Measurement resistance 200 Ω
Measurement mode |
Resistance 0..200 Ω |
Operation mode |
4.5 V feed voltage, fixed setting n +Uv 5 kΩ reference resistance at –I2 Supply current is given by: |
Measuring range, nominal |
0…200 Ω |
Measuring range, end value (FSV) |
200 Ω |
Measuring range, technically usable |
0 Ω… 214.7 Ω |
PDO resolution |
23 bit (unsigned) |
PDO LSB (Extended Range) |
25.6 µΩ |
PDO LSB (Legacy Range) |
23.8.. µΩ |
Specific data
Measurement mode | Resistance 0..200 Ω | ||||||||
2/3-wire | 4-wire | ||||||||
Basic accuracy: Measuring deviation at 23°C, with averaging, typ. 6) | < ±tbd. ppmFSV < ±tbd. | < ±70 ppmFSV < ±14 mΩ | |||||||
Extended basic accuracy: Measuring deviation at 0…55°C, with averaging, typ. 6) | < ±tbd. ppmFSV < ±tbd. | < ±185 ppmFSV < ±37 mΩ | |||||||
Offset/Zero point deviation (at 23°C) | EOffset | < tbd. ppmFSV
| < 45 ppmFSV
Gain/scale/amplification deviation (at 23°C) | EGain | < tbd. ppmFSV
| < 45 ppmFSV
Non-linearity over the whole measuring range | ELin | < tbd. ppmFSV | < 25 ppmFSV | ||||||
Repeatability, over 24 h, with averaging | ERep | < tbd. ppmFSV
| < 5 ppmFSV
Temperature coefficient, typ. | TcOffset | < tbd. ppmFSV/K < tbd. | < 1.5 ppmFSV/K < 0.30 mΩ/K | ||||||
TcGain | < tbd. ppm/K | < 5 ppm /K | |||||||
Noise (without filtering) | ENoise, PtP | < tbd. ppmFSV | < tbd. digits | < tbd. ppmFSV | < tbd. digits | ||||
ENoise, RMS | < tbd. ppmFSV | < tbd. digits | < tbd. ppmFSV | < tbd. digits | |||||
Max. SNR | > tbd. [dB] | > tbd. [dB] | |||||||
Noisedensity@1kHz | < tbd. | < tbd. | |||||||
Noise (with 50/60 Hz FIR filter) 5) | ENoise, PtP | < tbd. ppmFSV | < tbd. digits | < tbd. ppmFSV | < tbd. digits | ||||
Common-mode rejection ratio (without filter) 3) | DC: | 50/60 Hz: | 1 kHz: | DC: | 50/60 Hz: | 1 kHz: | |||
Common-mode rejection ratio (with 50/60 Hz FIR filter) 3) 5) | DC: | 50/60 Hz: | 1 kHz: | DC: | 50/60 Hz: | 1 kHz: | |||
Largest short-term deviation during a specified electrical interference test | ±tbd.%FSV = ±tbd. ppmFSV typ. | ±tbd.%FSV = ±tbd. ppmFSV typ. | |||||||
Input impedance (internal resistance) | tbd | ||||||||
3) Values related to a common mode interference between SGND and internal ground.
5) the 50/60 Hz filter setting must be selected via the settings in the CoE depending on the local mains frequency (50 or 60 Hz); the respective nominal mains frequency then applies as the measuring point for common mode rejection or crosstalk.
6) Calculated value according to the equation for estimating usability at the given ambient temperature point or estimating usability over the specified ambient temperature range in operation (Tambient) as stated in chapter "General information on measuring accuracy/measurement uncertainty". In real use, for example at a relatively constant ambient temperature Tambient, a lower (better) achievable uncertainty is attained. A specific calculation according to chapter "General information on measuring accuracy/measurement uncertainty" is recommended, especially if the instrument allows a wider ambient temperature range in operation than 0...55 °C.
Fig.74: Representation resistance measurement range 200 Ω|
Note: The channel also works in electrically bipolar mode and records negative values in the unipolar measuring ranges (measurement from 0 V, 0 mA, 4 mA, 0 Ω). This enables the channel to provide a precise diagnosis even with signals < 0. In these measuring ranges the limit value for the "Underrange Error" in Extended Mode is -1% of the full scale value (FSV). The limit value can be set in CoE object 0x80n0:32. This avoids irritating error messages if the channel is not wired (e.g. without sensor) or the electrical signal fluctuates slightly around zero. The process data value of 0x00000000 is not undershot. If the "UnderrangeError" detection is to be set even less sensitive, the magnitude of the negative limit value in the CoE object referred to above can be set even higher. |
Note: In Extended Range Mode the Underrange/Overrange display in the PDO status has the character of an information/warning when the nominal measuring range is exceeded, i.e. no Error is displayed in the PDO status and LED. If the technical measuring range is also exceeded, Error = TRUE is also displayed. The detection limit for Underrange/Overrange Error can be set in the CoE. In Legacy Range mode, an Underrange/Overrange event also leads to an Error in the PDO status. |
