Execution of a test run
Step 1: Preparation
- 1. Activate configuration.
- 2. Click on the axis and select the "Online" tab.
- 3. Move the motor shaft by hand to check the configuration of the encoder.
Does a relative movement of 360° actually correspond to a full revolution of the motor shaft? - If not: check the scaling factor. See chapter Configuration of the TwinCAT NC, section "Scaling Factor".
Step 2: Performing a test run
The motor may behave differently than expected Injuries and damage to property are possible.
- 1. Release the controller: click "Set" and then click "All" in the window that appears.
- If the release fails: check whether 24 V are present at the input "HW Enable". See chapter Wiring.
- 2. Try different commands.
- 3. Check whether the motor follows the commands in a stable and reliable manner.
Step 3: Checking the result
Check the following points, for example:
- Were errors reported in the Diag History? See chapter Diag History.
- Is the motor turning in the expected direction?
- Does the speed match the preset?