Objects for parameterization
Index 8000 FB Settings Ch.1
8000:0 | FB Settings Ch.1 |
| UINT8 | RO | 0x1C (28dec) |
8000:11 | Device type |
| UINT32 | RW | 0x00000005 (5dec) |
8000:12 | Singleturn bits | Number of single-turn bits in the position display (process data, CoE). The sum of the single-turn bits and multi-turn bits must be 32. Note: This parameter only influences the display and is independent of the physical resolution of the position sensor. | UINT8 | RW | 0x14 (20dec) |
8000:13 | Multiturn bits | Number of multi-turn bits in the position display (process data, CoE). The sum of the single-turn bits and multi-turn bits must be 32. Note: This parameter only influences the display and is independent of the physical resolution of the position sensor. | UINT8 | RW | 0x0C (12dec) |
8000:14 | Observer bandwidth | Bandwidth of the speed observer [Hz] | UINT16 | RW | 0x00C8 (200dec) |
8000:15 | Observer feed-forward | Load ratio [%] between internal rotor inertia of the motor and the total inertia of the driven system. Load ratio = internal moment of inertia / (internal moment of inertia + mass moment of inertia of the load). Examples:
| UINT8 | RW | 0x64 (100dec) |
8000:17 | Position offset | The Position offset is subtracted from the raw position of the encoder. It can only be written with the axis stopped. | UINT32 | RW | 0x00000000 (0dec) |
8000:18 | Secondary position offset | The Secondary Position Offset is subtracted from the "Secondary Position". It can only be written with the axis stopped. | UINT32 | RW | 0x00000000 (0dec) |
8000:19 | Gear ratio motor shaft revolutions | These parameters are used to scale all positions and speeds from the motor side to the load side of a gear unit. "Gear ratio motor shaft revolutions" describes the number of motor revolutions required to achieve the number of load revolutions configured in "Gear ratio driving shaft revolutions". Example: For a reduction gear in which 5 motor revolutions result in 2 load revolutions, set the parameters as follows:
| UINT32 | RW | 0x00000001 (1dec) |
8000:1A | Gear ratio driving shaft revolutions | UINT32 | RW | 0x00000001 (1dec) |
8000:1B | Min position range limit | Lowest value for the position display of setpoints and actual values. If the value falls below this, an underflow to the value "Max position range limit" occurs. "Min position range limit" must always be lower than "Max position range limit". | UINT32 | RW | 0x00000000 (0dec) |
8000:1C | Max position range limit | Highest value for the position display of setpoints and actual values. If this is exceeded, an overflow to the value "Min position range limit" occurs. "Max position range limit" must always be higher than "Min position range limit". | UINT32 | RW | 0xFFFFFFFF (4294967295dec) |
Index 8001 FB Touch probe Settings Ch.1
8001:0 | FB Touch probe Settings Ch.1 |
| UINT8 | RO | 0x16 (22dec) |
8001:11 | Touch probe 1 source | Selection of the input signal for Touch probe 1. Permitted values:
| INT16 | RW | 0x0001 (1dec) |
8001:12 | Touch probe 2 source | Selection of the input signal for Touch probe 2. Permitted values:
| INT16 | RW | 0x0002 (2dec) |
8001:15 | Touch probe 1 position source | Selection of the position held by Touch probe 1. Permitted values:
| INT16 | RW | 0x0000 (0dec) |
8001:16 | Touch probe 2 position source | Selection of the position held by Touch probe 2. Permitted values:
Index 8008 FB Settings ENC Ch.1
8008:0 | FB Settings ENC Ch.1 |
| UINT8 | RO | 0x13 (19dec) |
8008:01 | Invert feedback direction | Changes the counting direction of the encoder. This parameter can be used to adapt the encoder direction of rotation to the motor direction of rotation. | BOOLEAN | RW | 0x00 (0dec) |
8008:12 | Encoder type | permitted values:
| UINT16 | RW | 0x0000 (0dec) |
8008:13 | Encoder Increments per Revolution | Resolution of the encoder after 4-fold evaluation. | UINT32 | RW | 0x00001000 (4096dec) |
