EP3162-0002 - Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
EtherCAT
Connection
2 x M8 socket, 4-pin, A-coded, shielded
Electrical isolation
500 V
Distributed Clocks
yes
Supply voltages
Connection
Input: M8 connector, 4-pin, A-coded
Downstream connection: M8 socket, 4-pin, A-coded
US nominal voltage
24 VDC (-15 % / +20 %)
US sum current: IS,sum
max. 4 A
Current consumption from US
120 mA
+ sensor supply
Rated voltage UP
UP sum current: IP,sum
max. 4 A
Current consumption from UP
None. UP is only forwarded.
Electrical isolation GNDS / GNDP
yes
Analog inputs
Number
2
Connection
2 x M12 socket, 5-pin, A-coded
Cable length
max. 30 m
Input type
Single-ended
Signal range
Adjustable:
  • -10 … +10 V (default)
  • 0 … 10 V
  • 0 … 20 mA
  • 4 … 20 mA
  • -20 … +20 mA
Digital resolution
16 bit, including sign
Measuring error
max 0.3 %, relative to the full scale value.
Input resistance
Voltage measurement: min. 200 kΩ
Current measurement: 85 Ω + diode voltage
Dielectric strength
max. 30 V
300 V between the input channels.
Each analog input channel is electrically isolated from all other potentials in the box.
Conversion time
approx. 100 µs
Input filter limit frequency
5 kHz
Input filter characteristic
Adjustable
Sensor power supply UA and UB
24 VDC from the supply voltage US.
Output current per channel:
max. 50 mA continuous current
max. 100 mA peak current
Housing data
Dimensions W x H x D
30 mm x 126 mm x 26.5 mm (without connectors)
Weight
approx. 165 g
Installation position
variable
Material
PA6 (polyamide)
Environmental conditions
Ambient temperature during operation
-25 … +60 °C
-25 … +55 °C according to cURus
Ambient temperature during storage
-40 … +85 °C
Vibration resistance, shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
Additional tests
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection class
IP65, IP66, IP67 (conforms to EN 60529)
Approvals/markings
Approvals/markings *)
CE, cURus
Additional tests
The devices have undergone the following additional tests:
Test
Explanation
Vibration
10 frequency sweeps in 3 axes
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude
Shocks
1000 shocks in each direction, in 3 axes
35 g, 11 ms