | UINT8 | RO | 0x06 (6dec) |
1404:06 | Exclude RxPDOs | Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 5 | OCTET-STRING[6] | RO | 03 16 05 16 06 16 |
Index 1405 POS RxPDO-Par Control compact
1405:0 | POS RxPDO-Par Control compact | PDO Parameter RxPDO 6 | UINT8 | RO | 0x06 (6dec) |
1405:06 | Exclude RxPDOs | Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 6 | OCTET-STRING[6] | RO | 03 16 04 16 06 16 |
Index 1406 POS RxPDO-Par Control
1406:0 | POS RxPDO-Par Control | PDO Parameter RxPDO 7 | UINT8 | RO | 0x06 (6dec) |
1406:06 | Exclude RxPDOs | Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 7 | OCTET-STRING[6] | RO | 03 16 04 16 05 16 |
Index 1407 POS RxPDO-Par Control 2
1407:0 | POS RxPDO-Par Control | PDO Parameter RxPDO 8 | UINT8 | RO | 0x06 (6dez) |
1407:06 | Exclude RxPDOs | Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 8 | OCTET-STRING[6] | RO | 03 16 04 16 05 16 |
Index 1600 ENC RxPDO-Map Control compact
1600:0 | ENC RxPDO-Map Control compact | PDO Mapping RxPDO 1 | UINT8 | RO | 0x07 (7dec) |
1600:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x7000 (ENC Outputs Ch.1), entry 0x01 (Enable latch C)) | UINT32 | RO | 0x7000:01, 1 |
1600:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x7000 (ENC Outputs Ch.1), entry 0x02 (Enable latch extern on positive edge)) | UINT32 | RO | 0x7000:02, 1 |
1600:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x7000 (ENC Outputs Ch.1), entry 0x03 (Set counter)) | UINT32 | RO | 0x7000:03, 1 |
1600:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x7000 (ENC Outputs Ch.1), entry 0x04 (Enable latch extern on negative edge)) | UINT32 | RO | 0x7000:04, 1 |
1600:05 | SubIndex 005 | 5. PDO Mapping entry (4 bits align) | UINT32 | RO | 0x0000:00, 4 |
1600:06 | SubIndex 006 | 6. PDO Mapping entry (8 bits align) | UINT32 | RO | 0x0000:00, 8 |
1600:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x7000 (ENC Outputs Ch.1), entry 0x11 (Set counter value)) | UINT32 | RO | 0x7000:11, 16 |
Index 1601 ENC RxPDO-Map Control
1601:0 | ENC RxPDO-Map Control | PDO Mapping RxPDO 2 | UINT8 | RO | 0x07 (7dec) |
1601:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x7000 (ENC Outputs Ch.1), entry 0x01 (Enable latch C)) | UINT32 | RO | 0x7000:01, 1 |
1601:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x7000 (ENC Outputs Ch.1), entry 0x02 (Enable latch extern on positive edge)) | UINT32 | RO | 0x7000:02, 1 |
1601:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x7000 (ENC Outputs Ch.1), entry 0x03 (Set counter)) | UINT32 | RO | 0x7000:03, 1 |
1601:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x7000 (ENC Outputs Ch.1), entry 0x04 (Enable latch extern on negative edge)) | UINT32 | RO | 0x7000:04, 1 |
1601:05 | SubIndex 005 | 5. PDO Mapping entry (4 bits align) | UINT32 | RO | 0x0000:00, 4 |
1601:06 | SubIndex 006 | 6. PDO Mapping entry (8 bits align) | UINT32 | RO | 0x0000:00, 8 |
1601:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x7000 (ENC Outputs Ch.1), entry 0x11 (Set counter value)) | UINT32 | RO | 0x7000:11, 32 |
Index 1602 STM RxPDO-Map Control
1602:0 | STM RxPDO-Map Control | PDO Mapping RxPDO 3 | UINT8 | RO | 0x07 (7dec) |
1602:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x7010 (STM Outputs Ch.1), entry 0x01 (Enable)) | UINT32 | RO | 0x7010:01, 1 |
1602:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x7010 (STM Outputs Ch.1), entry 0x02 (Reset)) | UINT32 | RO | 0x7010:02, 1 |
1602:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x7010 (STM Outputs Ch.1), entry 0x03 (Reduce torque)) | UINT32 | RO | 0x7010:03, 1 |
1602:04 | SubIndex 004 | 4. PDO Mapping entry (5 bits align) | UINT32 | RO | 0x0000:00, 5 |
1602:05 | SubIndex 005 | 5. PDO Mapping entry (3 bits align) | UINT32 | RO | 0x0000:00, 3 |
1602:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x7010 (STM Outputs Ch.1), entry 0x0C (Digital output 1)) | UINT32 | RO | 0x7010:0C, 1 |
