Terminal-specific CoE objects
The terminal-specific CoE objects of the EL6695 bridge terminal start from index (hex) 0x10F4. The objects 0x10F4 and 0x10F5 contain the status and the settings for the external synchronization.
Index (hex) | Name | Meaning | Data type | Flags | Default value |
10F4:0 | External synchronization status | Information about the synchronization status | UINT8 | RO | 0x13 |
10F4:01 | Sync Mode | Synchronization mode 3 = both sides are SyncMaster - this state is not allowed and should be changed by appropriate EtherCAT Master settings by activating PDO Timestamp Mapping on one side only. | BIT2 | RO P | 0x00 |
10F4:0E | Control value update toggle | Bit toggles when a new control value is available | BOOLEAN | RO P | 0x00 |
10F4:0F | Time stamp update toggle | Bit toggles when new DC data were supplied | BOOLEAN | RO P | 0x00 |
10F4:10 | External device not connected | 0 = other side is connected to its EtherCAT fieldbus 1 = other side is not connected to its EtherCAT fieldbus | BOOLEAN | RO P | 0x00 |
10F4:11 | Internal time stamp | Distributed clocks time on the current side | UINT64 | RO P | - |
10F4:12 | External time stamp | Distributed clocks time on the other side (remote side) | UINT64 | RO P | - |
10F4:13 | Control Value for DC Master Clock | Offset for correction of the lower priority reference clock | INT32 | RO P | 0x00000000 (0dec) |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value | ||
10F5:0 |
External synchronization settings |
Setting for synchronizing the EtherCAT bridge |
UINT8 |
RO |
0x12 (18dec) | ||
10F5:01 |
Sync master |
0: Sync Master is on the primary side |
BOOLEAN |
RW |
0x00 (0dec) | ||
10F5:02 |
32 Bit time stamps |
0: 64-bit Timestamps |
BOOLEAN |
RW |
0x00 (0dec) | ||
10F5:11 |
Control Interval (ms) |
Interval in ms for calculating the control value |
UINT16 |
RW |
0x0000 (0dec) | ||
10F5:12 |
Additional System Time |
Additional DC time for calculating the control value |
UINT64 |
RW |
0x0000000000000000 | ||
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1608:0 |
RxPDO-Map - |
PDO mapping RxPDO 1 (PDO mapping of the declared output process data) - |
UINT8 - |
RW - |
0x00 (0dec) - |
..1608:FF | |||||
…161F:00… | |||||
161F:FF |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1801:0 |
TxPDO-Par External Sync Compact |
PDO parameter TxPDO 2 |
UINT8 |
RO |
0x09 (9dec) |
1801:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index (hex) of TxPDO mapping objects) that must not be transferred together with TxPDO 2 |
OCTET-STRING[4] |
RO |
02 1A 03 1A |
1801:07 |
TxPDO State |
The TxPDO state is set if it was not possible to correctly read in the associated input data |
BOOLEAN |
RO P |
0x00 (0dec) |
1801:09 |
TxPDO Toggle |
The TxPDO toggle is toggled with each update the corresponding input data |
BOOLEAN |
RO P |
0x00 (0dec) |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1802:0 |
TxPDO-Par External Sync |
PDO parameter TxPDO 3 |
UINT8 |
RO |
0x09 (9dec) |
1802:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index (hex) of TxPDO mapping objects) that must not be transferred together with TxPDO 3 |
OCTET-STRING[4] |
RO |
01 1A 03 1A |
1802:07 |
TxPDO State |
BOOLEAN |
RO P |
0x00 (0dec) |
1802:09 |
TxPDO Toggle |
BOOLEAN |
RO P |
0x00 (0dec) |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1803:0 |
TxPDO-Par External Sync (32 Bit) |
PDO parameter TxPDO 4 |
UINT8 |
RO |
0x09 (9dec) |
1803:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index (hex) of TxPDO mapping objects) that must not be transferred together with TxPDO 4 |
OCTET-STRING[4] |
RO |
01 1A 02 1A |
1803:07 |
TxPDO State |
BOOLEAN |
RO P |
0x00 (0dec) |
1803:09 |
TxPDO Toggle |
BOOLEAN |
RO P |
0x00 (0dec) |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1A01:0 |
TxPDO-Map External Sync Compact |
PDO Mapping TxPDO 1 |
UINT8 |
RW |
0x05 (5dec) |
1A01:01 |
SubIndex (hex) 001 |
12 bit align |
UINT32 |
RW |
0x0000:00, 12 |
1A01:02 |
SubIndex (hex) 002 |
PDO Mapping entry (object 0x1801, entry 0x09) |
UINT32 |
RW |
0x1801:09, 1 |
1A01:03 |
SubIndex (hex) 003 |
PDO Mapping entry (object 0x1801, entry 0x07) |
UINT32 |
RW |
0x1801:07, 1 |
1A01:04 |
SubIndex (hex) 004 |
1 bit align |
UINT32 |
RW |
0x0000:00, 1 |
1A01:05 |
SubIndex (hex) 005 |
PDO Mapping entry (object 0x10F4 (External synchronization status), entry 0x10) |
UINT32 |
RW |
0x10F4:10, 1 |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1A02:0 |
TxPDO-Map External Sync |
PDO Mapping TxPDO 2 |
UINT8 |
RW |
0x09 (9dec) |
1A02:01 |
PDO Mapping entry (object 0x10F4 (External synchronization status), entry 0x02) |
UINT32 |
RW |
0x10F4:01, 2 |
1A02:02 |
10 bit align |
UINT32 |
RW |
0x0000:00, 10 |
1A02:03 |
PDO Mapping entry (object 0x1802, entry 0x09) |
UINT32 |
RW |
0x1802:09, 1 |
1A02:04 |
PDO Mapping entry (object 0x1802, entry 0x07) |
UINT32 |
RW |
0x1802:07, 1 |
1A02:05 |
PDO Mapping entry (object 0x10F4 (External synchronization status), entry 0x0F (Time stamp update toggle)) |
UINT32 |
RW |
0x10F4:0F, 1 |
1A02:06 |
SubIndex (hex) 006 |
PDO Mapping entry (object 0x10F4 (External synchronization status), entry 0x10 (External device not connected)) |
UINT32 |
RW |
0x10F4:10, 1 |
1A02:07 |
SubIndex (hex) 007 |
PDO Mapping entry (object 0x10F4 (External synchronization status), entry 0x11 (Internal time stamp)) |
UINT32 |
RW |
0x10F4:11, 64 |
1A02:08 |
SubIndex (hex) 008 |
PDO Mapping entry (object 0x10F4 (External synchronization status), entry 0x12 (External time stamp)) |
UINT32 |
RW |
0x10F4:12, 64 |
1A02:09 |
SubIndex (hex) 009 |
PDO Mapping entry (object 0x10F4 (External synchronization status), entry 0x13 (Reserved)) |
UINT32 |
RW |
0x10F4:13, 32 |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1A03:0 |
PDO Mapping TxPDO 3 |
UINT8 |
RW |
0x09 (9dec) |
1A03:01 |
UINT32 |
RW |
0x10F4:01, 2 |
1A03:02 |
10 bit align |
UINT32 |
RW |
0x0000:00, 10 |
1A03:03 |
PDO Mapping entry (object 0x1803, entry 0x09) |
UINT32 |
RW |
0x1803:09, 1 |
1A03:04 |
PDO Mapping entry (object 0x1803, entry 0x07) |
UINT32 |
RW |
0x1803:07, 1 |
1A03:05 |
UINT32 |
RW |
0x10F4:0F, 1 |
1A03:06 |
UINT32 |
RW |
0x10F4:10, 1 |
1A03:07 |
UINT32 |
RW |
0x10F4:11, 32 |
1A03:08 |
UINT32 |
RW |
0x10F4:12, 32 |
1A03:09 |
UINT32 |
RW |
0x10F4:13, 32 |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1A04:0 |
Active TxPDOs-Map |
PDO Mapping TxPDO 4 |
UINT32 |
RW |
0x05 (5dec) |
1A04:01 |
SubIndex (hex) 01 |
PDO Mapping entry (object 0xF640:01(Remote Write Cycles u16Count)) |
UINT32 |
RW |
10 01 40 F6 |
1A04:02 |
SubIndex (hex) 02 |
PDO Mapping entry (object 0xF630:01 Active TxPdo Info PDO 1-8) |
UINT32 |
RW |
10 01 30 F6 |
1A04:03 |
SubIndex (hex) 03 |
PDO Mapping entry (object 0xF630:02 Active TxPdo Info PDO 9-16) |
UINT32 |
RW |
10 02 30 F6 |
1A04:04 |
SubIndex (hex) 04 |
PDO Mapping entry (object 0xF630:03 Active TxPdo Info PDO 17-24) |
UINT32 |
RW |
10 03 30 F6 |
1A04:05 |
SubIndex (hex) 05 |
PDO Mapping entry (object 0xF630:04 Active TxPdo Info PDO 25-32) |
UINT32 |
RW |
10 04 30 F6 |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1A05:0 |
FoE Info-Map |
PDO Mapping TxPDO 5 |
UINT8 |
RW |
0x01 (1dec) |
1A05:01 |
PDO Mapping entry (object 0xF650:01 Active TxPdo Info PDO 25-32) |
UINT32 |
RW |
10 01 50 F6 |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1A08:0 |
TxPDO-Map - |
PDO mapping TxPDO 1 (PDO mapping of the declared input process data) - |
UINT8 - |
RW - |
0x00 (0dec) - |
..1A08:FF | |||||
…1A1F:00… | |||||
1A1F:FF |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1C00:0 |
Syncmanager type |
Sync-Manager Type Channels (Mailbox/ Process Data, Read/ Write) |
UINT8 |
RO |
0x04 (4dec) |
1C00:01 |
Sync-Manager Type Channel 1: Mailbox Write |
UINT8 |
RO |
0x01 (1dec) |
1C00:02 |
Sync-Manager Type Channel 2: Mailbox Read |
UINT8 |
RO |
0x02 (2dec) |
1C00:03 |
Sync-Manager Type Channel 3: Process Data Write (Outputs) |
UINT8 |
RO |
0x03 (3dec) |
1C00:04 |
Sync-Manager Type Channel 4: Process Data Read (Inputs) |
UINT8 |
RO |
0x04 (4dec) |
1C12:0 | RxPDO assign | PDO Assign Outputs | UINT8 | RW | 0x00 (0dec) |
1C12:01 | SubIndex (hex) 001 | 1st allocated RxPDO (contains the index (hex) of the associated RxPDO mapping object) | UINT16 | RW | 0x0000 (0dec) |
1C13:0 | TxPDO assign | PDO Assign Inputs | UINT8 | RW | 0x01 (1dec) |
1C13:01 | SubIndex (hex) 001 | 1st allocated TxPDO (contains the index (hex) of the associated TxPDO mapping object) | UINT16 | RW | 0x1A01 (6657dec) |
1C13:02 | SubIndex (hex) 002 | 2nd allocated TxPDO (contains the index (hex) of the associated TxPDO mapping object) | UINT16 | RW | 0x0000 (0dec) |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1C32:0 |
SM output parameter |
Synchronization parameters for the outputs |
UINT8 |
RO |
0x20 (32dec) |
1C32:01 |
Sync mode |
Current synchronization mode: 0: Free Run 1: Synchronous with SM 2 event 2: DC-Mode - Synchronous with SYNC0 Event 3: DC-Mode - Synchronous with SYNC1 event |
UINT16 |
RW |
0x0000 (0dec) |
1C32:02 |
Cycle time |
Cycle time (in ns): Free Run: Cycle time of the local timer Synchronous with SM 2 event: Master cycle time DC-Mode: SYNC0/SYNC1 Cycle Time |
UINT32 |
RW |
0x00000000 (0dec) |
1C32:03 |
Shift time |
Time between SYNC0 event and output of the outputs (in ns, DC mode only) |
UINT32 |
RW |
0x00000000 (0dec) |
1C32:04 |
Sync modes supported |
Supported synchronization modes: Bit 0 = 1: free run is supported Bit 1 = 1: Synchronous with SM 2 event is supported Bit 2-3 = 01: DC mode is supported Bit 4-5 = 10: Output shift with SYNC1 event (only DC mode) Bit 14 = 1: dynamic times (measurement through writing of 1C32:08) |
UINT16 |
RO |
0xC007 (49159dec) |
1C32:05 |
Minimum cycle time |
Minimum cycle time (in ns) |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:06 |
Calc and copy time |
Minimum time between SYNC0 and SYNC1 event (in ns, DC mode only) |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:08 |
Command |
0: Measurement of the local cycle time is stopped 1: Measurement of the local cycle time is started The entries 1C32:03, 1C32:05, 1C32:06, 1C32:09, 1C33:03, 1C33:06, and 1C33:09 are updated with the maximum measured values. |
UINT16 |
RW |
0x0000 (0dec) |
1C32:09 |
Maximum delay time |
Time between SYNC1 event and output of the outputs (in ns, DC mode only) |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:0B |
SM event missed counter |
Number of missed SM events in OPERATIONAL (DC mode only) |
UINT16 |
RO |
0x0000 (0dec) |
1C32:0C |
Cycle exceeded counter |
Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) |
UINT16 |
RO |
0x0000 (0dec) |
1C32:0D |
Shift too short counter |
Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) |
UINT16 |
RO |
0x0000 (0dec) |
1C32:20 |
Sync error |
The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) |
BOOLEAN |
RO |
0x00 (0dec) |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1C33:0 |
SM input parameter |
Synchronization parameters for the inputs |
UINT8 |
RO |
0x20 (32dec) |
1C33:01 |
Sync mode |
Current synchronization mode: 0: Free Run 1: Synchronous with SM 3 event (no outputs available) 2: DC - Synchronous with SYNC0 Event 3: DC - Synchronous with SYNC1 Event 34: Synchronous with SM 2 event (outputs available) |
UINT16 |
RW |
0x0000 (0dec) |
1C33:02 |
Cycle time |
as 1C32:02 |
UINT32 |
RW |
0x00000000 (0dec) |
1C33:03 |
Shift time |
Time between SYNC0 event and reading of the inputs (in ns, only DC mode) |
UINT32 |
RW |
0x00000000 (0dec) |
1C33:04 |
Supported synchronization modes: Bit 0: free run is supported Bit 1: synchronous with SM 2 event is supported (outputs available) Bit 1: synchronous with SM 3 event is supported (no outputs available) Bit 2-3 = 01: DC mode is supported Bit 4-5 = 01: input shift through local event (outputs available) Bit 4-5 = 10: input shift with SYNC1 event (no outputs available) Bit 14 = 1: dynamic times (measurement through writing of 1C32:08 or 1C33:08) |
UINT16 |
RO |
0xC007 (49159dec) |
1C33:05 |
as 1C32:05 |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:06 |
Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode) |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:08 |
Command |
as 1C32:08 |
UINT16 |
RW |
0x0000 (0dec) |
1C33:09 |
Time between SYNC1 event and reading of the inputs (in ns, only DC mode) |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:0B |
as 1C32:11 |
UINT16 |
RO |
0x0000 (0dec) |
1C33:0C |
as 1C32:12 |
UINT16 |
RO |
0x0000 (0dec) |
1C33:0D |
as 1C32:13 |
UINT16 |
RO |
0x0000 (0dec) |
1C33:20 |
Sync error |
as 1C32:32 |
BOOLEAN |
RO |
0x00 (0dec) |