Standard objects
Index 1000 Device type
Index (hex)
Meaning
Data type
Flags
Default
1000:0
Device type
Device type of the EtherCAT slave: The low word contains the CoE profile used (5001). The high word contains the module profile according to the modular device profile.
UINT32
RO
0x00001389 (5001dec)
Index 1008 Device name
Index (hex)
Meaning
Data type
Flags
Default
1008:0
Device name
Device name of the EtherCAT slave
STRING
RO
EP6001-0002
Index 1009 Hardware version
Index (hex)
Meaning
Data type
Flags
Default
1009:0
Hardware version
Hardware version of the EtherCAT slave
STRING
RO
00
Index 100A Software Version
Index (hex)
Meaning
Data type
Flags
Default
100A:0
Software version
Firmware version of the EtherCAT slave
STRING
RO
00
Index 1018 Identity
Index (hex)
Meaning
Data type
Flags
Default
1018:0
Identity
Information for identifying the slave
UINT8
RO
0x04 (4dec)
1018:01
Vendor ID
Vendor ID of the EtherCAT slave
UINT32
RO
0x00000002 (2dec)
1018:02
Product code
Product code of the EtherCAT slave
UINT32
RO
0x17714052 (393298002dec)
1018:03
Revision
Revision number of the EtherCAT slave; the Low Word (bit 0-15) indicates the special terminal number, the High Word (bit 16-31) refers to the device description
UINT32
RO
0x00100002 (1048578dec)
1018:04
Serial number
Serial number of the EtherCAT slave; the Low Byte (bit 0-7) of the Low Word contains the year of production, the High Byte (bit 8-15) of the Low Word contains the week of production, the High Word (bit 16-31) is 0
UINT32
RO
0x00000000 (0dec)
Index (hex)
Meaning
Data type
Flags
Default
10F0:0
Information for standardized loading and saving of backup entries
UINT8
RO
0x01 (1dec)
10F0:01
Checksum
Checksum across all backup entries of the EtherCAT slave
UINT32
RO
0x00000000 (0dec)
Index 1400 COM RxPDO-Par Outputs
Index (hex)
Meaning
Data type
Flags
Default
1400:0
PDO Parameter RxPDO 1
UINT8
RO
0x06 (6dec)
1400:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 1
OCTET-STRING[2]
RO
04 16
Index 1404 COM RxPDO-Par Outputs
Index (hex)
Meaning
Data type
Flags
Default
1404:0
PDO Parameter RxPDO 2
UINT8
RO
0x06 (6dec)
1404:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 5
OCTET-STRING[2]
RO
00 16
Index 1600 COM RxPDO-Map Outputs
Index (hex)
Meaning
Data type
Flags
Default
1600:0
PDO Mapping RxPDO 1
UINT8
RO
0x1C (28dec)
1600:01
SubIndex 001
1. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x01 (Transmit request))
UINT32
RO
0x7000:01, 1
1600:02
SubIndex 002
2. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x02 (Receive accepted))
UINT32
RO
0x7000:02, 1
1600:03
SubIndex 003
3. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x03 (Init request))
UINT32
RO
0x7000:03, 1
1600:04
SubIndex 004
4. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x04 (Send continuous))
UINT32
RO
0x7000:04, 1
1600:05
SubIndex 005
5. PDO Mapping entry (4 bits align)
UINT32
RO
0x0000:00, 4
1600:06
SubIndex 006
6. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x09 (Output length))
UINT32
RO
0x7000:09, 8
1600:07
SubIndex 007
7. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x11 (Data Out 0))
UINT32
RO
0x7000:11, 8
1600:08
SubIndex 008
8. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x12 (Data Out 1))
UINT32
RO
0x7000:12, 8
1600:09
SubIndex 009
9. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x13 (Data Out 2))
UINT32
RO
0x7000:13, 8
1600:0A
SubIndex 010
10. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x14 (Data Out 3))
UINT32
RO
0x7000:14, 8
1600:0B
SubIndex 011
11. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x15 (Data Out 4))
UINT32
RO
0x7000:15, 8
1600:0C
SubIndex 012
12. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x16 (Data Out 5))
UINT32
RO
0x7000:16, 8
1600:0D
SubIndex 013
13. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x17 (Data Out 6))
