Quick start
Proceed as follows for standard commissioning of the EL5032 with EnDat 2.2 encoders.
- Install the EL5032 in the E-bus terminal strand on an EtherCAT coupler, e.g. EK1100 or EK1501.
- Connect the EnDat 2.2 encoder(s) according to the connection diagram (Data(+/-), Clock(+/-) and supply voltage).
 The encoders must support EnDat 2.2 and a clock frequency >= 8 MHz.
- Set up a correct EtherCAT configuration with the terminal.
 Since the device is present and is electrically reachable, the simplest way of accomplishing this is by scanning the devices.
- Activate the EtherCAT master and start the terminal in OP state.
 In the input variables the EL5032 must deliver State=8 and WC=0.
- Parameterize the CoE settings of the EL5032 according to the EnDat2.2 encoder data sheet.
- Reverse any previous parameter changes by means of a CoE reset: enter 0x64616F6C in object 0x1011:01.
- If an encoder voltage of, for sample, 9 V is set in object 0x8008:13, ensure before connecting that this is supported by both encoders.
- The data can now be read via the process data.