Index 8010 DRV Amplifier Settings Ch.1
8010:0 | DRV Amplifier Settings Ch.1 |
| UINT8 | RO | 0x73 (115dec)) |
8010:01 | Enable TxPDOToggle | Show TxPDO Toggle in the status word (bit 10). | BOOLEAN | RW | 0x00 (0dec) |
8010:02 | Enable input cycle counter | 1: enabled The Input cycle counter is a two-bit counter that is incremented with each process data cycle up to a maximum value of 3, after which it starts again at 0. The low bit is represented in bit 10 and the high bit in bit 14 of the status word. | BOOLEAN | RW | 0x00 (0dec) |
8010:04 | Repeat find commutation | Repeat the commutation angle determination. (Effective for all FOC operation modes). | BOOLEAN | RW | 0x01 (1dec) |
8010:12 | Current loop integral time | Integral component current controller [0.1 ms]. | UINT16 | RW | 0x0032 (50dec) |
8010:13 | Current loop proportional gain | Proportional component current controller [0.1 V/A] | UINT16 | RW | 0x0032 (50dec) |
8010:14 | Velocity loop integral time | Integral component velocity controller [0.1 ms]. | UINT32 | RW | 0x0000001E (30dec) |
8010:15 | Velocity loop proportional gain | Proportional component velocity controller [mA/(rad/s)]. | UINT32 | RW | 0x00000096 (150dec) |
8010:17 | Position loop proportional gain | Proportional component position controller [1/s] | UINT32 | RW | 0x0000000A (10dec) |
8010:31 | Velocity limitation | Limitation of the drive speed set value [1/min]. (Only effective in the CSV and CSP controller operation modes) When using a gear ratio, this parameter refers to the load side. | UINT32 | RW | 0x000186A0 (100000dec) |
8010:32 | Short-Circuit Brake duration max | Max. duration of armature short circuit brake. [ms] | UINT16 | RW | 0x0000 (0dec) |
8010:33 | Stand still window | Tolerance window for standstill monitoring [1/min] | UINT16 | RW | 0x0001 (1dec) |
8010:39 | Select info data 1 | permitted values:
| UINT8 | RW | 0x02 (2dec) |
8010:3A | Select info data 2 | permitted values:
| UINT8 | RW | 0x04 (4dec) |
8010:49 | Halt ramp deceleration | Halt ramp deceleration [0.1 rad / s²] | UINT32 | RW | 0x0000F570 (62832dec) |
8010:50 | Following error window | Following error monitoring: following error window. The value 0xFFFFFFFFFF (4294967295dec) disables the following error monitoring. | UINT32 | RW | 0xFFFFFFFF (4294967295dec) |
8010:51 | Following error time out | Following error monitoring: timeout [ms]. | UINT16 | RW | 0x0000 (0dec) |
8010:52 | Fault reaction option code | permitted values:
8010:54 | Feature bits | -- | UINT32 | RW | 0x00000000 (0dec) |
8010:57 | Position loop velocity feed forward gain | Scaling factor for velocity pre-control from the position interpolator. | UINT8 | RW | 0x64 (100dec) |
8010:58 | Select info data 3 | permitted values:
| UINT8 | RW | 0x0A (10dec) |
8010:59 | Error suppression mask |
8010:62 | Position loop deadband window | Deadband window of the position controller. Unit: corresponds to the process data scaling of the set position and actual positions. | UINT32 | RW | 0x00000000 (0dec) |
8010:63 | Find commutation time | For field-oriented control (FOC) with an incremental encoder, commutation determination is required, during which nominal current is applied to the motor. The "Find commutation time" describes the time used for this. | UINT16 | RW | 0x000A (10dec) |
8010:64 | Commutation type | permitted values:
| UINT8 | RW | 0x10 (16dec) |
8010:65 | Invert direction of rotation | Inverting the direction of rotation. This parameter inverts all setpoints and actual values and is used to ensure that the motor rotates in the correct direction for the application. Note: This parameter is not suitable for adapting the directions of rotation of the encoder and motor to each other. Use 8008:01 "Invert feedback direction" for this purpose. | BOOLEAN | RW | 0x00 (0dec) |
8010:6D | Torque feed forward gain | Internal torque pre-control: scaling factor | UINT32 | RW | 0x00000064 (100dec) |
