Object description and parameterization
![]() | Parameterization The terminal is parameterized via the CoE - Online tab (double-click on the respective object) or via the Process Data tab (assignment of PDOs). |
![]() | EtherCAT XML Device Description The display matches that of the CoE objects from the EtherCAT XML Device Description. It is strongly recommended to download the latest revision of the corresponding XML file from the Beckhoff website (http://www.beckhoff.com/english/default.htm?download/elconfg.htm) and follow the installation instructions. |
Introduction
- Objects required for parameterization during commissioning
- Objects for indicating internal settings (may be fixed)
- Further profile-specific objects indicating inputs, outputs and status information
The following section first describes the objects required for normal operation, followed by a complete overview of missing objects.
Objects to be parameterized during commissioning
Index 1011 Restore default parameters
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1011:0 |
Restore default parameters |
Restore default settings |
UINT8 |
RO |
0x01 (1dec) |
1011:01 |
SubIndex 001 |
If this object is set to 0x64616F6C in the set value dialog, all backup objects are reset to their delivery state. |
UINT32 |
RW |
0x00000000 (0dec) |
Index 8000 DIG Safe state active Ch.1
The outputs for which the DIG Safe state active bit is set are switched to the values specified in Safe state value in the event that the Operational (OP) status is left.
Status Operational (OP) is left if communication to the master is interrupted, for example at power breakdown at the master or cable breakage.
Index |
Name |
Meaning |
Data type |
Flags |
Default |
8000:0 |
DIG Safe state active |
UINT8 |
RO |
0x08 (8dec) |
8000:01 |
Output 1 |
0bin: DIG Safe state for output 1 is switched off 1bin: DIG Safe state for output 1 is switched on |
boolean |
RW |
1bin |
8000:02 |
Output 2 |
0bin: DIG Safe state for output 2 is switched off 1bin: DIG Safe state for output 2 is switched on |
boolean |
RW |
1bin |
8000:03 |
Output 3 |
0bin: DIG Safe state for output 3 is switched off 1bin: DIG Safe state for output 3 is switched on |
boolean |
RW |
1bin |
8000:04 |
Output 4 |
0bin: DIG Safe state for output 4 is switched off 1bin: DIG Safe state for output 4 is switched on |
boolean |
RW |
1bin |
8000:05 |
Output 5 |
0bin: DIG Safe state for output 5 is switched off 1bin: DIG Safe state for output 5 is switched on |
boolean |
RW |
1bin |
8000:06 |
Output 6 |
0bin: DIG Safe state for output 6 is switched off 1bin: DIG Safe state for output 6 is switched on |
boolean |
RW |
1bin |
8000:07 |
Output 7 |
0bin: DIG Safe state for output 7 is switched off 1bin: DIG Safe state for output 7 is switched on |
boolean |
RW |
1bin |
8000:08 |
Output 8 |
0bin: DIG Safe state for output 8 is switched off 1bin: DIG Safe state for output 8 is switched on |
boolean |
RW |
1bin |
Index 8001 DIG Safe state value Ch.1
The values to which the outputs are switched when the status Operational (OP) is left are specified here.
Index |
Name |
Meaning |
Data type |
Flags |
Default |
8001:0 |
DIG Safe state value |
UINT8 |
RO |
0x08 (8dec) |
8001:01 |
Output 1 |
0bin: DIG Safe state value for output 1 = 0 1bin: DIG Safe state value for output 1 = 1 |
boolean |
RW |
0x00 (0dec) |
8001:02 |
Output 2 |
0bin: DIG Safe state value for output 2 = 0 1bin: DIG Safe state value for output 2 = 1 |
boolean |
RW |
0x00 (0dec) |
8001:03 |
Output 3 |
0bin: DIG Safe state value for output 3 = 0 1bin: DIG Safe state value for output 3 = 1 |
boolean |
RW |
0x00 (0dec) |
8001:04 |
Output 4 |
0bin: DIG Safe state value for output 4 = 0 1bin: DIG Safe state value for output 4 = 1 |
boolean |
RW |
0x00 (0dec) |
8001:05 |
Output 5 |
0bin: DIG Safe state value for output 5 = 0 1bin: DIG Safe state value for output 5 = 1 |
boolean |
RW |
0x00 (0dec) |
8001:06 |
Output 6 |
0bin: DIG Safe state value for output 6 = 0 1bin: DIG Safe state value for output 6 = 1 |
boolean |
RW |
0x00 (0dec) |
8001:07 |
Output 7 |
0bin: DIG Safe state value for output 7 = 0 1bin: DIG Safe state value for output 7 = 1 |
boolean |
RW |
0x00 (0dec) |
8001:08 |
Output 8 |
0bin: DIG Safe state value for output 8 = 0 1bin: DIG Safe state value for output 8 = 1 |
boolean |
RW |
0x00 (0dec) |
Index 8010 DIG Safe state active Ch.2
Status Operational (OP) is left if communication to the master is interrupted, for example at power breakdown at the master or wire breakage.
Index |
Name |
Meaning |
Data type |
Flags |
Default |
8010:0 |
UINT8 |
RO |
0x08 (8dec) |
8010:01 |
Output 9 |
0bin: DIG Safe state for output 9 is switched off 1bin: DIG Safe state for output 9 is switched on |
boolean |
RW |
1bin |
8010:02 |
Output 10 |
0bin: DIG Safe state for output 10 is switched off 1bin: DIG Safe state for output 10 is switched on |
boolean |
RW |
1bin |
8010:03 |
Output 11 |
0bin: DIG Safe state for output 11 is switched off 1bin: DIG Safe state for output 11 is switched on |
boolean |
RW |
1bin |
8010:04 |
Output 12 |
0bin: DIG Safe state for output 12 is switched off 1bin: DIG Safe state for output 12 is switched on |
boolean |
RW |
1bin |
8010:05 |
Output 13 |
0bin: DIG Safe state for output 13 is switched off 1bin: DIG Safe state for output 13 is switched on |
boolean |
RW |
1bin |
8010:06 |
Output 14 |
0bin: DIG Safe state for output 14 is switched off 1bin: DIG Safe state for output 14 is switched on |
boolean |
RW |
1bin |
8010:07 |
Output 15 |
0bin: DIG Safe state for output 15 is switched off 1bin: DIG Safe state for output 15 is switched on |
boolean |
RW |
1bin |
8010:08 |
Output 16 |
0bin: DIG Safe state for output 16 is switched off 1bin: DIG Safe state for output 16 is switched on |
boolean |
RW |
1bin |
Index 8011 DIG Safe state value Ch.2
Index |
Name |
Meaning |
Data type |
Flags |
Default |
8011:0 |
UINT8 |
RO |
0x08 (8dec) |
8011:01 |
Output 9 |
0bin: DIG Safe state value for output 9 = 0 1bin: DIG Safe state value for output 9 = 1 |
boolean |
RW |
0x00 (0dec) |
8011:02 |
Output 10 |
0bin: DIG Safe state value for output 10 = 0 1bin: DIG Safe state value for output 10 = 1 |
boolean |
RW |
0x00 (0dec) |
8011:03 |
Output 11 |
0bin: DIG Safe state value for output 11 = 0 1bin: DIG Safe state value for output 11 = 1 |
boolean |
RW |
0x00 (0dec) |
8011:04 |
Output 12 |
0bin: DIG Safe state value for output 12 = 0 1bin: DIG Safe state value for output 12 = 1 |
boolean |
RW |
0x00 (0dec) |
8011:05 |
Output 13 |
0bin: DIG Safe state value for output 13 = 0 1bin: DIG Safe state value for output 13 = 1 |
boolean |
RW |
0x00 (0dec) |
8011:06 |
Output 14 |
0bin: DIG Safe state value for output 14 = 0 1bin: DIG Safe state value for output 14 = 1 |
boolean |
RW |
0x00 (0dec) |
8011:07 |
Output 15 |
0bin: DIG Safe state value for output 15 = 0 1bin: DIG Safe state value for output 15 = 1 |
boolean |
RW |
0x00 (0dec) |
8011:08 |
Output 16 |
0bin: DIG Safe state value for output 16 = 0 1bin: DIG Safe state value for output 16 = 1 |
boolean |
RW |
0x00 (0dec) |
Index 8020 DIG Safe state active Ch.3
Index |
Name |
Meaning |
Data type |
Flags |
Default |
8020:0 |
UINT8 |
RO |
0x08 (8dec) |
8020:01 |
Output 17 |
0bin: DIG Safe state for output 17 is switched off 1bin: DIG Safe state for output 17 is switched on |
boolean |
RW |
1bin |
8020:02 |
Output 18 |
0bin: DIG Safe state for output 18 is switched off 1bin: DIG Safe state for output 18 is switched on |
boolean |
RW |
1bin |
8020:03 |
Output 19 |
0bin: DIG Safe state for output 19 is switched off 1bin: DIG Safe state for output 19 is switched on |
boolean |
RW |
1bin |
8020:04 |
Output 20 |
0bin: DIG Safe state for output 20 is switched off 1bin: DIG Safe state for output 20 is switched on |
boolean |
RW |
1bin |
8020:05 |
Output 21 |
0bin: DIG Safe state for output 21 is switched off 1bin: DIG Safe state for output 21 is switched on |
boolean |
RW |
1bin |
8020:06 |
Output 22 |
0bin: DIG Safe state for output 22 is switched off 1bin: DIG Safe state for output 22 is switched on |
boolean |
RW |
1bin |
8020:07 |
Output 23 |
0bin: DIG Safe state for output 23 is switched off 1bin: DIG Safe state for output 23 is switched on |
boolean |
RW |
1bin |
8020:08 |
Output 24 |
0bin: DIG Safe state for output 24 is switched off 1bin: DIG Safe state for output 24 is switched on |
boolean |
RW |
1bin |
Index 8021 DIG Safe state value Ch.3
Index |
Name |
Meaning |
Data type |
Flags |
Default |
8021:0 |
UINT8 |
RO |
0x08 (8dec) |
8021:01 |
Output 17 |
0bin: DIG Safe state value for output 17 = 0 1bin: DIG Safe state value for output 17 = 1 |
boolean |
RW |
0bin |
8021:02 |
Output 18 |
0bin: DIG Safe state value for output 18 = 0 1bin: DIG Safe state value for output 18 = 1 |
boolean |
RW |
0bin |
8021:03 |
Output 19 |
0bin: DIG Safe state value for output 19 = 0 1bin: DIG Safe state value for output 19 = 1 |
boolean |
RW |
0bin |
8021:04 |
Output 20 |
0bin: DIG Safe state value for output 20 = 0 1bin: DIG Safe state value for output 20 = 1 |
boolean |
RW |
0bin |
8021:05 |
Output 21 |
0bin: DIG Safe state value for output 21 = 0 1bin: DIG Safe state value for output 21 = 1 |
boolean |
RW |
0bin |
8021:06 |
Output 22 |
0bin: DIG Safe state value for output 22 = 0 1bin: DIG Safe state value for output 22 = 1 |
boolean |
RW |
0bin |
8021:07 |
Output 23 |
0bin: DIG Safe state value for output 23 = 0 1bin: DIG Safe state value for output 23 = 1 |
boolean |
RW |
0bin |
8021:08 |
Output 24 |
0bin: DIG Safe state value for output 24 = 0 1bin: DIG Safe state value for output 24 = 1 |
boolean |
RW |
0bin |
Further objects
Standard objects (0x1000-0x1FFF)
The standard objects of all EtherCAT slaves have the same Meaning.