1602:07 | SubIndex 007 | 7. PDO Mapping entry (4 bits align) | UINT32 | RO | 0x0000:00, 4 |
Index 1603 STM RxPDO-Map Position
1603:0 | STM RxPDO-Map Position | PDO Mapping RxPDO 4 | UINT8 | RO | 0x01 (1dec) |
1603:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x7010 (STM Outputs Ch.1), entry 0x11 (Position)) | UINT32 | RO | 0x7010:11, 32 |
Index 1604 STM RxPDO-Map Velocity
1604:0 | STM RxPDO-Map Velocity | PDO Mapping RxPDO 5 | UINT8 | RO | 0x01 (1dec) |
1604:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x7010 (STM Outputs Ch.1), entry 0x21 (Velocity)) | UINT32 | RO | 0x7010:21, 16 |
Index 1605 POS RxPDO-Map Control compact
1605:0 | POS RxPDO-Map Control compact | PDO Mapping RxPDO 6 | UINT8 | RO | 0x05 (5dec) |
1605:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x7020 (POS Outputs Ch.1), entry 0x01 (Execute)) | UINT32 | RO | 0x7020:01, 1 |
1605:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x7020 (POS Outputs Ch.1), entry 0x02 (Emergency stop)) | UINT32 | RO | 0x7020:02, 1 |
1605:03 | SubIndex 003 | 3. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1605:04 | SubIndex 004 | 4. PDO Mapping entry (8 bits align) | UINT32 | RO | 0x0000:00, 8 |
1605:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x7020 (POS Outputs Ch.1), entry 0x11 (Target position)) | UINT32 | RO | 0x7020:11, 32 |
Index 1606 POS RxPDO-Map Control
1606:0 | POS RxPDO-Map Control | PDO Mapping RxPDO 7 | UINT8 | RO | 0x09 (9dec) |
1606:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x7020 (POS Outputs Ch.1), entry 0x01 (Execute)) | UINT32 | RO | 0x7020:01, 1 |
1606:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x7020 (POS Outputs Ch.1), entry 0x02 (Emergency stop)) | UINT32 | RO | 0x7020:02, 1 |
1606:03 | SubIndex 003 | 3. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1606:04 | SubIndex 004 | 4. PDO Mapping entry (8 bits align) | UINT32 | RO | 0x0000:00, 8 |
1606:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x7020 (POS Outputs Ch.1), entry 0x11 (Target position)) | UINT32 | RO | 0x7020:11, 32 |
1606:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x7020 (POS Outputs Ch.1), entry 0x21 (Velocity)) | UINT32 | RO | 0x7020:21, 16 |
1606:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x7020 (POS Outputs Ch.1), entry 0x22 (Start type)) | UINT32 | RO | 0x7020:22, 16 |
1606:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x7020 (POS Outputs Ch.1), entry 0x23 (Acceleration)) | UINT32 | RO | 0x7020:23, 16 |
1606:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x7020 (POS Outputs Ch.1), entry 0x24 (Deceleration)) | UINT32 | RO | 0x7020:24, 16 |
Index 1607 POS RxPDO-Map Control 2
1607:0 | POS RxPDO-Map Control 2 | PDO Mapping RxPDO 8 | UINT8 | RO | 0x09 (9dez) |
1607:01 | SubIndex 001 | 1. PDO Mapping entry | UINT32 | RO | 0x0000:00,2 |
1607:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x7020 (POS Outputs 2 Ch.1), entry 0x03 (Enable auto start)) | UINT32 | RO | 0x7020:03, 1 |
1607:03 | SubIndex 003 | 3. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00,5 |
1607:04 | SubIndex 004 | 4. PDO Mapping entry (8 bits align) | UINT32 | RO | 0x0000:00, 8 |
1607:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x7021 (POS Outputs 2 Ch.1), entry 0x11 (Target position)) | UINT32 | RO | 0x7021:11, 32 |
1607:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x7021 (POS Outputs 2 Ch.1), entry 0x21 (Velocity)) | UINT32 | RO | 0x7021:21, 16 |
1607:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x7021 (POS Outputs 2 Ch.1), entry 0x22 (Start type)) | UINT32 | RO | 0x7021:22, 16 |
1607:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x7021 (POS Outputs 2 Ch.1), entry 0x23 (Acceleration)) | UINT32 | RO | 0x7021:23, 16 |
1607:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x7021 (POS Outputs 2 Ch.1), entry 0x24 (Deceleration)) | UINT32 | RO | 0x7021:24, 16 |
Index 1800 ENC TxPDO-Par Status compact
