Configuration data
Index 80n0 ENC Settings 0 Ch.n (for n = 0 [channel 1], n = 1 [channel 2])
80n0:0 | ENC Settings 0 Ch.n | Maximum subindex | UINT8 | RO | 0x23 (35dec) |
80n0:01 | The counter is reset via the C input. | BOOLEAN | RW | 0x00 (0dec) | |
80n0:02 | Enable extern reset | A counter reset is triggered via the external latch input (24 V) | BOOLEAN | RW | 0x00 (0dec) |
80n0:04 | 0: Disable gate | BIT2 | RW | 0x01 (1dec) | |
80n0:06 | 0: 4-fold (four-fold evaluation) | BIT2 | RW | 0x00 (0dec) | |
80n0:08 | 0: Activates the input filter (inputs A, /A, B, /B, C, /C only) | BOOLEAN | RW | 0x01 (1dec) | |
80n0:0A | If activated, the terminal interpolates micro-increments between the integral encoder increments in DC mode. The lower 8 bits of the counter value are used in each case for the display. A 32-bit counter thus becomes a 24+8-bit counter, a 16-bit counter becomes an 8+8-bit counter. | BOOLEAN | RW | 0x00 (0dec) | |
80n0:0B | Error detection A | A broken wire or short circuit on track A is indicated in index 0x60n0:07 and as process data. Diagnostics is only possible, if the associated input is wired differentially. | BOOLEAN | RW | 0x01 (1dec) |
80n0:0C | Error detection B | A broken wire or short circuit on track B is indicated in index 0x60n0:07 and as process data. Diagnostics is only possible, if the associated input is wired differentially. | BOOLEAN | RW | 0x01 (1dec) |
80n0:0D | Error detection C | A broken wire or short circuit on track C is indicated in index 0x60n0:07 and as process data. Diagnostics is only possible, if the associated input is wired differentially. | BOOLEAN | RW | 0x00 (0dec) |
80n0:0E | Activates reversion of rotation | BOOLEAN | RW | 0x00 (0dec) | |
80n0:10 | Extern reset polarity | 0: Fall (the counter is set to zero with a falling edge) | BIT1 | RW | 0x01 (1dec) |
80n0:11 | Minimum time over which the frequency is determined; default value: 10 ms [resolution: 1 µs]. | UINT16 | RW | 0x2710 (10000dec) | |
80n0:13 | Scaling of the frequency measurement (must be divided by this value to obtain the unit in Hz): 100: "0.01 Hz" (default) | UINT32 | RW | 0x00000064 (100dec) | |
80n0:14 | Period scaling | Resolution of the period value in the process data: 10: "10 ns" Period value is a multiple of 10 ns | UINT32 | RW | 0x0000000A (10dec) |
80n0:17 | Waiting time [ms] for frequency measurement If no full period is detected within the frequency window, another frequency window is started to record a full period. This happens until the maximum frequency wait time has elapsed. At least double the period value of the minimum frequency to be measured should be entered here. t >= 2* (1 / fmin) | UINT16 | RW | 0x53E2 (21474dec) | |
80n0:1D | Frequency counter value, frequency scaling | UINT32 | RW | 0x00000001 (1dec) | |
80n0:1E | frequency counter value, used for scaling the frequency and the velocity calculation (increments / unit). | UINT32 | RW | 0x00000001 (1dec) | |
80n0:21 | Activation of plausibility check | BOOLEAN | RW | 0x00 (0dec) | |
80n0:22 | FALSE: TRUE: | BOOLEAN | RW | 0x00 (0dec) | |
80n0:23 | FALSE: TRUE: | BOOLEAN | RW | 0x00 (0dec) |
Index 80n1 ENC Settings 1 Ch.n (for n = 0 [channel 1], n = 1 [channel 2])
80n1:0 | ENC Settings 1 Ch.n | Maximum subindex | UINT8 | RO | 0x1D (29dec) |
80n1:17 | Setting the sensor supply 50dec: 5.0 V (default) Refer to the Note on setting the encoder supply | UINT32 | RW | 0x00000032 (50dec) | |
80n1:19 | Filter settings: 10dec: 10 kHz | UINT32 | RW | 0x00001388 (5000dec) | |
80n1:1A | Specifies the value for the upper counter limit. | UINT32 | RW | 0xFFFFFFFF (-1dez) | |
80n1:1B | Specifies the value for the lower counter limit. | UINT32 | RW | 0x00000000 (0dec) | |
80n1:1C | Enter the hysteresis in number of increments. A value greater than 0 must be selected. If the counter value exceeds the value, the bit in index 0x60n2:13 "Direction inversion detected" is set in the next PLC cycle. | UINT8 | RW | 0x0A (10dec) | |
80n1:1D | 0: Encoder RS422 (diff. input) | UINT32 | RW | 0x00000000 (0dec) |