Data stream
The flow chart below illustrates the data stream of the EM37xx.
The raw value of the sensor can be read in object 0x80nE:01.
After completion of the process chain, the "value" index: 0x60n0:11 is output to the controller.
The individual objects of the process are described below.
Data stream 1:Fig.142: EM37xx data stream
Undershoot and overshoot of the measuring range (underrange, overrange), index 0x60n0:01, 0x60n0:02
The limits refer to the raw value of the sensor.
Terminal module
Overrange / Underrange
PDO
index
Error bit
index
LED
EM3701
Nominal pressure range
-100 mbar < (P1-P2) < 100 mbar
(0x6000:01 and
0x6000:02): 0
0x60n0:07: 0
Overrange and underrange (red): off
Underrange
(P1-P2) < -100 mbar
0x6000:01: 1
0x60n0:07: 1
Overrange (red): on
Overrange
(P1-P2) > 100 mbar
0x6000:02: 1
0x60n0:07: 1
Underrange (red): on
EM3702
0 mbar < Pn < 7500 mbar
(0x60n0:01 and 0x60n0:02): 0
0x60n0:07: 0
Error Xn (red): off
Underrange
Pn < -100 mbar
0x60n0:01: 1
0x60n0:07: 1
Error Xn (red): on
Overrange
Pn > 7500 mbar
0x60n0:02: 1
0x60n0:07: 1
Error Xn (red): on
EM3712
-1000 mbar < Pn < +1000 mbar
0x60n0:07: 0
Error Xn (red): off
Underrange
Pn < -1000 mbar
0x60n0:01: 1
0x60n0:07: 1
Error Xn (red): on
Overrange
Pn > +1000 mbar
0x60n0:02: 1
0x60n0:07: 1
Error Xn (red): on
Notice
Measuring range exceeded
Pressure values below or above the permitted measuring range may lead to destruction of the pressure measuring unit. The limits must be observed.
The error LED lights up if the error bit is set.
Data stream 2:
Error bit (index 0x60n0:07)
The error bit indicates an overrange or underrange. Terminal EM3702 (0 to 7500 mbar) shows an overrange or an underrange of -100 mbar.