1800:0 | ENC TxPDO-Par Status compact | PDO Parameter TxPDO 1 | UINT8 | RO | 0x06 (6dec) |
1800:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 1 | OCTET-STRING[2] | RO | 01 1A |
Index 1801 ENC TxPDO-Par Status
1801:0 | ENC TxPDO-Par Status | PDO Parameter TxPDO 2 | UINT8 | RO | 0x06 (6dec) |
1801:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 2 | OCTET-STRING[2] | RO | 00 1A |
Index 1806 POS TxPDO-Par Status compact
1806:0 | POS TxPDO-Par Status compact | PDO parameter TxPDO 7 | UINT8 | RO | 0x06 (6dec) |
1806:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 7 | OCTET-STRING[2] | RO | 07 1A |
Index 1807 POS TxPDO-Par Status
1807:0 | POS TxPDO-Par Status | PDO parameter TxPDO 8 | UINT8 | RO | 0x06 (6dec) |
1807:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 8 | OCTET-STRING[2] | RO | 06 1A |
Index 1A00 ENC TxPDO-Map Status compact
1A00:0 | ENC TxPDO-Map Status compact | PDO Mapping TxPDO 1 | UINT8 | RO | 0x11 (17dec) |
1A00:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x01 (Latch C valid)) | UINT32 | RO | 0x6000:01, 1 |
1A00:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x02 (Latch extern valid)) | UINT32 | RO | 0x6000:02, 1 |
1A00:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x03 (Set counter done)) | UINT32 | RO | 0x6000:03, 1 |
1A00:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x04 (Counter underflow)) | UINT32 | RO | 0x6000:04, 1 |
1A00:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x05 (Counter overflow)) | UINT32 | RO | 0x6000:05, 1 |
1A00:06 | SubIndex 006 | 6. PDO Mapping entry (2 bits align) | UINT32 | RO | 0x0000:00, 2 |
1A00:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x08 (Extrapolation stall)) | UINT32 | RO | 0x6000:08, 1 |
1A00:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x09 (Status of input A)) | UINT32 | RO | 0x6000:09, 1 |
1A00:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x0A (Status of input B)) | UINT32 | RO | 0x6000:0A, 1 |
1A00:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x0B (Status of input C)) | UINT32 | RO | 0x6000:0B, 1 |
1A00:0B | SubIndex 011 | 11. PDO Mapping entry (1 bits align) | UINT32 | RO | 0x0000:00, 1 |
1A00:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x0D (Status of extern latch)) | UINT32 | RO | 0x6000:0D, 1 |
1A00:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x1C32 (SM output parameter), entry 0x20 (Sync error)) | UINT32 | RO | 0x1C32:20, 1 |
1A00:0E | SubIndex 014 | 14. PDO Mapping entry (1 bits align) | UINT32 | RO | 0x0000:00, 1 |
1A00:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x1800 (ENC TxPDO-Par Status compact), entry 0x09) | UINT32 | RO | 0x1800:09, 1 |
1A00:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x11 (Counter value)) | UINT32 | RO | 0x6000:11, 16 |
1A00:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x12 (Latch value)) | UINT32 | RO | 0x6000:12, 16 |
Index 1A01 ENC TxPDO-Map Status
1A01:0 | ENC TxPDO-Map Status | PDO Mapping TxPDO 2 | UINT8 | RO | 0x11 (17dec) |
1A01:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x01 (Latch C valid)) | UINT32 | RO | 0x6000:01, 1 |
1A01:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x02 (Latch extern valid)) | UINT32 | RO | 0x6000:02, 1 |
1A01:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x03 (Set counter done)) | UINT32 | RO | 0x6000:03, 1 |
1A01:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x04 (Counter underflow)) | UINT32 | RO | 0x6000:04, 1 |
1A01:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x05 (Counter overflow)) | UINT32 | RO | 0x6000:05, 1 |
1A01:06 | SubIndex 006 | 6. PDO Mapping entry (2 bits align) | UINT32 | RO | 0x0000:00, 2 |
1A01:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x08 (Extrapolation stall)) | UINT32 | RO | 0x6000:08, 1 |
1A01:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x09 (Status of input A)) | UINT32 | RO | 0x6000:09, 1 |
1A01:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x0A (Status of input B)) | UINT32 | RO | 0x6000:0A, 1 |
