Standard objects (0x1000-0x1FFF)
The standard objects have the same meaning for all EtherCAT slaves.
Index 1000 Device type
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1000:0 |
Device type |
Device type of the EtherCAT slave: The Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile. |
UINT32 |
RO |
0x00001389 (5001dec) |
Index 1008 Device name
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1008:0 |
Device name |
Device name of the EtherCAT slave |
STRING |
RO |
EL6751 |
Index 1009 Hardware version
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1009:0 |
Hardware version |
Hardware version of the EtherCAT slave |
STRING |
RO |
Index 100A Software version
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
100A:0 |
Software version |
Firmware version of the EtherCAT slave |
STRING |
RO |
Index 1010 Store parameters
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1010:0 |
Store parameters |
Save the CANopen configuration after scanning the CAN bus with entry 0xF002:01 |
UINT8 |
RO |
1010:01 |
SubIndex 001 |
If you set this entry to ‘0x65766173’, the Backup Parameter Storage (object 0x10F2) is generated from the InfoData 0x9yyz. |
UINT32 |
RW |
Index 1011 Restore default parameters
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1011:0 |
Restore default parameters |
UINT8 |
RO |
1011:01 |
SubIndex 001 |
If you set this entry to ‘0x64616F6C’, all backup objects are reset to the delivery state. |
UINT32 |
RW |
Index 1018 Identity
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1018:0 |
Identity |
Information for identifying the slave |
UINT8 |
RO |
0x04 (4dec) |
1018:01 |
Vendor ID |
Vendor ID of the EtherCAT slave |
UINT32 |
RO |
0x00000002 (2dec) |
1018:02 |
Product code |
Product code of the EtherCAT slave |
UINT32 |
RO |
0x1A5F3052 (442445906dec) |
1018:03 |
Revision |
Revision number of the EtherCAT slave; the low word (bit 0-15) indicates the special terminal number, the high word (bit 16-31) refers to the device description |
UINT32 |
RO |
0x00100000 (1048576dec) |
1018:04 |
Serial number |
Serial number of the EtherCAT slave; the low byte (bit 0-7) of the low word contains the year of production, the high byte (bit 8-15) of the low word contains the week of production, the high word (bit 16-31) is 0 |
UINT32 |
RO |
0x00000000 (0dec) |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
10F0:0 |
Backup parameter handling |
Information for standardized loading and saving of backup entries |
UINT8 |
RO |
10F0:01 |
Checksum |
Checksum of the Backup Parameter Storage (object 0x10F2, word 2-3) |
UINT32 |
RO |
Index 10F2 Backup parameter storage
Index |
Name |
Meaning |
Data type |
Flags |
Default | |
10F2:0 |
Backup parameter storage |
If this object is used, no StartUp SDOs may be transmitted in the PREOP state, since the Backup Parameter Storage contains the complete StartUp SDOs (see Configuration of the EL6751 with Backup Parameter Storage). The EL6751 is rebooted 5 s after the flashing of the Backup Parameter Storage (switches to INIT with AL status code = 0x60). The data have the following meaning: |
OCTET-STRING[n] |
RW |
Word-Offset |
Description | |||||
0 |
Command: with 0xC0DE, the received data are stored in the flash memory | |||||
1 |
Length of the data from word offset 4 in bytes | |||||
2-3 |
Checksum, which is calculated locally | |||||
4 |
Index of the object of the 1st StartUp SDO | |||||
5 |
len1: Length of the object of the 1st StartUp SDO as CompleteAccess (from SubIndex 0) in bytes | |||||
6-n1 |
Data of the object of the 1st StartUp SDO as CompleteAccess (n1 = 2*((len1+1)/2)+5) | |||||
n1+1 |
Index of the object of the 2nd StartUp SDO | |||||
n1+2 |
len2: Length of the object of the 2nd StartUp SDO as CompleteAccess (from SubIndex 0) in bytes | |||||
(n1+3)-n2 |
Data of the object of the 2nd StartUp SDO as CompleteAccess (n2 = 2*((len2+1)/2)+n1+2) | |||||
m |
Index of the object of the 3rd StartUp SDO | |||||
m+1 |
len3: Length of the object of the 3rd StartUp SDO as CompleteAccess (from SubIndex 0) in bytes | |||||
(m+2)-n3 |
Data of the object of the 3rd StartUp SDO as CompleteAccess (n3 = 2*((len3+1)/2)+m+1) | |||||
Index 1600-167E RxPDO-Map Node yyy
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1600+n:0 |
RxPDO-Map Node yyy |
For each configured CANopen slave there is one RxPDO, which contains all CAN RxPDOs of the CANopen slave. The CAN RxPDOs written in object 0x8008+ (n*16) are located in the RxPDO mapping object 0x1600+n. If a CANopen slave contains no CAN RxPDOs, then neither object 0x8008+16*n nor the PDO mapping object 0x1600+n exist. These PDOs are mandatory and must always be contained in the PDO Assign object 0x1C12, depending on the configured CANopen slaves. SubIndex 0 contains the number of CAN RxPDOs of the (n+1)th configured CANopen slave. The RxPDO mapping objects 0x1600-0x167E can be written in order to change the order of the CAN RxPDOs of a configured CANopen slave within its EtherCAT RxPDO. If a RxPDO mapping object of the EtherCAT RxPDOs 1-127 is written, then all PDO mapping objects of the EtherCAT RxPDOs 1-127 and the EtherCAT TxPDOs 1-127 must always be written. |
UINT8 |
RW |
(1600+n):01 |
first mapped CAN RxPDO of the (n+1)th configured CANopen slave |
UINT32 |
RW |
(1600+n):m |
last mapped CAN RxPDO of the (n+1)th configured CANopen slave |
UINT32 |
RW |
Index 1685 RxPDO-Map Control
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1685:0 |
RxPDO-Map Control |
The control word (index 0xF200) can be mapped into the EtherCAT output data with this PDO. This PDO is optional. |
UINT8 |
RO |
0x02 (2dec) |
1685:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0xF200 (Control), entry 0x01 (CAN Controller Auto Reset when BUS-OFF)) |
UINT32 |
RO |
0xF200:01, 1 |
1685:02 |
SubIndex 002 |
2. PDO Mapping entry (15 bits align) |
UINT32 |
RO |
0x0000:00, 15 |
Index 1881 TxPDO-Par PDO State
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1881:0 |
TxPDO-Par PDO State |
PDO Parameter TxPDO 130 |
UINT8 |
RO |
0x06 (6dec) |
1881:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 130 |
OCTET-STRING[14] |
RO |
80 1A 00 00 00 00 00 00 00 00 00 00 00 00 |
Index 1882 TxPDO-Par CANopen Diag Flag
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1882:0 |
TxPDO-Par CANopen Diag Flag |
PDO parameter TxPDO 131 |
UINT8 |
RO |
0x06 (6dec) |
1882:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 131 |
OCTET-STRING[14] |
RO |
Index 1883 TxPDO-Par Node State
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1883:0 |
TxPDO-Par Node State |
PDO parameter TxPDO 132 |
UINT8 |
RO |
0x06 (6dec) |
1883:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 132 |
OCTET-STRING[14] |
RO |
Index 1884 TxPDO-Par Extended Diag
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1884:0 |
TxPDO-Par Extended Diag |
PDO parameter TxPDO 133 |
UINT8 |
RO |
0x06 (6dec) |
1884:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 133 |
OCTET-STRING[14] |
RO |
80 1A 85 1A 00 00 00 00 00 00 00 00 00 00 |
Index 1885 TxPDO-Par CAN Status
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1885:0 |
TxPDO-Par CAN status |
PDO parameter TxPDO 134 |
UINT8 |
RO |
0x06 (6dec) |
1885:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 134 |
OCTET-STRING[14] |
RO |
80 1A 84 1A 00 00 00 00 00 00 00 00 00 00 |
Index 1888 TxPDO-Par CAN TxPDO Toggle 1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1888:0 |
TxPDO-Par CAN TxPDO Toggle 1 |
PDO parameter TxPDO 137 |
UINT8 |
RO |
0x06 (6dec) |
1888:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 137 |
OCTET-STRING[14] |
RO |
Index 1889 TxPDO-Par CAN TxPDO Toggle 2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1889:0 |
TxPDO-Par CAN TxPDO Toggle 2 |
PDO parameter TxPDO 138 |
UINT8 |
RO |
0x06 (6dec) |
1889:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 138 |
OCTET-STRING[14] |
RO |
Index 1A00-1A7E TxPDO-Map Node yyy
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A00+n:0 |
TxPDO-Map Node yyy |
For each configured CANopen slave there is one TxPDO, which contains all CAN TxPDOs of the CANopen slave. The CAN TxPDOs written in object 0x8006+ (n*16) are located in the TxPDO mapping object 0x1A00+n. If a CANopen slave contains no CAN TxPDOs, then neither object 0x8006+16*n nor the PDO mapping object 0x1A00+n exist. These PDOs are mandatory and must always be contained in the PDO Assign object 0x1C13, depending on the configured CANopen slaves. SubIndex 0 contains the number of CAN RxPDOs of the (n+1)th configured CANopen slave. The TxPDO mapping objects 0x1A00-0x1A7E can be written in order to change the order of the CAN TxPDOs of a configured CANopen slave within its EtherCAT TxPDO. If a TxPDO mapping object of the EtherCAT TxPDOs 1-127 is written, then all PDO mapping objects of the EtherCAT TxPDOs 1-127 and the EtherCAT RxPDOs 1-127 must always be written. |
UINT8 |
RW |
(1A00+n):01 |
first mapped CAN TxPDO of the (n+1)th configured CANopen slave |
UINT32 |
RW |
(1A00+n):m |
last mapped CAN TxPDO of the (n+1)th configured CANopen slave |
UINT32 |
RW |
Index 1A81 TxPDO-Map PDO State
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A81:0 |
TxPDO-Map PDO State |
In this PDO there is a bit for each configured CANopen slave that is set if the CAN communication to the CANopen slave is not OK (a more detailed error cause can be found in 0xF102:m for the mth configured CANopen slave). If the bit is set, the data of the associated TxPDO m is to be ignored. This PDO is optional. |
UINT8 |
RO |
Number of configured CANopen slaves |
1A81:01 |
PDO state of the first configured CANopen slave (configured via the objects 0x800z) |
UINT32 |
RO |
0x1800:07, 1 |
1A81:m |
PDO state of the last (mth) configured CANopen slave (configured via the objects 0x800z+(m-1)*16 (1 <= m <= 127)) |
UINT32 |
RO |
0x1800+(m-1):07, 1 |
Index 1A82 TxPDO-Map CANopen Diag Flag
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A82:0 |
TxPDO-Map CANopen Diag Flag |
In this PDO there is a bit for each configured CANopen slave that is set if the diagnostic information (object 0xF103) has changed. This PDO is optional. |
UINT8 |
RO |
1A82:01 |
Diag Flag of the first configured CANopen slave (configured via the objects 0x800z) |
UINT32 |
RO |
0xF103:01,1 |
1A82:m |
Diag Flag of the last (mth) configured CANopen slave (configured via the objects 0x800z+(m-1)*16 (1 <= m <= 127)) |
UINT32 |
RO |
0xF103:m,1 |
Index 1A83 TxPDO-Map Node State
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A83:0 |
TxPDO-Map Node State |
In this PDO there is a byte for each configured CANopen slave that contains the communication state (object 0xF102) to the CANopen slave. This PDO is optional. |
UINT8 |
RO |
0x00 (0dec) |
1A83:01 |
Node state of the first configured CANopen slave (configured via the objects 0x800z) |
UINT32 |
RO |
0xF102:01,8 |
1A83:m |
Node state of the last (mth) configured CANopen slave (configured via the objects 0x800z+(m-1)*16 (1 <= m <= 127)) |
UINT32 |
RO |
0xF102:m,8 |
Index 1A84 TxPDO-Map Extended Diag
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A84:0 |
TxPDO-Map Extended Diag |
This PDO contains the CAN status (object 0xF108) and the CANopen master diagnostics (object 0xF101) and is optional |
UINT8 |
RO |
0x16 (22dec) |
1A84:01 |
SubIndex 001 |
1. PDO Mapping entry (11 bits align) |
UINT32 |
RO |
0x0000:00, B |
1A84:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0xF101 (Extended Diag), entry 0x0C (SYNC Toggle)) |
UINT32 |
RO |
0xF101:0C, 1 |
1A84:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0xF101 (Extended Diag), entry 0x0D (Device Diag)) |
UINT32 |
RO |
0xF101:0D, 1 |
1A84:04 |
SubIndex 004 |
4. PDO Mapping entry (1 bits align) |
UINT32 |
RO |
0x0000:00, 1 |
1A84:05 |
SubIndex 005 |
5. PDO Mapping entry (object 0xF101 (Extended Diag), entry 0x0F (PDO Toggle)) |
UINT32 |
RO |
0xF101:0F, 1 |
1A84:06 |
SubIndex 006 |
6. PDO Mapping entry (object 0xF101 (Extended Diag), entry 0x10 (PDO State)) |
UINT32 |
RO |
0xF101:10, 1 |
1A84:07 |
SubIndex 007 |
7. PDO Mapping entry (object 0xF101 (Extended Diag), entry 0x11 (Cycle Counter)) |
UINT32 |
RO |
0xF101:11, 16 |
1A84:08 |
SubIndex 008 |
8. PDO Mapping entry (object 0xF101 (Extended Diag), entry 0x12 (Slave Status Counter)) |
UINT32 |
RO |
0xF101:12, 8 |
1A84:09 |
SubIndex 009 |
9. PDO Mapping entry (8 bits align) |
UINT32 |
RO |
0x0000:00, 8 |
1A84:0A |
SubIndex 010 |
10. PDO Mapping entry (object 0xF101 (Extended Diag), entry 0x14 (Cycle Time)) |
UINT32 |
RO |
0xF101:14, 16 |
1A84:0B |
SubIndex 011 |
11. PDO Mapping entry (16 bits align) |
UINT32 |
RO |
0x0000:00, 16 |
1A84:0C |
SubIndex 012 |
12. PDO Mapping entry (object 0xF108 (CAN Status), entry 0x21 (RX error counter)) |
UINT32 |
RO |
0xF108:21, 8 |
1A84:0D |
SubIndex 013 |
13. PDO Mapping entry (object 0xF108 (CAN Status), entry 0x22 (TX error counter)) |
UINT32 |
RO |
0xF108:22, 8 |
1A84:0E |
SubIndex 014 |
14. PDO Mapping entry (object 0xF108 (CAN Status), entry 0x01 (Bus-Off)) |
UINT32 |
RO |
0xF108:01, 1 |
1A84:0F |
SubIndex 015 |
15. PDO Mapping entry (object 0xF108 (CAN Status), entry 0x02 (warning limit reached)) |
UINT32 |
RO |
0xF108:02, 1 |
1A84:10 |
SubIndex 016 |
16. PDO Mapping entry (object 0xF108 (CAN Status), entry 0x03 (RX overflow)) |
UINT32 |
RO |
0xF108:03, 1 |
1A84:11 |
SubIndex 017 |
17. PDO Mapping entry (1 bits align) |
UINT32 |
RO |
0x0000:00, 1 |
1A84:12 |
SubIndex 018 |
18. PDO Mapping entry (object 0xF108 (CAN Status), entry 0x05 (TX overflow)) |
UINT32 |
RO |
0xF108:05, 1 |
1A84:13 |
SubIndex 019 |
19. PDO Mapping entry (object 0xF108 (CAN Status), entry 0x06 (Ack error)) |
UINT32 |
RO |
0xF108:06, 1 |
1A84:14 |
SubIndex 020 |
20. PDO Mapping entry (2 bits align) |
UINT32 |
RO |
0x0000:00, 2 |
1A84:15 |
SubIndex 021 |
21. PDO Mapping entry (8 bits align) |
UINT32 |
RO |
0x0000:00, 8 |
1A84:16 |
SubIndex 022 |
22. PDO Mapping entry (16 bits align) |
UINT32 |
RO |
0x0000:00, 16 |
Index 1A85 TxPDO-Map CAN Status
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A85:0 |
TxPDO-Map CAN status |
This PDO contains the CAN status (object 0xF108) and is optional |
UINT8 |
RO |
0x0B (11dec) |
1A85:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0xF108 (CAN Status), entry 0x01 (Bus-Off)) |
UINT32 |
RO |
0xF108:01, 1 |
1A85:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0xF108 (CAN Status), entry 0x02 (warning limit reached)) |
UINT32 |
RO |
0xF108:02, 1 |
1A85:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0xF108 (CAN Status), entry 0x03 (RX overflow)) |
UINT32 |
RO |
0xF108:03, 1 |
1A85:04 |
SubIndex 004 |
UINT32 |
RO |
0x0000:00, 1 |
1A85:05 |
SubIndex 005 |
5. PDO Mapping entry (object 0xF108 (CAN Status), entry 0x05 (TX overflow)) |
UINT32 |
RO |
0xF108:05, 1 |
1A85:06 |
SubIndex 006 |
6. PDO Mapping entry (object 0xF108 (CAN Status), entry 0x06 (Ack error)) |
UINT32 |
RO |
0xF108:06, 1 |
1A85:07 |
SubIndex 007 |
7. PDO Mapping entry (2 bits align) |
UINT32 |
RO |
0x0000:00, 2 |
1A85:08 |
SubIndex 008 |
8. PDO Mapping entry (8 bits align) |
UINT32 |
RO |
0x0000:00, 8 |
1A85:09 |
SubIndex 009 |
9. PDO Mapping entry (16 bits align) |
UINT32 |
RO |
0x0000:00, 16 |
1A85:0A |
SubIndex 010 |
10. PDO Mapping entry (object 0xF108 (CAN Status), entry 0x21 (RX error counter)) |
UINT32 |
RO |
0xF108:21, 8 |
1A85:0B |
SubIndex 011 |
11. PDO Mapping entry (object 0xF108 (CAN Status), entry 0x22 (TX error counter)) |
UINT32 |
RO |
0xF108:22, 8 |
Index 1A88 TxPDO-Map CAN TxPDO Toggle 1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A88:0 |
TxPDO-Map CAN TxPDO Toggle 1 |
This PDO can contain a toggle bit for each CAN TxPDO. Whether the toggle bit of a CAN TxPDO is mapped into this PDO depends on the setting in the respective TxPDO configuration object 0x8nn6. This PDO is optional |
UINT8 |
RO |
1A88:01 |
first CAN TxPDO toggle bit |
UINT32 |
RO |
1A88:n |
nth CAN TxPDO toggle bit (if no more than 255 CAN TxPDO toggle bits are mapped, this is also the last CAN TxPDO toggle bit) |
UINT32 |
RO |
Index 1A89 TxPDO-Map CAN TxPDO Toggle 2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A89:0 |
TxPDO-Map CAN TxPDO Toggle 2 |
If more than 255 CAN TxPDO toggle bits are mapped, the additional CAN TxPDO toggle bits are contained here |
UINT8 |
RO |
0x00 (0dec) |
1A89:01 |
(n+1)th CAN TxPDO toggle bit |
1A89:m |
mth CAN TxPDO toggle bit |
Index 1A8A CAN TxPDO State
1A8A:0 | CAN TxPDO State-Map | For each configured CAN TxPDO there is a bit that is set if the CAN communication is not ok. If this bit is set, the data of the corresponding TxPDO m has to be ignored. | UINT8 | RO | Number of configured TxPDOs |
1A8A:01 |
| PDO State of the first configured TxPDO. | UINT32 | RO | 0x6008:01, 1 |
1A8A:m |
| PDO State of the last (m.) configured TxPDO TxPDO. | UINT32 | RO | 0x67E8:02, 1 |
Index 1C00 Sync manager type
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C00:0 |
Sync manager type |
Using the sync managers |
UINT8 |
RO |
0x04 (4dec) |
1C00:01 |
SubIndex 001 |
Sync-Manager Type Channel 1: Mailbox Write |
UINT8 |
RO |
0x01 (1dec) |
1C00:02 |
SubIndex 002 |
Sync-Manager Type Channel 2: Mailbox Read |
UINT8 |
RO |
0x02 (2dec) |
1C00:03 |
SubIndex 003 |
Sync-Manager Type Channel 3: Process Data Write (Outputs) |
UINT8 |
RO |
0x03 (3dec) |
1C00:04 |
SubIndex 004 |
Sync-Manager Type Channel 4: Process Data Read (Inputs) |
UINT8 |
RO |
0x04 (4dec) |
Index 1C12 RxPDO assign
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C12:0 |
RxPDO assign |
PDO Assign Outputs: the RxPDOs must be assigned in the order of their indexes. The RxPDOs of the configured CANopen slaves (0x1600-0x167E) must be assigned if object 0x1C12 is transmitted in the StartUp SDOs. It can then still be decided via RxPDO Assign whether or not the RxPDO Control (index 0x1685) is transmitted in the EtherCAT output data. |
UINT8 |
RW |
1C12:01 |
1. allocated RxPDO (contains the index of the associated RxPDO mapping object) |
UINT16 |
RW |
1C12:80 |
128. allocated RxPDO (contains the index of the associated RxPDO mapping object) |
UINT16 |
RW |
Index 1C13 TxPDO assign
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C13:0 |
TxPDO assign |
PDO Assign Inputs: the TxPDOs must be assigned in the order of their indexes. The TxPDOs of the configured CANopen slaves (0x1A00-0x1A7E) must be assigned if object 0x1C13 is transmitted in the StartUp SDOs. It can then still be decided via TxPDO Assign whether or not the TxPDOs PDO State (index 0x1A81), DiagFlag (index 0x1A82), NodeState (index 0x1A83), ExtendedDiag (index 0x1A84), CAN Status (index 0x1A85) and CAN TxPDO Toggle (index 0x1A88) are transmitted in the EtherCAT input data. In addition to the TxPDOs of the configured CANopen slaves, the TxPDOs 0x1A83 and 0x1A85 are transmitted in the default settings. |
UINT8 |
RW |
1C13:01 |
1. allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
1C13:83 |
135. allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C32:0 |
SM output parameter |
Synchronisation parameters for the outputs |
UINT8 |
RO |
0x20 (32dec) |
1C32:01 |
Sync mode |
Current synchronisation mode:
UINT16 |
RW |
0x0001 (1dec) |
1C32:02 |
Cycle time |
Cycle time (in ns):
UINT32 |
RW |
0x00000000 (0dec) |
1C32:03 |
Shift time |
not used |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:04 |
Sync modes supported |
Supported synchronization modes:
UINT16 |
RO |
0x4006 (16390dec) |
1C32:05 |
Minimum cycle time |
Minimum cycle time (in ns) |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:06 |
Calc and copy time |
Minimum time between SYNC0 and SYNC1 event (in ns, DC mode only) |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:08 |
Command |
The entries 0x1C32:03, 0x1C32:05, 0x1C32:06, 0x1C32:09, 0x1C33:03, 0x1C33:06, 0x1C33:09 are updated with the maximum measured values. |
UINT16 |
RW |
0x0000 (0dec) |
1C32:09 |
Delay time |
Time between SYNC1 event and output of the outputs (in ns, DC mode only) |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:0B |
SM event missed counter |
Number of missed SM events in OPERATIONAL (DC mode only) |
UINT16 |
RO |
0x0000 (0dec) |
1C32:0C |
Cycle exceeded counter |
Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) |
UINT16 |
RO |
0x0000 (0dec) |
1C32:0D |
Shift too short counter |
Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) |
UINT16 |
RO |
0x0000 (0dec) |
1C32:20 |
Sync error |
The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) |
BOOLEAN |
RO |
0x00 (0dec) |
Index 1C33 SM input parameter
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C33:0 |
SM input parameter |
Synchronisation parameters for the inputs |
UINT8 |
RO |
0x20 (32dec) |
1C33:01 |
Sync mode |
UINT16 |
RW |
0x0022 (34dec) |
1C33:02 |
Cycle time |
as 0x1C32:02 |
UINT32 |
RW |
0x00000000 (0dec) |
1C33:03 |
Shift time |
Time between SYNC0 event and reading of the inputs (in ns, only DC mode) |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:04 |
Supported synchronization modes: |
UINT16 |
RO |
0x4006 (16390dec) |
1C33:05 |
as 0x1C32:05 |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:06 |
Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode) |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:08 |
Command |
as 0x1C32:08 |
UINT16 |
RW |
0x0000 (0dec) |
1C33:09 |
Delay time |
not supported |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:0B |
as 0x1C32:11 |
UINT16 |
RO |
0x0000 (0dec) |
1C33:0C |
as 0x1C32:12 |
UINT16 |
RO |
0x0000 (0dec) |
1C33:0D |
as 0x1C32:13 |
UINT16 |
RO |
0x0000 (0dec) |
1C33:20 |
Sync error |
as 0x1C32:32 |
BOOLEAN |
RO |
0x00 (0dec) |