Measurement resistance 500 Ω
Measurement mode
Resistance 0..500 Ω
Operation mode
4.5 V feed voltage, fixed setting n +Uv
5 kΩ reference resistance at –I2
Supply current is given by:
4.5 V / (5 kΩ + Rmeasurement)
Measuring range, nominal
0…500 Ω
Measuring range, end value (FSV)
500 Ω
Measuring range, technically usable
0 Ω…536.8 Ω
PDO resolution
23 bit (unsigned)
PDO LSB (Extended Range)
64 µΩ
PDO LSB (Legacy Range)
59.6.. µΩ
Specific data (preliminary data cursive format)
Measurement mode
Resistance 0..500 Ω
2/3-wire
4-wire
Basic accuracy: Measuring deviation at 23°C, with averaging, typ. 6)
< ±200 ppmFSV
< ±100 mΩ
< ±50 ppmFSV
< ±25 mΩ
Extended basic accuracy: Measuring deviation at 0…55°C, with averaging, typ. 6)
< ±415 ppmFSV
< ±0.21 Ω
< ±175 ppmFSV
< ±87.5 mΩ
Offset/Zero point deviation (at 23°C)
EOffset
< 145 ppmFSV
< 15 ppmFSV
Gain/scale/amplification deviation (at 23°C)
EGain
< 100 ppmFSV
< 40 ppmFSV
Non-linearity over the whole measuring range
ELin
< 75 ppmFSV
< 25 ppmFSV
Repeatability, over 24 h, with averaging
ERep
< 50 ppmFSV
< 5 ppmFSV
Temperature coefficient, typ.
TcOffset
< 8 ppmFSV/K
< 4 mΩ/K
< 1 ppmFSV/K
< 0.50 mΩ/K
TcGain
< 8 ppm/K
< 5 ppm/K
Noise (without filtering)
ENoise, PtP
< tbd. ppmFSV
< tbd. digits
< tbd. ppmFSV
< tbd. digits
ENoise, RMS
< tbd. ppmFSV
< tbd. digits
< tbd. ppmFSV
< tbd. digits
Max. SNR
> tbd. dB
> tbd. dB
Noisedensity@1kHz
< tbd. Measurement resistance 500 Ω 1:
< tbd. Measurement resistance 500 Ω 2:
Noise (with 50/60 Hz FIR filter) 5)
ENoise, PtP
< tbd. ppmFSV
< tbd. digits
< tbd. ppmFSV
< tbd. digits
ENoise, RMS
< tbd. ppmFSV
< tbd. digits
< tbd. ppmFSV
< tbd. digits
Max. SNR
> tbd. dB
> tbd. dB
Common-mode rejection ratio (without filter) 3)
DC:
< tbd. Ω/V
typ.
50/60 Hz:
< tbd. kΩ/V
typ.
1 kHz:
< tbd. kΩ/V
typ.
DC:
< tbd. Ω/V
typ.
50/60 Hz:
< tbd. kΩ/V
typ.
1 kHz:
< tbd. kΩ/V
typ.
Common-mode rejection ratio (with 50/60 Hz FIR filter) 3) 5)
DC:
< tbd. Ω/V
typ.
50/60 Hz:
< tbd. Ω/V
typ.
1 kHz:
< tbd. Ω/V
typ.
DC:
< tbd. Ω/V
typ.
50/60 Hz:
< tbd. kΩ/V
typ.
1 kHz:
< tbd. kΩ/V
typ.
Largest short-term deviation during a specified electrical interference test
±tbd. %FSV = ±tbd. ppmFSV typ.
Input impedance (internal resistance)
tbd.
3) Values related to a common mode interference between SGND and internal ground.
5) the 50/60 Hz filter setting must be selected via the settings in the CoE depending on the local mains frequency (50 or 60 Hz); the respective nominal mains frequency then applies as the measuring point for common mode rejection or crosstalk.
6) Calculated value according to the equation for estimating usability at the given ambient temperature point or estimating usability over the specified ambient temperature range in operation (Tambient) as stated in chapter "General information on measuring accuracy/measurement uncertainty". In real use, for example at a relatively constant ambient temperature Tambient, a lower (better) achievable uncertainty is attained. A specific calculation according to chapter "General information on measuring accuracy/measurement uncertainty" is recommended, especially if the instrument allows a wider ambient temperature range in operation than 0...55 °C.
Measurement resistance 500 Ω 3:Fig.75: Representation resistance measurement range 500 Ω
Note: The channel also works in electrically bipolar mode and records negative values in the unipolar measuring ranges (measurement from 0 V, 0 mA, 4 mA, 0 Ω). This enables the channel to provide a precise diagnosis even with signals < 0. In these measuring ranges the limit value for the "Underrange Error" in Extended Mode is -1% of the full scale value (FSV). The limit value can be set in CoE object 0x80n0:32. This avoids irritating error messages if the channel is not wired (e.g. without sensor) or the electrical signal fluctuates slightly around zero. The process data value of 0x00000000 is not undershot.
If the "UnderrangeError" detection is to be set even less sensitive, the magnitude of the negative limit value in the CoE object referred to above can be set even higher.
Note: In Extended Range Mode the Underrange/Overrange display in the PDO status has the character of an information/warning when the nominal measuring range is exceeded, i.e. no Error is displayed in the PDO status and LED. If the technical measuring range is also exceeded, Error = TRUE is also displayed. The detection limit for Underrange/Overrange Error can be set in the CoE.
In Legacy Range mode, an Underrange/Overrange event also leads to an Error in the PDO status.