8010:6E | Torque feed forward filter time | Internal torque pre-control: filter time. [0.1 ms] | UINT32 | RW | 0x0000000A (10dec) |
8010:6F | Torque offset | Torque offset. The value is given in thousandths of the nominal current. | INT16 | RW | 0x0000 (0dec) |
8010:70 | Torque limitation option code | Selection of the behavior in the CST controller operation mode (“Cyclic Synchronous Torque”). Permitted values:
| INT8 | RW | 0x00 (0dec) |
8010:72 | Stand still torque limitation | Only valid for commutation types "Stepper with internal counter" and "Stepper with encoder" (can be set via parameter 8010:64). Configures a current reduction at standstill, i.e. when the target velocity is within the "Stand still window" (parameter 8010:33). The value is given in thousandths of the nominal current. | UINT16 | RW | 0x7FFF (32767dec) |
8010:73 | Acceleration limitation | Limits the maximum acceleration or deceleration. [0.1 rad/s²] | UINT32 | RW | 0x0000F570 (62832dec) |
Index 8011 DRV Motor Settings Ch.1
8011:0 | DRV Motor Settings Ch.1 |
| UINT8 | RO | 0x34 (52dec) |
8011:12 | Rated current | The nominal current of the motor (data sheet value). Used for scaling "Torque actual value" and "Target torque". | UINT32 | RW | 0x00000BB8 (3000dec) |
8011:16 | Torque constant | Force constant of the motor. | UINT32 | RW | 0x0000012C (300dec) |
8011:18 | Rotor moment of inertia | Moment of inertia of the motor. | UINT32 | RW | 0x000001EF (495dec) |
8011:19 | Winding inductance | Winding inductance. | UINT16 | RW | 0x0186 (390dec) |
8011:1B | Motor speed limitation | Speed limit of the motor. When using a gear ratio, this limit still refers to the motor side. | UINT32 | RW | 0x000186A0 (100000dec) |
8011:2E | Rated speed | Nominal speed of the motor. | UINT32 | RW | 0x000003E8 (1000dec) |
8011:30 | Winding resistance | Winding resistance of the motor. | UINT32 | RW | 0x00000578 (1400dec) |
8011:31 | Voltage constant | Voltage constant of the motor. | UINT32 | RW | 0x00004E20 (20000dec) |
8011:33 | Motor fullsteps per revolution | Number of full motor steps per revolution. | UINT32 | RW | 0x000000C8 (200dec) |
8011:34 | Configured motor current | Configured motor current. If this is smaller than the "Rated current", the motor current is limited to the smaller of the two values. This value is used to distribute the load between the two channels of the terminal. | UINT32 | RW | 0x00000BB8 (3000dec) |
Index 8012 DRV Brake Settings Ch.1
8012:0 | DRV Brake Settings Ch.1 |
| UINT8 | RO | 0x14 (20dec) |
8012:01 | Enable manual override |
8012:02 | Manual brake state | Permitted values:
| BIT1 | RW | 0x00 (0dec) |
8012:05 | Brake option | Permitted values:
| BIT4 | RW | 0x00 (0dec) |
8012:09 | External override | Enables the brake to be released via an external hardware signal. The brake can only be released via the external signal, not applied. You can select which hardware input (Touch probe 1 / Touch probe 2) is used for this. It is also possible to restrict whether this configuration is always active or only in the EtherCAT states INIT/PREOP/SAFEOP, i.e. when the drive is not fully operational (e.g. during maintenance work) Permitted values:
| UINT8 | RW | 0x00 (0dec) |
8012:11 | Release delay | Time required for the holding brake to release after the current has been applied. | UINT16 | RW | 0x0000 (0dec) |
8012:12 | Application delay | Time required for the holding brake to apply after the current was switched off. | UINT16 | RW | 0x0000 (0dec) |
8012:13 | Emergency application timeout | Time that the amplifier waits for the speed to reach the standstill limit after a stop request. If the waiting time is exceeded, the holding brake is triggered, regardless of the speed. Note: This parameter must be set at least to the longest time the axis needs to come to a standstill after it has been switched torque-free. For vertical axes, this parameter should be set to a low value to prevent the axis or load from falling very far. Unit: ms | UINT16 | RW | 0x0000 (0dec) |
