Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
EtherCAT
Connection
2 x M8 socket, 4-pin, A-coded, shielded
Electrical isolation
500 V
Distributed Clocks
yes
Supply voltages
Connection
Input: 7/8" plug, 5-pin, 16-UN thread
Downstream connection: 7/8" socket, 5-pin, 16-UN thread
US nominal voltage
24 VDC (-15 % / +20 %)
US sum current
max. 16 A at 40 °C
Current consumption from US
120 mA
+ Encoder supply
+ Digital output currents
+ Current for the holding brake
UP rated voltage
8…48 VDC
UP sum current
max. 16 A at 40 °C
Current consumption from UP
= Current consumption of the motor output stage
Motor
Number of channels
1
Motor type
2-phase stepper motor, unipolar or bipolar
Connection
M12 socket, 5-pin, A-coded
Motor supply
8…48 VDC from UP
Rated current
3.5 A per phase
Peak current
5 A per phase
Overload- and short-circuit proof
Yes
Step frequency
max. 8,000 full steps/s
Current controller frequency
Dynamic
Microstepping
max. 256 intermediate steps per full step
Encoder interface
Number of channels
1
Protocols
  • BiSS® C unidirectional
  • SSI
Connection
1 x M12 socket, 8-pin, A-coded
Resolution
max. 64 bit position value, 2 bit status, 16 bit CRC
Encoder supply
Configurable: 5 VDC (default) or 9 VDC from US
max. 0.5 A
Digital outputs for control signals
Zero, Direction
See Technical data of the digital outputs
Holding brake
Number of channels
1
Connection
1 x M12 socket, 5-pin, A-coded
Rated voltage
24 VDC from US
Output current
max 0.5 A
Digital outputs
Number
2
Connection
Each digital output is available on two connections in parallel:
  • Encoder connection X05
  • Digital I/O connection X01 / X02
    (M12 sockets, 5-pin, A-coded)
Cable length
max. 30 m
Load type
Ohmic, inductive, lamp load
Output voltage
Corresponds to the configured encoder supply
Output current
max. 0.5 A per channel, individually short-circuit proof
Auxiliary voltage output
24 VDC from US,max. 0.5 A in total, short-circuit proof
Digital inputs
Number
2
Application options
  • Touch probe inputs
  • "Plc cam": referencing cams for homing
  • "Hardware Enable" to enable the output stage
  • "Auto start" for the Positioning Interface
  • Digital inputs can be used as required
Connection
2 x M12 socket, 5-pin, A-coded
Cable length
max. 30 m
Sensor power supply
24 VDC from US
Environmental conditions
Ambient temperature during operation
-25 … +60 °C
Ambient temperature during storage
-40 … +85 °C
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection class
IP65, IP66, IP67 conforms to EN 60529
Approvals/markings
Approvals/markings *)
CE, cURus
Additional tests
The devices have undergone the following additional tests:
Test
Explanation
Vibration
10 frequency sweeps in 3 axes
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude
Shocks
1000 shocks in each direction, in 3 axes
35 g, 11 ms