Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
EtherCAT
Connection
2 x M8 socket, 4-pin, A-coded, shielded
Electrical isolation
500 V
Supply voltages
Connection
Input: M8 connector, 4-pin, A-coded
Downstream connection: M8 socket, 4-pin, A-coded
US nominal voltage
24 VDC (-15 % / +20 %)
US sum current: IS,sum
max. 4 A
Current consumption from US
80 mA
UP voltage range
12…30 VDC
UP sum current: IP,sum
max. 4 A
Current consumption from UP
= Sensor power supply
Analog inputs
Number
8
Connection
4 x M12 socket, 5-pin
Two inputs per M12 socket.
Cable length
max. 30 m
Wiring
2-wire
Ground reference
Single-ended
Measuring range, nominal (FSVnom)
Adjustable:
  • -20…+20 mA (default)
  • 0…20 mA
  • 4…20 mA
Measuring range, technical (FSVtechn)
-21.47 mA…+21.47 mA
Resolution
16 bit (including sign)
Sampling rate
max. 2 ksps (min. 500 µs) per channel
Sampling type
Multiplex, approx. 60 µs delay between channels
Input resistance
100 Ω
Input filter limit frequency
1.2 kHz (-3 dB)
Input filter characteristic
First-order low-pass filter
Settling time
3 ms typ. (0…90 %)
Dielectric strength
30 V permanent
Overcurrent protection
50 mA
No electrical isolation between the channels.
The channels are set to UP/GNDP potential.
Conversion method
SAR
Measuring error, measurement uncertainty
max 0.3 %, relative to the full scale value.
Largest short-term deviation during a specified electrical interference test
±1 %FSV typ.
Sensor power supply
12…30 VDC from the supply voltage UP.
max. 0.5 A in total, short-circuit proof in total.
Housing data
Dimensions W x H x D
30 mm x 126 mm x 26.5 mm (without connectors)
Weight
approx. 165 g
Installation position
variable
Material
PA6 (polyamide)
Environmental conditions
Ambient temperature during operation
-25 … +60 °C
-25 … +55 °C according to cURus
Ambient temperature during storage
-40 … +85 °C
Vibration resistance, shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
Additional tests
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection class
IP65, IP66, IP67 (conforms to EN 60529)
Approvals/markings
Approvals/markings *)
CE, cURus
Additional tests
The devices have undergone the following additional tests:
Test
Explanation
Vibration
10 frequency sweeps in 3 axes
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude
Shocks
1000 shocks in each direction, in 3 axes
35 g, 11 ms