Standard objects
Index 1000 Device type
1000:0 | Device type | Device type of the EtherCAT slave: the low word contains the used CoE profile (5001). The high word contains the module profile according to the modular device profile. | UINT32 | RO | 0x00001389 (5001dec) |
Index 1008 Device name
1008:0 | Device name | Device name of the EtherCAT device. | STRING | RO | EP1839-0022 / EP1839-0042 |
Index 1009 Hardware version
1009:0 | Hardware version | Hardware version of the EtherCAT device. | STRING | RO |
Index 100A Software version
100A:0 | Software version | Firmware version of the EtherCAT device. | STRING | RO | 02 |
Index 100B Bootloader version
100B:0 | Bootloader version |
| STRING | RO | N/A |
Index 1011 Restore default parameters
1011:0 | Restore default parameters | Restore default parameters | UINT8 | RO | 0x01 (1dec) |
1011:01 | SubIndex 001 | If this object is set to the value "0x64616F6C", all backup objects are reset to the delivery state. | UINT32 | RW | 0x00000000 (0dec) |
Index 1018 Identity
1018:0 | Identity | Information for identifying the slave | UINT8 | RO | 0x04 (4dec) |
1018:01 | Vendor ID | Vendor ID of the EtherCAT slave | UINT32 | RO | 0x00000002 (2dec) |
1018:02 | Product code | Product code of the EtherCAT slave | UINT32 | RO | 0x072F4052 (120537170dec) |
1018:03 | Revision | Revision number of the EtherCAT slave; the Low Word (bit 0-15) indicates the special terminal number, the High Word (bit 16-31) refers to the device description | UINT32 | RO | 0x00000000 (0dec) |
1018:04 | Serial number | Serial number of the EtherCAT slave; the Low Byte (bit 0-7) of the Low Word contains the year of production, the High Byte (bit 8-15) of the Low Word contains the week of production, the High Word (bit 16-31) is 0 | UINT32 | RO | 0x00000000 (0dec) |
Index 10E2 Manufacturer-specific Identification Code
10E2:0 | Manufacturer-specific Identification Code |
10E2:01 | SubIndex 001 | reserved | STRING | RO |
10F0:01 | Checksum | Checksum across all backup entries of the EtherCAT slave | UINT32 | RO | 0x00000000 (0dec) |
Index 10F3 Diagnosis History
10F3:0 | Diagnosis History |
| UINT8 | RO | 0x15 (21dec) |
10F3:01 | Maximum Messages | Maximum number of stored messages | UINT8 | RO | 0x00 (0dec) |
10F3:02 | Newest Message | Subindex of the latest message. | UINT8 | RO | 0x00 (0dec) |
10F3:03 | Newest Acknowledged Message | Subindex of the last confirmed message. | UINT8 | RW | 0x00 (0dec) |
10F3:04 | New Messages Available | Indicates that a new message is available. | BOOLEAN | RO | 0x00 (0dec) |
10F3:05 | Flags |
| UINT16 | RW | 0x0000 (0dec) |
10F3:06 | Diagnosis Message 001 | Diag Message 1 | OCTET-STRING[20] | RO | {0} |
10F3:15 | Diagnosis Message 016 | Diag Message 16 | OCTET-STRING[20] | RO | {0} |
Index 10F8 Timestamp Object
10F8:0 | Timestamp Object | Timestamp | UINT64 | RO |
Index 10F9 Time Distribution Object
10F9:0 | Time Distribution Object |
10F9:01 | Distributed Time Value | Object for time distribution by the EtherCAT master. | UINT64 | RW |
Index 1602 DOS RxPDO-Map Output
1602:0 | DOS RxPDO-Map Output | PDO Mapping RxPDO 3 | UINT8 | RO | 0x08 (8dec) |
1602:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x7100 (DOS Output Ch.01), entry 0x01 (Output)) | UINT32 | RO | 0x7100:01, 1 |
1602:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x7110 (DOS Output Ch.02), entry 0x01 (Output)) | UINT32 | RO | 0x7110:01, 1 |
1602:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x7120 (DOS Output Ch.03), entry 0x01 (Output)) | UINT32 | RO | 0x7120:01, 1 |
1602:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x7130 (DOS Output Ch.04), entry 0x01 (Output)) | UINT32 | RO | 0x7130:01, 1 |
1602:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x7140 (DOS Output Ch.05), entry 0x01 (Output)) | UINT32 | RO | 0x7140:01, 1 |
1602:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x7150 (DOS Output Ch.06), entry 0x01 (Output)) | UINT32 | RO | 0x7150:01, 1 |
