BECKHOFF CANopen Bus Coupler
The BK51xx Bus Coupler and the IPxxx-B510 Fieldbus Box are installed in the CANopen bus. The specific properties which distinguish them from other Bus Couplers and/or fieldbus box modules are then described below.
Types
BK5110
Economy Bus Coupler
BK5120
Economy + Bus Coupler
LC5100
Low-Cost Bus Coupler
BK5150
Compact Bus Coupler
BK5151
Compact Bus Coupler with D-Sub connection
BC5150
Compact Bus Terminal Controller with 48 kbyte program memory
BX5100
BX Bus Terminal Controller with 256 kbyte program memory
IPxxxx-B510
Fieldbus compact box: CANopen in/output module, protection class IP67
"BK51x0" tab
BECKHOFF CANopen Bus Coupler 1:Fig.99: "BK51x0" tab
Node Id
Sets the node ID of the CAN bus device (between 1 and 63 (BK51x0) and/or 1 and 99 (IPxxxx-B510)). This value must comply with the value set at the Bus Coupler and/or at the compact box.
Guard time
Cycle time for the node monitoring (node guarding).
Lifetime factor
Guard time multiplied produces the watchdog time for the monitoring of the master by the coupler (life guarding). Life guarding is deactivated if the lifetime factor is set to zero.
Inhibit Time
Displays the minimum send interval for PDOs (telegrams) with analog and special signals. If more than digital 64 signals are present, these are also provided with this Inhibit Time.
Event Time
Event timer for transmit PDOs. Expiry of this timer is treated as an additional event for the corresponding PDO, so that the PDO will then be transmitted. If the application event occurs during a timer period, it will also be transmitted, and the timer is reset.
K-Bus update
Calculates the anticipated duration of a complete update of the terminal bus (according to type and number of connected terminals).
Use Heartbeat
Heartbeat is used for monitoring of the node. If deactivated, the guarding is used for monitoring.
Trans. type
Gives the Transmission Type for digital / analog input telegrams. 254 + 255 corresponds to the event-driven transfer, 1 ... 240 are synchronous transfer types. For further details see also BK51X0 manual.
Firmware Update
Enables the updating of the coupler firmware via the serial interface (requires KS2000 software package interface cable).
"SDOs" tab
BECKHOFF CANopen Bus Coupler 2:Fig.100: "SDOs" tab
SDO inputs sent to the node at StartUp are displayed/managed on this page. Inputs with an object index in straight brackets are automatically created on the basis of the updated terminal configuration. Other inputs can be managed using ”Add", ”Insert", ”Delete" and ”Edit".
"RxPDOs" tab
Displays the RxPDOs used for the node.
"TxPDOs" tab
Displays the TxPDOs used for the node.
“ADS” tab
The node (Bus Coupler) is assigned an ADS port to enable writing and reading of SDO objects at runtime (e.g. from the PLC). It can be changed if required. The ADS IndexGroup contains the CANopen object index and the ADS IndexOffset contains the CANopen Sub-Index. See chapter SDO communication for details of SDO communication via ADS.
“Diag” tab
Diagnostic information is displayed here. The window contents are not cyclically refreshed; select the "Refresh" button if necessary. The diagnostic information displayed can also be queried by ADS.