EL8601-8411 - LEDs
EL8601-8411 - LEDs 1:Fig.41: EL8601-8411 - LEDs
No.
Color
Meaning
1
Error
red
off
No error
on
Error
2
DI/ENC A/CNT Clk
green
off
Signal voltage "0" (-3 V ... 5 V) at the corresponding input
3
DI/ENC B/CNT Dir
4
DI/Latch/Thr. Out/DO
on
Signal voltage "1" (11 V ... 30 V) at the corresponding input/output
5
DI/Gate/DO
6
PWM 1/ DO
green
Signal at PWM 1 / DO - output
7
AI
green
Signal at analog input (AI)
8
Error AI
red
Fault indication for wire break and if the measuring range for the analog input is exceeded (see chapter "Measuring ranges and scaling type").
9
RUN
green
This LED indicates the terminal's operating state:
off
State of the EtherCAT State Machine: INIT = initialization of the terminal
flashing uniformly
State of the EtherCAT State Machine: PREOP = function for mailbox communication and different default settings set
flashing slowly
State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks.
Outputs remain in safe state
on
State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible
flashing rapidly
State of the EtherCAT State Machine: BOOTSTRAP = function for Firmware updates of the terminal
10
DI 1
green
off
11
DI 2
12
DI 3
on
13
DI 4
14
PWM 2 / DO
green
Signal at PWM 2 / DO output
15
AO
green
Signal at analog output (AO)
16
Error AO
red
Error at analog output:
There is a short circuit or wire break and if the measuring range is exceeded or not reached (see chapter "Output ranges and scaling type").
EL8601-8411 - LEDs 2:
Overcurrent protection of the 20 mA inputs
The current inputs are protected against damage due to overcurrent by an internal current limiter. Currents > 30 mA can occur.
  • To ensure that the current limiter is not overloaded in the event of a fault, no voltage > 30 V may originate from the source device.
  • Overcurrent is displayed in the process image as "Overrange". After occurrence
  • the error state must be rectified immediately,
  • shutdown the source device or disconnect it from the input terminal.
  • If the error state persists for a longer period of time, the terminal-internal current limitation reduces the signal current drawn for thermal reasons, even below 20 mA depending on the ambient conditions.