1602:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x7160 (DOS Output Ch.07), entry 0x01 (Output)) | UINT32 | RO | 0x7160:01, 1 |
1602:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x7170 (DOS Output Ch.08), entry 0x01 (Output)) | UINT32 | RO | 0x7170:01, 1 |
Index 1801 DIP TxPDO-Par Diagnosis
1801:0 | DIP TxPDO-Par Diagnosis | PDO parameter TxPDO 2 | UINT8 | RO | 0x06 (6dec) |
1801:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 2 | OCTET-STRING[2] | RO | 04 1A |
Index 1804 DIP TxPDO-Par Extended Diagnosis
1804:0 | DIP TxPDO-Par Extended Diagnosis | PDO parameter TxPDO 5 | UINT8 | RO | 0x06 (6dec) |
1804:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 5 | OCTET-STRING[2] | RO | 01 1A |
Index 1A00 DIP TxPDO-Map Input
1A00:0 | DIP TxPDO-Map Input | PDO Mapping TxPDO 1 | UINT8 | RO | 0x10 (16dec) |
1A00:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6000 (DIP Input Ch.01), entry 0x01 (Input)) | UINT32 | RO | 0x6000:01, 1 |
1A00:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6010 (DIP Input Ch.02), entry 0x01 (Input)) | UINT32 | RO | 0x6010:01, 1 |
1A00:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6020 (DIP Input Ch.03), entry 0x01 (Input)) | UINT32 | RO | 0x6020:01, 1 |
1A00:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6030 (DIP Input Ch.04), entry 0x01 (Input)) | UINT32 | RO | 0x6030:01, 1 |
1A00:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6040 (DIP Input Ch.05), entry 0x01 (Input)) | UINT32 | RO | 0x6040:01, 1 |
1A00:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6050 (DIP Input Ch.06), entry 0x01 (Input)) | UINT32 | RO | 0x6050:01, 1 |
1A00:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6060 (DIP Input Ch.07), entry 0x01 (Input)) | UINT32 | RO | 0x6060:01, 1 |
1A00:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6070 (DIP Input Ch.08), entry 0x01 (Input)) | UINT32 | RO | 0x6070:01, 1 |
1A00:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6080 (DIP Input Ch.09), entry 0x01 (Input)) | UINT32 | RO | 0x6080:01, 1 |
1A00:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6090 (DIP Input Ch.10), entry 0x01 (Input)) | UINT32 | RO | 0x6090:01, 1 |
1A00:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x60A0 (DIP Input Ch.11), entry 0x01 (Input)) | UINT32 | RO | 0x60A0:01, 1 |
1A00:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x60B0 (DIP Input Ch.12), entry 0x01 (Input)) | UINT32 | RO | 0x60B0:01, 1 |
1A00:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x60C0 (DIP Input Ch.13), entry 0x01 (Input)) | UINT32 | RO | 0x60C0:01, 1 |
1A00:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x60D0 (DIP Input Ch.14), entry 0x01 (Input)) | UINT32 | RO | 0x60D0:01, 1 |
1A00:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x60E0 (DIP Input Ch.15), entry 0x01 (Input)) | UINT32 | RO | 0x60E0:01, 1 |
1A00:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x60F0 (DIP Input Ch.16), entry 0x01 (Input)) | UINT32 | RO | 0x60F0:01, 1 |
Index 1A01 DIP TxPDO-Map Diagnosis
1A01:0 | DIP TxPDO-Map Diagnosis | PDO Mapping TxPDO 2 | UINT8 | RO | 0x10 (16dec) |
1A01:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (DIP Diagnosis Ch.01), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6001:01, 1 |
1A01:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6011 (DIP Diagnosis Ch.02), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6011:01, 1 |
1A01:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6021 (DIP Diagnosis Ch.03), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6021:01, 1 |
1A01:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6031 (DIP Diagnosis Ch.04), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6031:01, 1 |
1A01:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6041 (DIP Diagnosis Ch.05), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6041:01, 1 |
1A01:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6051 (DIP Diagnosis Ch.06), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6051:01, 1 |
