Specification KT/KTY1x/KTY21/23
Electrical measuring range used
2000 Ω
5000 Ω
Connection
4-wire
2/3-wire 1)
4-wire
2/3-wire 1)
Starting value
-50°C
-50°C
End value
126°C
150°C
Basic accuracy: Measuring deviation at 23°C terminal environment, with averaging, typ. 6)
< ±0.011 K
< ±tbd. K
< ±0.029 K
< ±tbd. K
Basic accuracy: Measuring deviation at 55°C terminal environment, with averaging, typ. 6)
< ±0.024 K
< ±tbd. K
< ±0.041 K
< ±tbd. K
Temperature coefficient 2), type
< 0.6 mK/K
< tbd. mK/K
< 0.72 mK/K
< tbd. mK/K
PDO LSB (Legacy Range only)
0.01/0.001°C/digit, per to PDO-setting
1) See initial remarks about 2/3-wire operation. The offset specification does not apply in 2-wire operation, as the offset is increased due to the connection. In 2-wire operation, an offset compensation is to be carried out after installation; refer to the ELM's internal functions Tare (chapter “ELM Features“/ “Tare“) or Zero Offset (chapter “ELM Features“/ “ZeroOffset“). The given offset specification of the terminal thus plays practically no further part. The offset deviation of a resistance measurement can change over time, therefore Beckhoff recommends a regular offset compensation or attentive monitoring of the change.
2) The temperature coefficient, i.e. the change in the measured temperature value in relation to the change in the ambient temperature of the terminal, is not constant, as can be seen in the following plot. The value at a sensor temperature of 0 °C is given here as an orientation value. Further values can be taken from the plot.
6) Calculated value according to the equation for estimating usability at the given ambient temperature point or estimating usability over the specified ambient temperature range in operation (Tambient) as stated in chapter "General information on measuring accuracy/measurement uncertainty". In real use, for example at a relatively constant ambient temperature Tambient, a lower (better) achievable uncertainty is attained. A specific calculation according to chapter "General information on measuring accuracy/measurement uncertainty" is recommended, especially if the instrument allows a wider ambient temperature range in operation than 0...55 °C.
Measurement uncertainty for KT/KTY1x/KTY21/23 in the electr. measuring range 2000 Ω, 4-wire connection:
Specification KT/KTY1x/KTY21/23 1:
Measurement uncertainty for KT/KTY1x/KTY21/23 in the electr. measuring range 2000 Ω, 3-wire connection:
Specification KT/KTY1x/KTY21/23 2:
Measurement uncertainty for KT/KTY1x/KTY21/23 in the electr. measuring range 5000 Ω, 4-wire connection:
Specification KT/KTY1x/KTY21/23 3:
Measurement uncertainty for KT/KTY1x/KTY21/23 in the electr. measuring range 5000 Ω, 3-wire connection:
Specification KT/KTY1x/KTY21/23 4: