Control and status byte
Control byte
The control byte (CB) is located in the output process image, and is transmitted from the controller to the terminal.
Bit
CB.7
CB.6
CB.5
CB.4
CB.3
CB.2
CB.1
CB.0
EN_LATCH_EXTN
CNT_SET
EN_LATCH_EXTP
EN_LATC
Legend
Bit
CB.3
EN_LATCH_EXTN
1bin
After the EN_LATCH_EXTN bit becomes active, the counter value is stored in the latch input (index 0x6000:03) upon the first external latch pulse with a falling edge. The subsequent pulses have no influence on the latch value.
Please note: A new counter value can be written to the latch input only after the “Latch°valid” bit (LAT_EXT_VAL) in the status byte has a low-level.
CB.2
CNT_SET
rise
The counter is set with rising edge of CNT_SET to the value specified via the process data (index 0x7000:02).
CB.1
EN_LATCH_EXTP
1bin
Once the EN_LATCH_EXTP bit is set, the counter value is stored in the latch input (index 0x6000:03) on the rising edge of the first external latch pulse. The subsequent pulses have no influence on the latch value.
CB.0
EN_LATC
1bin
The zero point latch (C input) is activated. The counter value is saved upon the first external latch pulse after the EN_LATC bit becomes valid (this takes precedence over EN_LAT_EXTN/EN_LAT_EXTP). If the bit is set, subsequent pulses have no influence on the latch value.
Please note: Only when the “Latch°valid” bit (LATC_VAL) in the status byte is at a low-level can a new counter value be written to the latch input (the LATC_VAL bit (SB.0) is not cleared by the terminal until the C pulse = LOW).
Status byte
The status byte (SB) is located in the input process image, and is transmitted from terminal to the controller.
Bit
SB.7
SB.6
SB.5
SB.4
SB.3
SB.2
SB.1
SB.0
STATUS_INPUT
OVERFLOW
UNDERFLOW
CNTSET_ACC
LAT_EXT_VAL
LATC_VAL
Legend
Bit
SB.5
STATUS_INPUT
0bin/ 1bin
Indicates the status of INPUT 1
SB.4
OVERFLOW
1bin
This bit is set if the 16-bit counter overflows (65535 to 0). It is reset when the counter exceeds one third of its measuring range (21845 to 21846) or immediately an underflow occurs.
SB.3
UNDERFLOW
1bin
This bit is set if the 16-bit counter underflows (0 to 65535). It is reset when the counter drops below two thirds of its measuring range (43690 to 43689) or immediately an overflow occurs.
SB.2
CNTSET_ACC
1bin
The data for setting the counter (index 0x7000:02) is accepted from the terminal.
SB.1
LAT_EXT_VAL
1bin
An external latch pulse has occurred. The data with index 0x6000:03 match the latched value when the bit is set. To reactivate the latch input EN_LAT_EXTN or EN_LATCH_EXTP (CB.3 or CB.1) has first to be cleared and then to be set once more.
SB.0
LATC_VAL
1bin
A zero point latch has occurred. The data with index 0x6000:03 match the latched value when the bit is set. In order to reactivate the latch input, it is necessary for EN_LATC (CB.0) first be cleared and then to be set once more.