Index 1000 Device type
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1000:0 |
Device type |
Device type of the EtherCAT slave: The Lo-Word contains the supported CoE Profile (5001). The Hi-Word contains the Module Profile corresponding to the Modular Device Profile. |
UINT32 |
RO |
0x01181389 (18355081dec) |
Index 1008 Device name
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1008:0 |
Device name |
Device name of the EtherCAT slave |
string |
RO |
EP2817-0008 |
Index 1009 Hardware version
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1009:0 |
Hardware version |
Hardware version of the EtherCAT slaves |
string |
RO |
Index 100A Software version
Index |
Name |
Meaning |
Data type |
Flags |
Default |
100A:0 |
Software version |
Firmware version of the EtherCAT slaves |
string |
RO |
00 |
Index 1018 Identity
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1018:0 |
Identity |
contains information to identify the EtherCAT slave |
UINT8 |
RO |
0x04 (4dec) |
1018:01 |
Vendor ID |
Vendor ID of the EtherCAT slave |
UINT32 |
RO |
0x00000002 (2dec) |
1018:02 |
Product code |
Product code of the EtherCAT slave |
UINT32 |
RO |
0x0B014052 (184631378dec) |
1018:03 |
Revision |
Revision number of the EtherCAT-Slave, the Lo-Word (Bit 0-15) indicates the special functions terminal number; the Hi-Word (Bit 16-31) refers to the device description. |
UINT32 |
RO |
0x00000000 (0dec) |
1018:04 |
Serial number |
Serial number of the EtherCAT-Slave, the Lo-Byte (Bit 0-7) of the Lo-Word contains the year of manufacturing, the Hi-Byte (Bit 8-15) of the Lo-Word contains the week of manufacturing, the Hi-Word (Bit 16-31) is 0 . |
UINT32 |
RO |
0x00000000 (0dec) |
Index |
Name |
Meaning |
Data type |
Flags |
Default |
10F0:0 |
Backup parameter handling |
contains information for the standardized Upload and Download of the Backup Entries |
UINT8 |
RO |
0x01 (1dec) |
10F0:01 |
Checksum |
Checksum over all backup entries |
UINT32 |
RO |
0x00000000 (0dec) |
Index 1600 DIG RxPDO-Map OutputsCh.1
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1600:0 |
DIG RxPDO-Map OutputsCh.1 |
PDO Mapping RxPDO 1 |
UINT8 |
RO |
0x09 (9dec) |
1600:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x7000 (DIG Outputs Ch.1), entry 0x01 (Output 1)) |
UINT32 |
RO |
0x7000:01, 1 |
1600:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x7000 (DIG Outputs Ch.1), entry 0x02 (Output 2)) |
UINT32 |
RO |
0x7000:02, 1 |
1600:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0x7000 (DIG Outputs Ch.1), entry 0x03 (Output 3)) |
UINT32 |
RO |
0x7000:03, 1 |
1600:04 |
SubIndex 004 |
4. PDO Mapping entry (object 0x7000 (DIG Outputs Ch.1), entry 0x04 (Output 4)) |
UINT32 |
RO |
0x7000:04, 1 |
1600:05 |
SubIndex 005 |
5. PDO Mapping entry (object 0x7000 (DIG Outputs Ch.1), entry 0x05 (Output 5)) |
UINT32 |
RO |
0x7000:05, 1 |
1600:06 |
SubIndex 006 |
6. PDO Mapping entry (object 0x7000 (DIG Outputs Ch.1), entry 0x06 (Output 6)) |
UINT32 |
RO |
0x7000:06, 1 |
1600:07 |
SubIndex 007 |
7. PDO Mapping entry (object 0x7000 (DIG Outputs Ch.1), entry 0x07 (Output 7)) |
UINT32 |
RO |
0x7000:07, 1 |
1600:08 |
SubIndex 008 |
8. PDO Mapping entry (object 0x7000 (DIG Outputs Ch.1), entry 0x08 (Output 8)) |
UINT32 |
RO |
0x7000:08, 1 |
1600:09 |
SubIndex 009 |
9. PDO Mapping entry (8 bits align) |
UINT32 |
RO |
0x0000:00, 8 |
Index 1601 DIG RxPDO-Map OutputsCh.2
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1601:0 |
DIG RxPDO-Map OutputsCh.2 |
PDO Mapping RxPDO 2 |
UINT8 |
RO |
0x09 (9dec) |
1601:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x7010 (DIG Outputs Ch.2), entry 0x01 (Output 1)) |
UINT32 |
RO |
0x7010:01, 1 |
1601:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x7010 (DIG Outputs Ch.2), entry 0x02 (Output 2)) |