8012:14 | Brake moment of inertia | Moment of inertia of the brake. Unit: g cm² | UINT16 | RW | 0x0000 (0dec) |
Index 8013 DRV Filter Settings Ch.1
8013:0 | DRV Filter Settings Ch.1 |
| UINT8 | RO | 0x19 (25dec) |
8013:10 | Low pass frequency 1 |
| REAL32 | RW | 0x00000000 (0dec) |
8013:11 | Low pass damping 1 |
8013:12 | High pass frequency 1 |
8013:13 | High pass damping 1 |
8013:14 | Filter type 1 | permitted values:
8013:15 | Low pass frequency 2 |
8013:16 | Low pass damping 2 |
8013:17 | High pass frequency 2 |
8013:18 | High pass damping 2 |
8013:19 | Filter type 2 | permitted values:
Index 801F DRV Vendor data Ch.1
801F:0 | DRV Vendor data Ch.1 |
801F:12 | Amplifier rated current | Maximum current per channel (without fan). | UINT32 | RW | 0x00001388 (5000dec) |
801F:14 | Amplifier overcurrent threshold | Switching threshold for the overcurrent switch-off. | UINT32 | RW | 0x00002710 (10000dec) |
801F:15 | Max rotary field frequency |
| UINT16 | RW | 0x0257 (599dec) |
801F:17 | Amplifier rated current with fan | Maximum current per channel (with fan) | UINT32 | RW | 0x00001770 (6000dec) |
801F:18 | Vendor feature bits |
801F:1A | Amplifier Rated Sum Current | Maximum sum current for all channels (without fan) | UINT32 | RW | 0x00001770 (6000dec) |
801F:1C | Amplifier Rated Sum Current with Fan | Maximum sum current for all channels (with fan) | UINT32 | RW | 0x00002710 (10000dec) |
Index 8060 DMC Settings Ch.1
8060:0 | DMC Settings Ch.1 |
| UINT8 | RO | 0x17 (23dec) |
8060:07 | Emergency deceleration | Deceleration for the emergency stop ramp. (In ms from motor nominal speed to standstill) Unit: 1 ms | UINT16 | RW | 0x0064 (100dec) |
8060:08 | Calibration position | If homing is successful, the "Actual position" is set to this value. | INT64 | RW |
8060:09 | Calibration velocity (towards plc cam) | Velocity when hitting the cam in 10000ths of the motor nominal speed. | INT16 | RW | 0x0064 (100dec) |
8060:0A | Calibration Velocity (off plc cam) | Velocity when driving off the cam in 10000ths of the motor nominal speed. | INT16 | RW | 0x000A (10dec) |
8060:0E | Modulo factor | Feedback increments for one mechanical revolution. | INT64 | RW |
8060:12 | Block calibration torque limit | Torque limitation for approaching the end stop. In parts per thousand of the nominal motor current. | UINT16 | RW | 0x0064 (100dec) |
8060:13 | Block calibration stop distance | After reaching the calibration position, the axis moves out of the end position by this distance. | INT64 | RW |
8060:14 | Block calibration lag threshold | When this following error is exceeded, the axis is in the end position. | INT64 | RW |
8060:15 | Target position window | Target position window: The In-Target bit is set when the axis is within this window for at least the time set in 8060:16. | INT64 | RW |
8060:16 | Target position monitor time | see 8060:15 Unit: ms | UINT16 | RW | 0x0014 (20dec) |
8060:17 | Target position timeout | When the setpoint generator has reached its end position and the axis is not in the target window after this time has elapsed, the task is terminated and the in-target bit is not set. Unit: ms | UINT16 | RW | 0x1770 (6000dec) |
Index 8061 DMC Features Ch.1
8061:0 | DMC Features Ch.1 |
| UINT8 | RO | 0x1B (27dec) |
8061:13 | Invert calibration cam search direction | Invert the direction of movement to search for the limit switch. Default: FALSE = search with positive direction of rotation. | BOOLEAN | RW | 0x00 (0dec) |
8061:14 | Invert sync impulse search direction | Invert the direction of rotation to exit the limit switch. Default: TRUE = exit in negative direction of rotation. | BOOLEAN | RW | 0x01 (1dec) |
8061:19 | Calibration cam source | Source for the reference switch.
8061:1A | Calibration cam active level | State of the reference switch in the actuated state.
8061:1B | Latch source | Source for the latch unit.
Index 8100 FB Settings Ch.2
8100:0 | FB Settings Ch.2 |
8100:11 | Device type |
8100:12 | Singleturn bits | Number of single-turn bits in the position display (process data, CoE). The sum of the single-turn bits and multi-turn bits must be 32. Note: This parameter only influences the display and is independent of the physical resolution of the position sensor. | UINT8 | RW | 0x14 (20dec) |
8100:13 | Multiturn bits | Number of multi-turn bits in the position display (process data, CoE). The sum of the single-turn bits and multi-turn bits must be 32. Note: This parameter only influences the display and is independent of the physical resolution of the position sensor. | UINT8 | RW | 0x0C (12dec) |
8100:14 | Observer bandwidth | Bandwidth of the speed observer [Hz] | UINT16 | RW | 0x00C8 (200dec) |
8100:15 | Observer feed-forward | Load ratio [%] between internal rotor inertia of the motor and the total inertia of the driven system. Load ratio = internal moment of inertia / (internal moment of inertia + mass moment of inertia of the load). Examples:
8100:17 | Position offset | The Position offset is subtracted from the raw position of the encoder. It can only be written with the axis stopped. | UINT32 | RW | 0x00000000 (0dec) |
8100:18 | Secondary position offset | The Secondary Position Offset is subtracted from the "Secondary Position". It can only be written with the axis stopped. | UINT32 | RW | 0x00000000 (0dec) |
8100:19 | Gear ratio motor shaft revolutions | These parameters are used to scale all positions and speeds from the motor side to the load side of a gear unit. "Gear ratio motor shaft revolutions" describes the number of motor revolutions required to achieve the number of load revolutions configured in "Gear ratio driving shaft revolutions". Example: For a reduction gear in which 5 motor revolutions result in 2 load revolutions, set the parameters as follows:
8100:1A | Gear ratio driving shaft revolutions | UINT32 | RW | 0x00000001 (1dec) | |
8100:1B | Min position range limit | Lowest value for the position display of setpoints and actual values. If the value falls below this, an underflow to the value "Max position range limit" occurs. "Min position range limit" must always be lower than "Max position range limit". | UINT32 | RW | 0x00000000 (0dec) |
8100:1C | Max position range limit | Highest value for the position display of setpoints and actual values. If this is exceeded, an overflow to the value "Min position range limit" occurs. "Max position range limit" must always be higher than "Min position range limit". | UINT32 | RW | 0xFFFFFFFF (4294967295dec) |
Index 8101 FB Touch probe Settings Ch.2
8101:0 | FB Touch probe Settings Ch.2 |
8101:11 | Touch probe 1 source | Selection of the input signal for Touch probe 1. Permitted values:
8101:12 | Touch probe 2 source | Selection of the input signal for Touch probe 2. Permitted values:
8101:15 | Touch probe 1 position source | Selection of the position held by Touch probe 1. Permitted values:
8101:16 | Touch probe 2 position source | Selection of the position held by Touch probe 2. Permitted values:
Index 8108 FB Settings ENC Ch.2
8108:0 | FB Settings ENC Ch.2 |
8108:01 | Invert feedback direction | Changes the counting direction of the encoder. This parameter can be used to adapt the encoder direction of rotation to the motor direction of rotation. | BOOLEAN | RW | 0x00 (0dec) |
8108:12 | Encoder type | permitted values:
8108:13 | Encoder Increments per Revolution | Resolution of the encoder after 4-fold evaluation. | UINT32 | RW | 0x00001000 (4096dec) |
Index 8110 DRV Amplifier Settings Ch.2
8110:0 | DRV Amplifier Settings Ch.2 |
8110:01 | Enable TxPDOToggle | Show TxPDO Toggle in the status word (bit 10). | BOOLEAN | RW | 0x00 (0dec) |