1A01:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6061 (DIP Diagnosis Ch.07), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6061:01, 1 |
1A01:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6071 (DIP Diagnosis Ch.08), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6071:01, 1 |
1A01:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6081 (DIP Diagnosis Ch.09), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6081:01, 1 |
1A01:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6091 (DIP Diagnosis Ch.10), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6091:01, 1 |
1A01:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x60A1 (DIP Diagnosis Ch.11), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x60A1:01, 1 |
1A01:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x60B1 (DIP Diagnosis Ch.12), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x60B1:01, 1 |
1A01:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x60C1 (DIP Diagnosis Ch.13), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x60C1:01, 1 |
1A01:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x60D1 (DIP Diagnosis Ch.14), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x60D1:01, 1 |
1A01:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x60E1 (DIP Diagnosis Ch.15), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x60E1:01, 1 |
1A01:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x60F1 (DIP Diagnosis Ch.16), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x60F1:01, 1 |
Index 1A02 DOS TxPDO-Map Diagnosis
1A02:0 | DOS TxPDO-Map Diagnosis | PDO Mapping TxPDO 3 | UINT8 | RO | 0x20 (32dec) |
1A02:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6100 (DOS Diagnosis Ch.01), entry 0x01 (Overcurrent)) | UINT32 | RO | 0x6100:01, 1 |
1A02:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6100 (DOS Diagnosis Ch.01), entry 0x02 (Overload)) | UINT32 | RO | 0x6100:02, 1 |
1A02:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6100 (DOS Diagnosis Ch.01), entry 0x03 (Open Load)) | UINT32 | RO | 0x6100:03, 1 |
1A02:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6100 (DOS Diagnosis Ch.01), entry 0x04 (Short to 24V)) | UINT32 | RO | 0x6100:04, 1 |
1A02:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6110 (DOS Diagnosis Ch.02), entry 0x01 (Overcurrent)) | UINT32 | RO | 0x6110:01, 1 |
1A02:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6110 (DOS Diagnosis Ch.02), entry 0x02 (Overload)) | UINT32 | RO | 0x6110:02, 1 |
1A02:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6110 (DOS Diagnosis Ch.02), entry 0x03 (Open Load)) | UINT32 | RO | 0x6110:03, 1 |
1A02:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6110 (DOS Diagnosis Ch.02), entry 0x04 (Short to 24V)) | UINT32 | RO | 0x6110:04, 1 |
1A02:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6120 (DOS Diagnosis Ch.03), entry 0x01 (Overcurrent)) | UINT32 | RO | 0x6120:01, 1 |
1A02:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6120 (DOS Diagnosis Ch.03), entry 0x02 (Overload)) | UINT32 | RO | 0x6120:02, 1 |
1A02:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6120 (DOS Diagnosis Ch.03), entry 0x03 (Open Load)) | UINT32 | RO | 0x6120:03, 1 |
1A02:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x6120 (DOS Diagnosis Ch.03), entry 0x04 (Short to 24V)) | UINT32 | RO | 0x6120:04, 1 |
1A02:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x6130 (DOS Diagnosis Ch.04), entry 0x01 (Overcurrent)) | UINT32 | RO | 0x6130:01, 1 |
1A02:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x6130 (DOS Diagnosis Ch.04), entry 0x02 (Overload)) | UINT32 | RO | 0x6130:02, 1 |
1A02:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x6130 (DOS Diagnosis Ch.04), entry 0x03 (Open Load)) | UINT32 | RO | 0x6130:03, 1 |
1A02:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x6130 (DOS Diagnosis Ch.04), entry 0x04 (Short to 24V)) | UINT32 | RO | 0x6130:04, 1 |
1A02:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x6140 (DOS Diagnosis Ch.05), entry 0x01 (Overcurrent)) | UINT32 | RO | 0x6140:01, 1 |