1A01:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x0B (Status of input C)) | UINT32 | RO | 0x6000:0B, 1 |
1A01:0B | SubIndex 011 | 11. PDO Mapping entry (1 bits align) | UINT32 | RO | 0x0000:00, 1 |
1A01:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x0D (Status of extern latch)) | UINT32 | RO | 0x6000:0D, 1 |
1A01:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x1C32 (SM output parameter), entry 0x20 (Sync error)) | UINT32 | RO | 0x1C32:20, 1 |
1A01:0E | SubIndex 014 | 14. PDO Mapping entry (1 bits align) | UINT32 | RO | 0x0000:00, 1 |
1A01:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x1801 (ENC TxPDO-Par Status), entry 0x09) | UINT32 | RO | 0x1801:09, 1 |
1A01:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x11 (Counter value)) | UINT32 | RO | 0x6000:11, 32 |
1A01:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x12 (Latch value)) | UINT32 | RO | 0x6000:12, 32 |
Index 1A02 ENC TxPDO-Map Timest. compact
1A02:0 | ENC TxPDO-Map Timest. compact | PDO Mapping TxPDO 3 | UINT8 | RO | 0x01 (1dec) |
1A02:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6000 (ENC Inputs Ch.1), entry 0x16 (Timestamp)) | UINT32 | RO | 0x6000:16, 32 |
Index 1A03 STM TxPDO-Map Status
1A03:0 | STM TxPDO-Map Status | PDO Mapping TxPDO 4 | UINT8 | RO | 0x0E (14dec) |
1A03:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6010 (STM Inputs Ch.1), entry 0x01 (Ready to enable)) | UINT32 | RO | 0x6010:01, 1 |
1A03:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6010 (STM Inputs Ch.1), entry 0x02 (Ready)) | UINT32 | RO | 0x6010:02, 1 |
1A03:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6010 (STM Inputs Ch.1), entry 0x03 (Warning)) | UINT32 | RO | 0x6010:03, 1 |
1A03:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6010 (STM Inputs Ch.1), entry 0x04 (Error)) | UINT32 | RO | 0x6010:04, 1 |
1A03:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6010 (STM Inputs Ch.1), entry 0x05 (Moving positive)) | UINT32 | RO | 0x6010:05, 1 |
1A03:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6010 (STM Inputs Ch.1), entry 0x06 (Moving negative)) | UINT32 | RO | 0x6010:06, 1 |
1A03:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6010 (STM Inputs Ch.1), entry 0x07 (Torque reduced)) | UINT32 | RO | 0x6010:07, 1 |
1A03:08 | SubIndex 008 | 8. PDO Mapping entry (1 bits align) | UINT32 | RO | 0x6010:08, 1 |
1A03:09 | SubIndex 009 | 9. PDO Mapping entry (3 bits align) | UINT32 | RO | 0x0000:00, 3 |
1A03:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6010 (STM Inputs Ch.1), entry 0x0C (Digital input 1)) | UINT32 | RO | 0x6010:0C, 1 |
1A03:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6010 (STM Inputs Ch.1), entry 0x0D (Digital input 2)) | UINT32 | RO | 0x6010:0D, 1 |
1A03:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x1C32 (SM output parameter), entry 0x20 (Sync error)) | UINT32 | RO | 0x6010:0E, 1 |
1A03:0D | SubIndex 013 | 13. PDO Mapping entry (1 bits align) | UINT32 | RO | 0x0000:00, 1 |
1A03:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x1803, entry 0x09) | UINT32 | RO | 0x6010:10, 1 |
Index 1A04 STM TxPDO-Map Synchron info data
1A04:0 | STM TxPDO-Map Synchron info data | PDO Mapping TxPDO 5 | UINT8 | RO | 0x02 (2dec) |
1A04:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6010 (STM Inputs Ch.1), entry 0x11 (Info data 1)) | UINT32 | RO | 0x6010:11, 16 |
1A04:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6010 (STM Inputs Ch.1), entry 0x12 (Info data 2)) | UINT32 | RO | 0x6010:12, 16 |
Index 1A05 STM TxPDO-Map Motor load
1A05:0 | STM TxPDO-Map Motor load | PDO Mapping TxPDO 6 | UINT8 | RO | 0x01 (1dec) |
1A05:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x01 (Busy)) | UINT32 | RO | 0x6010:13, 16 |
Index 1A06 POS TxPDO-Map Status compact
1A06:0 | POS TxPDO-Map Status compact | PDO Mapping TxPDO 7 | UINT8 | RO | 0x09 (9dec) |
1A06:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x01 (Busy)) | UINT32 | RO | 0x6020:01, 1 |
1A06:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x02 (In-Target)) | UINT32 | RO | 0x6020:02, 1 |
1A06:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x03 (Warning)) | UINT32 | RO | 0x6020:03, 1 |
1A06:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x04 (Error)) | UINT32 | RO | 0x6020:04, 1 |
1A06:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x05 (Calibrated)) | UINT32 | RO | 0x6020:05, 1 |
1A06:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x06 (Accelerate)) | UINT32 | RO | 0x6020:06, 1 |
1A06:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x07 (Decelerate)) | UINT32 | RO | 0x6020:07, 1 |
1A06:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x08 (Ready to execute)) | UINT32 | RO | 0x6020:08, 1 |
1A06:09 | SubIndex 009 | 9. PDO Mapping entry (8 bits align) | UINT32 | RO | 0x0000:00, 8 |
Index 1A07 POS TxPDO-Map Status
1A07:0 | POS TxPDO-Map Status | PDO Mapping TxPDO 8 | UINT8 | RO | 0x0C (12dec) |
1A07:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x01 (Busy)) | UINT32 | RO | 0x6020:01, 1 |
1A07:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x02 (In-Target)) | UINT32 | RO | 0x6020:02, 1 |
1A07:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x03 (Warning)) | UINT32 | RO | 0x6020:03, 1 |
1A07:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x04 (Error)) | UINT32 | RO | 0x6020:04, 1 |
1A07:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x05 (Calibrated)) | UINT32 | RO | 0x6020:05, 1 |
1A07:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x06 (Accelerate)) | UINT32 | RO | 0x6020:06, 1 |
1A07:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x07 (Decelerate)) | UINT32 | RO | 0x6020:07, 1 |
1A07:08 | SubIndex 008 | 8. PDO Mapping entry (1 bits align) | UINT32 | RO | 0x0000:00, 1 |
1A07:09 | SubIndex 009 | 9. PDO Mapping entry (8 bits align) | UINT32 | RO | 0x0000:00, 8 |
1A07:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x11 (Actual position)) | UINT32 | RO | 0x6020:11, 32 |
1A07:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x21 (Actual velocity)) | UINT32 | RO | 0x6020:21, 16 |
1A07:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x6020 (POS Inputs Ch.1), entry 0x22 (Actual drive time)) | UINT32 | RO | 0x6020:22, 32 |
Index 1A08 STM TxPDO-Map Internal Position
1A08:0 | STM TxPDO-Map Internal Position | PDO Mapping TxPDO 9 | UINT8 | RO | 0x01 (1dec) |
1A08:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6010 (STM Inputs Ch. 1), entry 0x14 (Internal Position)) | UINT32 | RO | 0x6010:14, 32 |
Index 1A09 STM TxPDO-Map External Position
1A09:0 | STM TxPDO-Map External Position | PDO Mapping TxPDO 10 | UINT8 | RO | 0x01 (1dec) |
1A09:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6010 (STM Inputs Ch. 1), entry 0x15 (External Position)) | UINT32 | RO | 0x6010:15, 32 |
Index 1A0A POS TxPDO-Map Actual Position lag
1A0A:0 | POS TxPDO-Map Actual Position lag | PDO Mapping TxPDO 11 | UINT8 | RO | 0x01 (1dec) |
1A0A:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6010 (POS Inputs Ch. 1), entry 0x23 (Actual position lag)) | UINT32 | RO | 0x6020:23, 32 |
Index 1C00 Sync manager type
1C00:0 | Sync manager type | Benutzung der Sync Manager | UINT8 | RO | 0x04 (4dez) |
1C00:01 | SubIndex 001 | Sync-Manager Type Channel 1: Mailbox Write | UINT8 | RO | 0x01 (1dez) |
1C00:02 | SubIndex 002 | Sync-Manager Type Channel 2: Mailbox Read | UINT8 | RO | 0x02 (2dez) |
1C00:03 | SubIndex 003 | Sync-Manager Type Channel 3: Process Data Write (Outputs) | UINT8 | RO | 0x03 (3dez) |
1C00:04 | SubIndex 004 | Sync-Manager Type Channel 4: Process Data Read (Inputs) | UINT8 | RO | 0x04 (4dez) |
Index 1C12 RxPDO assign
1C12:0 | RxPDO assign | PDO Assign Outputs | UINT8 | RW | 0x03 (3dez) |
1C12:01 | Subindex 001 | 1. allocated RxPDO (contains the index of the associated RxPDO mapping object) | UINT16 | RW | 0x1600 (5632dez) |
