Measurement ±20 mV
Measurement mode
±20 mV
Measuring range, nominal
-20…+20 mV
Measuring range, end value (FSV)
20 mV
Measuring range, technically usable
-21.474…+21.474 mV
PDO resolution (including sign)
24 bit
16 bit 2)
PDO LSB (Extended Range)
2.56 nV
655.36 nV
PDO LSB (Legacy Range)
2.384.. nV
610.37.. nV
Input impedance ±Input 1
(internal resistance)
Differential typ. 4.12 MΩ || 11 nF
CommonMode typ. 40 nF against SGND
2) The analog measurement is always done with 24 bits, in 16-bit mode the eight least significant bits are cut off. For further information see chapter “Commissioning”/ “Process data overview”
Measurement mode
±20 mV
Basic accuracy: Measuring deviation at 23°C, with averaging 6)
< ±0.04 %, < ±400 ppmFSV typ.
< ±8.0 µV typ.
Offset/Zero point deviation (at 23°C)
EOffset
< 380 ppmFSV
Gain/scale/amplification deviation (at 23°C)
EGain
< 60 ppm
Non-linearity over the whole measuring range
ELin
< 100 ppmFSV
Repeatability, over 24 h, with averaging
ERep
< 25.0 ppmFSV
Temperature coefficient
TcGain
< 4 ppm/K typ.
TcOffset
< 20.0 ppmFSV/K typ.
< 0.40 µV/K typ.
6) Calculated value according to the equation for estimating usability at the given ambient temperature point or estimating usability over the specified ambient temperature range in operation (Tambient) as stated in chapter "General information on measuring accuracy/measurement uncertainty". In real use, for example at a relatively constant ambient temperature Tambient, a lower (better) achievable uncertainty is attained. A specific calculation according to chapter "General information on measuring accuracy/measurement uncertainty" is recommended, especially if the instrument allows a wider ambient temperature range in operation than 0...55 °C.
Preliminary data
Measurement mode
±20 mV
Noise (without filtering)
ENoise, PtP
< 540 ppmFSV
< 4219 digits
< 10.80 µV
ENoise, RMS
< 90 ppmFSV
< 703 digits
< 1.80 µV
Max. SNR
> 80.9 dB
Noisedensity@1kHz
< 0.03 Measurement ±20 mV 1:
Noise (with 50/60 Hz FIR filter 5))
ENoise, PtP
< 80 ppmFSV
< 625 digits
< 1.60 µV
ENoise, RMS
< 13.0 ppmFSV
< 102 digits
< 0.26 µV
Max. SNR
> 97.7 dB
Common-mode rejection ratio (without filter)
DC: >115 dB typ.
50/60 Hz: >105 dB typ.
1 kHz: >80 dB typ.
Common-mode rejection ratio (with 50/60 Hz FIR filter 5))
DC: >115 dB typ.
50/60 Hz: >115 dB typ.
1 kHz: >115 dB typ.
Largest short-term deviation during a specified electrical interference test
Value to follow
5) the 50/60 Hz filter setting must be selected via the settings in the CoE depending on the local mains frequency (50 or 60 Hz); the respective nominal mains frequency then applies as the measuring point for common mode rejection or crosstalk.
Measurement ±20 mV 2:Fig.20: Representation ±20 mV measurement range
Note: In Extended Range Mode the Underrange/Overrange display in the PDO status has the character of an information/warning when the nominal measuring range is exceeded, i.e. no Error is displayed in the PDO status and LED. If the technical measuring range is also exceeded, Error = TRUE is also displayed. The detection limit for Underrange/Overrange Error can be set in the CoE.
In Legacy Range mode, an Underrange/Overrange event also leads to an Error in the PDO status.