UINT32 |
RO |
0x7010:02, 1 |
1601:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0x7010 (DIG Outputs Ch.2), entry 0x03 (Output 3)) |
UINT32 |
RO |
0x7010:03, 1 |
1601:04 |
SubIndex 004 |
4. PDO Mapping entry (object 0x7010 (DIG Outputs Ch.2), entry 0x04 (Output 4)) |
UINT32 |
RO |
0x7010:04, 1 |
1601:05 |
SubIndex 005 |
5. PDO Mapping entry (object 0x7010 (DIG Outputs Ch.2), entry 0x05 (Output 5)) |
UINT32 |
RO |
0x7010:05, 1 |
1601:06 |
SubIndex 006 |
6. PDO Mapping entry (object 0x7010 (DIG Outputs Ch.2), entry 0x06 (Output 6)) |
UINT32 |
RO |
0x7010:06, 1 |
1601:07 |
SubIndex 007 |
7. PDO Mapping entry (object 0x7010 (DIG Outputs Ch.2), entry 0x07 (Output 7)) |
UINT32 |
RO |
0x7010:07, 1 |
1601:08 |
SubIndex 008 |
8. PDO Mapping entry (object 0x7010 (DIG Outputs Ch.2), entry 0x08 (Output 8)) |
UINT32 |
RO |
0x7010:08, 1 |
1601:09 |
SubIndex 009 |
UINT32 |
RO |
0x0000:00, 8 |
Index 1602 DIG RxPDO-Map OutputsCh.3
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1602:0 |
DIG RxPDO-Map OutputsCh.3 |
PDO Mapping RxPDO 3 |
UINT8 |
RO |
0x09 (9dec) |
1602:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x7020 (DIG Outputs Ch.3), entry 0x01 (Output 1)) |
UINT32 |
RO |
0x7020:01, 1 |
1602:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x7020 (DIG Outputs Ch.3), entry 0x02 (Output 2)) |
UINT32 |
RO |
0x7020:02, 1 |
1602:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0x7020 (DIG Outputs Ch.3), entry 0x03 (Output 3)) |
UINT32 |
RO |
0x7020:03, 1 |
1602:04 |
SubIndex 004 |
4. PDO Mapping entry (object 0x7020 (DIG Outputs Ch.3), entry 0x04 (Output 4)) |
UINT32 |
RO |
0x7020:04, 1 |
1602:05 |
SubIndex 005 |
5. PDO Mapping entry (object 0x7020 (DIG Outputs Ch.3), entry 0x05 (Output 5)) |
UINT32 |
RO |
0x7020:05, 1 |
1602:06 |
SubIndex 006 |
6. PDO Mapping entry (object 0x7020 (DIG Outputs Ch.3), entry 0x06 (Output 6)) |
UINT32 |
RO |
0x7020:06, 1 |
1602:07 |
SubIndex 007 |
7. PDO Mapping entry (object 0x7020 (DIG Outputs Ch.3), entry 0x07 (Output 7)) |
UINT32 |
RO |
0x7020:07, 1 |
1602:08 |
SubIndex 008 |
8. PDO Mapping entry (object 0x7020 (DIG Outputs Ch.3), entry 0x08 (Output 8)) |
UINT32 |
RO |
0x7020:08, 1 |
1602:09 |
SubIndex 009 |
UINT32 |
RO |
0x0000:00, 8 |
Index 1603 DIG RxPDO-Map Outputs Device
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1603:0 |
DIG RxPDO-Map Outputs Device |
PDO Mapping RxPDO 4 |
UINT8 |
RO |
0x03 (3dec) |
1603:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0xF700 (DIG Outputs), entry 0x01 (Set safe state)) |
UINT32 |
RO |
0xF700:01, 1 |
1603:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0xF700 (DIG Outputs), entry 0x02 (Reset outputs)) |
UINT32 |
RO |
0xF700:02, 1 |
1603:03 |
SubIndex 003 |
3. PDO Mapping entry (14 bits align) |
UINT32 |
RO |
0x0000:00, 14 |
Index 1A00 DIG TxPDO-Map Diag Inputs Ch.1
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1A00:0 |
DIG TxPDO-Map Diag Inputs Ch.1 |
PDO Mapping TxPDO 1 |
UINT8 |
RO |
0x09 (9dec) |
1A00:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6001 (DIG Diag Inputs Ch.1), entry 0x01 (Diag Input 1)) |
UINT32 |
RO |
0x6001:01, 1 |
1A00:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x6001 (DIG Diag Inputs Ch.1), entry 0x02 (Diag Input 2)) |
UINT32 |
RO |
0x6001:02, 1 |
1A00:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0x6001 (DIG Diag Inputs Ch.1), entry 0x03 (Diag Input 3)) |
UINT32 |
RO |
0x6001:03, 1 |
1A00:04 |
SubIndex 004 |
4. PDO Mapping entry (object 0x6001 (DIG Diag Inputs Ch.1), entry 0x04 (Diag Input 4)) |
UINT32 |
RO |
0x6001:04, 1 |
1A00:05 |
SubIndex 005 |
5. PDO Mapping entry (object 0x6001 (DIG Diag Inputs Ch.1), entry 0x05 (Diag Input 5)) |
UINT32 |
RO |
0x6001:05, 1 |
1A00:06 |
SubIndex 006 |