8110:02 | Enable input cycle counter | 1: enabled The Input cycle counter is a two-bit counter that is incremented with each process data cycle up to a maximum value of 3, after which it starts again at 0. The low bit is represented in bit 10 and the high bit in bit 14 of the status word. | BOOLEAN | RW | 0x00 (0dec) |
8110:04 | Repeat find commutation | Repeat the commutation angle determination. (Effective for all FOC operation modes). | BOOLEAN | RW | 0x01 (1dec) |
8110:12 | Current loop integral time | Integral component current controller [0.1 ms]. | UINT16 | RW | 0x0032 (50dec) |
8110:13 | Current loop proportional gain | Proportional component current controller [0.1 V/A] | UINT16 | RW | 0x0032 (50dec) |
8110:14 | Velocity loop integral time | Integral component velocity controller [0.1 ms]. | UINT32 | RW | 0x0000001E (30dec) |
8110:15 | Velocity loop proportional gain | Proportional component velocity controller [mA/(rad/s)]. | UINT32 | RW | 0x00000096 (150dec) |
8110:17 | Position loop proportional gain | Proportional component position controller [1/s] | UINT32 | RW | 0x0000000A (10dec) |
8110:31 | Velocity limitation | Limitation of the drive speed set value [1/min]. (Only effective in the CSV and CSP controller operation modes) When using a gear ratio, this parameter refers to the load side. | UINT32 | RW | 0x000186A0 (100000dec) |
8110:32 | Short-Circuit Brake duration max | Max. duration of armature short circuit brake. [ms] | UINT16 | RW | 0x0000 (0dec) |
8110:33 | Stand still window | Tolerance window for standstill monitoring [1/min] | UINT16 | RW | 0x0001 (1dec) |
8110:39 | Select info data 1 | permitted values:
8110:3A | Select info data 2 | permitted values:
8110:49 | Halt ramp deceleration | Halt ramp deceleration [0.1 rad / s²] | UINT32 | RW | 0x0000F570 (62832dec) |
8110:50 | Following error window | Following error monitoring: following error window. The value 0xFFFFFFFFFF (4294967295dec) disables the following error monitoring. | UINT32 | RW | 0xFFFFFFFF (4294967295dec) |
8110:51 | Following error time out | Following error monitoring: timeout [ms]. | UINT16 | RW | 0x0000 (0dec) |
8110:52 | Fault reaction option code | permitted values:
8110:54 | Feature bits | -- | UINT32 | RW | 0x00000000 (0dec) |
8110:57 | Position loop velocity feed forward gain | Scaling factor for velocity pre-control from the position interpolator. | UINT8 | RW | 0x64 (100dec) |
8110:58 | Select info data 3 | permitted values:
8110:59 | Error suppression mask |
8110:62 | Position loop deadband window | Deadband window of the position controller. Unit: corresponds to the process data scaling of the set position and actual positions. | UINT32 | RW | 0x00000000 (0dec) |
8110:63 | Find commutation time | For field-oriented control (FOC) with an incremental encoder, commutation determination is required, during which nominal current is applied to the motor. The "Find commutation time" describes the time used for this. | UINT16 | RW | 0x000A (10dec) |
8110:64 | Commutation type | permitted values:
8110:65 | Invert direction of rotation | Inverting the direction of rotation. This parameter inverts all setpoints and actual values and is used to ensure that the motor rotates in the correct direction for the application. Note: This parameter is not suitable for adapting the directions of rotation of the encoder and motor to each other. Use 8008:01 "Invert feedback direction" for this purpose. | BOOLEAN | RW | 0x00 (0dec) |
8110:6D | Torque feed forward gain | Internal torque pre-control: scaling factor | UINT32 | RW | 0x00000064 (100dec) |
8110:6E | Torque feed forward filter time | Internal torque pre-control: filter time. [0.1 ms] | UINT32 | RW | 0x0000000A (10dec) |
8110:6F | Torque offset | Torque offset. The value is given in thousandths of the nominal current. | INT16 | RW | 0x0000 (0dec) |
8110:70 | Torque limitation option code | Selection of the behavior in the CST controller operation mode (“Cyclic Synchronous Torque”). Permitted values:
8110:72 | Stand still torque limitation | Only valid for commutation types "Stepper with internal counter" and "Stepper with encoder" (can be set via parameter 8110:64). Configures a current reduction at standstill, i.e. when the target velocity is within the "Stand still window" (parameter 8110:33). The value is given in thousandths of the nominal current. | UINT16 | RW | 0x7FFF (32767dec) |
8110:73 | Acceleration limitation | Limits the maximum acceleration or deceleration. [0.1 rad/s²] | UINT32 | RW | 0x0000F570 (62832dec) |
Index 8111 DRV Motor Settings Ch.2
8111:0 | DRV Motor Settings Ch.2 |
8111:12 | Rated current | The nominal current of the motor (data sheet value). Used for scaling "Torque actual value" and "Target torque". | UINT32 | RW | 0x00000BB8 (3000dec) |
8111:16 | Torque constant | Force constant of the motor. | UINT32 | RW | 0x0000012C (300dec) |
8111:18 | Rotor moment of inertia | Moment of inertia of the motor. | UINT32 | RW | 0x000001EF (495dec) |
8111:19 | Winding inductance | Winding inductance. | UINT16 | RW | 0x0186 (390dec) |
8111:1B | Motor speed limitation | Speed limit of the motor. When using a gear ratio, this limit still refers to the motor side. | UINT32 | RW | 0x000186A0 (100000dec) |
8111:2E | Rated speed | Nominal speed of the motor. | UINT32 | RW | 0x000003E8 (1000dec) |
8111:30 | Winding resistance | Winding resistance of the motor. | UINT32 | RW | 0x00000578 (1400dec) |
8111:31 | Voltage constant | Voltage constant of the motor. | UINT32 | RW | 0x00004E20 (20000dec) |
8111:33 | Motor fullsteps per revolution | Number of full motor steps per revolution. | UINT32 | RW | 0x000000C8 (200dec) |
8111:34 | Configured motor current | Configured motor current. If this is smaller than the "Rated current", the motor current is limited to the smaller of the two values. This value is used to distribute the load between the two channels of the terminal. | UINT32 | RW | 0x00000BB8 (3000dec) |
Index 8112 DRV Brake Settings Ch.2
8112:0 | DRV Brake Settings Ch.2 |
8112:01 | Enable manual override |
8112:02 | Manual brake state | Permitted values:
8112:05 | Brake option | Permitted values:
8112:09 | External override | Enables the brake to be released via an external hardware signal. The brake can only be released via the external signal, not applied. You can select which hardware input (Touch probe 1 / Touch probe 2) is used for this. It is also possible to restrict whether this configuration is always active or only in the EtherCAT states INIT/PREOP/SAFEOP, i.e. when the drive is not fully operational (e.g. during maintenance work) Permitted values:
8112:11 | Release delay | Time required for the holding brake to release after the current has been applied. | UINT16 | RW | 0x0000 (0dec) |
8112:12 | Application delay | Time required for the holding brake to apply after the current was switched off. | UINT16 | RW | 0x0000 (0dec) |
8112:13 | Emergency application timeout | Time that the amplifier waits for the speed to reach the standstill limit after a stop request. If the waiting time is exceeded, the holding brake is triggered, regardless of the speed. Note: This parameter must be set at least to the longest time the axis needs to come to a standstill after it has been switched torque-free. For vertical axes, this parameter should be set to a low value to prevent the axis or load from falling very far. Unit: ms | UINT16 | RW | 0x0000 (0dec) |
8112:14 | Brake moment of inertia | Moment of inertia of the brake. Unit: g cm² | UINT16 | RW | 0x0000 (0dec) |
Index 8113 DRV Filter Settings Ch.2
8113:0 | DRV Filter Settings Ch.2 |
8113:10 | Low pass frequency 1 |
8113:11 | Low pass damping 1 |
8113:12 | High pass frequency 1 |
8113:13 | High pass damping 1 |
8113:14 | Filter type 1 | permitted values:
8113:15 | Low pass frequency 2 |
8113:16 | Low pass damping 2 |
8113:17 | High pass frequency 2 |
8113:18 | High pass damping 2 |
8113:19 | Filter type 2 | permitted values:
Index 811F DRV Vendor data Ch.2
811F:0 | DRV Vendor data Ch.2 |
811F:12 | Amplifier rated current | Maximum current per channel (without fan). | UINT32 | RW | 0x00001388 (5000dec) |