UINT32
RO
0x7000:17, 8
1600:0E
SubIndex 014
14. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x18 (Data Out 7))
UINT32
RO
0x7000:18, 8
1600:0F
SubIndex 015
15. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x19 (Data Out 8))
UINT32
RO
0x7000:19, 8
1600:10
SubIndex 016
16. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1A (Data Out 9))
UINT32
RO
0x7000:1A, 8
1600:11
SubIndex 017
17. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1B (Data Out 10))
UINT32
RO
0x7000:1B, 8
1600:12
SubIndex 018
18. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1C (Data Out 11))
UINT32
RO
0x7000:1C, 8
1600:13
SubIndex 019
19. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1D (Data Out 12))
UINT32
RO
0x7000:1D, 8
1600:14
SubIndex 020
20. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1E (Data Out 13))
UINT32
RO
0x7000:1E, 8
1600:15
SubIndex 021
21. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1F (Data Out 14))
UINT32
RO
0x7000:1F, 8
1600:16
SubIndex 022
22. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x20 (Data Out 15))
UINT32
RO
0x7000:20, 8
1600:17
SubIndex 023
23. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x21 (Data Out 16))
UINT32
RO
0x7000:21, 8
1600:18
SubIndex 024
24. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x22 (Data Out 17))
UINT32
RO
0x7000:22, 8
1600:19
SubIndex 025
25. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x23 (Data Out 18))
UINT32
RO
0x7000:23, 8
1600:1A
SubIndex 026
26. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x24 (Data Out 19))
UINT32
RO
0x7000:24, 8
1600:1B
SubIndex 027
27. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x25 (Data Out 20))
UINT32
RO
0x7000:25, 8
1600:1C
SubIndex 028
28. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x26 (Data Out 21))
UINT32
RO
0x7000:26, 8
Index 1604 COM RxPDO-Map Outputs
Index (hex)
Meaning
Data type
Flags
Default
1604:0
PDO Mapping RxPDO 2
UINT8
RO
0x17 (23dec)
1604:01
SubIndex 001
1. PDO Mapping entry (object 0x7001 (Ctrl Ch.1), entry 0x01 (Ctrl))
UINT32
RO
0x7001:01, 16
1604:02
SubIndex 002
2. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x11 (Data Out 0))
UINT32
RO
0x7000:11, 8
1604:03
SubIndex 003
3. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x12 (Data Out 1))
UINT32
RO
0x7000:12, 8
1604:04
SubIndex 004
4. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x13 (Data Out 2))
UINT32
RO
0x7000:13, 8
1604:05
SubIndex 005
5. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x14 (Data Out 3))
UINT32
RO
0x7000:14, 8
1604:06
SubIndex 006
6. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x15 (Data Out 4))
UINT32
RO
0x7000:15, 8
1604:07
SubIndex 007
7. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x16 (Data Out 5))
UINT32
RO
0x7000:16, 8
1604:08
SubIndex 008
8. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x17 (Data Out 6))
UINT32
RO
0x7000:17, 8
1604:09
SubIndex 009
9. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x18 (Data Out 7))
UINT32
RO
0x7000:18, 8
1604:0A
SubIndex 010
10. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x19 (Data Out 8))
UINT32
RO
0x7000:19, 8
1604:0B
SubIndex 011
11. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1A (Data Out 9))
UINT32
RO
0x7000:1A, 8
1604:0C
SubIndex 012
12. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1B (Data Out 10))
UINT32
RO
0x7000:1B, 8
1604:0D
SubIndex 013
13. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1C (Data Out 11))
UINT32
RO
0x7000:1C, 8
1604:0E
SubIndex 014
14. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1D (Data Out 12))
UINT32
RO
0x7000:1D, 8
1604:0F
SubIndex 015
15. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1E (Data Out 13))
UINT32
RO
0x7000:1E, 8
1604:10
SubIndex 016
16. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1F (Data Out 14))
