RTD measurement with Beckhoff terminals
RTD specification and conversion
Temperature measurement with a resistance-dependent RTD sensor generally consists of two steps:
Both steps can take place locally in the Beckhoff measurement device. The transformation in the device can also be deactivated if it is to be calculated on a higher level in the control. Depending on the device type, several RTD conversions can be implemented which only differs in software. This means for Beckhoff RTD measurement devices that
Notes to 2/3/4 wire connection within R/RTD operation
With 2‑wire measurement, the line resistance of the sensor supply lines influences the measured value. If a reduction of this systematic error component is desirable for 2‑wire measurements, the resistance of the supply line to the measuring resistance should be taken into account, in which case the resistance of the supply line has to be determined first.
Taking into account the uncertainty associated with this supply line resistance, it can then be included statically in the calculation, e.g., for the EL3751 via the CoE object 0x8000:13 and for the ELM324x via the CoE object 0x80n0:13.
Any change in resistance of the supply line due to ageing, for example, is not taken into account automatically. Just the temperature dependency of copper lines with approx. 4000 ppm/K (corresponds to 0.4%/K!) is not insignificant during 24/7 operation.
A 3‑wire measurement enables the systematic component to be eliminated, assuming that the two supply lines are identical. With this type of measurement, the lead resistance of a supply line is measured continuously. The value determined in this way is then deducted twice from the measurement result, thereby eliminating the line resistance. Technically, this leads to a significantly more reliable measurement. However, taking into account the measurement uncertainty, the gain from the 3‑wire connection is less significant, since this assumption is subject to high uncertainty, in view of the fact that the individual line that was not measured may be damaged, or a varying resistance may have gone unnoticed.
Therefore, although technically the 3‑wire connection is a tried and tested approach, for measurements that are methodological assessed based on measurement uncertainty, we strongly recommend fully‑compensated 4‑wire connection.
With both 2‑wire and 3‑wire connection, the contact resistances of the terminal contacts influence the measuring process. The measuring accuracy can be further increased by a user‑side adjustment with the signal connection plugged in.
Notice
Measurement of small resistances
Especially for measurements in the range < 10 Ω, the 4‑wire connection is absolutely necessary due to the relatively high supply and contact resistances. It should also be considered that with such low resistances the relative measurement error in relation to the full scale value (FSV) can become high ‑ for such measurements resistance measurement terminals with small measuring ranges such as EL3692 in 4‑wire measurement should be used if necessary.
Corresponding considerations also lead to the common connection methods in bridge operation:
  • Full bridge: 4‑wire connection without line compensation, 6‑wire connection with full line compensation
  • Half bridge: 3‑wire connection without line compensation, 5‑wire connection with full line compensation
  • Quarter bridge: 2‑wire connection without line compensation, 3‑wire connection with theoretical line compensation and 4‑wire connection with full line compensation
RTD measurement with Beckhoff terminals 1:
Data for the sensor types in the following table
The values for the sensor types listed in the following table are shown here merely for informative purposes as an orientation aid. All data are given without guarantee and must be cross-checked against the data sheet for the respective sensor employed.
The RTD measurement consists of a chain of measuring and computing elements that affect the attainable measurement deviation:
RTD measurement with Beckhoff terminals 2:Fig.79: Concatenation of the uncertainties in RTD measurement
The given resistance specification is decisive for the attainable temperature measurement accuracy. It is applied to the possible RTD types in the following.
On account of
no detailed temperature specification table is given in the following, but
  • a short table specifying the electrical measuring range and orientation value for the basic accuracy
  • a graph of the basic accuracy over Tsens (this at two example ambient temperatures so that the attainable basic accuracy is implied on account of the actual existing ambient temperature)
  • equations for calculating further parameters (offset/gain/non-linearity/repeatability/noise) if necessary from the resistance specification at the desired operating point
Notes on the calculation of detailed specification data
If further specification data are of interest, they can or must be calculated from the values given in the resistance specification.
The sequence:
The numerical values used in the following three examples are for illustration purposes. The specification values given in the technical data remain authoritative.
Example 1:
Basic accuracy of an ELM3504 at 35 °C ambient temperature, measurement of -100 °C in the PT1000 interface (4-wire), without the influence of noise and aging:
TMeasuring point = -100 °C
MW = RPT1000, -100 °C = 602.56 Ω
RTD measurement with Beckhoff terminals 5:
= 86.238 ppmFSV
EResistance(RMeasuring point) = 86.238 ppmFSV ⋅ 2000 Ω = 0.1725 Ω
ΔRproK(TMeasuring point) = (R(-99 °C) – R(-100 °C)) / (1 °C) = 4.05 Ω/°C
EELM3504@35°C, PT1000, -100 °C = (0.1725 Ω)/(4.05 Ω/°C) ≈ 0.043 °C (means ±0.043 °C)
Example 2:
Consideration of the repeatability alone under the above conditions:
MW = RMeasuring point (-100 °C) = 602.56 Ω
ESingle = 10 ppmFSV
EResistance= 10 ppmFSV ⋅ 2000 Ω = 0.02 Ω
ΔRproK(TMeasuring point) = (R-99 °C – R-100 °C) / 1 °C = 4.05 Ω/°C
ETemp(RMeasuring point) = 0.02 Ω / 4.05 Ω/°C ≈ 0.005 °C (means ±0.005 °C)
Example 3:
Consideration of the RMS noise alone without filter under the above conditions:
ESingle = 37 ppmFSV
EResistance= 37 ppmFSV ⋅ 2000 Ω = 0.074 Ω
ETemp(RMeasuring point) = 0.074 Ω / 4.05 Ω/°C ≈ 0.018 °C (means ± 0.018 °C)
Example 4:
If the noise ENoise, PtP of the above example terminal is considered not for one sensor point -100 °C but in general, the following plot results:
RTD measurement with Beckhoff terminals 6:Fig.80: Diagram noise ENoise, PtP in dependence on sensor temperature
“B-parameter equation” setting for NTC sensors
The B-parameter equation can be used for NTC sensors (thermistors), i.e. RTD elements with negative coefficient k.
RTD measurement with Beckhoff terminals 7:
The coefficient RT0 indicates the resistance at temperature T0. The B-parameter can be taken from the information provided by the sensor manufacturer, or it can be determined by measuring the resistance at two known temperatures.
A helpful Excel file can be found for this in the documentation for the EL3204-0200.
The parameters must then be entered in the CoE 0x80n7
RTD measurement with Beckhoff terminals 8:Fig.81: ELM37xx/ CoE object 0x80n7: PAI RTD Settings Ch.1
with
RT0 → 0x80n7:01
B → 0x80n7:04
T0 → 0x80n7:02
“DIN IEC 60751” setting for Pt sensors
The calculation for T > 0°C according to
RTD measurement with Beckhoff terminals 9:
is implemented; the parameters must then be entered in the CoE 0x80n7
RTD measurement with Beckhoff terminals 10:
with
A or α → 0x80n7:03
B or β → 0x80n7:04
R0 → 0x80n7:01
“Steinhart-Hart” setting for NTC sensors
The Steinhart-Hart equation can be used for NTC sensors (thermistors), i.e. RTD elements with negative coefficient k.
RTD measurement with Beckhoff terminals 11:
The coefficients C1, C2, and C4 can either be taken directly from the manufacturer data or calculated. A sample file for the calculation of the Steinhart-Hart parameters is also available in the EL3204-0200 documentation. For determining the parameters the resistance values at three known temperatures are required. These can either be taken from the manufacturer data or measured directly at the sensor. In most cases the parameter C3 is close to zero, i.e. negligible. It is therefore not used in the sample file calculation.
RTD measurement with Beckhoff terminals 12:
with
A → 0x80n7:03
B → 0x80n7:04
C → 0x80n7:05
D → 0x80n7:06