ELM3102-01x0 - Technical data
Technical data | ELM3102-0100/ ELM3102-0120/ ELM3102-0130 |
Analog inputs | 2 channel (differential) |
Time relation between channels to each other | Simultaneous conversion of all channels in the terminal, synchronous conversion between terminals, if DistributedClocks will be used |
ADC conversion method | ΔΣ (Delta-Sigma) with internal sample rate |
5.12 Msps | |
Cutoff frequency input filter hardware | Before AD converter: Within ADC after conversion: |
Low pass | |
Type sinc3/average filter The ramp-up time/ settling time/ delay caused by the filtering will be considered within the DistributedClocks-Timestamp. | |
Resolution | 24 bit (including sign) |
Connection technology | 2/3/4/5/6-wire |
Sampling rate (per channel, simultaneous) | 50 µs/20 ksps Free down sampling by Firmware via decimation factor |
Oversampling | 1…100 selectable |
Supported EtherCAT cycle time (depending on the operation mode) | DistributedClocks: min. 100 µs, max. 10 ms FrameTriggered/Synchron: min. 200 µs, max. 100 ms FreeRun: not yet supported |
Internal resistance | > 500 kΩ (60 V); > 4 MΩ (other) ; 150 Ω (current) |
Operation range voltage measurement | ±60/10/5/2.5/1.25 V, 2-wire-connection |
Operation range current measurement | ±20 mA, 0/4…20 mA, NAMUR NE43, 2-wire-connection |
Connection diagnosis | Wire break/short cut |
Internal analog ground AGND | Existing by external connection to -Uv |
Surge voltage protection of the inputs related to GND | Value to follow |
Internal power supply | via E-bus |
Current consumption E-bus | typ. 390 mA |
Current consumption power contacts | - |
Thermal power dissipation | typ. 3 W |
Dielectric strength - destruction limit | Max. permitted short-term/continuous voltage between each contact points ±I1, ±I2, +Uv and –Uv: non-supplied ±40 V, supplied ±36 V Note: -Uv corresponds to internal AGND |
Recommended operation voltage range to compliance with specification | Max. permitted voltage during specified normal operation between ±I1 and ±I2: typ. ±35 V against –Uv within 60 V-measuring range ±10 V against –Uv in all other measurement ranges Note: -Uv corresponds to internal AGND |
Common data | ELM3102-0100/ ELM3102-0120/ ELM3102-0130 |
Distributed Clocks | Yes, with Oversampling n = 1…100, accuracy << 1 μs |
Special features | Extended Range 107 %, freely configurable numeric filters, TrueRMS, integrator/differentiator, non-linear scaling, PeakHold |
Functional diagnosis 1) | Yes |
Electrical isolation channel/channel 2) |
Functional insulation, 707 V DC (type test) |
Electrical isolation channel/E-bus 2) |
Electrical isolation channel/GND 2) |
Configuration | via the EtherCAT Master, e.g. TwinCAT |
Note to cable length | Signal cable lengths to the sensor / encoder over 3 m must be shielded, the shield design must be in line with the state of the art and be effective. For larger cable lengths > 30 m, a suitable surge protection should be provided if appropriate interference could affect the signal cable. |
1) see chapters Self-test and self-test report and Connection test/switchable connection diagnosis
2) see notes to potential groups within chapter Power supply, potential groups
Basic mechanical | ELM3102-0100/ ELM3102-0120/ ELM3102-0130 |
Connection type | 2-pin push-in cage clamp, service plug |
Dimensions (W x H x D) | See chapter Housing |
Mounting | on 35 mm rail conforms to EN 60715 |
Note mounting | Plug partly not within scope of delivery, see chapter |
Weight | Approx. 350 g |
Permissible ambient temperature range during operation | 0…+55 °C |
Permissible ambient temperature range during storage | -25…+85 °C |
Environmental data | ELM3102-0100/ ELM3102-0120/ ELM3102-0130 |
Permissible operating altitude range | 0 up to 2000 m (derating at higher altitudes on request) |
Relative humidity | max. 95%, no condensation |
Protection class | IP 20 |
Normative data | ELM3102-0100/ ELM3102-0120/ ELM3102-0130 |
Vibration-/shock resistance | Conforms to EN 60068-2-6 / EN 60068-2-27 |
EMC-resistance / emission | Conforms to EN 61000-6-2 / EN 61000-6-4 |
Approvals/ markings *) | CE, UKCA, EAC, cULus |
EMC notes |
In case of push-in and mini-TC connectors, ESD air discharges conforming to EN 61000-6-4 into the connectors or to the lines connected there can lead to measurement deviations up to ±FSV within the respective channel or to other channels by crosstalk. Peak voltages (surge) conforming to EN 61000-6-2 that are applied to the cable shield can lead to measurement deviations up to ±FSV. |