1A02:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x6140 (DOS Diagnosis Ch.05), entry 0x02 (Overload)) | UINT32 | RO | 0x6140:02, 1 |
1A02:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x6140 (DOS Diagnosis Ch.05), entry 0x03 (Open Load)) | UINT32 | RO | 0x6140:03, 1 |
1A02:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x6140 (DOS Diagnosis Ch.05), entry 0x04 (Short to 24V)) | UINT32 | RO | 0x6140:04, 1 |
1A02:15 | SubIndex 021 | 21. PDO Mapping entry (object 0x6150 (DOS Diagnosis Ch.06), entry 0x01 (Overcurrent)) | UINT32 | RO | 0x6150:01, 1 |
1A02:16 | SubIndex 022 | 22. PDO Mapping entry (object 0x6150 (DOS Diagnosis Ch.06), entry 0x02 (Overload)) | UINT32 | RO | 0x6150:02, 1 |
1A02:17 | SubIndex 023 | 23. PDO Mapping entry (object 0x6150 (DOS Diagnosis Ch.06), entry 0x03 (Open Load)) | UINT32 | RO | 0x6150:03, 1 |
1A02:18 | SubIndex 024 | 24. PDO Mapping entry (object 0x6150 (DOS Diagnosis Ch.06), entry 0x04 (Short to 24V)) | UINT32 | RO | 0x6150:04, 1 |
1A02:19 | SubIndex 025 | 25. PDO Mapping entry (object 0x6160 (DOS Diagnosis Ch.07), entry 0x01 (Overcurrent)) | UINT32 | RO | 0x6160:01, 1 |
1A02:1A | SubIndex 026 | 26. PDO Mapping entry (object 0x6160 (DOS Diagnosis Ch.07), entry 0x02 (Overload)) | UINT32 | RO | 0x6160:02, 1 |
1A02:1B | SubIndex 027 | 27. PDO Mapping entry (object 0x6160 (DOS Diagnosis Ch.07), entry 0x03 (Open Load)) | UINT32 | RO | 0x6160:03, 1 |
1A02:1C | SubIndex 028 | 28. PDO Mapping entry (object 0x6160 (DOS Diagnosis Ch.07), entry 0x04 (Short to 24V)) | UINT32 | RO | 0x6160:04, 1 |
1A02:1D | SubIndex 029 | 29. PDO Mapping entry (object 0x6170 (DOS Diagnosis Ch.08), entry 0x01 (Overcurrent)) | UINT32 | RO | 0x6170:01, 1 |
1A02:1E | SubIndex 030 | 30. PDO Mapping entry (object 0x6170 (DOS Diagnosis Ch.08), entry 0x02 (Overload)) | UINT32 | RO | 0x6170:02, 1 |
1A02:1F | SubIndex 031 | 31. PDO Mapping entry (object 0x6170 (DOS Diagnosis Ch.08), entry 0x03 (Open Load)) | UINT32 | RO | 0x6170:03, 1 |
1A02:20 | SubIndex 032 | 32. PDO Mapping entry (object 0x6170 (DOS Diagnosis Ch.08), entry 0x04 (Short to 24V)) | UINT32 | RO | 0x6170:04, 1 |
Index 1A03 DEV TxPDO-Map Inputs Device
1A03:0 | DEV TxPDO-Map Inputs Device | PDO Mapping TxPDO 4 | UINT8 | RO | 0x07 (7dec) |
1A03:01 | SubIndex 001 | 1. PDO Mapping entry (object 0xF600 (DEV Inputs), entry 0x01 (Undervoltage Us)) | UINT32 | RO | 0xF600:01, 1 |
1A03:02 | SubIndex 002 | 2. PDO Mapping entry (1 bits align) | UINT32 | RO | 0x0000:00, 1 |
1A03:03 | SubIndex 003 | 3. PDO Mapping entry (object 0xF600 (DEV Inputs), entry 0x03 (Overtemperature)) | UINT32 | RO | 0xF600:03, 1 |
1A03:04 | SubIndex 004 | 4. PDO Mapping entry (9 bits align) | UINT32 | RO | 0x0000:00, 9 |
1A03:05 | SubIndex 005 | 5. PDO Mapping entry (object 0xF600 (DEV Inputs), entry 0x0D (Diag)) | UINT32 | RO | 0xF600:0D, 1 |
1A03:06 | SubIndex 006 | 6. PDO Mapping entry (object 0xF600 (DEV Inputs), entry 0x0E (TxPDO State)) | UINT32 | RO | 0xF600:0E, 1 |
1A03:07 | SubIndex 007 | 7. PDO Mapping entry (object 0xF600 (DEV Inputs), entry 0x0F (Input cycle counter)) | UINT32 | RO | 0xF600:0F, 2 |
Index 1A04 DIP TxPDO-Map Extended Diagnosis
1A04:0 | DIP TxPDO-Map Extended Diagnosis | PDO Mapping TxPDO 5 | UINT8 | RO | 0x20 (32dec) |
1A04:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (DIP Diagnosis Ch.01), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6001:01, 1 |
1A04:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6001 (DIP Diagnosis Ch.01), entry 0x03 (Power Supply Missing)) | UINT32 | RO | 0x6001:03, 1 |
1A04:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6011 (DIP Diagnosis Ch.02), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6011:01, 1 |
1A04:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6011 (DIP Diagnosis Ch.02), entry 0x03 (Power Supply Missing)) | UINT32 | RO | 0x6011:03, 1 |
1A04:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6021 (DIP Diagnosis Ch.03), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6021:01, 1 |
1A04:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6021 (DIP Diagnosis Ch.03), entry 0x03 (Power Supply Missing)) | UINT32 | RO | 0x6021:03, 1 |
1A04:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6031 (DIP Diagnosis Ch.04), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6031:01, 1 |
1A04:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6031 (DIP Diagnosis Ch.04), entry 0x03 (Power Supply Missing)) | UINT32 | RO | 0x6031:03, 1 |
1A04:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6041 (DIP Diagnosis Ch.05), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6041:01, 1 |
1A04:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6041 (DIP Diagnosis Ch.05), entry 0x03 (Power Supply Missing)) | UINT32 | RO | 0x6041:03, 1 |
1A04:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6051 (DIP Diagnosis Ch.06), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6051:01, 1 |
1A04:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x6051 (DIP Diagnosis Ch.06), entry 0x03 (Power Supply Missing)) | UINT32 | RO | 0x6051:03, 1 |
1A04:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x6061 (DIP Diagnosis Ch.07), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6061:01, 1 |
1A04:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x6061 (DIP Diagnosis Ch.07), entry 0x03 (Power Supply Missing)) | UINT32 | RO | 0x6061:03, 1 |
1A04:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x6071 (DIP Diagnosis Ch.08), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6071:01, 1 |
1A04:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x6071 (DIP Diagnosis Ch.08), entry 0x03 (Power Supply Missing)) | UINT32 | RO | 0x6071:03, 1 |
1A04:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x6081 (DIP Diagnosis Ch.09), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6081:01, 1 |
1A04:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x6081 (DIP Diagnosis Ch.09), entry 0x03 (Power Supply Missing)) | UINT32 | RO | 0x6081:03, 1 |
1A04:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x6091 (DIP Diagnosis Ch.10), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x6091:01, 1 |
1A04:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x6091 (DIP Diagnosis Ch.10), entry 0x03 (Power Supply Missing)) | UINT32 | RO | 0x6091:03, 1 |
1A04:15 | SubIndex 021 | 21. PDO Mapping entry (object 0x60A1 (DIP Diagnosis Ch.11), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x60A1:01, 1 |
1A04:16 | SubIndex 022 | 22. PDO Mapping entry (object 0x60A1 (DIP Diagnosis Ch.11), entry 0x03 (Power Supply Missing)) | UINT32 | RO | 0x60A1:03, 1 |
1A04:17 | SubIndex 023 | 23. PDO Mapping entry (object 0x60B1 (DIP Diagnosis Ch.12), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x60B1:01, 1 |
1A04:18 | SubIndex 024 | 24. PDO Mapping entry (object 0x60B1 (DIP Diagnosis Ch.12), entry 0x03 (Power Supply Missing)) | UINT32 | RO | 0x60B1:03, 1 |
1A04:19 | SubIndex 025 | 25. PDO Mapping entry (object 0x60C1 (DIP Diagnosis Ch.13), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x60C1:01, 1 |
1A04:1A | SubIndex 026 | 26. PDO Mapping entry (object 0x60C1 (DIP Diagnosis Ch.13), entry 0x03 (Power Supply Missing)) | UINT32 | RO | 0x60C1:03, 1 |
1A04:1B | SubIndex 027 | 27. PDO Mapping entry (object 0x60D1 (DIP Diagnosis Ch.14), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x60D1:01, 1 |
1A04:1C | SubIndex 028 | 28. PDO Mapping entry (object 0x60D1 (DIP Diagnosis Ch.14), entry 0x03 (Power Supply Missing)) | UINT32 | RO | 0x60D1:03, 1 |
1A04:1D | SubIndex 029 | 29. PDO Mapping entry (object 0x60E1 (DIP Diagnosis Ch.15), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x60E1:01, 1 |
1A04:1E | SubIndex 030 | 30. PDO Mapping entry (object 0x60E1 (DIP Diagnosis Ch.15), entry 0x03 (Power Supply Missing)) | UINT32 | RO | 0x60E1:03, 1 |
1A04:1F | SubIndex 031 | 31. PDO Mapping entry (object 0x60F1 (DIP Diagnosis Ch.16), entry 0x01 (Wirebreak)) | UINT32 | RO | 0x60F1:01, 1 |
1A04:20 | SubIndex 032 | 32. PDO Mapping entry (object 0x60F1 (DIP Diagnosis Ch.16), entry 0x03 (Power Supply Missing)) | UINT32 | RO | 0x60F1:03, 1 |
Index 1C00 Sync manager type
1C00:0 | Sync manager type | Using the Sync Managers | UINT8 | RO | 0x04 (4dec) |
1C00:01 | SubIndex 001 | Sync-Manager Type Channel 1: Mailbox Write | UINT8 | RO | 0x01 (1dec) |
1C00:02 | SubIndex 002 | Sync-Manager Type Channel 2: Mailbox Read | UINT8 | RO | 0x02 (2dec) |
1C00:03 | SubIndex 003 | Sync-Manager Type Channel 3: Process Data Write (Outputs) | UINT8 | RO | 0x03 (3dec) |
1C00:04 | SubIndex 004 | Sync-Manager Type Channel 4: Process Data Read (Inputs) | UINT8 | RO | 0x04 (4dec) |
Index 1C12 RxPDO assign
1C12:0 | RxPDO assign | PDO Assign Outputs | UINT8 | RW | 0x00 (0dec) |
1C12:01 | Subindex 001 | 1. allocated RxPDO (contains the index of the associated RxPDO mapping object) | UINT16 | RW | 0x0000 (0dec) |
Index 1C13 TxPDO assign
1C13:0 | TxPDO assign | PDO Assign Inputs | UINT8 | RW | 0x03 (3dec) |
1C13:01 | Subindex 001 | 1. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A00 (6656dec) |
1C13:02 | Subindex 002 | 2. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A01 (6657dec) |
1C13:03 | Subindex 003 | 3. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A03 (6659dec) |
1C13:04 | Subindex 004 | 4. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x0000 (0dec) |
1C32:0 | SM output parameter | Synchronization parameters for the outputs | UINT8 | RO | 0x20 (32dec) |
1C32:01 | Sync mode | Current synchronization mode:
1C32:02 | Cycle time | Cycle time (in ns):
1C32:03 | Shift time | Time between SYNC0 event and output of the outputs (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C32:04 | Sync modes supported | Supported synchronization modes:
| UINT16 | RO | 0x440B (17419dec) |
1C32:05 | Minimum cycle time | Minimum cycle time (in ns) | UINT32 | RO | 0x00000000 (0dec) |
1C32:06 | Calc and copy time | Minimum time between SYNC0 and SYNC1 event (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C32:07 | Minimum delay time |
1C32:08 | Get Cycle Time | Possible values:
The parameters 1C32:03, 1C32:05, 1C32:06, 1C32:09, 1C33:03, 1C33:06, 1C33:09 are updated with the maximum measured values. | UINT16 | RW | 0x0000 (0dec) |
1C32:09 | Maximum delay time | Time between SYNC1 event and output of the outputs (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C32:0B | SM event missed counter | Number of missed SM events in OPERATIONAL (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C32:0C | Cycle exceeded counter | Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) | UINT16 | RO | 0x0000 (0dec) |
1C32:0D | Shift too short counter | Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C32:20 | Sync error | The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) | BOOLEAN | RO | 0x00 (0dec) |
Index 1C33 SM input parameter
1C33:0 | SM input parameter | Synchronization parameters for the inputs | UINT8 | RO | 0x20 (32dec) |
1C33:01 | Sync mode | Current synchronization mode:
| UINT16 | RW | 0x0001 (1dec) |
1C33:02 | Cycle time | as 1C32:02 | UINT32 | RW | 0x000F4240 (1000000dec) |
1C33:03 | Shift time | Time between SYNC0 event and reading of the inputs (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C33:04 | Sync modes supported | Supported synchronization modes:
1C33:05 | Minimum cycle time | as 1C32:05 | UINT32 | RO | 0x000249F0 (150000dec) |
1C33:06 | Calc and copy time | Time between reading of the inputs and the inputs being available for the master (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:07 | Minimum delay time |
1C33:08 | Get Cycle Time | as 1C32:08 | UINT16 | RW | 0x0000 (0dec) |
1C33:09 | Maximum delay time | Time between SYNC1 event and reading of the inputs (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C33:0B | SM event missed counter | as 1C32:11 | UINT16 | RO | 0x0000 (0dec) |
1C33:0C | Cycle exceeded counter | as 1C32:12 | UINT16 | RO | 0x0000 (0dec) |
1C33:0D | Shift too short counter | as 1C32:13 | UINT16 | RO | 0x0000 (0dec) |
1C33:20 | Sync error | as 1C32:32 | BOOLEAN | RO | 0x00 (0dec) |