Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
Supply voltages | |
Connection | Input: M8 connector, 4-pin, A-coded Forwarding: M8 socket, 4-pin, A-coded |
US rated voltage | 24 VDC (-15 % / +20 %) |
Current consumption from US | 80 mA |
US sum current: IS,sum | max. 4 A |
UP rated voltage | 24 VDC (-15 % / +20 %) |
Current consumption from UP | 30 mA + load |
UP sum current: IP,sum | max. 4 A |
PWM outputs | |
Number | 4 |
Connection | 4x M12 socket, 5-pin, A-coded |
Cable length | max. 30 m |
Load type | Inductive loads with min. 1 mH (For ohmic loads, you must enable the operation mode "Voltage Control", see chapter Basic configuration. This disables the current controller.) |
Output current | max. 2 A per channel, max. 4 A in total. |
Short-circuit current 1) | max. 2.5 A in nominal operation. max. 4.0 A in the event of a fault. |
PWM clock frequency | 30 kHz |
PWM resolution | 16 bit |
PWM duty cycle in Operation Mode "Voltage Control" | 0 … 97 % |
Output driver supply | From the supply voltage UP. |
1) The EP2534-0002 is protected against the following types of short circuits:
- Short circuit between the PWM+ and PWM- contacts.
- Short circuit from one of these contacts to GNDP.
Housing data | |
Dimensions W × H × D | 30 mm × 126 mm × 26.5 mm (without connectors) |
Weight | approx. 165 g |
Material |
PA6 (polyamide) |
Environmental conditions | |
Ambient temperature during operation | -25 … +60 °C |
Ambient temperature during storage | -40 … +85 °C |
Vibration resistance, shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 |
Protection class | IP65, IP66, IP67 (conforms to EN 60529) |
Approvals/markings | |
Approvals/markings *) | CE, cURus |
Additional tests
The devices have undergone the following additional tests:
Test | Explanation |
Vibration | 10 frequency sweeps in 3 axes |
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude | |
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude | |
Shocks | 1000 shocks in each direction, in 3 axes |
35 g, 11 ms |