1C12:02 | Subindex 002 | 2. allocated RxPDO (contains the index of the associated RxPDO mapping object) | UINT16 | RW | 0x1602 (5634dez) |
1C12:03 | Subindex 003 | 3. allocated RxPDO (contains the index of the associated RxPDO mapping object) | UINT16 | RW | 0x1604 (5636dez) |
Index 1C13 TxPDO assign
1C13:0 | TxPDO assign | PDO Assign Inputs | UINT8 | RW | 0x02 (2dec) |
1C13:01 | Subindex 001 | 1. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A00 (6656dec) |
1C13:02 | Subindex 002 | 2. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A03 (6659dec) |
1C13:03 | Subindex 003 | 3. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x0000 (0dec) |
1C13:04 | Subindex 004 | 4. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x0000 (0dec) |
1C13:05 | Subindex 005 | 5. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x0000 (0dec) |
1C13:06 | Subindex 006 | 6. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x0000 (0dec) |
1C13:07 | Subindex 007 | 7. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x0000 (0dec) |
1C13:08 | Subindex 008 | 8. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x0000 (0dec) |
1C13:09 | Subindex 009 | 9. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x0000 (0dec) |
1C32:0 | SM output parameter | Synchronization parameters for the outputs | UINT8 | RO | 0x20 (32dec) |
1C32:01 | Sync mode | Current synchronization mode:
| UINT16 | RW | 0x0001 (1dec) |
1C32:02 | Cycle time | Cycle time (in ns):
| UINT32 | RW | 0x000F4240 (1000000dec) |
1C32:03 | Shift time | Time between SYNC0 event and output of the outputs (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C32:04 | Sync modes supported | Supported synchronization modes:
| UINT16 | RO | 0xC007 (49159dec) |
1C32:05 | Minimum cycle time | Minimum cycle time (in ns) | UINT32 | RO | 0x0003D090 (250000dec) |
1C32:06 | Calc and copy time | Minimum time between SYNC0 and SYNC1 event (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C32:07 | Minimum delay time |
1C32:08 | Command |
The entries 0x1C32:03, 0x1C32:05, 0x1C32:06, 0x1C32:09, 0x1C33:03, 0x1C33:06, 0x1C33:09 are updated with the maximum measured values. | UINT16 | RW | 0x0000 (0dec) |
1C32:09 | Maximum delay time | Time between SYNC1 event and output of the outputs (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C32:0B | SM event missed counter | Number of missed SM events in OPERATIONAL (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C32:0C | Cycle exceeded counter | Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) | UINT16 | RO | 0x0000 (0dec) |
1C32:0D | Shift too short counter | Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C32:20 | Sync error | The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) | BOOLEAN | RO | 0x00 (0dec) |
Index 1C33 SM input parameter
1C33:0 | SM input parameter | Synchronization parameters for the inputs | UINT8 | RO | 0x20 (32dec) |
1C33:01 | Sync mode | Current synchronization mode:
| UINT16 | RW | 0x0022 (34dec) |
1C33:02 | Cycle time | as 0x1C32:02 | UINT32 | RW | 0x000F4240 (1000000dec) |
1C33:03 | Shift time | Time between SYNC0 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:04 | Sync modes supported | Supported synchronization modes:
1C33:05 | Minimum cycle time | as 0x1C32:05 | UINT32 | RO | 0x0003D090 (250000dec) |
1C33:06 | Calc and copy time | Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:07 | Minimum delay time |
1C33:08 | Command | as 0x1C32:08 | UINT16 | RW | 0x0000 (0dec) |
1C33:09 | Maximum delay time | Time between SYNC1 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:0B | SM event missed counter | as 0x1C32:11 | UINT16 | RO | 0x0000 (0dec) |
1C33:0C | Cycle exceeded counter | as 0x1C32:12 | UINT16 | RO | 0x0000 (0dec) |
1C33:0D | Shift too short counter | as 0x1C32:13 | UINT16 | RO | 0x0000 (0dec) |
1C33:20 | Sync error | as 0x1C32:32 | BOOLEAN | RO | 0x00 (0dec) |