6. PDO Mapping entry (object 0x6001 (DIG Diag Inputs Ch.1), entry 0x06 (Diag Input 6)) |
UINT32 |
RO |
0x6001:06, 1 |
1A00:07 |
SubIndex 007 |
7. PDO Mapping entry (object 0x6001 (DIG Diag Inputs Ch.1), entry 0x07 (Diag Input 7)) |
UINT32 |
RO |
0x6001:07, 1 |
1A00:08 |
SubIndex 008 |
8. PDO Mapping entry (object 0x6001 (DIG Diag Inputs Ch.1), entry 0x08 (Diag Input 8)) |
UINT32 |
RO |
0x6001:08, 1 |
1A00:09 |
SubIndex 009 |
UINT32 |
RO |
0x0000:00, 8 |
Index 1A01 DIG TxPDO-Map Diag Inputs Ch.2
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1A01:0 |
DIG TxPDO-Map Diag Inputs Ch.2 |
PDO Mapping TxPDO 2 |
UINT8 |
RO |
0x09 (9dec) |
1A01:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6011 (DIG Diag Inputs Ch.2), entry 0x01 (Diag Input 1)) |
UINT32 |
RO |
0x6011:01, 1 |
1A01:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x6011 (DIG Diag Inputs Ch.2), entry 0x02 (Diag Input 2)) |
UINT32 |
RO |
0x6011:02, 1 |
1A01:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0x6011 (DIG Diag Inputs Ch.2), entry 0x03 (Diag Input 3)) |
UINT32 |
RO |
0x6011:03, 1 |
1A01:04 |
SubIndex 004 |
4. PDO Mapping entry (object 0x6011 (DIG Diag Inputs Ch.2), entry 0x04 (Diag Input 4)) |
UINT32 |
RO |
0x6011:04, 1 |
1A01:05 |
SubIndex 005 |
5. PDO Mapping entry (object 0x6011 (DIG Diag Inputs Ch.2), entry 0x05 (Diag Input 5)) |
UINT32 |
RO |
0x6011:05, 1 |
1A01:06 |
SubIndex 006 |
6. PDO Mapping entry (object 0x6011 (DIG Diag Inputs Ch.2), entry 0x06 (Diag Input 6)) |
UINT32 |
RO |
0x6011:06, 1 |
1A01:07 |
SubIndex 007 |
7. PDO Mapping entry (object 0x6011 (DIG Diag Inputs Ch.2), entry 0x07 (Diag Input 7)) |
UINT32 |
RO |
0x6011:07, 1 |
1A01:08 |
SubIndex 008 |
8. PDO Mapping entry (object 0x6011 (DIG Diag Inputs Ch.2), entry 0x08 (Diag Input 8)) |
UINT32 |
RO |
0x6011:08, 1 |
1A01:09 |
SubIndex 009 |
UINT32 |
RO |
0x0000:00, 8 |
Index 1A02 DIG TxPDO-Map Diag Inputs Ch.3
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1A02:0 |
DIG TxPDO-Map Diag Inputs Ch.3 |
PDO Mapping TxPDO 3 |
UINT8 |
RO |
0x09 (9dec) |
1A02:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6021 (DIG Diag Inputs Ch.3), entry 0x01 (Diag Input 1)) |
UINT32 |
RO |
0x6021:01, 1 |
1A02:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x6021 (DIG Diag Inputs Ch.3), entry 0x02 (Diag Input 2)) |
UINT32 |
RO |
0x6021:02, 1 |
1A02:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0x6021 (DIG Diag Inputs Ch.3), entry 0x03 (Diag Input 3)) |
UINT32 |
RO |
0x6021:03, 1 |
1A02:04 |
SubIndex 004 |
4. PDO Mapping entry (object 0x6021 (DIG Diag Inputs Ch.3), entry 0x04 (Diag Input 4)) |
UINT32 |
RO |
0x6021:04, 1 |
1A02:05 |
SubIndex 005 |
5. PDO Mapping entry (object 0x6021 (DIG Diag Inputs Ch.3), entry 0x05 (Diag Input 5)) |
UINT32 |
RO |
0x6021:05, 1 |
1A02:06 |
SubIndex 006 |
6. PDO Mapping entry (object 0x6021 (DIG Diag Inputs Ch.3), entry 0x06 (Diag Input 6)) |
UINT32 |
RO |
0x6021:06, 1 |
1A02:07 |
SubIndex 007 |
7. PDO Mapping entry (object 0x6021 (DIG Diag Inputs Ch.3), entry 0x07 (Diag Input 7)) |
UINT32 |
RO |
0x6021:07, 1 |
1A02:08 |
SubIndex 008 |
8. PDO Mapping entry (object 0x6021 (DIG Diag Inputs Ch.3), entry 0x08 (Diag Input 8)) |
UINT32 |
RO |
0x6021:08, 1 |
1A02:09 |
SubIndex 009 |
UINT32 |
RO |
0x0000:00, 8 |
Index 1A03 DIG TxPDO-Map Inputs Device
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1A03:0 |
DIG TxPDO-Map Inputs Device |
PDO Mapping TxPDO 4 |
UINT8 |
RO |
0x0A (10dec) |
1A03:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0xF600 (DIG Inputs), entry 0x01 (Safe state active)) |
UINT32 |
RO |
0xF600:01, 1 |
1A03:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0xF600 (DIG Inputs), entry 0x02 (Error channel 1)) |
UINT32 |
RO |
0xF600:02, 1 |
1A03:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0xF600 (DIG Inputs), entry 0x03 (Error channel 2)) |