UINT32
RO
0x7000:1F, 8
1604:11
SubIndex 017
17. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x20 (Data Out 15))
UINT32
RO
0x7000:20, 8
1604:12
SubIndex 018
18. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x21 (Data Out 16))
UINT32
RO
0x7000:21, 8
1604:13
SubIndex 019
19. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x22 (Data Out 17))
UINT32
RO
0x7000:22, 8
1604:14
SubIndex 020
20. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x23 (Data Out 18))
UINT32
RO
0x7000:23, 8
1604:15
SubIndex 021
21. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x24 (Data Out 19))
UINT32
RO
0x7000:24, 8
1604:16
SubIndex 022
22. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x25 (Data Out 20))
UINT32
RO
0x7000:25, 8
1604:17
SubIndex 023
23. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x26 (Data Out 21))
UINT32
RO
0x7000:26, 8
Index 1608 DIG RxPDO-Map Outputs
Index (hex)
Meaning
Data type
Flags
Default
1608:0
PDO Mapping RxPDO 3
UINT8
RO
0x03 (3dec)
1608:01
SubIndex 001
1. PDO Mapping entry (object 0x7010 (DIG Outputs), entry 0x01 (Digital Output 1))
UINT32
RO
0x7001:01, 1
1608:02
SubIndex 002
2. PDO Mapping entry (object 0x7010 (DIG Outputs), entry 0x02 (Digital Output 2))
UINT32
RO
0x7010:02, 1
1608:03
SubIndex 003
3. PDO Mapping entry (14 bits align)
UINT32
RO
0x0000:00, 14
Index 1800 COM TxPDO-Par Inputs
Index (hex)
Meaning
Data type
Flags
Default
1800:0
PDO parameter TxPDO 1
UINT8
RO
0x06 (6dec)
1800:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 1
OCTET-STRING[2]
RO
04 1A
Index 1804 COM TxPDO-Par Inputs
Index (hex)
Meaning
Data type
Flags
Default
1804:0
PDO parameter TxPDO 2
UINT8
RO
0x06 (6dec)
1804:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 2
OCTET-STRING[2]
RO
00 1A
Index 1A00 COM TxPDO-Map Inputs
Index (hex)
Meaning
Data type
Flags
Default
1A00:0
PDO Mapping TxPDO 1
UINT8
RO
0x1F (31dec)
1A00:01
SubIndex 001
1. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x01 (Transmit accepted))
UINT32
RO
0x6000:01, 1
1A00:02
SubIndex 002
2. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x02 (Receive request))
UINT32
RO
0x6000:02, 1
1A00:03
SubIndex 003
3. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x03 (Init accepted))
UINT32
RO
0x6000:03, 1
1A00:04
SubIndex 004
4. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x04 (Buffer full))
UINT32
RO
0x6000:04, 1
1A00:05
SubIndex 005
5. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x05 (Parity error))
UINT32
RO
0x6000:05, 1
1A00:06
SubIndex 006
6. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x06 (Framing error))
UINT32
RO
0x6000:06, 1
1A00:07
SubIndex 007
7. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x07 (Overrun error))
UINT32
RO
0x6000:07, 1
1A00:08
SubIndex 008
8. PDO Mapping entry (1 bits align)
UINT32
RO
0x0000:00, 1
1A00:09
SubIndex 009
9. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x09 (Input length))
UINT32
RO
0x6000:09, 8
1A00:0A
SubIndex 010
10. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x11 (Data In 0))
UINT32
RO
0x6000:11, 8
1A00:0B
SubIndex 011
11. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x12 (Data In 1))
UINT32
RO
0x6000:12, 8
1A00:0C
SubIndex 012
12. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x13 (Data In 2))
UINT32
RO
0x6000:13, 8
1A00:0D
SubIndex 013
13. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x14 (Data In 3))
UINT32
RO
0x6000:14, 8
1A00:0E
SubIndex 014
14. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x15 (Data In 4))
UINT32
RO
0x6000:15, 8
1A00:0F
SubIndex 015
15. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x16 (Data In 5))
UINT32
RO
0x6000:16, 8
1A00:10
SubIndex 016
16. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x17 (Data In 6))
UINT32
RO
0x6000:17, 8
1A00:11
SubIndex 017
17. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x18 (Data In 7))
UINT32
RO
0x6000:18, 8
1A00:12
SubIndex 018
18. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x19 (Data In 8))
UINT32
RO
0x6000:19, 8
1A00:13
SubIndex 019
19. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1A (Data In 9))
UINT32
RO
0x6000:1A, 8
1A00:14
SubIndex 020
20. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1B (Data In 10))
UINT32
RO
0x6000:1B, 8
1A00:15
SubIndex 021
21. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1C (Data In 11))
UINT32
RO
0x6000:1C, 8
1A00:16
SubIndex 022
22. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1D (Data In 12))
UINT32
RO
0x6000:1D, 8
1A00:17
SubIndex 023
23. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1E (Data In 13))
UINT32
RO
0x6000:1E, 8
1A00:18
SubIndex 024
24. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1F (Data In 14))
UINT32
RO
0x6000:1F, 8
1A00:19
SubIndex 025
25. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x20 (Data In 15))
UINT32
RO
0x6000:20, 8
1A00:1A
SubIndex 026
26. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x21 (Data In 16))
UINT32
RO
0x6000:21, 8
1A00:1B
SubIndex 027
27. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x22 (Data In 17))
UINT32
RO
0x6000:22, 8
1A00:1C
SubIndex 028
28. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x23 (Data In 18))
UINT32
RO
0x6000:23, 8
1A00:1D
SubIndex 029
29. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x24 (Data In 19))
UINT32
RO
0x6000:24, 8
1A00:1E
SubIndex 030
30. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x25 (Data In 20))
UINT32
RO
0x6000:25, 8
1A00:1F
SubIndex 031
31. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x26 (Data In 21))
UINT32
RO
0x6000:26, 8
Index 1A04 COM TxPDO-Map Inputs
Index (hex)
Meaning
Data type
Flags
Default
1A04:0
PDO Mapping TxPDO 2
UINT8
RO
0x17 (23dec)
1A04:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Status Ch.1), entry 0x01 (Status))
UINT32
RO
0x6001:01, 16
1A04:02
SubIndex 002
2. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x11 (Data In 0))
UINT32
RO
0x6000:11, 8
1A04:03
SubIndex 003
3. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x12 (Data In 1))
UINT32
RO
0x6000:12, 8
1A04:04
SubIndex 004
4. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x13 (Data In 2))
UINT32
RO
0x6000:13, 8
1A04:05
SubIndex 005
5. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x14 (Data In 3))
UINT32
RO
0x6000:14, 8
1A04:06
SubIndex 006
6. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x15 (Data In 4))
UINT32
RO
0x6000:15, 8
1A04:07
SubIndex 007
7. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x16 (Data In 5))
UINT32
RO
0x6000:16, 8
1A04:08
SubIndex 008
8. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x17 (Data In 6))
UINT32
RO
0x6000:17, 8
1A04:09
SubIndex 009
9. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x18 (Data In 7))
UINT32
RO
0x6000:18, 8
1A04:0A
SubIndex 010
10. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x19 (Data In 8))
UINT32
RO
0x6000:19, 8
1A04:0B
SubIndex 011
11. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1A (Data In 9))
UINT32
RO
0x6000:1A, 8
1A04:0C
SubIndex 012
12. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1B (Data In 10))
UINT32
RO
0x6000:1B, 8
1A04:0D
SubIndex 013
13. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1C (Data In 11))
UINT32
RO
0x6000:1C, 8
1A04:0E
SubIndex 014
14. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1D (Data In 12))
UINT32
RO
0x6000:1D, 8
1A04:0F
SubIndex 015
15. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1E (Data In 13))
UINT32
RO
0x6000:1E, 8
1A04:10
SubIndex 016
16. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1F (Data In 14))
UINT32
RO
0x6000:1F, 8
1A04:11
SubIndex 017
17. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x20 (Data In 15))
UINT32
RO
0x6000:20, 8
1A04:12
SubIndex 018
18. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x21 (Data In 16))
UINT32
RO
0x6000:21, 8
1A04:13
SubIndex 019
19. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x22 (Data In 17))
UINT32
RO
0x6000:22, 8
1A04:14
SubIndex 020
20. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x23 (Data In 18))
UINT32
RO
0x6000:23, 8
1A04:15
SubIndex 021
21. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x24 (Data In 19))
UINT32
RO
0x6000:24, 8
1A04:16
SubIndex 022
22. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x25 (Data In 20))
UINT32
RO
0x6000:25, 8
1A04:17
SubIndex 023
23. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x26 (Data In 21))
UINT32
RO
0x6000:26, 8
Index 1A08 DIG TxPDO-Map Inputs
Index (hex)
Meaning
Data type
Flags
Default
1A08:0
COM TxPDO-Map Inputs Ch.2
PDO Mapping TxPDO 6
UINT8
RO
0x03 (3dec)
1A08:01
SubIndex 001
1. PDO Mapping entry (object 0x6010 (DIG Inputs), entry 0x01 (Digital Input 1))
UINT32
RO
0x6010:01, 1
1A08:02
SubIndex 002
2. PDO Mapping entry (object 0x6010 (DIG Inputs), entry 0x02 (Digital Input 2))
UINT32
RO
0x6010:02, 1
1A08:03
SubIndex 003
UINT32
RO
0x0000:00, 14
Index 1C00 Sync manager type
Index (hex)
Meaning
Data type
Flags
Default
1C00:0
Sync manager type
Using the Sync Managers
UINT8
RO
0x04 (4dec)
1C00:01
SubIndex 001
Sync-Manager Type Channel 1: Mailbox Write
UINT8
RO
0x01 (1dec)
1C00:02
SubIndex 002
Sync-Manager Type Channel 2: Mailbox Read
UINT8
RO
0x02 (2dec)
1C00:03
SubIndex 003
Sync-Manager Type Channel 3: Process Data Write (Outputs)
UINT8
RO
0x03 (3dec)
1C00:04
SubIndex 004
Sync-Manager Type Channel 4: Process Data Read (Inputs)
UINT8
RO
0x04 (4dec)
Index 1C12 RxPDO assign
Index (hex)
Meaning
Data type
Flags
Default
1C12:0
RxPDO assign
PDO Assign Outputs
UINT8
RW
0x02 (2dec)
1C12:01
Subindex 001
1. allocated RxPDO (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x1604 (5636dec)
1C12:02
Subindex 002
2. reserved
UINT16
RW
Index 1C13 TxPDO assign
Index (hex)
Meaning
Data type
Flags
Default
1C13:0
TxPDO assign
PDO Assign Inputs
UINT8
RW
0x02 (2dec)
1C13:01
Subindex 001
1. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A04 (6660dec)
1C13:02
Subindex 002
2. reserved
UINT16
RW
Index (hex)
Meaning
Data type
Flags
Default
1C32:0
SM output parameter
Synchronization parameters for the outputs
UINT8
RO
0x20 (32dec)
1C32:01
Sync mode
Current synchronization mode:
  • 0: Free Run
  • 1: Synchron with SM 2 Event
  • 2: DC-Mode - Synchron with SYNC0 Event
  • 3: DC-Mode - Synchron with SYNC1 Event
UINT16
RW
0x0000 (0dec)
1C32:02
Cycle time
Cycle time (in ns):
  • Free Run: Cycle time of the local timer
  • Synchron with SM 2 Event: Master cycle time
  • DC mode: SYNC0/SYNC1 Cycle Time
UINT32
RW
0x0003D090 (250000dec)
1C32:03
Shift time
Time between SYNC0 event and output of the outputs (in ns, DC mode only)
UINT32
RO
0x00000384 (900dec)
1C32:04
Sync modes supported
Supported synchronization modes:
  • Bit 0 = 1: free run is supported
  • Bit 1 = 1: Synchron with SM 2 Event is supported
  • Bit 2-3 = 01: DC mode is supported
  • Bit 4-5 = 10: Output Shift with SYNC1 Event (only DC mode)
  • Bit 14 = 1: dynamic times (measurement through writing of 1C32:08)
UINT16
RO
0x0001 (1dec)
1C32:05
Minimum cycle time
Minimum cycle time (in ns)
UINT32
RO
1C32:06
Calc and copy time
Minimum time between SYNC0 and SYNC1 event (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C32:07
Minimum delay time
UINT32
RO
0x00000384 (900dec)
1C32:08
Command
  • 0: Measurement of the local cycle time is stopped
  • 1: Measurement of the local cycle time is started
The entries 1C32:03, 1C32:05, 1C32:06, 1C32:09, 1C33:03, 1C33:06, 1C33:09 are updated with the maximum measured values.
