EL7211-901x, EL7221-901x - LEDs and connection
EL7211-901x, EL7221-901x - LEDs and connection 1:
Fig.23: EL7211-901x, EL7221-901x - LEDs
LED
Color
Meaning
RUN
green
This LED indicates the terminal's operating state:
off
State of the EtherCAT State Machine: INIT = initialization of the terminal
flashing
rapidly
State of the EtherCAT State Machine: BOOTSTRAP = function for terminal firmware updates
flashing
State of the EtherCAT State Machine: PREOP = function for mailbox communication and different standard-settings set
Single flash
State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks.
Outputs remain in safe state
on
State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible
Drive OK
green
on
Driver stage ready for operation
Limit
orange
on
The LED is linked with bit 11 of the status word (MDP742 / DS402) (internal limit active)
Limit reached (e.g. torque or speed limit)
Read OCT
green
flashing
The electronic type plate is being read
off
The reading of the electronic type plate has been completed
Warning
orange
flashing
Error while reading the type plate
on
The LED is linked with bit 7 of the status word (MDP742 / DS402) (warning)
The “Warning” threshold value is exceeded.
I²T model
Voltage missing at STO input
Temperature (80°C) exceeded
Voltage
Enable
green
on
The LED is linked with the bits 1 and 2 of status word  (MDP742 / DS402) (if "Switched on" or "Operation enabled")
Driver stage enabled
Input 1
Input 2
green
on
Signal is present at digital inputs
(e.g. end position, reference or latch sensors/switches)
Error
red
on
The LED is linked with bit 3 of the status word (MDP742 / DS402) (fault)
The “Error” threshold value is exceeded.
Overcurrent
STO triggered with active axis
Voltage not available
Resolver not connected
Max. temperature (100°C) exceeded
+24 V via power contacts
green
on
24 V voltage supply for the terminal is present.
DC link supply
green
on
Voltage for the DC link supply is present.
Notice
Fuse protection of the supply voltage
The electrical protection of the load voltage must be selected in such a way that the maximum flowing current is limited to 3 times the rated current (max. 1 second)!
EL7211-901x, EL7221-901x - Connection
EL7211-901x, EL7221-901x - LEDs and connection 2:
Fig.2: EL7211-901x, EL7221-901x - Connection
Terminal point
Comment
1
OCT +
Positive input of the absolute feedback
2
Input 1
Digital input 1
3
+24 V
Power contact +24 V
4
U
Motor phase U
5
W
Motor phase W
6
Brake +
Motor brake +
7
48 V
DC link supply + (8 ... 48 V)
8
9
OCT -
Negative input of the absolute feedback
10
Input 2
Digital input 2
11
0 V
Power contact 0 V
12
V
Motor phase V
13
STO input
Input for STO signal (24 V)
14
Brake GND
Motor brake 0 V
15
0 V
DC link 0 V supply
16
1' - 16'
n.c.