UINT32 |
RO |
0xF600:03, 1 |
1A03:04 |
SubIndex 004 |
4. PDO Mapping entry (object 0xF600 (DIG Inputs), entry 0x04 (Error channel 3)) |
UINT32 |
RO |
0xF600:04, 1 |
1A03:05 |
SubIndex 005 |
5. PDO Mapping entry (object 0xF600 (DIG Inputs), entry 0x05 (Us Undervoltage)) |
UINT32 |
RO |
0xF600:05, 1 |
1A03:06 |
SubIndex 006 |
6. PDO Mapping entry (object 0xF600 (DIG Inputs), entry 0x06 (Up Undervoltage)) |
UINT32 |
RO |
0xF600:06, 1 |
1A03:07 |
SubIndex 007 |
7. PDO Mapping entry (7 bits align) |
UINT32 |
RO |
0x0000:00, 7 |
1A03:08 |
SubIndex 008 |
8. PDO Mapping entry (object 0xF600 (DIG Inputs), entry 0x0E (Sync error)) |
UINT32 |
RO |
0xF600:0E, 1 |
1A03:09 |
SubIndex 009 |
9. PDO Mapping entry (1 bits align) |
UINT32 |
RO |
0x0000:00, 1 |
1A03:0A |
SubIndex 010 |
10. PDO Mapping entry (object 0xF600 (DIG Inputs), entry 0x10 (TxPDO Toggle)) |
UINT32 |
RO |
0xF600:10, 1 |
Index 1C00 Sync manager type
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1C00:0 |
Sync manager type |
Usage of the Sync Manager channels |
UINT8 |
RO |
0x04 (4dec) |
1C00:01 |
SubIndex 001 |
Sync-Manager Type Channel 1: Mailbox Write |
UINT8 |
RO |
0x01 (1dec) |
1C00:02 |
SubIndex 002 |
Sync-Manager Type Channel 2: Mailbox Read |
UINT8 |
RO |
0x02 (2dec) |
1C00:03 |
SubIndex 003 |
Sync-Manager Type Channel 3: Process Data Write (Outputs) |
UINT8 |
RO |
0x03 (3dec) |
1C00:04 |
SubIndex 004 |
Sync-Manager Type Channel 4: Process Data Read (Inputs) |
UINT8 |
RO |
0x04 (4dec) |
Index 1C12 RxPDO assign
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1C12:0 |
RxPDO assign |
PDO Assign Outputs |
UINT8 |
RW |
0x04 (4dec) |
1C12:01 |
Subindex 001 |
1. assigned RxPDO (contains the index of the corresponding RxPDO Mapping object) |
UINT16 |
RW |
0x1600 (5632dec) |
1C12:02 |
Subindex 002 |
2. assigned RxPDO (contains the index of the corresponding RxPDO Mapping object) |
UINT16 |
RW |
0x1601 (5633dec) |
1C12:03 |
Subindex 003 |
3. assigned RxPDO (contains the index of the corresponding RxPDO Mapping object) |
UINT16 |
RW |
0x1602 (5634dec) |
1C12:04 |
Subindex 004 |
4. assigned RxPDO (contains the index of the corresponding RxPDO Mapping object) |
UINT16 |
RW |
0x1603 (5635dec) |
Index 1C13 TxPDO assign
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1C13:0 |
TxPDO assign |
PDO Assign Inputs |
UINT8 |
RW |
0x04 (4dec) |
1C13:01 |
Subindex 001 |
1. assigned TxPDO (contains the index of the corresponding TxPDO Mapping object) |
UINT16 |
RW |
0x1A00 (6656dec) |
1C13:02 |
Subindex 002 |
2. assigned TxPDO (contains the index of the corresponding TxPDO Mapping object) |
UINT16 |
RW |
0x1A01 (6657dec) |
1C13:03 |
Subindex 003 |
3. assigned TxPDO (contains the index of the corresponding TxPDO Mapping object) |
UINT16 |
RW |
0x1A02 (6658dec) |
1C13:04 |
Subindex 004 |
4. assigned TxPDO (contains the index of the corresponding TxPDO Mapping object) |
UINT16 |
RW |
0x1A03 (6659dec) |
Index 1C32SM Output parameter
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1C32:0 |
SM output parameter |
Synchronization parameter of the outputs |
UINT8 |
RO |
0x20 (32dec) |
1C32:01 |
Sync mode |
actual synchronization mode:
UINT16 |
RW |
0x0001 (1dec) |
1C32:02 |
Cycle time |
Cycle time (in ns):
UINT32 |
RW |
0x003D0900 (4000000dec) |
1C32:03 |
Shift time |
Time between SYNC0 Event and Outputs Valid (in ns, only in DC-Mode) |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:04 |
Sync modes supported |
Supported synchronization modes:
UINT16 |
RO |
0x000A (10dec) |
1C32:05 |
Minimum cycle time |
Minimum cycle time supported (in ns) |
UINT32 |
RO |
0x000493E0 (300000dec) |
1C32:06 |
Calc and copy time |
Minimal time between SYNC0 and SYNC1 Event (in ns, only in DC-Mode) |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:07 |