811F:14 | Amplifier overcurrent threshold | Switching threshold for the overcurrent switch-off. | UINT32 | RW | 0x00002710 (10000dec) |
811F:15 | Max rotary field frequency |
811F:17 | Amplifier rated current with fan | Maximum current per channel (with fan) | UINT32 | RW | 0x00001770 (6000dec) |
811F:18 | Vendor feature bits |
811F:1A | Amplifier Rated Sum Current | Maximum sum current for all channels (without fan) | UINT32 | RW | 0x00001770 (6000dec) |
811F:1C | Amplifier Rated Sum Current with Fan | Maximum sum current for all channels (with fan) | UINT32 | RW | 0x00002710 (10000dec) |
Index 8160 DMC Settings Ch.2
8160:0 | DMC Settings Ch.2 |
8160:07 | Emergency deceleration | Deceleration for the emergency stop ramp. (In ms from motor nominal speed to standstill) Unit: 1 ms | UINT16 | RW | 0x0064 (100dec) |
8160:08 | Calibration position | If homing is successful, the "Actual position" is set to this value. | INT64 | RW |
8160:09 | Calibration velocity (towards plc cam) | Velocity when hitting the cam in 10000ths of the motor nominal speed. | INT16 | RW | 0x0064 (100dec) |
8160:0A | Calibration Velocity (off plc cam) | Velocity when driving off the cam in 10000ths of the motor nominal speed. | INT16 | RW | 0x000A (10dec) |
8160:0E | Modulo factor | Feedback increments for one mechanical revolution. | INT64 | RW |
8160:12 | Block calibration torque limit | Torque limitation for approaching the end stop. In parts per thousand of the nominal motor current. | UINT16 | RW | 0x0064 (100dec) |
8160:13 | Block calibration stop distance | After reaching the calibration position, the axis moves out of the end position by this distance. | INT64 | RW |
8160:14 | Block calibration lag threshold | When this following error is exceeded, the axis is in the end position. | INT64 | RW |
8160:15 | Target position window | Target position window: The In-Target bit is set when the axis is within this window for at least the time set in 8160:16. | INT64 | RW |
8160:16 | Target position monitor time | see 8160:15 Unit: ms | UINT16 | RW | 0x0014 (20dec) |
8160:17 | Target position timeout | When the setpoint generator has reached its end position and the axis is not in the target window after this time has elapsed, the task is terminated and the in-target bit is not set. Unit: ms | UINT16 | RW | 0x1770 (6000dec) |
Index 8161 DMC Features Ch.2
8161:0 | DMC Features Ch.2 |
8161:13 | Invert calibration cam search direction | Invert the direction of movement to search for the limit switch. Default: FALSE = search with positive direction of rotation. | BOOLEAN | RW | 0x00 (0dec) |
8161:14 | Invert sync impulse search direction | Invert the direction of rotation to exit the limit switch. Default: TRUE = exit in negative direction of rotation. | BOOLEAN | RW | 0x01 (1dec) |
8161:19 | Calibration cam source | Source for the reference switch.
8161:1A | Calibration cam active level | State of the reference switch in the actuated state.
8161:1B | Latch source | Source for the latch unit.
Index F800 DRV Amplifier Settings
F800:0 | DRV Amplifier Settings |
| UINT8 | RO | 0x18 (24dec) |
F800:10 | Nominal DC link voltage | Nominal DC link voltage. | UINT32 | RW | 0x0000BB80 (48000dec) |
F800:11 | Min DC link voltage | Min. DC link voltage. If the value falls below this, a drive error is triggered or an inactive axis cannot be switched on. | UINT32 | RW | 0x00001A90 (6800dec) |
F800:12 | Max DC link voltage | Max. DC link voltage. If this value is exceeded, a drive error is triggered or an inactive axis cannot be switched on. | UINT32 | RW | 0x0000EA60 (60000dec) |
F800:15 | Amplifier Temperature warn level | Amplifier temperature warning threshold. | UINT16 | RW | 0x0320 (800dec) |
F800:16 | Amplifier Temperature error level | Amplifier temperature error threshold. | UINT16 | RW | 0x03E8 (1000dec) |
F800:17 | Feature bits |
F800:18 | Fan Configuration | An external fan can be used to increase the permissible motor current for the terminal. Permitted values: