Object description and parameterization
![]() | EtherCAT XML Device Description The display matches that of the CoE objects from the EtherCAT XML Device Description. We recommend downloading the latest XML file from the download area of the Beckhoff website and installing it according to installation instructions. |
![]() | Parameterization via the CoE list (CAN over EtherCAT) The EtherCAT device is parameterized via the CoE - Online tab (double-click on the respective object) or via the Process Data tab (allocation of PDOs). |
Introduction
- Objects required for parameterization during commissioning
- Objects for indicating internal settings (may be fixed)
- Further profile-specific objects indicating inputs, outputs and status information
The following section first describes the objects required for normal operation, followed by a complete overview of missing objects.
Objects to be parameterized during commissioning
Index 1011 Restore default parameters
1011:0 | Restore default parameters | Restore default settings | UINT8 | RO | 0x01 (1dec) |
1011:01 | SubIndex 001 | If this object is set to "0x64616F6C" in the Set Value Dialog, all backup objects are reset to their delivery state. | UINT32 | RW | 0x00000000 (0dec) |
Index 8000 AI Settings Ch.1
Index (hex) | Name | Meaning | Data type | Flags | Default | |
8000:0 | AI Settings Ch.1 |
| UINT8 | RO | 0x1A (26dec) | |
8000:06 | Enable filter | Activates the filter. | BOOLEAN | RW | 0x00 (0dec) | |
8000:15 | Filter settings | This object determines the filter settings of all channels of the module when it is activated via Enable filter index 0x80n0:06. | UINT16 | RW | 0x0002 (2dec) | |
0 | FIR | |||||
2 | IIR1 | |||||
3 | IIR2 | |||||
4 | IIR3 | |||||
5 | IIR4 | |||||
6 | IIR5 | |||||
7 | IIR6 | |||||
8 | IIR7 | |||||
9 | IIR8 | |||||
8000:19 | Range | Setting the measuring range:
| UINT16 | RW | 0x0000 (0dec) | |
8000:1A | Presentation | Representation of the data
| UINT16 | RW | 0x0001 (1dec) | |
Index 8010 AI Settings Ch.2
8010:0 | AI Settings Ch.2 |
8010:06 | Enable filter | Activates the filter. | BOOLEAN | RW | 0x00 (0dec) | |
8010:15 | Filter settings | This object determines the filter settings of all channels of the module when it is activated via Enable filter index 0x80n0:06. | UINT16 | RW | 0x0002 (2dec) | |
0 | FIR | |||||
2 | IIR1 | |||||
3 | IIR2 | |||||
4 | IIR3 | |||||
5 | IIR4 | |||||
6 | IIR5 | |||||
7 | IIR6 | |||||
8 | IIR7 | |||||
9 | IIR8 | |||||
8010:19 | Range | Setting the measuring range:
8010:1A | Presentation | Representation of the data
Index 8020 AI Settings Ch.3
8020:0 | AI Settings Ch.3 |
8020:06 | Enable filter | Activates the filter. | BOOLEAN | RW | 0x00 (0dec) | |
8020:15 | Filter settings | This object determines the filter settings of all channels of the module when it is activated via Enable filter index 0x80n0:06. | UINT16 | RW | 0x0002 (2dec) | |
0 | FIR | |||||
2 | IIR1 | |||||
3 | IIR2 | |||||
4 | IIR3 | |||||
5 | IIR4 | |||||
6 | IIR5 | |||||
7 | IIR6 | |||||
8 | IIR7 | |||||
9 | IIR8 | |||||
8020:19 | Range | Setting the measuring range:
8020:1A | Presentation | Representation of the data
Index 8030 AI Settings Ch.4
8030:0 | AI Settings Ch.4 |
| UINT8 | RO | 0x11 (21dec) | |
8030:06 | Enable filter | Activates the filter. | BOOLEAN | RW | 0x00 (0dec) | |
8030:15 | Filter settings | This object determines the filter settings of all channels of the module when it is activated via Enable filter index 0x80n0:06. | UINT16 | RW | 0x0002 (2dec) | |
0 | FIR | |||||
2 | IIR1 | |||||
3 | IIR2 | |||||
4 | IIR3 | |||||
5 | IIR4 | |||||
6 | IIR5 | |||||
7 | IIR6 | |||||
8 | IIR7 | |||||
9 | IIR8 | |||||
8030:19 | Range | Setting the measuring range:
8030:1A | Presentation | Representation of the data
Index 8040 AI Settings Ch.5
8040:0 | AI Settings Ch.5 |
8040:06 | Enable filter | Activates the filter. | BOOLEAN | RW | 0x00 (0dec) | |
8040:15 | Filter settings | This object determines the filter settings of all channels of the module when it is activated via Enable filter index 0x80n0:06. | UINT16 | RW | 0x0002 (2dec) | |
0 | FIR | |||||
2 | IIR1 | |||||
3 | IIR2 | |||||
4 | IIR3 | |||||
5 | IIR4 | |||||
6 | IIR5 | |||||
7 | IIR6 | |||||
8 | IIR7 | |||||
9 | IIR8 | |||||
8040:19 | Range | Setting the measuring range:
8040:1A | Presentation | Representation of the data
Index 8050 AI Settings Ch.6
8050:0 | AI Settings Ch.6 |
8050:06 | Enable filter | Activates the filter. | BOOLEAN | RW | 0x00 (0dec) | |
8050:15 | Filter settings | This object determines the filter settings of all channels of the module when it is activated via Enable filter index 0x80n0:06. | UINT16 | RW | 0x0002 (2dec) | |
0 | FIR | |||||
2 | IIR1 | |||||
3 | IIR2 | |||||
4 | IIR3 | |||||
5 | IIR4 | |||||
6 | IIR5 | |||||
7 | IIR6 | |||||
8 | IIR7 | |||||
9 | IIR8 | |||||
8050:19 | Range | Setting the measuring range:
8050:1A | Presentation | Representation of the data
Index 8060 SAI Settings (Firmware 01)
The object with index 8060 is invisible in the object directory from Firmware 02. However, it can still be read and written via SDO access. This ensures backward compatibility with PLC programs that were written prior to the release of Firmware 02.
The content of index 8060 is mirrored in index F800 from Firmware 02.
8060:0 | SAI Settings |
| UINT8 | RO | 0x1D (29dec) |
8060:0D | Filter sampling rate | Selection of the internal sampling rate:
8060:11 | Range | Setting the measuring range:
8060:1D | Presentation | Representation of the data
Index F800 SAI Settings (from Firmware 02)
F800:0 | SAI Settings |
F800:0D | Filter sampling rate | Selection of the internal sampling rate:
F800:11 | Range | Setting the measuring range:
F800:1D | Presentation | Representation of the data
Additional objects
Standard objects (0x1000-0x1FFF)
The standard objects have the same meaning for all EtherCAT slaves.
Index 1000 Device type
1000:0 | Device type | Device type of the EtherCAT slave: The Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile. | UINT32 | RO | 0x00001389 (5001dec) |
Index 1008 Device name
1008:0 | Device name | Device name of the EtherCAT slave | STRING | RO | EP3752-0000 |
Index 1009 Hardware version
1009:0 | Hardware version | Hardware version of the EtherCAT slave | STRING | RO | 00 |
Index 100A Software Version
100A:0 | Software version | Firmware version of the EtherCAT slave | STRING | RO | 00 |
Index 1018 Identity
1018:0 | Identity | Information for identifying the slave | UINT8 | RO | 0x04 (4dec) |
1018:01 | Vendor ID | Vendor ID of the EtherCAT slave | UINT32 | RO | 0x00000002 (2dec) |
1018:02 | Product code | Product code of the EtherCAT slave | UINT32 | RO | 0x0EA84052 (245907538dec) |
1018:03 | Revision | Revision number of the EtherCAT slave; the Low Word (bit 0-15) indicates the special terminal number, the High Word (bit 16-31) refers to the device description | UINT32 | RO | 0x00100002 (1048578dec) |
1018:04 | Serial number | Serial number of the EtherCAT slave; the Low Byte (bit 0-7) of the Low Word contains the year of production, the High Byte (bit 8-15) of the Low Word contains the week of production, the High Word (bit 16-31) is 0 | UINT32 | RO | 0x00000000 (0dec) |
10F0:0 | Backup parameter handling | Information for standardized loading and saving of backup entries | UINT8 | RO | 0x01 (1dec) |
10F0:01 | Checksum | Checksum across all backup entries of the EtherCAT slave | UINT32 | RO | 0x00000000 (0dec) |
Index 1A00 AI TxPDO-Map Inputs Ch.1
1A00:0 | AI TxPDO-Map Inputs Ch.1 | PDO Mapping TxPDO 1 | UINT8 | RO | 0x06 (6dec) |
1A00:01 | SubIndex 001 | 1. PDO Mapping entry (6 bit align) | UINT32 | RO | 0x0000:00, 6 |
1A00:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x07 (Error)) | UINT32 | RO | 0x6000:07, 1 |
1A00:03 | SubIndex 003 | 3. PDO Mapping entry (7 bit align) | UINT32 | RO | 0x0000:00, 7 |
1A00:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6000:0F, 1 |
1A00:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6000:10, 1 |
1A00:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x11 (Value)) | UINT32 | RO | 0x6000:11, 16 |
Index 1A01 AI TxPDO-Map Inputs Ch.2
1A01:0 | AI TxPDO-Map Inputs Ch.1 | PDO Mapping TxPDO 2 | UINT8 | RO | 0x06 (6dec) |
1A01:01 | SubIndex 001 | 1. PDO Mapping entry (6 bit align) | UINT32 | RO | 0x0000:00, 6 |
1A01:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x07 (Error)) | UINT32 | RO | 0x6010:07, 1 |
1A01:03 | SubIndex 003 | 3. PDO Mapping entry (7 bit align) | UINT32 | RO | 0x0010:00, 7 |
1A01:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6010:0F, 1 |
1A01:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6010:10, 1 |
1A01:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x11 (Value)) | UINT32 | RO | 0x6010:11, 16 |
Index 1A02 AI TxPDO-Map Inputs Ch.3
1A02:0 | AI TxPDO-Map Inputs Ch.3 | PDO Mapping TxPDO 3 | UINT8 | RO | 0x06 (6dec) |
1A02:01 | SubIndex 001 | 1. PDO Mapping entry (6 bit align) | UINT32 | RO | 0x0000:00, 6 |
1A02:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6020 (AI Inputs Ch.3), entry 0x07 (Error)) | UINT32 | RO | 0x6020:07, 1 |
1A02:03 | SubIndex 003 | 3. PDO Mapping entry (7 bit align) | UINT32 | RO | 0x0000:00, 7 |
1A02:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6020 (AI Inputs Ch.3), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6020:0F, 1 |
1A02:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6020 (AI Inputs Ch.3), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6020:10, 1 |
1A02:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6020 (AI Inputs Ch.3), entry 0x11 (Value)) | UINT32 | RO | 0x6020:11, 16 |
Index 1A03 AI TxPDO-Map Inputs Ch.4
1A03:0 | AI TxPDO-Map Inputs Ch.4 | PDO Mapping TxPDO 4 | UINT8 | RO | 0x06 (6dec) |
1A03:01 | SubIndex 001 | 1. PDO Mapping entry (6 bit align) | UINT32 | RO | 0x0000:00, 6 |
1A03:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6030 (AI Inputs Ch.4), entry 0x07 (Error)) | UINT32 | RO | 0x6030:07, 1 |
1A03:03 | SubIndex 003 | 3. PDO Mapping entry (7 bit align) | UINT32 | RO | 0x0000:00, 7 |
1A03:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6030 (AI Inputs Ch.4), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6030:0F, 1 |
1A03:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6030 (AI Inputs Ch.4), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6030:10, 1 |
1A03:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6030 (AI Inputs Ch.4), entry 0x11 (Value)) | UINT32 | RO | 0x6030:11, 16 |
Index 1A04 AI TxPDO-Map Inputs Ch.5
1A04:0 | AI TxPDO-Map Inputs Ch.5 | PDO Mapping TxPDO 5 | UINT8 | RO | 0x06 (6dec) |
1A04:01 | SubIndex 001 | 1. PDO Mapping entry (6 bit align) | UINT32 | RO | 0x0000:00, 6 |
1A04:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6040 (AI Inputs Ch.5), entry 0x07 (Error)) | UINT32 | RO | 0x6040:07, 1 |
1A04:03 | SubIndex 003 | 3. PDO Mapping entry (7 bit align) | UINT32 | RO | 0x0000:00, 7 |
1A04:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6040 (AI Inputs Ch.5), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6040:0F, 1 |
1A04:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6040 (AI Inputs Ch.5), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6040:10, 1 |
1A04:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6040 (AI Inputs Ch.5), entry 0x11 (Value)) | UINT32 | RO | 0x6040:11, 16 |
Index 1A05 AI TxPDO-Map Inputs Ch.6
1A05:0 | AI TxPDO-Map Inputs Ch.6 | PDO Mapping TxPDO 5 | UINT8 | RO | 0x06 (6dec) |
1A05:01 | SubIndex 001 | 1. PDO Mapping entry (6 bit align) | UINT32 | RO | 0x0000:00, 6 |
1A05:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6050 (AI Inputs Ch.6), entry 0x07 (Error)) | UINT32 | RO | 0x6050:07, 1 |
1A05:03 | SubIndex 003 | 3. PDO Mapping entry (7 bit align) | UINT32 | RO | 0x0000:00, 7 |
1A05:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6050 (AI Inputs Ch.6), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6050:0F, 1 |
1A05:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6050 (AI Inputs Ch.6), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6050:10, 1 |
1A05:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6050 (AI Inputs Ch.6), entry 0x11 (Value)) | UINT32 | RO | 0x6050:11, 16 |
Index 1C00 Sync manager type
1C00:0 | Sync manager type | Using the Sync Managers | UINT8 | RO | 0x04 (4dec) |
1C00:01 | SubIndex 001 | Sync-Manager Type Channel 1: Mailbox Write | UINT8 | RO | 0x01 (1dec) |
1C00:02 | SubIndex 002 | Sync-Manager Type Channel 2: Mailbox Read | UINT8 | RO | 0x02 (2dec) |
1C00:03 | SubIndex 003 | Sync-Manager Type Channel 3: Process Data Write (Outputs) | UINT8 | RO | 0x03 (3dec) |
1C00:04 | SubIndex 004 | Sync-Manager Type Channel 4: Process Data Read (Inputs) | UINT8 | RO | 0x04 (4dec) |
Index 1C12 RxPDO assign
1C12:0 | RxPDO assign | PDO Assign Outputs | UINT8 | RW | 0x00 (0dec) |
Index 1C13 TxPDO assign
1C13:0 | TxPDO assign | PDO Assign Inputs | UINT8 | RW | 0x04 (4dec) |
1C13:01 | Subindex 001 | 1. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A00 (6656dec) |
1C13:02 | Subindex 002 | 2. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A01 (6657dec) |
1C13:03 | Subindex 003 | 3. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A02 (6658dec) |
1C13:04 | Subindex 004 | 4. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A03 (6659dec) |
1C13:05 | Subindex 005 | 5. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A04 (6660dec) |
1C13:06 | Subindex 006 | 6. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A06 (6662dec) |
Index 1C33 SM input parameter
1C33:0 | SM input parameter | Synchronization parameters for the inputs | UINT8 | RO | 0x20 (32dec) |
1C33:01 | Sync mode | Current synchronization mode:
| UINT16 | RW | 0x0022 (34dec) |
1C33:02 | Cycle time | Cycle time (in ns):
| UINT32 | RW | 0x000F4240 (1000000dec) |
1C33:03 | Shift time | Time between SYNC0 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:04 | Sync modes supported | Supported synchronization modes:
| UINT16 | RO | 0x0003 (3dec) |
1C33:05 | Minimum cycle time | Minimum cycle time supported (in ns) | UINT32 | RO | 0x0003D040 (20000dec) |
1C33:06 | Calc and copy time | Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:07 | Minimum delay time |
1C33:08 | Command | With this entry the real required process data provision time can be measured. 0: Measurement of the local cycle time is stopped 1: Measurement of the local cycle time is started The entries 0x1C33:03, 0x1C33:06, 0x1C33:09 are updated with the maximum measured values. | UINT16 | RW | 0x0000 (0dec) |
1C33:09 | Maximum Delay time | Time between SYNC1 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:0B | SM event missed counter | Number of missed SM events in OPERATIONAL (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C33:0C | Cycle exceeded counter | Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) | UINT16 | RO | 0x0000 (0dec) |
1C33:0D | Shift too short counter | Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C33:20 | Sync error | The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) | BOOLEAN | RO | 0x00 (0dec) |
Profile-specific objects (0x6000-0xFFFF)
The profile-specific objects have the same meaning for all EtherCAT slaves that support the profile 5001.
Index 6000 AI Inputs Ch.1
6000:0 | AI Inputs Ch.1 |
| UINT8 | RO | 0x11 (17dec) |
6000:07 | Error |
6000:0F | TxPDO State |
6000:10 | TxPDO Toggle |
6000:11 | Value |
Index 6010 AI Inputs Ch.2
6010:0 | AI Inputs Ch.2 |
6010:07 | Error |
6010:0F | TxPDO State |
6010:10 | TxPDO Toggle |
6010:11 | Value |
Index 6020 AI Inputs Ch.3
6020:0 | AI Inputs Ch.3 |
6020:07 | Error |
6020:0F | TxPDO State |
6020:10 | TxPDO Toggle |
6020:11 | Value |
Index 6030 AI Inputs Ch.4
6030:0 | AI Inputs Ch.4 |
6030:07 | Error |
6030:0F | TxPDO State |
6030:10 | TxPDO Toggle |
6030:11 | Value |
Index 6040 AI Inputs Ch.5
6040:0 | AI Inputs Ch.5 |
6040:07 | Error |
6040:0F | TxPDO State |
6040:10 | TxPDO Toggle |
6040:11 | Value |
Index 6050 AI Inputs Ch.6
6050:0 | AI Inputs Ch.6 |
6050:07 | Error |
6050:0F | TxPDO State |
6050:10 | TxPDO Toggle |
6050:11 | Value |
F000:0 | Modular device profile | General information for the modular device profile | UINT8 | RO | 0x02 (2dec) |
F000:01 | Module index distance | Index distance of the objects of the individual channels | UINT16 | RO | 0x0010 (16dec) |
F000:02 | Maximum number of modules | Number of channels | UINT16 | RO | 0x0002 (2dec) |
Index F008 Code word
F008:0 | Code word |
Index F010 Module list
F010:0 | Module list |
| UINT8 | RW | 0x02 (2dec) |
F010:01 | SubIndex 001 |
| UINT32 | RW | 0x00000258 (600dec) |
F010:02 | SubIndex 002 |