For a subsequent measurement the measured values are reset
UINT16
RW
0x0000 (0dec)
1C32:09
Maximum Delay time
Time between SYNC1 event and output of the outputs (in ns, DC mode only)
UINT32
RO
0x00000384 (900dec)
1C32:0B
SM event missed counter
Number of missed SM events in OPERATIONAL (DC mode only)
UINT16
RO
0x0000 (0dec)
1C32:0C
Cycle exceeded counter
Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early)
UINT16
RO
0x0000 (0dec)
1C32:0D
Shift too short counter
Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only)
UINT16
RO
0x0000 (0dec)
1C32:20
Sync error
The synchronization was not correct in the last cycle (outputs were output too late; DC mode only)
BOOLEAN
RO
0x00 (0dec)
Index 1C33 SM input parameter
Index (hex)
Meaning
Data type
Flags
Default
1C33:0
SM input parameter
Synchronization parameters for the inputs
UINT8
RO
0x20 (32dec)
1C33:01
Sync mode
  • 0: Free Run
  • 1: Synchron with SM 3 Event (no outputs available)
  • 2: DC - Synchron with SYNC0 Event
  • 3: DC - Synchron with SYNC1 Event
  • 34: Synchron with SM 2 Event (outputs available)
UINT16
RW
0x0000 (0dec)
1C33:02
Cycle time
as 1C32:02
UINT32
RW
1C33:03
Shift time
Time between SYNC0 event and reading of the inputs (in ns, only DC mode)
UINT32
RO
0x00000384 (900dec)
1C33:04
  • Bit 0: free run is supported
  • Bit 1: Synchron with SM 2 Event is supported (outputs available)
  • Bit 1: Synchron with SM 3 Event is supported (no outputs available)
  • Bit 4-5 = 01: Input Shift through local event (outputs available)
  • Bit 4-5 = 10: Input Shift with SYNC1 Event (no outputs available)
  • Bit 14 = 1: dynamic times (measurement through writing of 1C32:08 or 1C33:08)
UINT16
RO
0x0001 (1dec)
1C33:05
Minimum cycle time
as 1C32:05
UINT32
RO
1C33:06
Calc and copy time
Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode)
UINT32
RO
0x00000000 (0dec)
1C33:07
Minimum delay time
UINT32
RO
0x00000384 (900dec)
1C33:08
Command
as 1C32:08
UINT16
RW
0x0000 (0dec)
1C33:09
Maximum Delay time
Time between SYNC1 event and reading of the inputs (in ns, only DC mode)
UINT32
RO
0x00000384 (900dec)
1C33:0B
as 1C32:11
UINT16
RO
0x0000 (0dec)
1C33:0C
as 1C32:12
UINT16
RO
0x0000 (0dec)
1C33:0D
as 1C32:13
UINT16
RO
0x0000 (0dec)
1C33:20
Sync error
as 1C32:32
BOOLEAN
RO
0x00 (0dec)
