Configuration data
![]() | Automatic configuration Some parameters are set automatically when the electronic identification plate is read in. The index of these parameters is marked with an asterisk (*). You can activate the reading of the electronic identification plate in the parameters "Enable auto config": Channel 1: 8008:01 |
Index 8000 FB Settings Ch.1
8000:0 | FB Settings Ch.1 |
| UINT8 | RO | 0x17 (23dec) |
8000:02 | Referenced | Can be set to TRUE by the user. Is automatically set to FALSE as soon as a motor with a deviating serial number is recognized or if the feedback is single-turn. Must be set to TRUE if a gear ratio or modulo factor is configured. | BOOLEAN | RW | 0x00 (0dec) |
8000:0D | Offset position actual value source | permitted values:
| BIT4 | RW | 0x00 (0dec) |
8000:11 | Device type |
| UINT32 | RW | 0x00000605 (1541dec) |
8000:12 | Singleturn bits 1) | Number of single-turn bits. The sum of the single-turn bits and multi-turn bits must be 32. | UINT8 | RW | 0x14 (20dec) |
8000:13 | Multiturn bits 1) | Number of multi-turn bits. The sum of the single-turn bits and multi-turn bits must be 32. | UINT8 | RW | 0x0C (12dec) |
8000:14 | Observer bandwidth | Bandwidth of the speed observer [Hz] | UINT16 | RW | 0x01F4 (500dec) |
8000:15 | Observer feed-forward | Load ratio [%] between internal rotor inertia of the motor and the total inertia of the driven system. Load ratio = internal moment of inertia / (internal moment of inertia + mass moment of inertia of the load). Examples: 100 % = load-free 50 % = mass moments of inertia of input and output are equal | UINT8 | RW | 0x64 (100dec) |
8000:17 | Position offset | The position offset is subtracted from the raw position of the encoder. It can only be written with the axis stopped. This object maps the value of the 'Drive Memory' (see 8000:0D); the 'Encoder Memory' cannot be influenced/read via this object. | UINT32 | RW | 0x00000000 (0dec) |
1) This is only the representation of the position in the PDO, the physical resolution of the feedback is unaffected.
Index 8001 FB Touch probe Settings Ch.1
8001:0 | FB Touch probe Settings Ch.1 |
| UINT8 | RO | 0x12 (18dec) |
8001:11 | Touch probe 1 source | Permitted values: 1: Touch probe input 1 | INT16 | RW | 0x0001 (1dec) |
8001:12 | Touch probe 2 source | Permitted values: 2: Touch probe input 2 | INT16 | RW | 0x0002 (2dec) |
Index 8008 FB OCT Settings Ch.1
8008:0 | FB OCT Settings Ch.1 |
| UINT8 | RO | 0x03 (3dec) |
8008:01 | Enable auto config | Configuration takes place automatically after the reading of the electronic identification plate. | BOOLEAN | RW | 0x00 (0dec) |
8008:02 | Reconfig identical motor | When replacing identical motors 1), reconfiguration takes place automatically after reading the electronic identification plate. 8008:01 "Enable auto config" must be TRUE. | BOOLEAN | RW | 0x00 (0dec) |
8008:03 | Reconfig non-identical motor | When replacing non-identical motors 1), reconfiguration takes place automatically after reading the electronic identification plate. 8008:01 "Enable auto config" must be TRUE. | BOOLEAN | RW | 0x00 (0dec) |
1) The terminal uses parameter 9009:04 "Order code" to check whether the motor is identical.
Index 8010 DRV Amplifier Settings Ch.1
8010:0 | DRV Amplifier Settings Ch.1 |
| UINT8 | RO | 0x70 (112dec) |
8010:01 | Enable TxPDOToggle | Show TxPDO Toggle in the status word (bit 10). | BOOLEAN | RW | 0x00 (0dec) |
8010:02 | Enable input cycle counter | 1: enabled The Input cycle counter is a two-bit counter that is incremented with each process data cycle up to a maximum value of 3, after which it starts again at 0. The low bit is represented in bit 10 and the high bit in bit 14 of the status word. | BOOLEAN | RW | 0x00 (0dec) |
8010:12* | Current loop integral time | Integral component of current controller. Unit: 0.1 ms This value is affected by automatic scanning. | UINT16 | RW | 0x000A (10dec) |
8010:13* | Current loop proportional gain | Proportional component of current controller. Unit: 0.1 V/A This value is affected by automatic scanning. | UINT16 | RW | 0x000A (10dec) |
8010:14 | Velocity loop integral time | Integral component of velocity controller. Unit: 0.1 ms | UINT32 | RW | 0x00000032 (50dec) |
8010:15 | Velocity loop proportional gain | Proportional component of velocity controller. Unit: mA / (rad/s) | UINT32 | RW | 0x00000096 (150dec) |
8010:17 | Position loop proportional gain | Proportional component position controller. Unit: (rad/s) / rad | UINT32 | RW | 0x0000000A (10dec) |
8010:29 | Amplifier I2T warn level | I²T model warning threshold. Unit: % | UINT8 | RW | 0x50 (80dec) |
8010:2A | Amplifier I2T error level | I²T model error threshold. Unit: % | UINT8 | RW | 0x69 (105dec) |
8010:31 | Velocity limitation | Velocity limitation. Unit: 1/min | UINT32 | RW | 0x000186A0 (100000dec) |
8010:33 | Stand still window | Standstill window Unit: 1/min | UINT16 | RW | 0x0000 (0dec) |
8010:39 | Select info data 1 | Permitted values:
| UINT8 | RW | 0x02 (2dec) |
8010:3A | Select info data 2 | Permitted values:
| UINT8 | RW | 0x04 (4dec) |
8010:49 | Halt ramp deceleration | Halt ramp deceleration. Unit: 0.1 rad / s² | UINT32 | RW | 0x0000F570 (62832dec) |
8010:50 | Following error window | Following error monitor: following error window. Unit: the given value must be multiplied by the corresponding scaling factor 0xFFFFFFFF (-1dec) = following error monitor off. Any other value = following error monitor on. | UINT32 | RW | 0xFFFFFFFF (-1dec) |
8010:51 | Following error time out | Following error monitor: timeout. Unit: ms If the following error is larger than the following error window for a time that exceeds the timeout, this leads to an error reaction. | UINT16 | RW | 0x0000 (0dec) |
8010:52 | Fault reaction option code | Permitted values:
8010:54 | Feature bits |
8010:57 | Position loop velocity feed forward gain | Scaling factor for velocity pre-control from the position interpolator. | UINT8 | RW | 0x64 (100dec) |
8010:58 | Select info data 3 | Permitted values:
| UINT8 | RW | 0x07 (7dec) |
8010:59 | Error suppression mask |
8010:62 | Position loop deadband window | Deadband window of the position controller. Unit: increments | UINT32 | RW | 0x00000000 (0dec) |
8010:66 | Enable cogging torque compensation | Activate cogging compensation. | BOOLEAN | RW | 0x01 (1dec) |
8010:6D | Torque feed forward gain | Internal torque pre-control: scaling factor | UINT32 | RW | 0x00000064 (100dec) |
8010:6E | Torque feed forward filter time | Internal torque pre-control: filter time. Unit: 0.1 ms | UINT32 | RW | 0x00000000 (0dec) |
8010:6F | Torque offset | Torque offset. The value is given in thousandths of the nominal current. | INT16 | RW | 0x0000 (0dec) |
8010:70 | Torque limitation option code | Permitted values:
| INT8 | RW | 0x00 (0dec) |
Index 8011 DRV Motor Settings Ch.1
8011:0 | DRV Motor Settings Ch.1 |
| UINT8 | RO | 0x2D (45dec) |
8011:11* | Max current | Peak current. Unit: mA | UINT32 | RW | 0x00001770 (6000dec) |
8011:12* | Rated current | Nominal current. Unit: mA | UINT32 | RW | 0x000003E8 (1000dec) |
8011:13* | Motor pole pairs | Number of pole pairs. | UINT8 | RW | 0x01 (1dec) |
8011:15* | Commutation offset | Commutation offset between the electrical zero position and the mechanical single-turn zero position. Unit: ° | INT16 | RW | 0xFFA6 (65446dec) |
8011:16* | Torque constant | Torque constant. Unit: mNm / A | UINT32 | RW | 0x00000001 (1dec) |
8011:18* | Rotor moment of inertia | Mass moment of inertia of the motor. Unit: g cm² | UINT32 | RW | 0x000001F4 (500dec) |
8011:19* | Winding inductance | Winding inductance. Unit: 0.1 mH | UINT16 | RW | 0x0064 (100dec) |
8011:1B* | Motor speed limitation | Velocity limitation. Unit: 1/min | UINT32 | RW | 0x000186A0 (100000dec) |
8011:29 | I2T warn level | I2T model warning threshold. Unit: % | UINT8 | RW | 0x50 (80dec) |
8011:2A | I2T error level | I2T model error threshold. Unit: % | UINT8 | RW | 0x69 (105dec) |
8011:2B* | Motor Temperature warn level | Overtemperature warning threshold. Unit: 0.1 °C | UINT16 | RW | 0x03E8 (1000dec) |
8011:2C | Motor Temperature error level | Overtemperature error threshold. Unit: 0.1 °C | UINT16 | RW | 0x05DC (1500dec) |
8011:2D* | Motor thermal time constant | Thermal time constant. Unit: 0.1 s | UINT16 | RW | 0x0028 (40dec) |
Index 8012 DRV Brake Settings Ch.1
8012:0 | DRV Brake Settings Ch.1 |
| UINT8 | RO | 0x14 (20dec) |
8012:01 | Enable manual override | Enable for manual control of the holding brake. | BOOLEAN | RW | 0x00 (0dec) |
8012:02 | Manual brake state | Permitted values:
| BIT1 | RW | 0x00 (0dec) |
8012:11* | Release delay | Time the holding brake requires for opening (releasing) after the current was applied. | UINT16 | RW | 0x0000 (0dec) |
8012:12* | Application delay | Time the holding brake requires for closing (holding) after the current was switched off. | UINT16 | RW | 0x0000 (0dec) |
8012:13 | Emergency application timeout | Time that the amplifier waits for the velocity to reach the standstill limit after a stop request. Note: This parameter must be set at least to the longest time the axis needs to come to a standstill after it has been switched torque-free. For vertical axes, this parameter should be set to a low value to prevent the axis or load from falling very far. Unit: ms | UINT16 | RW | 0x0000 (0dec) |
8012:14* | Brake moment of inertia | Mass moment of inertia of the brake. Unit: g cm² | UINT16 | RW | 0x0000 (0dec) |
Index 8013 DRV Filter Settings Ch.1
8013:0 | DRV Filter Settings Ch.1 |
| UINT8 | RO | 0x19 (25dec) |
8013:10 | Low pass frequency 1 |
| REAL32 | RW | 0x00000000 (0dec) |
8013:11 | Low pass damping 1 |
8013:12 | High pass frequency 1 |
8013:13 | High pass damping 1 |
8013:14 | Filter type 1 | Permitted values:
8013:15 | Low pass frequency 2 |
8013:16 | Low pass damping 2 |
8013:17 | High pass frequency 2 |
8013:18 | High pass damping 2 |
8013:19 | Filter type 2 | Permitted values:
Index 8020 DMC Settings Ch.1
8020:0 | DMC Settings Ch.1 |
8020:07 | Emergency deceleration | Deceleration for the emergency stop ramp. (In ms from motor nominal speed to standstill) Unit: 1 ms | UINT16 | RW | 0x0064 (100dec) |
8020:08 | Calibration position | If homing is successful, the "Actual position" is set to this value. | INT64 | RW | 0 |
8020:09 | Calibration velocity (towards plc cam) | Velocity when hitting the cam in 10000ths of the motor nominal speed. | INT16 | RW | 0x0064 (100dec) |
8020:0A | Calibration Velocity (off plc cam) | Velocity when driving off the cam in 10000ths of the motor nominal speed. | INT16 | RW | 0x000A (10dec) |
8020:0E | Modulo factor | Feedback increments for one mechanical revolution. | INT64 | RW | 0x100000000 (4294967296dec) |
8020:12 | Block calibration torque limit | Torque limitation for approaching the end stop. In parts per thousand of the nominal motor current. | UINT16 | RW | 0x0064 (100dec) |
8020:13 | Block calibration stop distance | After reaching the calibration position, the axis moves out of the end position by this distance. | INT64 | RW | 0x100000000 (4294967296dec) |
8020:14 | Block calibration lag threshold | When this following error is exceeded, the axis is in the end position. | INT64 | RW | 0x100000000 (4294967296dec) |
8020:15 | Target position window | Target position window: The In-Target bit is set when the axis is within this window for at least the time set under 0x8020:16. | INT64 | RW | 0x16C16C1 (23860929dec) |
8020:16 | Target position monitor time | see 0x8020:15 Unit: ms | UINT16 | RW | 0x0014 (20dec) |
8020:17 | Target position timeout | When the setpoint generator has reached its end position and the axis is not in the target window after this time has elapsed, the task is terminated and the in-target bit is not set. Unit: ms | UINT16 | RW | 0x1770 (6000dec) |
Index 8021 DMC Features Ch.1
8021:0 | DMC Features Ch.1 |
| UINT8 | RO | 0x1B (27dec) |
8021:13 | Invert calibration cam search direction | Invert the direction of movement to search for the limit switch. Default: FALSE = search with positive direction of rotation. | BOOLEAN | RW | 0x00 (0dec) |
8021:14 | Invert sync impulse search direction | Invert the direction of rotation to exit the limit switch. Default: TRUE = exit in negative direction of rotation. | BOOLEAN | RW | 0x01 (1dec) |
8021:19 | Calibration cam source | Source for the reference switch.
| UINT8 | RW | 0x00 (0dec) |
8021:1A | Calibration cam active level | State of the reference switch in the actuated state.
8021:1B* | Latch source | Source for the latch unit.
Index 8100 FB Settings Ch.2 (ELM72x2 only)
8100:0 | FB Settings Ch.2 |
8100:02 | Referenced | Can be set to TRUE by the user. Is automatically set to FALSE as soon as a motor with a deviating serial number is recognized or if the feedback is single-turn. Must be set to TRUE if a gear ratio or modulo factor is configured. | BOOLEAN | RW | 0x00 (0dec) |
8100:0D | Offset position actual value source | permitted values:
8100:11 | Device type |
8100:12 | Singleturn bits 1) | Number of single-turn bits. The sum of the single-turn bits and multi-turn bits must be 32. | UINT8 | RW | 0x14 (20dec) |
8100:13 | Multiturn bits 1) | Number of multi-turn bits. The sum of the single-turn bits and multi-turn bits must be 32. | UINT8 | RW | 0x0C (12dec) |
8100:14 | Observer bandwidth | Bandwidth of the speed observer [Hz] | UINT16 | RW | 0x01F4 (500dec) |
8100:15 | Observer feed-forward | Load ratio [%] between internal rotor inertia of the motor and the total inertia of the driven system. Load ratio = internal moment of inertia / (internal moment of inertia + mass moment of inertia of the load). Examples: 100 % = load-free 50 % = mass moments of inertia of input and output are equal | UINT8 | RW | 0x64 (100dec) |
8100:17 | Position offset | The position offset is subtracted from the raw position of the encoder. It can only be written with the axis stopped. This object maps the value of the 'Drive Memory' (see 8100:0D); the 'Encoder Memory' cannot be influenced/read via this object. | UINT32 | RW | 0x00000000 (0dec) |
Index 8101 FB Touch probe Settings Ch.2 (ELM72x2 only)
8101:0 | FB Touch probe Settings Ch.2 |
8101:11 | Touch probe 1 source | Permitted values: 1: Touch probe input 1 | INT16 | RW | 0x0001 (1dec) |
8101:12 | Touch probe 2 source | Permitted values: 2: Touch probe input 2 | INT16 | RW | 0x0002 (2dec) |
Index 8108 FB OCT Settings Ch.2 (ELM72x2 only)
8108:0 | FB OCT Settings Ch.2 |
8108:01 | Enable auto config | Configuration takes place automatically after the reading of the electronic identification plate. | BOOLEAN | RW | 0x00 (0dec) |
8108:02 | Reconfig identical motor | When replacing identical motors 1), reconfiguration takes place automatically after reading the electronic identification plate. 8108:01 "Enable auto config" must be TRUE. | BOOLEAN | RW | 0x00 (0dec) |
8108:03 | Reconfig non-identical motor | When replacing non-identical motors 1), reconfiguration takes place automatically after reading the electronic identification plate. 8108:01 "Enable auto config" must be TRUE. | BOOLEAN | RW | 0x00 (0dec) |
1) The terminal uses parameter 9109:04 "Order code" to check whether the motor is identical.
Index 8110 DRV Amplifier Settings Ch.2 (ELM72x2 only)
8110:0 | DRV Amplifier Settings Ch.2 |
8110:01 | Enable TxPDOToggle | Show TxPDO Toggle in the status word (bit 10). | BOOLEAN | RW | 0x00 (0dec) |
8110:02 | Enable input cycle counter | 1: enabled The Input cycle counter is a two-bit counter that is incremented with each process data cycle up to a maximum value of 3, after which it starts again at 0. The low bit is represented in bit 10 and the high bit in bit 14 of the status word. | BOOLEAN | RW | 0x00 (0dec) |
8110:12* | Current loop integral time | Integral component of current controller. Unit: 0.1 ms This value is affected by automatic scanning. | UINT16 | RW | 0x000A (10dec) |
8110:13* | Current loop proportional gain | Proportional component of current controller. Unit: 0.1 V/A This value is affected by automatic scanning. | UINT16 | RW | 0x000A (10dec) |
8110:14 | Velocity loop integral time | Integral component of velocity controller. Unit: 0.1 ms | UINT32 | RW | 0x00000032 (50dec) |
8110:15 | Velocity loop proportional gain | Proportional component of velocity controller. Unit: mA / (rad/s) | UINT32 | RW | 0x00000096 (150dec) |
8110:17 | Position loop proportional gain | Proportional component position controller. Unit: (rad/s) / rad | UINT32 | RW | 0x0000000A (10dec) |
8110:29 | Amplifier I2T warn level | I²T model warning threshold. Unit: % | UINT8 | RW | 0x50 (80dec) |
8110:2A | Amplifier I2T error level | I²T model error threshold. Unit: % | UINT8 | RW | 0x69 (105dec) |
8110:31 | Velocity limitation | Velocity limitation. Unit: 1/min | UINT32 | RW | 0x000186A0 (100000dec) |
8110:33 | Stand still window | Standstill window Unit: 1/min | UINT16 | RW | 0x0000 (0dec) |
8110:39 | Select info data 1 | Permitted values:
8110:3A | Select info data 2 | Permitted values:
8110:49 | Halt ramp deceleration | Halt ramp deceleration. Unit: 0.1 rad / s² | UINT32 | RW | 0x0000F570 (62832dec) |
8110:50 | Following error window | Following error monitor: following error window. Unit: the given value must be multiplied by the corresponding scaling factor 0xFFFFFFFF (-1dec) = following error monitor off. Any other value = following error monitor on. | UINT32 | RW | 0xFFFFFFFF (-1dec) |
8110:51 | Following error time out | Following error monitor: timeout. Unit: ms If the following error is larger than the following error window for a time that exceeds the timeout, this leads to an error reaction. | UINT16 | RW | 0x0000 (0dec) |
8110:52 | Fault reaction option code | Permitted values:
8110:54 | Feature bits |
8110:57 | Position loop velocity feed forward gain | Scaling factor for velocity pre-control from the position interpolator. | UINT8 | RW | 0x64 (100dec) |
8110:58 | Select info data 3 | Permitted values:
8110:59 | Error suppression mask |
8110:62 | Position loop deadband window | Deadband window of the position controller. Unit: increments | UINT32 | RW | 0x00000000 (0dec) |
8110:66 | Enable cogging torque compensation | Activate cogging compensation. | BOOLEAN | RW | 0x01 (1dec) |
8110:6D | Torque feed forward gain | Internal torque pre-control: scaling factor | UINT32 | RW | 0x00000064 (100dec) |
8110:6E | Torque feed forward filter time | Internal torque pre-control: filter time. Unit: 0.1 ms | UINT32 | RW | 0x00000000 (0dec) |
8110:6F | Torque offset | Torque offset. The value is given in thousandths of the nominal current. | INT16 | RW | 0x0000 (0dec) |
8110:70 | Torque limitation option code | Permitted values:
Index 8111 DRV Motor Settings Ch.2 (ELM72x2 only)
8111:0 | DRV Motor Settings Ch.2 |
8111:11* | Max current | Peak current. Unit: mA | UINT32 | RW | 0x00001770 (6000dec) |
8111:12* | Rated current | Nominal current. Unit: mA | UINT32 | RW | 0x000003E8 (1000dec) |
8111:13* | Motor pole pairs | Number of pole pairs. | UINT8 | RW | 0x01 (1dec) |
8111:15* | Commutation offset | Commutation offset between the electrical zero position and the mechanical single-turn zero position. Unit: ° | INT16 | RW | 0xFFA6 (65446dec) |
8111:16* | Torque constant | Torque constant. Unit: mNm / A | UINT32 | RW | 0x00000001 (1dec) |
8111:18* | Rotor moment of inertia | Mass moment of inertia of the motor. Unit: g cm² | UINT32 | RW | 0x000001F4 (500dec) |
8111:19* | Winding inductance | Winding inductance. Unit: 0.1 mH | UINT16 | RW | 0x0064 (100dec) |
8111:1B* | Motor speed limitation | Velocity limitation. Unit: 1/min | UINT32 | RW | 0x000186A0 (100000dec) |
8111:29 | I2T warn level | I2T model warning threshold. Unit: % | UINT8 | RW | 0x50 (80dec) |
8111:2A | I2T error level | I2T model error threshold. Unit: % | UINT8 | RW | 0x69 (105dec) |
8111:2B* | Motor Temperature warn level | Overtemperature warning threshold. Unit: 0.1 °C | UINT16 | RW | 0x03E8 (1000dec) |
8111:2C* | Motor Temperature error level | Overtemperature error threshold. Unit: 0.1 °C | UINT16 | RW | 0x05DC (1500dec) |
8111:2D* | Motor thermal time constant | Thermal time constant. Unit: 0.1 s | UINT16 | RW | 0x0028 (40dec) |
Index 8112 DRV Brake Settings Ch.2 (ELM72x2 only)
8112:0 | DRV Brake Settings Ch.2 |
8112:01 | Enable manual override | Enable for manual control of the holding brake. | BOOLEAN | RW | 0x00 (0dec) |
8112:02 | Manual brake state | Permitted values:
8112:11* | Release delay | Time the holding brake requires for opening (releasing) after the current was applied. | UINT16 | RW | 0x0000 (0dec) |
8112:12* | Application delay | Time the holding brake requires for closing (holding) after the current was switched off. | UINT16 | RW | 0x0000 (0dec) |
8112:13 | Emergency application timeout | Time that the amplifier waits for the velocity to reach the standstill limit after a stop request. Note: This parameter must be set at least to the longest time the axis needs to come to a standstill after it has been switched torque-free. For vertical axes, this parameter should be set to a low value to prevent the axis or load from falling very far. Unit: ms | UINT16 | RW | 0x0000 (0dec) |
8112:14* | Brake moment of inertia | Mass moment of inertia of the brake. Unit: g cm² | UINT16 | RW | 0x0000 (0dec) |
Index 8113 DRV Filter Settings Ch.2 (ELM72x2 only)
8113:0 | DRV Filter Settings Ch.2 |
8113:10 | Low pass frequency 1 |
8113:11 | Low pass damping 1 |
8113:12 | High pass frequency 1 |
8113:13 | High pass damping 1 |
8113:14 | Filter type 1 | Permitted values:
8113:15 | Low pass frequency 2 |
8113:16 | Low pass damping 2 |
8113:17 | High pass frequency 2 |
8113:18 | High pass damping 2 |
8113:19 | Filter type 2 | Permitted values:
Index 8120 DMC Settings Ch.2 (ELM72x2 only)
8120:0 | DMC Settings Ch.2 |
8120:07 | Emergency deceleration | Deceleration for the emergency stop ramp. (In ms from motor nominal speed to standstill) Unit: 1 ms | UINT16 | RW | 0x0064 (100dec) |
8120:08 | Calibration position | If homing is successful, the "Actual position" is set to this value. | INT64 | RW | 0 |
8120:09 | Calibration velocity (towards plc cam) | Velocity when hitting the cam in 10000ths of the motor nominal speed. | INT16 | RW | 0x0064 (100dec) |
8120:0A | Calibration Velocity (off plc cam) | Velocity when driving off the cam in 10000ths of the motor nominal speed. | INT16 | RW | 0x000A (10dec) |
8120:0E | Modulo factor | Feedback increments for one mechanical revolution. | INT64 | RW | 0x100000000 (4294967296dec) |
8120:12 | Block calibration torque limit | Torque limitation for approaching the end stop. In parts per thousand of the nominal motor current. | UINT16 | RW | 0x0064 (100dec) |
8120:13 | Block calibration stop distance | After reaching the calibration position, the axis moves out of the end position by this distance. | INT64 | RW | 0x100000000 (4294967296dec) |
8120:14 | Block calibration lag threshold | When this following error is exceeded, the axis is in the end position. | INT64 | RW | 0x100000000 (4294967296dec) |
8120:15 | Target position window | Target position window: The In-Target bit is set when the axis is within this window for at least the time set under 0x8120:16. | INT64 | RW | 0x16C16C1 (23860929dec) |
8120:16 | Target position monitor time | see 0x8120:15 Unit: ms | UINT16 | RW | 0x0014 (20dec) |
8120:17 | Target position timeout | When the setpoint generator has reached its end position and the axis is not in the target window after this time has elapsed, the task is terminated and the in-target bit is not set. Unit: ms | UINT16 | RW | 0x1770 (6000dec) |
Index 8121 DMC Features Ch.2 (ELM72x2 only)
8121:0 | DMC Features Ch.2 |
8121:13 | Invert calibration cam search direction | Invert the direction of movement to search for the limit switch. Default: FALSE = search with positive direction of rotation. | BOOLEAN | RW | 0x00 (0dec) |
8121:14 | Invert sync impulse search direction | Invert the direction of rotation to exit the limit switch. Default: TRUE = exit in negative direction of rotation. | BOOLEAN | RW | 0x01 (1dec) |
8121:19 | Calibration cam source | Source for the reference switch.
8121:1A | Calibration cam active level | State of the reference switch in the actuated state.
8121:1B* | Latch source | Source for the latch unit.
Index F800 DRV Amplifier Settings
800F:0 | DRV Amplifier Settings |
800F:10 | Nominal DC link voltage | Nominal DC link voltage. Unit: mV | UINT32 | RW | 0x0000BB80 (48000dec) |
800F:11 | Min DC link voltage | Minimum DC link voltage. Unit: mV | UINT32 | RW | 0x00001A90 (6800dec) |
800F:12 | Max DC link voltage | Maximum DC link voltage. Unit: mV | UINT32 | RW | 0x0000EA60 (60000dec) |
800F:15 | Amplifier Temperature warn level | Amplifier temperature warning threshold. Unit: 0.1 °C | UINT16 | RW | 0x0320 (800dec) |
800F:16 | Amplifier Temperature error level | Amplifier temperature error threshold. Unit: 0.1 °C | UINT16 | RW | 0x03E8 (1000dec) |
800F:17 | Feature bits |
Index F801 DRV Brake Chopper Settings
F801:0 | DRV Brake Chopper Settings |
F801:11 | External brake resistor value | Resistance value of the external braking resistor Unit: 0.1 Ω | UINT16 | RW | 0x001E (30dec) |
F801:12 | External brake resistor continuous power | Nominal output of the external braking resistor. Unit: W | UINT16 | RW | 0x0064 (100dec) |
F801:13 | Brake resistor power warning threshold | If this value is exceeded, an overload warning is issued for the braking resistor. The value is given as a percentage of the nominal output of the braking resistor (F801:12). | UINT16 | RW | 0x005A (90dec) |
F801:16 | Ext brake resistor overload factor at 1% duty cycle | Overload factor of the resistor at a duty cycle of 1% | UINT8 | RW | 0x26 (38dec) |
F801:18 | Brake chopper threshold overvoltage | DC link voltage above which the brake chopper switches on the resistor. Unit: mV | UINT32 | RW | 0x0000CB20 (52000dec) |
F801:19 | Brake chopper hysteresis voltage | Hysteresis of the brake chopper. The resistor is switched off when the DC link voltage has fallen below 'Brake chopper threshold overvoltage' - 'Brake chopper hysteresis voltage'. Unit: mV | UINT32 | RW | 0x000003E8 (1000dec) |
Index F810 FAN Settings
F810:0 | FAN Settings |
| UINT8 | RO | 0x11 (17dec) |
F810:11 | Fan behaviour | permitted values:
| UINT8 | RW | 0x0A (10dec) |