Minimum delay time |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:08 |
Command |
The Entries 1C32:03, 1C32:05, 1C32:06, 1C32:09, 1C33:03, 1C33:06, 1C33:09 will be updated with the maximum measured values. |
UINT16 |
RW |
0x0000 (0dec) |
1C32:09 |
Maximum delay time |
Time between SYNC1 Event and Outputs Valid (in ns, only in DC-Mode) |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:0B |
SM event missed counter |
Number of the missed SM-Events in state OPERATIONAL (only in DC Mode) |
UINT16 |
RO |
0x0000 (0dec) |
1C32:0C |
Cycle exceeded counter |
Number of exceeded cycles in state OPERATIONAL |
UINT16 |
RO |
0x0000 (0dec) |
1C32:0D |
Shift too short counter |
Number of inadequate distances between SYNC0 and SYNC1 events (only in DC Mode) |
UINT16 |
RO |
0x0000 (0dec) |
1C32:20 |
Sync error |
TRUE: In the last cycle the synchronization was not correct (only in DC Mode) |
boolean |
RO |
0x00 (0dec) |
Index 1C33 SM input parameter
Index |
Name |
Meaning |
Data type |
Flags |
Default |
1C33:0 |
SM input parameter |
Synchronization parameter of the inputs |
UINT8 |
RO |
0x20 (32dec) |
1C33:01 |
Sync mode |
UINT16 |
RW |
0x0022 (34dec) |
1C33:02 |
Cycle time |
same as 1C32:02 |
UINT32 |
RW |
1C33:03 |
Shift time |
time between SYNC0-Event and Input Latch (in ns, only in DC-Mode) |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:04 |
UINT16 |
RO |
0x000A (10dec) |
1C33:05 |
same as 1C32:05 |
UINT32 |
RO |
1C33:06 |
time between Input Latch and the availability of the inputs for the master (in ns, only in DC-Mode) |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:07 |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:08 |
Command |
same as 1C32:08 |
UINT16 |
RW |
0x0000 (0dec) |
1C33:09 |
time between SYNC1-Event and Input Latch (in ns, only in DC-Mode) |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:0B |
same as 1C32:11 |
UINT16 |
RO |
0x0000 (0dec) |
1C33:0C |
same as 1C32:12 |
UINT16 |
RO |
0x0000 (0dec) |
1C33:0D |
same as 1C32:13 |
UINT16 |
RO |
0x0000 (0dec) |
1C33:20 |
Sync error |
same as 1C32:32 |
boolean |
RO |
0x00 (0dec) |
Profile specific objects (0x6000-0xFFFF)
The profile specific objects have the same meaning for all EtherCAT Slaves which support the profile 5001.
Index 6001 DIG Diag Inputs Ch.1
Index |
Name |
Meaning |
Data type |
Flags |
Default |
6001:0 |
DIG Diag Inputs Ch.1 |
UINT8 |
RO |
0x08 (8dec) |
6001:01 |
Diag Input 1 |
boolean |
RO |
0x00 (0dec) |
6001:02 |
Diag Input 2 |
boolean |
RO |
0x00 (0dec) |
6001:03 |
Diag Input 3 |
boolean |
RO |
0x00 (0dec) |
6001:04 |
Diag Input 4 |
boolean |
RO |
0x00 (0dec) |
6001:05 |
Diag Input 5 |
boolean |
RO |
0x00 (0dec) |
6001:06 |
Diag Input 6 |
boolean |
RO |
0x00 (0dec) |
6001:07 |
Diag Input 7 |
boolean |
RO |
0x00 (0dec) |
6001:08 |
Diag Input 8 |
boolean |
RO |
0x00 (0dec) |
Index 6011 DIG Diag Inputs Ch.2
Index |
Name |
Meaning |
Data type |
Flags |
Default |
6011:0 |
DIG Diag Inputs Ch.2 |
UINT8 |
RO |
0x08 (8dec) |
6011:01 |
Diag Input 1 |
boolean |
RO |
0x00 (0dec) |
6011:02 |
Diag Input 2 |
boolean |
RO |
0x00 (0dec) |
6011:03 |
Diag Input 3 |
boolean |
RO |
0x00 (0dec) |
6011:04 |
Diag Input 4 |
boolean |
RO |
0x00 (0dec) |
6011:05 |
Diag Input 5 |
boolean |
RO |
0x00 (0dec) |
6011:06 |
Diag Input 6 |
boolean |
RO |
0x00 (0dec) |
6011:07 |
Diag Input 7 |
boolean |
RO |
0x00 (0dec) |
6011:08 |
Diag Input 8 |
boolean |
RO |
0x00 (0dec) |
Index 6021 DIG Diag Inputs Ch.3
Index |
Name |
Meaning |
Data type |
Flags |
Default |
6021:0 |
DIG Diag Inputs Ch.3 |
UINT8 |
RO |
0x08 (8dec) |
6021:01 |
Diag Input 1 |
boolean |
RO |
0x00 (0dec) |
6021:02 |
Diag Input 2 |
boolean |
RO |
0x00 (0dec) |
6021:03 |
Diag Input 3 |
boolean |
RO |
0x00 (0dec) |
6021:04 |
Diag Input 4 |
boolean |
RO |
0x00 (0dec) |
6021:05 |
Diag Input 5 |
boolean |
RO |
0x00 (0dec) |
6021:06 |
Diag Input 6 |
boolean |
RO |
0x00 (0dec) |
6021:07 |
Diag Input 7 |
boolean |
RO |
0x00 (0dec) |
6021:08 |
Diag Input 8 |
boolean |
RO |
0x00 (0dec) |
Index 7000 DIG Outputs Ch.1
Index |
Name |
Meaning |
Data type |
Flags |
Default |
7000:0 |
DIG Outputs Ch.1 |
UINT8 |
RO |
0x08 (8dec) |
7000:01 |
Output 1 |
boolean |
RO |
0x00 (0dec) |
7000:02 |
Output 2 |
boolean |
RO |
0x00 (0dec) |
7000:03 |
Output 3 |
boolean |
RO |
0x00 (0dec) |
7000:04 |
Output 4 |
boolean |
RO |
0x00 (0dec) |
7000:05 |
Output 5 |
boolean |
RO |
0x00 (0dec) |
7000:06 |
Output 6 |
boolean |
RO |
0x00 (0dec) |
7000:07 |
Output 7 |
boolean |
RO |
0x00 (0dec) |
7000:08 |
Output 8 |
boolean |
RO |
0x00 (0dec) |
Index 7010 DIG Outputs Ch.2
Index |
Name |
Meaning |
Data type |
Flags |
Default |
7010:0 |
DIG Outputs Ch.2 |
UINT8 |
RO |
0x08 (8dec) |
7010:01 |
Output 1 |
boolean |
RO |
0x00 (0dec) |
7010:02 |
Output 2 |
boolean |
RO |
0x00 (0dec) |
7010:03 |
Output 3 |
boolean |
RO |
0x00 (0dec) |
7010:04 |
Output 4 |
boolean |
RO |
0x00 (0dec) |
7010:05 |
Output 5 |
boolean |
RO |
0x00 (0dec) |
7010:06 |
Output 6 |
boolean |
RO |
0x00 (0dec) |
7010:07 |
Output 7 |
boolean |
RO |
0x00 (0dec) |
7010:08 |
Output 8 |
boolean |
RO |
0x00 (0dec) |
Index 7020 DIG Outputs Ch.3
Index |
Name |
Meaning |
Data type |
Flags |
Default |
7020:0 |
DIG Outputs Ch.3 |
UINT8 |
RO |
0x08 (8dec) |
7020:01 |
Output 1 |
boolean |
RO |
0x00 (0dec) |
7020:02 |
Output 2 |
boolean |
RO |
0x00 (0dec) |
7020:03 |
Output 3 |
boolean |
RO |
0x00 (0dec) |
7020:04 |
Output 4 |
boolean |
RO |
0x00 (0dec) |
7020:05 |
Output 5 |
boolean |
RO |
0x00 (0dec) |
7020:06 |
Output 6 |
boolean |
RO |
0x00 (0dec) |
7020:07 |
Output 7 |
boolean |
RO |
0x00 (0dec) |
7020:08 |
Output 8 |
boolean |
RO |
0x00 (0dec) |
Index |
Name |
Meaning |
Data type |
Flags |
Default |
F000:0 |
Modular device profile |
general information about the Modular Device Profile |
UINT8 |
RO |
0x02 (2dec) |
F000:01 |
Module index distance |
Index distance between the objects of two channels |
UINT16 |
RO |
0x0010 (16dec) |
F000:02 |
Maximum number of modules |
number of channels |
UINT16 |
RO |
0x0003 (3dec) |
Index F008 Code word
Index |
Name |
Meaning |
Data type |
Flags |
Default |
F008:0 |
Code word |
UINT32 |
RW |
0x00000000 (0dec) |
Index F010 Module list
Index |
Name |
Meaning |
Data type |
Flags |
Default |
F010:0 |
Module list |
UINT8 |
RW |
0x03 (3dec) |
F010:01 |
SubIndex 001 |
UINT32 |
RW |
0x00000118 (280dec) |
F010:02 |
SubIndex 002 |
UINT32 |
RW |
F010:03 |
SubIndex 003 |
UINT32 |
RW |
Index F600 DIG Inputs
Index |
Name |
Meaning |
Data type |
Flags |
Default |
F600:0 |
DIG Inputs |
UINT8 |
RO |
0x10 (16dec) |
F600:01 |
Safe state active |
boolean |
RO |
0x00 (0dec) |
F600:02 |
Error channel 1 |
boolean |
RO |
0x00 (0dec) |
F600:03 |
Error channel 2 |
boolean |
RO |
0x00 (0dec) |
F600:04 |
Error channel 3 |
boolean |
RO |
0x00 (0dec) |
F600:05 |
Us Undervoltage |
boolean |
RO |
0x00 (0dec) |
F600:06 |
Up Undervoltage |
boolean |
RO |
0x00 (0dec) |
F600:0E |
Sync error |
boolean |
RO |
0x00 (0dec) |
F600:10 |
TxPDO Toggle |
boolean |
RO |
0x00 (0dec) |
Index F700 DIG Outputs
Index |
Name |
Meaning |
Data type |
Flags |
Default |
F700:0 |
DIG Outputs |
UINT8 |
RO |
0x02 (2dec) |
F700:01 |
Set safe state |
boolean |
RO |
0x00 (0dec) |
F700:02 |
Reset outputs |
boolean |
RO |
0x00 (0dec) |
Index F800 DIG Settings
Index |
Name |
Meaning |
Data type |
Flags |
Default |
F800:0 |
DIG Settings |
UINT8 |
RO |
0x11 (17dec) |
F800:01 |
Disable shut off |
boolean |
RW |
0x00 (0dec) |
F800:11 |
Switch off time |
UINT16 |
RW |
0x000A (10dec) |